fout 203

Post by jappiedepappie »

Hi,

I've got the OTGW up and running, but it seems to have a problem.
On my thermostat (celcia 20) I read "fout 203"

In the OTmonitor I get: T800500CB read data application-specific flags: 00000000 203

Could someone point my in the right direction?

Thanks,
Jasper
“Intellectual growth should commence at birth and cease only at death.”
― Albert Einstein
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: fout 203

Post by hvxl »

You're only showing one message that's actually a request for information from the thermostat to the boiler. It's a bit hard to say anything useful based on such little information. But if that's all you get, there's probably a problem communicating with the boiler. In that case I suggest you follow the troubleshooting instructions.
Schelte
jappiedepappie
Starting Member
Starting Member
Posts: 9
Joined: Mon Feb 23, 2015 3:56 pm

Re: fout 203

Post by jappiedepappie »

I understand the info is minimal, but thats what the monitor shows, only this error.
I believe there is a mistake with soldering.
I'll go through the components and troubleshooting guide tonight. Any findings i'll share asap!

Thanks for replying!
/Jasper
“Intellectual growth should commence at birth and cease only at death.”
― Albert Einstein
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: fout 203

Post by hvxl »

jappiedepappie wrote:I understand the info is minimal, but thats what the monitor shows, only this error.
It's not an error. It's a perfectly fine message from the thermostat.
Schelte
jappiedepappie
Starting Member
Starting Member
Posts: 9
Joined: Mon Feb 23, 2015 3:56 pm

Re: fout 203

Post by jappiedepappie »

Problem solved! I mixed the two diodes (15v and 4v3). Soldered them in the correct order and everything works.
I get full info from Thermostat and Boiler now and I'm able to set different parameters.

Thanks Schelte for replying!
“Intellectual growth should commence at birth and cease only at death.”
― Albert Einstein
joepurlings
Starting Member
Starting Member
Posts: 5
Joined: Wed Sep 02, 2015 9:47 am

Re: fout 203

Post by joepurlings »

Fout 203 is actually the error that the Celia shows when it gets no response from the boiler.
Seen it before, after thunder killed both my boiler's as the Celia's opentherm interface :evil:
Replacing one of both did not solve the problem, so I eventually exchanged both the boiler main board and the thermostat.
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: fout 203

Post by hvxl »

jappiedepappie wrote:Problem solved!
Great. Thanks for reporting back what the problem was.