How to interpret the modulation value

Post by dirkx@webweaving.org »

How should one interpret the modulation value. Looking at graphs like http://otgw.tclcode.com/otmonitor.html#graph and my own (http://people.apache.org/~dirkx/ot.png) - I am wondering what 0% modulation means. Does it perhaps mean not modulated at all - and 100% in effect means maximal reduction of the heat applied ?

Thanks,

Dw.
hvxl
Senior Member
Senior Member
Posts: 1966
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: How to interpret the modulation value

Post by hvxl »

From the logs I've seen, my understanding is that a modulation value of 0% indicates to the boiler to burn as low as possible and 100% is: Burn at maximum capacity.

The specs also indicate: "The default value in the slave device should be 100% (i.e. no throttling back of the capacity)."
Schelte