Issue with Max CH setpoint

This Forum is about the Opentherm gateway (OTGW) from Schelte

Moderator: hvxl

hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Issue with Max CH setpoint

Post by hvxl »

I'm talking about the setpoint belonging to the bounds. MsgID 49 gives the upper and lower bounds for the "Max CH water Setpoint". MsgID 57 is that "Max CH water Setpoint". Your boiler changes the Max CH water Setpoint upper bound to the Max CH water Setpoint. That's wrong. So the issue is not somewhere else. Your boiler is buggy.
Schelte