New setup - no statistics showing
Posted: Mon Dec 11, 2023 1:16 pm
Hi,
I'm hoping someone can help or point me to where I'm going wrong or need to look?
I've just installed an OTGW between my Drayton Wiser Thermostat and a Baxi Platinum 40 boiler, the goal was to set a maximum flow temperature which I couldn't when connected directly.
The OTGW is passing OT commands to the boiler as before so everything is working as normal, but I see no statistic data in Opentherm Monitor or the web interface and my log just looks like this over and over again:
I do see a correct 'flame' status when the boiler is fired up but that's it.
Update: The data does populate and is picked up when in 'Monitor' mode. But not in Gateway mode.
I have seen a previous post where someone had this problem and was resolved by an older experimental firmware, however as I'm on v6.5 I assumed I'm on the most recent update so didn't think it was trying that?
Any ideas where I'm going wrong? I'm sure it'll be me
Huge thanks in advance,
Andrew
I'm hoping someone can help or point me to where I'm going wrong or need to look?
I've just installed an OTGW between my Drayton Wiser Thermostat and a Baxi Platinum 40 boiler, the goal was to set a maximum flow temperature which I couldn't when connected directly.
The OTGW is passing OT commands to the boiler as before so everything is working as normal, but I see no statistic data in Opentherm Monitor or the web interface and my log just looks like this over and over again:
Code: Select all
\f0\fs24 \cf0 11:55:20.583443 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:20.718721 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:21.212509 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:21.756459 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:22.164367 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:22.283157 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:22.765229 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:23.330613 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:23.756636 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:23.852319 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:24.156390 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:24.337617 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:24.748482 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:24.882564 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:25.363023 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:25.911124 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:26.336727 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:26.472103 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:26.735880 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:26.936350 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:27.811638 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:27.844113 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:27.959214 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:28.502650 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:29.012817 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:29.056362 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:29.524655 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:30.072170 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:30.535219 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:30.616699 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:30.910178 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:31.102483 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:31.502981 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:31.641543 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:32.122393 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:32.677118 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:33.093858 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:33.209250 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:33.490575 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:33.716614 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:34.091817 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:34.232919 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:34.694230 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:34.777843 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:35.264938 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:35.688893 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:35.815460 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:36.347743 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:36.830335 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:37.270415 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:37.375690 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:37.674266 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:37.851514 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:38.260848 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:38.396524 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:39.022858 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:39.424205 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:39.858900 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:39.968375 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:40.259515 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:40.457075 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:40.861017 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:41.042675 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:41.448380 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:41.584166 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:42.068512 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:42.616979 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:43.032462 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:43.154895 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:43.650231 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:44.253844 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:44.802561 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:44.844235 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:45.022152 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:45.208268 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:45.620926 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:45.769684 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:46.234387 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:46.777228 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:47.217231 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:47.345830 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:47.915893 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:47.946361 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:48.489143 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:48.522822 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:48.983240 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:49.370531 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:49.791039 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:49.918616 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:50.404466 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:50.943282 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:51.385997 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:51.491148 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:51.780184 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:51.969467 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
11:55:52.377959 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000\
- Fault indication: no fault (0)\
- CH mode: not active (0)\
- DHW mode: not active (0)\
- Flame status: flame off (0)\
- Cooling status: not active (0)\
- CH2 mode: not active (0)\
- Diagnostic indication: no diagnostics (0)\
- Electricity production: not active (0)\
11:55:53.837568 T80000200 Read-Data Status (MsgID=0): 00000010 00000000\
- CH enable: disabled (0)\
- DHW enable: enabled (1)\
- Cooling enable: disabled (0)\
- OTC active: not active (0)\
- CH2 enable: disabled (0)\
- Summer/winter mode: winter (0)\
- DHW blocking: unblocked (0)\
Update: The data does populate and is picked up when in 'Monitor' mode. But not in Gateway mode.
I have seen a previous post where someone had this problem and was resolved by an older experimental firmware, however as I'm on v6.5 I assumed I'm on the most recent update so didn't think it was trying that?
Any ideas where I'm going wrong? I'm sure it'll be me
Huge thanks in advance,