Hello,
I understand correctly that Opentherm gateway firmware does not contain the command ID 16 - W Room Setpoint Current room temperature setpoint (° C)? If not, can this command be added?
Thank you Marek
Command ID 16
Moderator: hvxl
Re: Command ID 16
What exactly are you looking for? The Current Room Setpoint is something a thermostat may indicate. If it does, the OTGW will report it and/or store so it can be included in a summary report. So there is support for MsgID 16.
If the thermostat does not send MsgID 16, then the OTGW has no way of knowing what the Current Room Setpoint is. That's not normally a problem, because boilers generally have no need for this information.
If the thermostat does not send MsgID 16, then the OTGW has no way of knowing what the Current Room Setpoint is. That's not normally a problem, because boilers generally have no need for this information.
Schelte
Re: Command ID 16
Hello
Thank you very much for your advice. I'm so sorry I'm this beginner. This log generates a room setpoint change of 17 ° C. Can you please send me the procedure to change the room temperature using the Opentherm gateway?
Thank you Mark
Thank you very much for your advice. I'm so sorry I'm this beginner. This log generates a room setpoint change of 17 ° C. Can you please send me the procedure to change the room temperature using the Opentherm gateway?
Thank you Mark
Code: Select all
21:47:18.208537 T80000200 Read-Data Status: 00000010 00000000
- CH enable: disabled (0)
- DHW enable: enabled (1)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
21:47:18.354106 B4000020C Read-Ack Status: 00000010 00001100
- Fault indication: no fault (0)
- CH mode: not active (0)
- DHW mode: active (1)
- Flame status: flame on (1)
- Cooling status: not active (0)
- CH2 mode: not active (0)
- Diagnostic indication: no diagnostics (0)
- Electricity production: not active (0)
21:47:19.202848 T90181B27 Write-Data Room temperature: 27.15
21:47:19.264141 B50181B27 Write-Ack Room temperature: 27.15
21:47:20.198645 T800BFF00 Read-Data TSP setting: 255 0
21:47:20.264186 B400BFF00 Read-Ack TSP setting: 255 0
21:47:21.205801 T90181B27 Write-Data Room temperature: 27.15
21:47:21.280695 B50181B27 Write-Ack Room temperature: 27.15
21:47:22.208848 T800BF000 Read-Data TSP setting: 240 0
21:47:22.279182 B400BF000 Read-Ack TSP setting: 240 0
21:47:23.209907 T90181B28 Write-Data Room temperature: 27.16
21:47:23.278119 B50181B28 Write-Ack Room temperature: 27.16
21:47:24.214441 T90101101 Write-Data Room setpoint: 17.00
21:47:24.279104 B50101101 Write-Ack Room setpoint: 17.00
21:47:25.210467 T90181B2E Write-Data Room temperature: 27.18
21:47:25.278441 B50181B2E Write-Ack Room temperature: 27.18
21:47:26.201235 T80190000 Read-Data Boiler water temperature: 0.00
21:47:26.278465 BC0193980 Read-Ack Boiler water temperature: 57.50
21:47:27.212141 T10181B34 Write-Data Room temperature: 27.20
21:47:27.286057 BD0181B34 Write-Ack Room temperature: 27.20
21:47:28.217426 T001B0000 Read-Data Outside temperature: 0.00
21:47:28.280328 BC01B1766 Read-Ack Outside temperature: 23.40
21:47:29.203534 T90181B35 Write-Data Room temperature: 27.21
21:47:29.265651 B50181B35 Write-Ack Room temperature: 27.21
21:47:30.209298 T801A0000 Read-Data DHW temperature: 0.00
21:47:30.273215 BC01A2D4C Read-Ack DHW temperature: 45.30
Re: Command ID 16
Sorry, but I still don't understand what you want to do.
Initially you asked about the Room Setpoint, MsgID 16. Now you talk about Room Temperature, which is MsgID 24.
The log shows the thermostat sends a Room Setpoint of 17. There is no setpoint change. Are you referring to MsgID 9 (Remote Override Room Setpoint) with that remark?
Do you want to change the value in MsgID 16 that gets sent to the boiler? As I mentioned before, boilers don't normally use that information. So, even if you could change the value, it would be unusual for it to have any effect.
Initially you asked about the Room Setpoint, MsgID 16. Now you talk about Room Temperature, which is MsgID 24.
The log shows the thermostat sends a Room Setpoint of 17. There is no setpoint change. Are you referring to MsgID 9 (Remote Override Room Setpoint) with that remark?
Do you want to change the value in MsgID 16 that gets sent to the boiler? As I mentioned before, boilers don't normally use that information. So, even if you could change the value, it would be unusual for it to have any effect.
Schelte