Inside temperature

This Forum is about the Opentherm gateway (OTGW) from Schelte

Moderator: hvxl

Post Reply
steefje
Starting Member
Starting Member
Posts: 4
Joined: Wed Jan 26, 2022 11:49 pm

Inside temperature

Post by steefje »

Hello,

I always used version 4.3 on my raspbian 32bit version.
Now i gonna use the 64 bit version of raspbian.

I have installed the aarch64 version and it works, only the Inside temperature is always 20.00°C.

I have found when i go back to version 4.3 it wil work, but where can i found version 4.3 of aarch64?
Or is there someone who can help me how to get it to work with this version?
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Inside temperature

Post by hvxl »

I suspect you may be misdiagnosing the issue. As far as I can recall, nothing has changed regarding the way OTmonitor 5.2 handles the room temperature compared to 4.3.

Please provide a log of the situation that isn't working in your assessment. Also indicate how you verify the room temperature (GUI, web, MQTT, ...).
Schelte
steefje
Starting Member
Starting Member
Posts: 4
Joined: Wed Jan 26, 2022 11:49 pm

Re: Inside temperature

Post by steefje »

I also see that I cannot adjust the temperature remotely.
In the log file I see that there is a request to reset the temperature to 13 degrees. But nothing changes.

I copied all settings from the 32bit version.

Log:

Code: Select all

10:02:23.938143  T90181130  Write-Data  Room temperature: 17.19
10:02:23.947102  R00740000  Read-Data   Burner starts: 0
10:02:24.086099  B40743B56  Read-Ack    Burner starts: 15190
10:02:24.093137  AF0181130  Unk-DataId  Room temperature: 17.19
10:02:24.971174  T80190000  Read-Data   Boiler water temperature: 0.00
10:02:25.093076  B40193C00  Read-Ack    Boiler water temperature: 60.00
10:02:26.015145  T10010A00  Write-Data  Control setpoint: 10.00
10:02:27.062327  T80000200  Read-Data   Status: 00000010 00000000
10:02:27.213354  B40000200  Read-Ack    Status: 00000010 00000000
10:02:28.154753  T90100C80  Write-Data  Room setpoint: 12.50
10:02:28.161640  R00780000  Read-Data   Burner operation hours: 0
10:02:28.306142  BC07819BA  Read-Ack    Burner operation hours: 6586
10:02:28.314312  A50100C80  Write-Ack   Room setpoint: 12.50
10:02:29.154468  T80190000  Read-Data   Boiler water temperature: 0.00
10:02:29.306790  B40193C00  Read-Ack    Boiler water temperature: 60.00
10:02:30.212895  T10010A00  Write-Data  Control setpoint: 10.00
10:02:30.331043  BD0010A00  Write-Ack   Control setpoint: 10.00
10:02:31.250421  T80000200  Read-Data   Status: 00000010 00000000
10:02:31.423216  B40000200  Read-Ack    Status: 00000010 00000000
10:02:31.862765  Command (via websocket): TT=13
10:02:31.926781  TT: 13.00
10:02:32.297408  T90181130  Write-Data  Room temperature: 17.19
10:02:32.309442  R007B0000  Read-Data   DHW burner operation hours: 0
10:02:32.320671  Command (via websocket): TT=13.5
10:02:32.439988  B407B046A  Read-Ack    DHW burner operation hours: 1130
10:02:32.442424  AF0181130  Unk-DataId  Room temperature: 17.19
10:02:32.480844  TT: 13.50
10:02:32.740524  Command (via websocket): TT=14
10:02:32.854748  TT: 14.00
10:02:33.183361  Command (via websocket): TT=14.5
10:02:33.373232  TT: 14.50
10:02:33.384138  T80190000  Read-Data   Boiler water temperature: 0.00
10:02:33.542132  B40193C00  Read-Ack    Boiler water temperature: 60.00
10:02:33.633161  Command (via websocket): TT=15
10:02:33.742303  TT: 15.00
10:02:34.111988  Command (via websocket): TT=15.5
10:02:34.252666  TT: 15.50
10:02:34.396644  T10010A00  Write-Data  Control setpoint: 10.00
10:02:34.545794  BD0010A00  Write-Ack   Control setpoint: 10.00
10:02:34.610693  Command (via websocket): TT=16
10:02:34.666983  TT: 16.00
10:02:35.121677  Command (via websocket): TT=16.5
10:02:35.174549  TT: 16.50
10:02:35.442425  T80000200  Read-Data   Status: 00000010 00000000
10:02:35.552323  B40000200  Read-Ack    Status: 00000010 00000000
10:02:35.601440  Command (via websocket): TT=17
10:02:35.678852  TT: 17.00
10:02:36.498215  T90100C80  Write-Data  Room setpoint: 12.50
10:02:36.506153  R00740000  Read-Data   Burner starts: 0
10:02:36.648295  B40743B56  Read-Ack    Burner starts: 15190
10:02:36.663311  A50100C80  Write-Ack   Room setpoint: 12.50
10:02:37.533534  T80190000  Read-Data   Boiler water temperature: 0.00
10:02:37.670096  B40193C00  Read-Ack    Boiler water temperature: 60.00
10:02:38.586312  T10010A00  Write-Data  Control setpoint: 10.00
10:02:38.751006  BD0010A00  Write-Ack   Control setpoint: 10.00
10:02:39.626789  T80000200  Read-Data   Status: 00000010 00000000
10:02:39.804816  B40000200  Read-Ack    Status: 00000010 00000000
10:02:40.670491  T90181130  Write-Data  Room temperature: 17.19
10:02:40.686417  R00780000  Read-Data   Burner operation hours: 0
10:02:40.872575  BC07819BA  Read-Ack    Burner operation hours: 6586
10:02:40.887747  AF0181130  Unk-DataId  Room temperature: 17.19
10:02:41.718181  T80190000  Read-Data   Boiler water temperature: 0.00
10:02:41.871111  B40193C00  Read-Ack    Boiler water temperature: 60.00
10:02:42.763326  T10010A00  Write-Data  Control setpoint: 10.00
10:02:42.888522  BD0010A00  Write-Ack   Control setpoint: 10.00
10:02:43.810846  T80000200  Read-Data   Status: 00000010 00000000
10:02:43.989197  B40000200  Read-Ack    Status: 00000010 00000000
10:02:44.868916  T90100C80  Write-Data  Room setpoint: 12.50
10:02:44.883919  R007B0000  Read-Data   DHW burner operation hours: 0
10:02:44.992178  B407B046A  Read-Ack    DHW burner operation hours: 1130
10:02:45.006890  A50100C80  Write-Ack   Room setpoint: 12.50
This is what i use (on my iphone to change the temperature.
Last edited by steefje on Fri Jan 28, 2022 11:09 am, edited 1 time in total.
steefje
Starting Member
Starting Member
Posts: 4
Joined: Wed Jan 26, 2022 11:49 pm

Re: Inside temperature

Post by steefje »

Did some more research on the internet today.
I once used the nodo shop manual and it says port 6638.
But now I use port 25238 and I can now adjust the temperature on my phone via the iphone.html page.
Only I keep seeing 20 degrees on the iphone.html page.
While the Opentherm Gateway Status Summary page can read the correct temperature.
hvxl
Senior Member
Senior Member
Posts: 1965
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Inside temperature

Post by hvxl »

The port was changed in version 0.7.1 of the NodeMCU firmware by rvdbreemen: "Changed to port 25238 for serial TCP connections (default of OTmonitor application by Schelte Bron)"

Now that you finally mention that the issue you have with the temperature is on the iphone.html page, I suspect that you ran into the problem mentioned in this bug report. That bug report also indicates how to patch it.
Schelte
steefje
Starting Member
Starting Member
Posts: 4
Joined: Wed Jan 26, 2022 11:49 pm

Re: Inside temperature

Post by steefje »

Thanks it works.
Now i got the right temperature.