Hello,
can someone tell me which command can be used to change the RoomSetpoint?
I was of the opinion that this value was changed from the OT monitor via the thermostat tab Can be.
Unfortunately that doesn't work.
Nothing changes directly via Miscellaneous with the command TT=.
It is shown in the log but there is no change.
Thanks in advance
Greetings Mirko
Modification RoomSetpoint
Moderator: hvxl
Re: Modification RoomSetpoint
The command is "TT" or "TC", not "tt". All OTGW commands are uppercase. As the OTGW site indicates: "These functions are only available if supported by the thermostat." Unfortunately, the Siemens QAA73 does not appear to support this. At least the equipment matrix shows that that thermostat doesn't request MsgID 9, which is necessary for this functionality.
Schelte
Re: Modification RoomSetpoint
Hello,
many thanks for the answer.
I accidentally wrote "TT" in lower case in the text.
I know it has to be capitalized in the gateway.
I have on "https://otgw.tclcode.com/"
seen that "MsgID 9" is indeed not supported.
Greetings Mirko