GW firmware 5.4 @P16F88
OTmonitor 6.1 @Linux-armhf
I would like to switch off both circuit of central heating. So I do the following command:
CS=19
CH=0
C2=19
H2=0
but the result is, that CS is reset (set back to 0)
Here is the log file:
Code: Select all
07:39:50.193941 T80001300 Read-Data Status: 00010011 00000000
07:39:50.462432 BC000132A Read-Ack Status: 00010011 00101010
07:39:51.233557 T900121BC Write-Data Control setpoint: 33.73
07:39:51.586052 B500121BC Write-Ack Control setpoint: 33.73
07:39:52.205850 T90081AD4 Write-Data Control setpoint 2: 26.83
07:39:52.574420 B50081AD4 Write-Ack Control setpoint 2: 26.83
07:39:53.195697 T90383200 Write-Data DHW setpoint: 50.00
07:39:53.564173 B50383200 Write-Ack DHW setpoint: 50.00
07:39:54.184092 T80200000 Read-Data DHW2 temperature: 0.00
07:39:54.218921 Command (via websocket from 192.168.111.203:53656): CS=19
07:39:54.237437 CS: 19.00
07:39:54.553422 BE0200000 Data-Inv DHW2 temperature: 0.00
07:39:55.174687 T801A0000 Read-Data DHW temperature: 0.00
07:39:55.543546 BC01A380C Read-Ack DHW temperature: 56.05
07:39:56.213417 T80001300 Read-Data Status: 00010011 00000000
07:39:56.224431 R00001200 Read-Data Status: 00010010 00000000
07:39:56.531882 B4000122A Read-Ack Status: 00010010 00101010
07:39:56.544146 AC000132A Read-Ack Status: 00010011 00101010
07:39:57.202692 T001B0000 Read-Data Outside temperature: 0.00
07:39:57.521309 B401B0B88 Read-Ack Outside temperature: 11.53
07:39:58.192433 T80190000 Read-Data Boiler water temperature: 0.00
07:39:58.511171 BC019244C Read-Ack Boiler water temperature: 36.30
07:39:59.181059 T801C0000 Read-Data Return water temperature: 0.00
07:39:59.499535 B401C1CD0 Read-Ack Return water temperature: 28.81
07:40:00.170551 T801F0000 Read-Data Flow temperature CH2: 0.00
07:40:00.489061 BC01F18C4 Read-Ack Flow temperature CH2: 24.77
07:40:01.160231 T00110000 Read-Data Relative modulation level: 0.00
07:40:01.478713 BC0110000 Read-Ack Relative modulation level: 0.00
07:40:02.150038 T80001300 Read-Data Status: 00010011 00000000
07:40:02.160900 R00001200 Read-Data Status: 00010010 00000000
07:40:02.468240 B40001220 Read-Ack Status: 00010010 00100000
07:40:02.479355 AC0001320 Read-Ack Status: 00010011 00100000
07:40:03.189220 T80130000 Read-Data DHW flow rate: 0.00
07:40:03.458173 B70130000 Unk-DataId DHW flow rate: 0.00
07:40:04.178937 T001D0000 Read-Data Solar storage temperature: 0.00
07:40:04.446312 BF01D0000 Unk-DataId Solar storage temperature: 0.00
07:40:05.168812 T001E0000 Read-Data Solar collector temperature: 0.00
07:40:05.436289 B601E0000 Data-Inv Solar collector temperature: 0.00
07:40:06.155953 T00210000 Read-Data Exhaust temperature: 0
07:40:06.425281 B40210020 Read-Ack Exhaust temperature: 32
07:40:07.146322 T9081020E Write-Data Message ID 129: 526
07:40:07.414542 B5081020E Write-Ack Message ID 129: 526
07:40:08.135877 T80001300 Read-Data Status: 00010011 00000000
07:40:10.724194 R00001200 Read-Data Status: 00010010 00000000
07:40:10.806855 B40001220 Read-Ack Status: 00010010 00100000
07:40:10.810090 AC0001320 Read-Ack Status: 00010011 00100000
07:40:10.813083 T10101580 Write-Data Room setpoint: 21.50
07:40:10.815314 BD0101580 Write-Ack Room setpoint: 21.50
07:40:10.817567 T90171580 Write-Data Room Setpoint CH2: 21.50
07:40:10.820377 B50171580 Write-Ack Room Setpoint CH2: 21.50
07:40:11.167140 T10181590 Write-Data Room temperature: 21.56
07:40:11.435656 BD0181590 Write-Ack Room temperature: 21.56
07:40:12.156658 T80800000 Read-Data Message ID 128: 0
07:40:12.425259 BE0800000 Data-Inv Message ID 128: 0
07:40:13.146390 T10825453 Write-Data Message ID 130: 21587
07:40:13.415009 BD0825453 Write-Ack Message ID 130: 21587
07:40:14.134806 T80001300 Read-Data Status: 00010011 00000000
07:40:14.147106 R00001200 Read-Data Status: 00010010 00000000
07:40:14.404752 B40001220 Read-Ack Status: 00010010 00100000
07:40:14.415761 AC0001320 Read-Ack Status: 00010011 00100000
07:40:14.464518 Command (via websocket from 192.168.111.203:53656): CH=0
07:40:14.477648 CH: 0
07:40:15.124885 T900121BC Write-Data Control setpoint: 33.73
07:40:15.137234 R90011300 Write-Data Control setpoint: 19.00
07:40:15.393255 B50011300 Write-Ack Control setpoint: 19.00
07:40:15.404236 A500121BC Write-Ack Control setpoint: 33.73
07:40:16.114016 T90081AD4 Write-Data Control setpoint 2: 26.83
07:40:16.382685 B50081AD4 Write-Ack Control setpoint 2: 26.83
07:40:17.102687 T90383200 Write-Data DHW setpoint: 50.00
07:40:17.372494 B50383200 Write-Ack DHW setpoint: 50.00
07:40:18.142385 T80200000 Read-Data DHW2 temperature: 0.00
07:40:18.494706 BE0200000 Data-Inv DHW2 temperature: 0.00
07:40:19.115672 T801A0000 Read-Data DHW temperature: 0.00
07:40:19.484370 BC01A380C Read-Ack DHW temperature: 56.05
07:40:20.104126 T80001300 Read-Data Status: 00010011 00000000
07:40:20.115103 R00001200 Read-Data Status: 00010010 00000000
07:40:20.473782 B40001220 Read-Ack Status: 00010010 00100000
07:40:20.484760 AC0001320 Read-Ack Status: 00010011 00100000
07:40:21.093320 T001B0000 Read-Data Outside temperature: 0.00
07:40:21.462022 BC01B0B70 Read-Ack Outside temperature: 11.44
07:40:22.083244 T80190000 Read-Data Boiler water temperature: 0.00
07:40:22.451876 B401923F4 Read-Ack Boiler water temperature: 35.95
07:40:23.121880 T801C0000 Read-Data Return water temperature: 0.00
07:40:23.441876 BC01C1988 Read-Ack Return water temperature: 25.53
07:40:24.111642 T801F0000 Read-Data Flow temperature CH2: 0.00
07:40:24.430252 B401F1AF8 Read-Ack Flow temperature CH2: 26.97
07:40:25.100307 T00110000 Read-Data Relative modulation level: 0.00
07:40:25.420062 BC0110000 Read-Ack Relative modulation level: 0.00
07:40:26.091241 T80001300 Read-Data Status: 00010011 00000000
07:40:26.102246 R00001200 Read-Data Status: 00010010 00000000
07:40:26.409674 B40001220 Read-Ack Status: 00010010 00100000
07:40:26.420638 AC0001320 Read-Ack Status: 00010011 00100000
07:40:27.080640 T80130000 Read-Data DHW flow rate: 0.00
07:40:27.397948 B70130000 Unk-DataId DHW flow rate: 0.00
07:40:28.070487 T001D0000 Read-Data Solar storage temperature: 0.00
07:40:28.387775 BF01D0000 Unk-DataId Solar storage temperature: 0.00
07:40:29.058769 T001E0000 Read-Data Solar collector temperature: 0.00
07:40:29.377354 B601E0000 Data-Inv Solar collector temperature: 0.00
07:40:30.098591 T00210000 Read-Data Exhaust temperature: 0
07:40:30.365847 B40210020 Read-Ack Exhaust temperature: 32
07:40:31.087093 T9081020E Write-Data Message ID 129: 526
07:40:31.355611 B5081020E Write-Ack Message ID 129: 526
07:40:32.076856 T80001300 Read-Data Status: 00010011 00000000
07:40:32.087830 R00001200 Read-Data Status: 00010010 00000000
07:40:32.345564 B40001220 Read-Ack Status: 00010010 00100000
07:40:32.356450 AC0001320 Read-Ack Status: 00010011 00100000
07:40:33.066342 T10101580 Write-Data Room setpoint: 21.50
07:40:33.334981 BD0101580 Write-Ack Room setpoint: 21.50
07:40:34.054866 T90171580 Write-Data Room Setpoint CH2: 21.50
07:40:34.323457 B50171580 Write-Ack Room Setpoint CH2: 21.50
07:40:35.044617 T10181590 Write-Data Room temperature: 21.56
07:40:35.313344 BD0181590 Write-Ack Room temperature: 21.56
07:40:36.083223 T80800000 Read-Data Message ID 128: 0
07:40:36.366764 BE0800000 Data-Inv Message ID 128: 0
07:40:37.037853 T10825453 Write-Data Message ID 130: 21587
07:40:37.355094 BD0825453 Write-Ack Message ID 130: 21587
07:40:38.076211 T90020004 Write-Data Master configuration: 00000000 4
07:40:38.344972 B50020004 Write-Ack Master configuration: 00000000 4
07:40:39.066086 T80001300 Read-Data Status: 00010011 00000000
07:40:39.077314 R00001200 Read-Data Status: 00010010 00000000
07:40:39.334740 B40001220 Read-Ack Status: 00010010 00100000
07:40:39.345709 AC0001320 Read-Ack Status: 00010011 00100000
07:40:40.055590 T900121C8 Write-Data Control setpoint: 33.78
07:40:40.066570 R90011300 Write-Data Control setpoint: 19.00
07:40:40.323947 B50011300 Write-Ack Control setpoint: 19.00
07:40:40.334923 A500121C8 Write-Ack Control setpoint: 33.78
07:40:41.044815 T90081AD8 Write-Data Control setpoint 2: 26.84
07:40:41.313591 B50081AD8 Write-Ack Control setpoint 2: 26.84
07:40:42.033460 T90383200 Write-Data DHW setpoint: 50.00
07:40:42.302077 B50383200 Write-Ack DHW setpoint: 50.00
07:40:43.023310 T80200000 Read-Data DHW2 temperature: 0.00
07:40:43.291807 BE0200000 Data-Inv DHW2 temperature: 0.00
07:40:44.013045 T801A0000 Read-Data DHW temperature: 0.00
07:40:44.280423 BC01A380C Read-Ack DHW temperature: 56.05
07:40:45.051559 T80001300 Read-Data Status: 00010011 00000000
07:40:45.063897 R00001200 Read-Data Status: 00010010 00000000
07:40:45.403673 B40001220 Read-Ack Status: 00010010 00100000
07:40:45.414691 AC0001320 Read-Ack Status: 00010011 00100000
07:40:46.024408 T001B0000 Read-Data Outside temperature: 0.00
07:40:46.393048 B401B0BA0 Read-Ack Outside temperature: 11.62
07:40:47.012839 T80190000 Read-Data Boiler water temperature: 0.00
07:40:47.382843 B40191FC8 Read-Ack Boiler water temperature: 31.78
07:40:48.002903 T801C0000 Read-Data Return water temperature: 0.00
07:40:48.371433 B401C1940 Read-Ack Return water temperature: 25.25
07:40:48.991195 T801F0000 Read-Data Flow temperature CH2: 0.00
07:40:49.361056 BC01F1A3C Read-Ack Flow temperature CH2: 26.23
07:40:50.032166 T00110000 Read-Data Relative modulation level: 0.00
07:40:50.350853 BC0110000 Read-Ack Relative modulation level: 0.00
07:40:51.020554 T80001300 Read-Data Status: 00010011 00000000
07:40:51.031741 R00001200 Read-Data Status: 00010010 00000000
07:40:51.339045 B40001220 Read-Ack Status: 00010010 00100000
07:40:51.351440 AC0001320 Read-Ack Status: 00010011 00100000
07:40:52.010041 T80130000 Read-Data DHW flow rate: 0.00
07:40:52.328419 B70130000 Unk-DataId DHW flow rate: 0.00
07:40:53.000812 T001D0000 Read-Data Solar storage temperature: 0.00
07:40:53.318162 BF01D0000 Unk-DataId Solar storage temperature: 0.00
07:40:53.989289 T001E0000 Read-Data Solar collector temperature: 0.00
07:40:54.308037 B601E0000 Data-Inv Solar collector temperature: 0.00
07:40:54.977917 T00210000 Read-Data Exhaust temperature: 0
07:40:55.296408 B40210020 Read-Ack Exhaust temperature: 32
07:40:55.967542 T9081020E Write-Data Message ID 129: 526
07:40:56.286146 B5081020E Write-Ack Message ID 129: 526
07:40:57.006072 T80001300 Read-Data Status: 00010011 00000000
07:40:57.280306 BC0001320 Read-Ack Status: 00010011 00100000
07:40:57.995825 T10101580 Write-Data Room setpoint: 21.50
07:40:58.264580 BD0101580 Write-Ack Room setpoint: 21.50
07:40:58.985816 T90171580 Write-Data Room Setpoint CH2: 21.50
07:40:59.254416 B50171580 Write-Ack Room Setpoint CH2: 21.50
07:40:59.974312 T10181590 Write-Data Room temperature: 21.56
07:41:00.242941 BD0181590 Write-Ack Room temperature: 21.56
07:41:00.964069 T80800000 Read-Data Message ID 128: 0
07:41:01.232578 BE0800000 Data-Inv Message ID 128: 0
07:41:01.953939 T10825453 Write-Data Message ID 130: 21587
07:41:02.221177 BD0825453 Write-Ack Message ID 130: 21587
07:41:02.992205 T00030000 Read-Data Slave configuration: 00000000 0
07:41:03.275934 BC0032904 Read-Ack Slave configuration: 00101001 4
07:41:03.945811 T80001300 Read-Data Status: 00010011 00000000
07:41:04.264294 B40001322 Read-Ack Status: 00010011 00100010
07:41:04.985423 T900121B0 Write-Data Control setpoint: 33.69
07:41:05.253912 B500121B0 Write-Ack Control setpoint: 33.69
07:41:05.975049 T90081ACC Write-Data Control setpoint 2: 26.80
07:41:06.243789 B50081ACC Write-Ack Control setpoint 2: 26.80
07:41:06.963711 T90383200 Write-Data DHW setpoint: 50.00
07:41:07.232164 B50383200 Write-Ack DHW setpoint: 50.00
07:41:07.953174 T80200000 Read-Data DHW2 temperature: 0.00
07:41:08.221804 BE0200000 Data-Inv DHW2 temperature: 0.00
07:41:08.624933 Command (via websocket from 192.168.111.203:53660): C2=19
07:41:08.644177 C2: 19.00
07:41:08.942711 T801A0000 Read-Data DHW temperature: 0.00
07:41:09.211162 BC01A380C Read-Ack DHW temperature: 56.05
07:41:09.932282 T80001300 Read-Data Status: 00010011 00000000
07:41:09.943254 R00000300 Read-Data Status: 00000011 00000000
07:41:10.200584 BC0000322 Read-Ack Status: 00000011 00100010
07:41:10.211551 A40001322 Read-Ack Status: 00010011 00100010
07:41:10.921309 T001B0000 Read-Data Outside temperature: 0.00
07:41:11.189903 B401B0B88 Read-Ack Outside temperature: 11.53
07:41:11.961166 T80190000 Read-Data Boiler water temperature: 0.00
07:41:12.312159 B40191D14 Read-Ack Boiler water temperature: 29.08
07:41:12.933285 T801C0000 Read-Data Return water temperature: 0.00
07:41:13.301792 B401C1C8C Read-Ack Return water temperature: 28.55
07:41:13.921689 T801F0000 Read-Data Flow temperature CH2: 0.00
07:41:14.291579 B401F18E8 Read-Ack Flow temperature CH2: 24.91
07:41:14.911292 T00110000 Read-Data Relative modulation level: 0.00
07:41:15.281156 BC0110000 Read-Ack Relative modulation level: 0.00
07:41:15.901031 T80001300 Read-Data Status: 00010011 00000000
07:41:15.912011 R00000300 Read-Data Status: 00000011 00000000
07:41:16.270705 B40000302 Read-Ack Status: 00000011 00000010
07:41:16.281880 AC0001302 Read-Ack Status: 00010011 00000010
07:41:16.940573 T80130000 Read-Data DHW flow rate: 0.00
07:41:17.259145 B70130000 Unk-DataId DHW flow rate: 0.00
07:41:17.930290 T001D0000 Read-Data Solar storage temperature: 0.00
07:41:18.248901 BF01D0000 Unk-DataId Solar storage temperature: 0.00
07:41:18.920110 T001E0000 Read-Data Solar collector temperature: 0.00
07:41:19.237378 B601E0000 Data-Inv Solar collector temperature: 0.00
07:41:19.908389 T00210000 Read-Data Exhaust temperature: 0
07:41:20.227009 B40210020 Read-Ack Exhaust temperature: 32
07:41:20.898111 T9081020E Write-Data Message ID 129: 526
07:41:21.216890 B5081020E Write-Ack Message ID 129: 526
07:41:21.886791 T80001300 Read-Data Status: 00010011 00000000
07:41:21.897740 R00000300 Read-Data Status: 00000011 00000000
07:41:22.206384 B40000302 Read-Ack Status: 00000011 00000010
07:41:22.217360 AC0001302 Read-Ack Status: 00010011 00000010
07:41:22.877395 T10101580 Write-Data Room setpoint: 21.50
07:41:23.051605 Command (via websocket from 192.168.111.203:53660): H2=0
07:41:23.065658 H2: 0
07:41:23.195521 BD0101580 Write-Ack Room setpoint: 21.50
07:41:23.915392 T90171580 Write-Data Room Setpoint CH2: 21.50
07:41:24.184130 B50171580 Write-Ack Room Setpoint CH2: 21.50
07:41:24.905270 T10181590 Write-Data Room temperature: 21.56
07:41:25.173992 BD0181590 Write-Ack Room temperature: 21.56
07:41:25.895017 T80800000 Read-Data Message ID 128: 0
07:41:26.163657 BE0800000 Data-Inv Message ID 128: 0
07:41:26.883386 T10825453 Write-Data Message ID 130: 21587
07:41:27.151878 BD0825453 Write-Ack Message ID 130: 21587
07:41:27.872995 T00060000 Read-Data Remote parameter flags: 00000000 00000000
07:41:28.185562 BC0060707 Read-Ack Remote parameter flags: 00000111 00000111
07:41:28.862787 T80001300 Read-Data Status: 00010011 00000000
07:41:28.873753 R00000300 Read-Data Status: 00000011 00000000
07:41:29.131127 B40000302 Read-Ack Status: 00000011 00000010
07:41:29.142098 AC0001302 Read-Ack Status: 00010011 00000010
07:41:29.901875 T900121BC Write-Data Control setpoint: 33.73
07:41:30.184374 B500121BC Write-Ack Control setpoint: 33.73
07:41:30.855556 T90081AD4 Write-Data Control setpoint 2: 26.83
07:41:30.866489 R90081300 Write-Data Control setpoint 2: 19.00
07:41:31.173730 B50081300 Write-Ack Control setpoint 2: 19.00
07:41:31.184700 A50081AD4 Write-Ack Control setpoint 2: 26.83
07:41:31.894638 T90383200 Write-Data DHW setpoint: 50.00
07:41:32.163212 B50383200 Write-Ack DHW setpoint: 50.00
07:41:32.883219 T80200000 Read-Data DHW2 temperature: 0.00
07:41:33.153097 BE0200000 Data-Inv DHW2 temperature: 0.00
07:41:33.872856 T801A0000 Read-Data DHW temperature: 0.00
07:41:34.141469 BC01A380C Read-Ack DHW temperature: 56.05
07:41:34.862469 T80001300 Read-Data Status: 00010011 00000000
07:41:34.873688 R00000300 Read-Data Status: 00000011 00000000
07:41:35.130959 B40000302 Read-Ack Status: 00000011 00000010
07:41:35.141954 AC0001302 Read-Ack Status: 00010011 00000010
07:41:35.851878 T001B0000 Read-Data Outside temperature: 0.00
07:41:36.120652 B401B0B88 Read-Ack Outside temperature: 11.53
07:41:36.840487 T80190000 Read-Data Boiler water temperature: 0.00
07:41:37.108981 B40191E84 Read-Ack Boiler water temperature: 30.52
07:41:37.830066 T801C0000 Read-Data Return water temperature: 0.00
07:41:38.098508 BC01C1D58 Read-Ack Return water temperature: 29.34
07:41:38.869540 T801F0000 Read-Data Flow temperature CH2: 0.00
07:41:39.221861 B401F1860 Read-Ack Flow temperature CH2: 24.38