I recently bought a OTGW from Nodo Shop which is giving me a hard time when running in gateway mode.
Board v2.8 running FW 6.4 coupled with WeMos D1 mini running rvdbreemen/OTGW-firmware v0.10.0.
Boiler is a Keston C36 Combi and thermostat a Salus RT520RF.
The setup seems to work just fine in monitor mode (except for a random Error FF):
Code: Select all
2:21:29.419651 Command: PR=A
22:21:29.485344 PR: A=OpenTherm Gateway 6.4
22:21:30.251362 Error FF
22:21:30.252154 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
22:21:30.346328 B70130000 Unk-DataId DHW flow rate (MsgID=19): 0.00
22:21:31.630022 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
22:21:31.637324 B70130000 Unk-DataId DHW flow rate (MsgID=19): 0.00
22:21:32.451395 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
22:21:32.455342 B70130000 Unk-DataId DHW flow rate (MsgID=19): 0.00
22:21:33.379911 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:21:33.385592 B40192E00 Read-Ack Boiler water temperature (MsgID=25): 46.00
22:21:34.168486 PR: I=11
22:21:34.543333 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:21:34.545341 B40192E00 Read-Ack Boiler water temperature (MsgID=25): 46.00
22:21:35.428297 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:21:35.435129 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
22:21:36.439884 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:21:36.482733 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
22:21:37.449169 T00300000 Read-Data DHW setpoint boundaries (MsgID=48): 0 0
22:21:38.482442 T00300000 Read-Data DHW setpoint boundaries (MsgID=48): 0 0
22:21:38.870250 BC0304128 Read-Ack DHW setpoint boundaries (MsgID=48): 65 40
22:21:39.499493 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:21:39.547552 B40192E00 Read-Ack Boiler water temperature (MsgID=25): 46.00
22:21:40.536701 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:21:40.593868 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
22:21:41.553145 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:21:41.599985 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
22:21:42.570590 T80730000 Read-Data OEM diagnostic code (MsgID=115): 0
22:21:42.617161 B70730000 Unk-DataId OEM diagnostic code (MsgID=115): 0
22:21:43.605372 T80730000 Read-Data OEM diagnostic code (MsgID=115): 0
22:21:43.649687 B70730000 Unk-DataId OEM diagnostic code (MsgID=115): 0
22:21:44.210516 PR: I=11
22:21:44.620270 T80730000 Read-Data OEM diagnostic code (MsgID=115): 0
22:21:44.667866 B70730000 Unk-DataId OEM diagnostic code (MsgID=115): 0
22:21:45.650964 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:21:45.700262 B40192E00 Read-Ack Boiler water temperature (MsgID=25): 46.00
22:21:46.671095 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:21:46.717481 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
22:21:47.685560 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:21:47.734860 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
22:21:48.717268 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:21:48.766040 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
22:21:49.754071 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:21:49.801123 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
22:21:50.770956 T000F0000 Read-Data Boiler capacity and modulation limits (MsgID=15): 0 0
22:21:50.817551 BF00F0000 Unk-DataId Boiler capacity and modulation limits (MsgID=15): 0 0
22:21:51.784081 T000F0000 Read-Data Boiler capacity and modulation limits (MsgID=15): 0 0
22:21:51.832394 BF00F0000 Unk-DataId Boiler capacity and modulation limits (MsgID=15): 0 0
22:21:52.826029 T000F0000 Read-Data Boiler capacity and modulation limits (MsgID=15): 0 0
22:21:52.883888 BF00F0000 Unk-DataId Boiler capacity and modulation limits (MsgID=15): 0 0
22:21:53.834994 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:21:53.883260 B40192E00 Read-Ack Boiler water temperature (MsgID=25): 46.00
22:21:54.235733 PR: I=11
22:21:54.870495 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:21:54.917077 B40192E00 Read-Ack Boiler water temperature (MsgID=25): 46.00
22:21:55.996202 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:21:56.059953 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
22:21:56.918242 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:21:56.967097 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
22:21:58.048285 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:21:58.109056 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
22:21:58.959432 T10620000 Write-Data RF sensor status information (MsgID=98): 0 0 0 0
22:21:59.019920 B70620000 Unk-DataId RF sensor status information (MsgID=98): 0 0 0 0
22:21:59.987628 T10620000 Write-Data RF sensor status information (MsgID=98): 0 0 0 0
22:22:00.037331 B70620000 Unk-DataId RF sensor status information (MsgID=98): 0 0 0 0
22:22:01.001490 T10620000 Write-Data RF sensor status information (MsgID=98): 0 0 0 0
22:22:01.051285 SC: 22:22/3
22:22:01.054765 B70620000 Unk-DataId RF sensor status information (MsgID=98): 0 0 0 0
22:22:02.033822 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:22:02.084432 B40192E00 Read-Ack Boiler water temperature (MsgID=25): 46.00
22:22:03.051450 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:22:03.102265 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
22:22:04.092759 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:22:04.140206 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
22:22:04.273167 PR: I=11
22:22:05.104119 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:22:05.151467 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
22:22:06.135987 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
22:22:06.183818 B401B0400 Read-Ack Outside temperature (MsgID=27): 4.00
22:22:07.174709 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:22:07.222481 B40192E00 Read-Ack Boiler water temperature (MsgID=25): 46.00
22:22:08.187970 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:22:08.235419 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
22:22:09.207767 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:22:09.257431 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
22:22:10.204139 Error FF
22:22:10.211382 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:22:10.258618 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
22:22:11.252797 T90110000 Write-Data Relative modulation level (MsgID=17): 0.00
22:22:12.280509 T90110000 Write-Data Relative modulation level (MsgID=17): 0.00
22:22:12.336282 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
22:22:13.314816 T90110000 Write-Data Relative modulation level (MsgID=17): 0.00
22:22:13.369581 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
22:22:14.303467 PR: I=11
22:22:14.321128 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:22:14.354713 B40192E00 Read-Ack Boiler water temperature (MsgID=25): 46.00
22:22:15.355675 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:22:15.403616 B40192E00 Read-Ack Boiler water temperature (MsgID=25): 46.00
Code: Select all
22:37:40.823004 Command: GW=R
22:37:42.130528 OpenTherm Gateway 6.4
22:37:42.298435 T00060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
22:37:42.396956 Error 03
22:37:43.332479 T00060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
22:37:43.378831 Error 03
22:37:44.348062 T00060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
22:37:44.464990 Error 03
22:37:45.612089 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:37:45.624451 Error 03
22:37:46.401378 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:37:46.447497 Error 03
22:37:47.434711 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:37:47.482722 Error 03
22:37:48.346517 PR: I=11
22:37:48.453543 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:37:48.511306 Error 03
22:37:49.469524 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:37:49.566745 Error 03
22:37:50.501753 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:37:50.548337 Error 03
22:37:51.693256 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:37:51.746765 Error 03
22:37:52.550668 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:37:52.602512 Error 03
22:37:53.566773 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:37:53.662952 Error 03
22:37:54.598458 T10393700 Write-Data Max CH water setpoint (MsgID=57): 55.00
22:37:54.989491 Error 03
22:37:55.788810 T10393700 Write-Data Max CH water setpoint (MsgID=57): 55.00
22:37:55.844615 Error 03
22:37:56.631293 T10393700 Write-Data Max CH water setpoint (MsgID=57): 55.00
22:37:56.952565 Error 03
22:37:57.666777 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:37:57.718705 Error 03
22:37:58.369024 PR: I=11
22:37:58.700249 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:37:58.753037 Error 04
22:37:58.757437 ED55D7F55
22:37:59.831581 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:38:00.732397 Error 03
22:38:01.136390 SC: 22:38/3
22:38:01.950316 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:38:01.957807 Error 03
22:38:02.792417 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:38:02.863537 Error 03
22:38:04.099757 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:04.156336 Error 03
22:38:04.973433 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:04.981167 Error 03
22:38:05.864204 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:05.914339 Error 03
22:38:06.891658 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:06.945191 Error 03
22:38:07.898343 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:07.998047 Error 03
22:38:08.425749 PR: I=11
22:38:08.933355 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:08.983266 Error 03
22:38:09.950812 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:38:10.047968 Error 03
22:38:10.984160 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:38:11.031159 Error 03
22:38:12.003047 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:38:12.118316 Error 03
22:38:13.198427 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:38:13.250075 Error 03
22:38:14.051764 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:38:14.150444 Error 03
22:38:15.071239 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:38:15.171313 Error 03
22:38:16.101586 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:16.199741 Error 03
22:38:17.116462 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:17.214842 Error 03
22:38:18.152211 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:18.202729 Error 03
22:38:18.450064 PR: I=11
22:38:19.169588 T90101600 Write-Data Room setpoint (MsgID=16): 22.00
22:38:19.265565 Error 03
22:38:20.202083 T90101600 Write-Data Room setpoint (MsgID=16): 22.00
22:38:20.251590 Error 03
22:38:21.216004 T90101600 Write-Data Room setpoint (MsgID=16): 22.00
22:38:21.315879 Error 03
22:38:22.252456 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:38:22.301528 Error 03
22:38:23.438971 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:38:23.482288 Error 03
22:38:24.307554 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:38:24.354397 Error 03
22:38:25.323843 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:38:25.385627 Error 03
22:38:26.335557 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:38:26.435702 Error 03
22:38:27.375354 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:38:27.436223 Error 03
22:38:28.397438 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:28.451841 PR: I=11
22:38:28.460477 Error 03
22:38:29.417598 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:29.469894 Error 03
22:38:30.443852 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:30.512807 Error 03
22:38:31.466368 T10181600 Write-Data Room temperature (MsgID=24): 22.00
22:38:31.517371 Error 03
22:38:32.484636 T10181600 Write-Data Room temperature (MsgID=24): 22.00
22:38:32.564602 Error 03
22:38:33.503507 T10181600 Write-Data Room temperature (MsgID=24): 22.00
22:38:33.598976 Error 03
22:38:34.535356 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:38:34.586269 Error 03
22:38:35.551819 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:38:35.650708 Error 03
22:38:36.571221 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:38:36.665023 Error 03
22:38:37.603122 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:38:37.703275 Error 03
22:38:38.517737 PR: I=11
22:38:38.621871 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:38:38.717690 Error 03
22:38:39.652856 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:38:39.703763 Error 03
22:38:40.671713 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:40.765952 Error 03
22:38:41.711345 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:41.775603 Error 03
22:38:42.717104 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:42.837095 Error 03
22:38:43.753618 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
22:38:43.852639 Error 03
22:38:44.767819 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
22:38:44.867138 Error 03
22:38:45.813714 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
22:38:45.868180 Error 03
22:38:46.817602 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:38:46.921686 Error 03
22:38:47.851815 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:38:47.904249 Error 03
22:38:48.538013 PR: I=11
22:38:48.870181 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:38:48.931314 Error 03
22:38:50.063958 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:38:50.118187 Error 03
22:38:50.919509 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:38:50.969443 Error 03
22:38:51.946052 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:38:52.021959 Error 03
22:38:52.968359 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:53.020252 Error 03
22:38:53.986878 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:54.086573 Error 03
22:38:55.025648 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:38:55.085257 Error 03
22:38:56.036180 T900E6400 Write-Data Maximum relative modulation level (MsgID=14): 100.00
22:38:56.136733 Error 03
22:38:57.069555 T900E6400 Write-Data Maximum relative modulation level (MsgID=14): 100.00
22:38:57.120336 Error 03
22:38:58.095756 T900E6400 Write-Data Maximum relative modulation level (MsgID=14): 100.00
22:38:58.161316 Error 03
22:38:58.568101 PR: I=11
22:38:59.117001 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:38:59.169230 Error 03
22:39:00.304417 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:39:00.347197 Error 03
22:39:01.124275 SC: 22:39/3
22:39:01.168786 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:39:01.219592 Error 03
22:39:02.187636 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:02.286865 Error 03
22:39:03.204755 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:03.302961 Error 03
22:39:04.237535 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:04.286562 Error 03
22:39:05.254777 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:39:05.357640 Error 03
22:39:06.287846 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:39:06.333164 Error 03
22:39:07.305027 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:39:07.401999 Error 03
22:39:08.337765 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
22:39:08.591133 Error 03
22:39:08.597533 PR: I=11
22:39:08.602776 PR: I=11
22:39:09.353504 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
22:39:09.669431 Error 03
22:39:10.397619 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
22:39:10.739388 Error 03
22:39:11.407705 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:39:11.476219 Error 03
22:39:12.422105 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:39:12.519806 Error 03
22:39:13.469391 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:39:13.527740 Error 03
22:39:14.472986 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:14.568417 Error 03
22:39:15.503954 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:15.553726 Error 03
22:39:16.531307 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:16.599018 Error 03
22:39:17.553129 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:39:17.601542 Error 03
22:39:18.570743 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:39:18.619356 PR: I=11
22:39:18.669662 Error 03
22:39:19.606140 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:39:19.655884 Error 03
22:39:20.619543 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
22:39:20.718698 Error 03
22:39:21.474740 Command: GW=1
22:39:21.538083 GW: 1
22:39:21.640175 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
22:39:21.751903 Error 03
22:39:22.669405 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
22:39:22.721819 Error 03
22:39:23.706047 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:39:23.759087 Error 03
22:39:24.722529 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:39:24.775656 Error 03
22:39:25.752005 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:39:25.804814 Error 03
22:39:26.781655 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:26.843540 Error 03
22:39:27.790789 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:27.889840 Error 03
22:39:28.691231 PR: I=11
22:39:28.819812 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:28.870558 Error 03
22:39:29.841188 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:39:29.939215 Error 03
22:39:30.874566 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:39:30.925645 Error 03
22:39:31.888874 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:39:31.952147 Error 04
22:39:32.010565 E55555755
22:39:32.922558 T00300000 Read-Data DHW setpoint boundaries (MsgID=48): 0 0
22:39:33.947864 Error 03
22:39:34.958788 T00300000 Read-Data DHW setpoint boundaries (MsgID=48): 0 0
22:39:35.229315 Error 03
22:39:35.992064 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:39:36.046653 Error 03
22:39:37.006863 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:39:37.105300 Error 03
22:39:38.042729 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:39:38.086841 Error 03
22:39:38.721578 PR: I=11
22:39:39.056841 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:39.154686 Error 03
22:39:40.098468 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:40.162516 Error 03
22:39:41.104689 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:41.205691 Error 03
22:39:42.290080 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:39:42.340542 Error 04
22:39:42.344367 E55555755
22:39:43.155437 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:39:44.191854 Error 03
22:39:45.208353 T80730000 Read-Data OEM diagnostic code (MsgID=115): 0
22:39:45.336329 Error 03
22:39:46.224863 T80730000 Read-Data OEM diagnostic code (MsgID=115): 0
22:39:46.319323 Error 03
22:39:47.259451 T80730000 Read-Data OEM diagnostic code (MsgID=115): 0
22:39:47.314388 Error 03
22:39:48.275801 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:39:48.316053 Command: PR=V
22:39:48.318632 Command: PR=T
22:39:48.323761 Command: PR=S
22:39:48.343424 Error 03
22:39:48.392562 PR: V=5
22:39:48.395008 PR: T=11
22:39:48.400087 PR: S=16.00
22:39:48.756204 PR: I=11
22:39:49.306985 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:39:49.360041 Error 03
22:39:50.329419 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:39:50.449395 Error 03
22:39:51.356486 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:51.406801 Error 03
22:39:52.397126 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:52.455467 Error 03
22:39:53.391359 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:39:53.489530 Error 03
22:39:53.886586 Command: VR=0
22:39:53.965575 VR: 0
22:39:54.432860 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:39:54.489145 Error 03
22:39:55.451429 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:39:55.524129 Error 03
22:39:56.472222 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:39:56.526471 Error 03
22:39:57.507127 T000F0000 Read-Data Boiler capacity and modulation limits (MsgID=15): 0 0
22:39:57.553785 Error 03
22:39:58.523721 T000F0000 Read-Data Boiler capacity and modulation limits (MsgID=15): 0 0
22:39:58.576090 Error 03
22:39:58.791507 PR: I=11
22:39:59.540726 T000F0000 Read-Data Boiler capacity and modulation limits (MsgID=15): 0 0
22:39:59.657428 Error 03
22:40:00.572656 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:00.624464 Error 03
22:40:01.121676 SC: 22:40/3
22:40:01.593849 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:01.649880 Error 03
22:40:02.631061 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:02.692349 Error 03
22:40:03.643797 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:40:03.743288 Error 03
22:40:04.658102 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:40:04.755765 Error 03
22:40:05.691841 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:40:05.748434 Error 03
22:40:06.713156 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:40:06.804749 Error 03
22:40:07.744946 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:40:07.795888 Error 03
22:40:08.761075 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:40:08.809967 PR: I=11
22:40:08.856350 Error 03
22:40:09.940722 T10620000 Write-Data RF sensor status information (MsgID=98): 0 0 0 0
22:40:09.992131 Error 03
22:40:10.811892 T10620000 Write-Data RF sensor status information (MsgID=98): 0 0 0 0
22:40:10.930125 Error 03
22:40:11.844575 T10620000 Write-Data RF sensor status information (MsgID=98): 0 0 0 0
22:40:11.890831 Error 03
22:40:13.011608 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:13.064212 Error 03
22:40:13.893091 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:13.941175 Error 03
22:40:14.750735 Command: VR=1
22:40:14.830366 VR: 1
22:40:14.883636 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:14.992416 Error 03
22:40:15.940179 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:40:16.006856 Error 03
22:40:16.956900 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:40:17.009155 Error 03
22:40:18.001670 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:40:18.067062 Error 03
22:40:18.892194 PR: I=11
22:40:19.008864 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:40:19.058004 Error 03
22:40:20.025449 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:40:20.122768 Error 03
22:40:21.057462 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:40:21.106990 Error 03
22:40:22.076123 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
22:40:22.172351 Error 03
22:40:23.094012 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
22:40:23.191937 Error 03
22:40:24.123067 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
22:40:24.176482 Error 03
22:40:25.160310 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:25.205936 Error 03
22:40:26.177924 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:26.226017 Error 03
22:40:27.203713 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:27.269587 Error 03
22:40:28.222234 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:40:28.324660 Error 03
22:40:28.908873 PR: I=11
22:40:29.244506 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:40:29.357878 Error 03
22:40:30.277980 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:40:30.330262 Error 03
22:40:31.293482 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:40:31.408370 Error 03
22:40:32.324770 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:40:32.337806 Command: VR=2
22:40:32.411107 VR: 2
22:40:32.414728 Error 03
22:40:33.347034 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:40:33.396465 Error 03
22:40:34.376571 T90110000 Write-Data Relative modulation level (MsgID=17): 0.00
22:40:34.435596 Error 03
22:40:35.398464 T90110000 Write-Data Relative modulation level (MsgID=17): 0.00
22:40:35.444183 Error 03
22:40:36.421512 T90110000 Write-Data Relative modulation level (MsgID=17): 0.00
22:40:36.486064 Error 03
22:40:37.444390 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:37.494946 Error 03
22:40:38.467129 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:38.537801 B555D7F55 Write-Ack Message ID 93 (MsgID=93): 32597
22:40:38.961338 PR: I=11
22:40:39.494516 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:40.526170 Error 03
22:40:41.538268 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:40:41.604602 Error 03
22:40:42.560386 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:40:42.612690 Error 03
22:40:43.596083 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:40:43.649497 Error 04
22:40:43.696743 E55555755
22:40:44.612438 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:40:45.644856 Error 03
22:40:46.661914 T00030000 Read-Data Slave configuration (MsgID=3): 00000000 0
22:40:46.760386 Error 03
22:40:47.678115 T00030000 Read-Data Slave configuration (MsgID=3): 00000000 0
22:40:47.794284 Error 03
22:40:48.711558 T00030000 Read-Data Slave configuration (MsgID=3): 00000000 0
22:40:48.760784 Error 03
22:40:48.994923 PR: I=11
22:40:49.134726 Command: VR=3
22:40:49.193597 VR: 3
22:40:49.725017 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:49.829168 Error 03
22:40:50.761921 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:50.810085 Error 03
22:40:51.778396 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:40:51.876858 Error 03
22:40:52.810716 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:40:52.910005 Error 03
22:40:53.835487 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:40:53.898918 Error 03
22:40:54.860187 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:40:54.913597 Error 03
22:40:55.887840 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:40:55.943720 Error 03
22:40:56.898311 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:40:57.008836 Error 04
22:40:57.014661 E55555755
22:40:57.925725 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:40:58.959012 Error 03
22:40:59.009815 PR: I=11
22:40:59.984601 T00060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
22:41:00.039580 Error 03
22:41:00.996742 T00060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
22:41:01.093716 Error 03
22:41:01.100486 SC: 22:41/3
22:41:02.025946 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:02.078918 Error 03
22:41:03.189857 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:03.243867 Error 03
22:41:04.078306 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:04.128813 Error 03
22:41:04.974659 Command: VR=4
22:41:05.046992 VR: 4
22:41:05.094645 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:05.195654 Error 03
22:41:06.262048 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:06.311148 Error 03
22:41:07.145431 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:07.195675 Error 03
22:41:08.181222 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:08.230162 Error 03
22:41:09.045829 PR: I=11
22:41:09.196026 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:09.246425 Error 03
22:41:10.213206 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:10.312568 Error 03
22:41:11.246018 T10393700 Write-Data Max CH water setpoint (MsgID=57): 55.00
22:41:11.495437 Error 03
22:41:12.263192 T10393700 Write-Data Max CH water setpoint (MsgID=57): 55.00
22:41:12.575896 Error 03
22:41:13.303164 T10393700 Write-Data Max CH water setpoint (MsgID=57): 55.00
22:41:13.663319 Error 03
22:41:14.311138 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:14.420755 Error 03
22:41:15.345175 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:15.399861 Error 03
22:41:16.363531 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:16.424950 Error 03
22:41:17.400200 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:17.444376 Error 03
22:41:18.420787 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:18.487339 Error 03
22:41:19.083249 PR: I=11
22:41:19.444039 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:19.494383 Error 03
22:41:20.469665 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:20.535575 Error 03
22:41:21.481955 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:21.577491 Error 03
22:41:22.531895 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:22.580143 Error 03
22:41:23.536555 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:23.590976 Error 03
22:41:24.694946 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:24.745703 Error 03
22:41:25.246845 Command: VR=5
22:41:25.331864 VR: 5
22:41:25.586467 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:25.650948 Error 03
22:41:26.743023 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:26.796463 Error 03
22:41:27.632178 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:27.690211 Error 03
22:41:28.667257 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:28.719132 Error 03
22:41:29.112284 PR: I=11
22:41:29.684525 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:29.736176 Error 03
22:41:30.698332 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:30.795748 Error 03
22:41:31.729880 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:31.779516 Error 03
22:41:32.765512 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:32.819137 Error 03
22:41:33.781647 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:33.838738 Error 03
22:41:34.804745 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:34.868648 Error 03
22:41:35.831238 T90101600 Write-Data Room setpoint (MsgID=16): 22.00
22:41:35.881937 Error 03
22:41:36.847544 T90101600 Write-Data Room setpoint (MsgID=16): 22.00
22:41:36.947631 Error 03
22:41:37.882942 T90101600 Write-Data Room setpoint (MsgID=16): 22.00
22:41:37.929176 Error 03
22:41:38.896210 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:38.959771 Error 03
22:41:39.152601 PR: I=11
22:41:39.930833 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:39.981055 Error 03
22:41:40.955043 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:41.026501 Error 03
22:41:41.506746 Command: VR=6
22:41:41.581691 VR: 6
22:41:41.966227 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:42.065865 Error 03
22:41:43.002279 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:43.068185 Error 04
22:41:43.072181 ED5555F55
22:41:44.017450 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:45.175734 Error 03
22:41:46.065718 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:46.129811 Error 03
22:41:47.100769 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:47.150207 Error 03
22:41:48.116143 T10181600 Write-Data Room temperature (MsgID=24): 22.00
22:41:48.215078 Error 03
22:41:49.150657 T10181600 Write-Data Room temperature (MsgID=24): 22.00
22:41:49.196968 PR: I=11
22:41:49.199623 Error 03
22:41:50.164710 T10181600 Write-Data Room temperature (MsgID=24): 22.00
22:41:50.215774 Error 03
22:41:51.183901 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:51.281804 Error 03
22:41:52.216077 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:52.263433 Error 03
22:41:53.238138 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:41:53.302554 Error 03
22:41:54.263334 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:54.314000 Error 03
22:41:55.281182 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:55.333385 Error 03
22:41:56.316144 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:41:56.367894 Error 03
22:41:57.333937 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:41:57.447000 Error 03
22:42:02.557770 Error 03
22:42:03.481283 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:42:03.532885 Error 03
22:42:04.498180 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:42:04.596858 Error 03
22:42:05.520735 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:42:05.611839 Error 03
22:42:05.898642 Command: VR=6
22:42:05.965453 VR: 6
22:42:06.665391 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:06.714852 Error 03
22:42:07.574774 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:07.639307 Error 03
22:42:08.600643 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:08.697841 Error 03
22:42:09.298757 PR: I=11
22:42:09.618879 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:42:09.713016 Error 03
22:42:10.650303 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:42:10.699321 Error 03
22:42:11.664612 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:42:11.763368 Error 03
22:42:12.825657 T900E6400 Write-Data Maximum relative modulation level (MsgID=14): 100.00
22:42:12.883716 Error 03
22:42:13.715406 T900E6400 Write-Data Maximum relative modulation level (MsgID=14): 100.00
22:42:14.748707 Error 03
22:42:15.770376 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:42:15.836093 Error 03
22:42:16.783441 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:42:16.883155 Error 03
22:42:17.824210 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:42:17.890482 Error 03
22:42:18.835180 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:18.933643 Error 03
22:42:19.335136 PR: I=11
22:42:19.863792 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:19.919338 Error 03
22:42:20.698861 Command: VR=7
22:42:20.766120 VR: 7
22:42:20.884653 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:20.951549 Error 03
22:42:21.913670 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:42:21.972502 Error 03
22:42:22.934487 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:42:23.033435 Error 03
22:42:23.976363 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:42:24.040233 Error 03
22:42:24.984257 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
22:42:25.266961 Error 03
22:42:26.015676 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
22:42:26.351745 Error 03
22:42:27.041778 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
22:42:27.433827 Error 03
22:42:28.185877 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:42:28.236300 Error 03
22:42:28.298738 Command: VR=8
22:42:28.364827 VR: 8
22:42:29.209197 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:42:29.267774 Error 03
22:42:29.315904 PR: I=11
22:42:30.116733 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:42:30.165189 Error 03
22:42:31.135926 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:31.234898 Error 03
22:42:32.158428 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:32.223876 Error 03
22:42:33.188093 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:33.239782 Error 03
22:42:34.202039 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:42:34.298888 Error 03
22:42:35.235384 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:42:35.285699 Error 03
22:42:36.268946 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:42:36.317167 Error 03
22:42:37.285451 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
22:42:37.335786 Error 03
22:42:37.690817 Command: VR=9
22:42:37.750054 VR: 9
22:42:38.310457 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
22:42:38.372926 B75575555 Unk-DataId Nominal ventilation value (MsgID=87): 85
22:42:39.336390 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
22:42:39.384010 PR: I=11
22:42:40.360547 Error 03
22:42:41.498118 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:42:41.549741 Error 03
22:42:42.411156 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:42:42.469151 Error 03
22:42:43.436981 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:43.484261 Error 03
22:42:44.453324 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:44.506669 Error 03
22:42:45.466932 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:45.572817 Error 03
22:42:46.500260 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:42:46.600299 Error 03
22:42:47.515361 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:42:47.615952 Error 03
22:42:48.666613 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:42:48.717486 Error 03
22:42:49.455615 PR: I=11
22:42:49.572889 T00300000 Read-Data DHW setpoint boundaries (MsgID=48): 0 0
22:42:49.925453 Error 03
22:42:50.601971 T00300000 Read-Data DHW setpoint boundaries (MsgID=48): 0 0
22:42:51.006941 Error 03
22:42:51.622007 T00300000 Read-Data DHW setpoint boundaries (MsgID=48): 0 0
22:42:51.904711 Error 03
22:42:52.653497 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:42:52.700033 Error 03
22:42:53.676656 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:42:53.748206 Error 03
22:42:54.499017 Command: VR=0
22:42:54.569716 VR: 0
22:42:54.704487 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:42:54.756080 Error 03
22:42:55.718364 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:55.814706 Error 03
22:42:56.736150 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:56.835555 Error 03
22:42:57.767810 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:42:57.818902 Error 03
22:42:58.786823 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:42:58.885635 Error 03
22:42:59.486287 PR: I=11
22:42:59.806644 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:42:59.901553 Error 03
22:43:00.837412 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:43:00.930371 Error 03
22:43:01.136738 SC: 22:43/3
22:43:01.862491 T80730000 Read-Data OEM diagnostic code (MsgID=115): 0
22:43:01.917153 Error 03
22:43:02.891853 T80730000 Read-Data OEM diagnostic code (MsgID=115): 0
22:43:02.938188 Error 03
22:43:03.917066 T80730000 Read-Data OEM diagnostic code (MsgID=115): 0
22:43:03.974144 Error 03
22:43:04.938671 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:43:04.986986 Error 03
22:43:05.960254 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:43:06.029037 Error 03
22:43:06.989594 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:43:07.040363 Error 03
22:43:07.498722 Command: VR=5
22:43:07.567552 VR: 5
22:43:08.002666 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:43:08.101986 Error 03
22:43:09.037653 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:43:09.086141 Error 03
22:43:09.518944 PR: I=11
22:43:10.060420 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:43:10.110330 Error 03
22:43:11.087781 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:43:11.135532 Error 03
22:43:12.105116 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:43:12.201709 Error 03
22:43:12.874837 Command: GW=0
22:43:12.941236 GW: 0
22:43:13.143434 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:43:13.188886 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
22:43:14.137760 Error FF
22:43:14.150515 T000F0000 Read-Data Boiler capacity and modulation limits (MsgID=15): 0 0
22:43:14.186102 BF00F0000 Unk-DataId Boiler capacity and modulation limits (MsgID=15): 0 0
22:43:14.338835 Command: GW=1
22:43:14.402138 GW: 1
22:43:15.168336 T000F0000 Read-Data Boiler capacity and modulation limits (MsgID=15): 0 0
22:43:15.267033 Error 03
22:43:16.189859 T000F0000 Read-Data Boiler capacity and modulation limits (MsgID=15): 0 0
22:43:16.286928 Error 03
22:43:17.220426 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:43:17.317203 B555D7F55 Write-Ack Message ID 93 (MsgID=93): 32597
22:43:18.253494 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:43:19.269432 Error 03
22:43:19.562291 PR: I=11
22:43:20.304121 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:43:20.353521 Error 03
22:43:21.320486 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:43:21.368695 Error 03
22:43:22.347756 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:43:22.424051 Error 03
22:43:23.373523 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:43:23.422458 Error 03
22:43:24.389073 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:43:24.444527 Error 03
22:43:25.419884 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:43:25.470689 Error 03
22:43:26.445303 T10620000 Write-Data RF sensor status information (MsgID=98): 0 0 0 0
22:43:26.520236 Error 03
22:43:27.470980 T10620000 Write-Data RF sensor status information (MsgID=98): 0 0 0 0
22:43:27.519521 Error 03
22:43:28.498892 T10620000 Write-Data RF sensor status information (MsgID=98): 0 0 0 0
22:43:28.565276 Error 03
22:43:29.524479 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:43:29.575082 PR: I=11
22:43:29.577811 Error 03
22:43:30.539401 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:43:30.587719 Error 03
22:43:31.555613 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:43:31.653364 Error 03
22:43:32.702285 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:43:32.756719 Error 03
22:43:33.606018 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:43:33.702883 Error 03
22:43:33.810953 Command: GW=R
22:43:35.104957 OpenTherm Gateway 6.4
22:43:35.676308 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:43:35.723371 Error 03
22:43:36.672850 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:43:36.770018 Error 03
22:43:37.706826 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:43:37.803722 Error 03
22:43:38.723670 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
22:43:38.818393 Error 03
22:43:39.621716 PR: I=11
22:43:39.756582 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
22:43:39.807712 Error 03
22:43:40.771404 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
22:43:40.873161 Error 03
22:43:42.019522 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:43:42.071269 B555D7F55 Write-Ack Message ID 93 (MsgID=93): 32597
22:43:42.830101 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
22:43:43.844848 Error 03
22:43:44.893389 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:43:44.949964 Error 03
22:43:45.890008 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:43:45.989413 Error 03
22:43:46.923377 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
22:43:47.018181 Error 03
22:43:47.964977 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:43:48.023896 Error 03
22:43:48.970518 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
22:43:49.020500 Error 04
22:43:49.070470 E55555755
22:43:49.656649 PR: I=11
22:43:50.001802 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
Code: Select all
Opentherm gateway diagnostics - Version 2.1
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 5
Power supply: 3.292
Reference: 1.472
Thermostat: 0.697, 2.108
Boiler: 0.000, 2.626
Reference voltage setting (0..9) [4]: 5
Opentherm gateway diagnostics - Version 2.1
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 2
496,1039,496,527,497,526,1009,1038,497,527,496,527,496,527,496,527,497,526,497,527,496,527,497,526,497,527,496,527,1008,1039,496,527,1008,527,496,1039,1008,1039,1008,1038,497,527,496,527,496,527,497,526,497,527,496,527,497,527,1008.
10013500 Write-Data Control setpoint (MsgID=1): 53.00
497,1038,497,526,497,527,1008,1038,497,527,496,527,497,526,497,527,496,527,497,526,497,527,496,527,497,526,497,527,1008,1039,496,527,1008,527,497,1038,1008,1039,1008,1038,497,526,497,527,496,527,497,527,496,527,497,526,498,526,1008.
10013500 Write-Data Control setpoint (MsgID=1): 53.00
497,1038,497,526,497,527,497,526,497,527,496,527,497,527,496,527,496,527,497,527,496,527,497,526,497,527,496,527,497,526,497,527,496,527,497,526,497,527,496,527,497,526,497,527,1008,527,497,1038,497,527,497,526,497,527,496,527,497,526,497,527,496,527,1009.
00000300 Read-Data Status (MsgID=0): 00000011 00000000
Opentherm gateway diagnostics - Version 2.1
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 3
24,1511,24,999,24,1512,24,1511,24,999,24,1000,24,999,24,1000,24,999,24,1512,24,1511,24,999,24,1512,24,2023,24,999,24,1512,24,1511,24,1511,24,1000,24,999,24,999,24,1000,24,1000,24,999,24,999,24,1000,24,1512,24,21907,507,945,979,468,483,479,493,946,491,480,482,471,492,477,484,471,491,477,485,471,974,950,492,474,487,471,972,952,981,466,484,957,490,471,969,955,491,470,492,471,491,471,491,471,491,471,491,471,491,471,491,471,491,471,968.
Error 01
24,998,24,1512,24,999,24,1000,24,999,24,1000,24,999,24,1000,24,999,24,1000,24,1512,24,999,24,1512,24,1511,24,1511,24,1000,24,1000,24,999,24,1000,24,999,24,1000,24,1000,24,999,24,1000,24,1000,24,999,24,1000,24,1000,24,999,24,1512,24,21902,506,498,485,488,494,976,502,494,488,481,501,481,501,483,526,454,502,480,502,481,507,475,989,489,493,986,491,481,989,975,516,467,988,500,483,975,989,975,502,497,485,481,501,481,502,480,513,470,501,481,501,481,502,495,487,480,989.
Error 01
24,1511,24,999,24,1512,24,1511,24,999,24,1000,24,1000,24,999,24,1000,24,999,24,1000,24,999,24,1000,24,1512,24,1512,24,1510,24,999,24,2023,24,2023,24,1511,24,999,24,1000,24,999,24,1000,24,999,24,1000,24,1512,24,21895,506,489,494,488,494,975,989,975,502,489,493,481,501,481,502,480,514,468,502,480,502,481,502,506,475,481,501,481,995,969,502,480,989,498,484,976,988,990,974,976,501,483,499,481,502,480,501,481,518,464,502,480,502,480,999.
Error 01
Opentherm gateway diagnostics - Version 2.1
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 6
T: 936.099
B: 22.421
T: 936.233
B: 22.436
T: 936.417
B: 22.428
T: 1007.713
B: 22.428
T: 935.723
B: 22.425
Opentherm gateway diagnostics - Version 2.1
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 4
OK1A high-to-low: 10.50us
OK1A low-to-high: 34.75us
OK1B high-to-low: 13.25us
OK1B low-to-high: 4.50us
Regards,
George