"Comm failure timeout" - which value to use?

Post by DJF3 »

Hi,

After 2 days I found out that my RFXMETER wasn't working (resetting the power aparently solved the problem).

The RFXCOM DB lists the same values since it started to fail for: power, gas and water

After changing the "comm failure timeout" of the Gas device in HomeSeer (from 170 minutes to 60 minutes), the device suddenly showed "Communication Failure".

Question: Is there a reason why I shouldn't set the "comm failure timeout" from 170 min (default) to, say 60 minutes? The "Communication Failure" allows me identify the problem sooner.

Question: If it says "Communication Failure", will the plugin still write values to the DB?


Thank you!
DJ
User avatar
b_weijenberg
Forum Moderator
Forum Moderator
Posts: 1744
Joined: Sun May 14, 2006 4:32 pm
Location: Netherlands

Re: "Comm failure timeout" - which value to use?

Post by b_weijenberg »

Default can be used and should show the comm failure too.

The comm failure timeout for the RFXMeter can be set to (2 x reporting interval ) + 1 minute
The best value for the reporting interval of the RFXMeter is 1 or 6 minutes. (30 seconds is producing too much RF traffic)
DJF3
Advanced Member
Advanced Member
Posts: 895
Joined: Thu Jul 12, 2007 9:28 am
Contact:

Re: "Comm failure timeout" - which value to use?

Post by DJF3 »

Thank you Bert!