2. control heating circuit (C2 ) setpoint2 via Home Assistant.

Post by Thision9 »

Hello,


can anyone here give me a tip on how to control the 2nd heating circuit in Home Assistant?

I can use the OTMonitor to change the flow temperature using the “ C2= ” command.
But the service is not made available to me in Home Assistant.

Attached are pictures of the services that can be called up.
I can also retrieve data via MQTT.

Auszug von der Logging:

Code: Select all

15:49:09.348914  T807F0000  Read-Data   Slave product version: 0 0
15:49:09.675630  B407F6401  Read-Ack    Slave product version: 100 1
15:49:10.352055  T80000200  Read-Data   Status: 00000010 00000000
15:49:10.674293  B40000200  Read-Ack    Status: 00000010 00000000
15:49:11.345072  T90010800  Write-Data  Control setpoint: 8.00
15:49:11.676570  B50010800  Write-Ack   Control setpoint: 8.00
15:49:12.094502  PR: I=11
15:49:12.345449  T90080800  Write-Data  Control setpoint 2: 8.00
15:49:12.673864  B50080800  Write-Ack   Control setpoint 2: 8.00
15:49:13.341245  T90383200  Write-Data  DHW setpoint: 50.00
15:49:13.674118  B50383200  Write-Ack   DHW setpoint: 50.00
15:49:14.338394  T80200000  Read-Data   DHW2 temperature: 0.00
15:49:14.666083  BE0200000  Data-Inv    DHW2 temperature: 0.00
15:49:15.337464  T801A0000  Read-Data   DHW temperature: 0.00
15:49:15.667225  BC01A3418  Read-Ack    DHW temperature: 52.09
15:49:16.339303  T80000200  Read-Data   Status: 00000010 00000000
15:49:16.667722  B40000200  Read-Ack    Status: 00000010 00000000
15:49:17.333598  T001B0000  Read-Data   Outside temperature: 0.00
15:49:17.659806  BC01B15F8  Read-Ack    Outside temperature: 21.97
15:49:18.331160  T80190000  Read-Data   Boiler water temperature: 0.00
15:49:18.658366  BC0191600  Read-Ack    Boiler water temperature: 22.00
15:49:19.328740  T801C0000  Read-Data   Return water temperature: 0.00
15:49:19.661046  BC01C15B4  Read-Ack    Return water temperature: 21.70
15:49:20.336521  T801F0000  Read-Data   Flow temperature CH2: 0.00
15:49:20.655164  B401F16C8  Read-Ack    Flow temperature CH2: 22.78
15:49:21.324878  T00110000  Read-Data   Relative modulation level: 0.00
15:49:21.655416  BC0110000  Read-Ack    Relative modulation level: 0.00
15:49:22.127305  PR: I=11
15:49:22.327334  T80000200  Read-Data   Status: 00000010 00000000
15:49:22.655901  B40000200  Read-Ack    Status: 00000010 00000000
15:49:23.321012  T80130000  Read-Data   DHW flow rate: 0.00
15:49:23.647203  B70130000  Unk-DataId  DHW flow rate: 0.00
15:49:24.319390  T001D0000  Read-Data   Solar storage temperature: 0.00
15:49:24.645814  BF01D0000  Unk-DataId  Solar storage temperature: 0.00
15:49:25.321902  T001E0000  Read-Data   Solar collector temperature: 0.00
15:49:25.670506  BF01E0000  Unk-DataId  Solar collector temperature: 0.00
15:49:26.314749  T00210000  Read-Data   Exhaust temperature: 0
15:49:26.643047  BC0210021  Read-Ack    Exhaust temperature: 33
15:49:27.312072  T9081100E  Write-Data  Message ID 129: 4110
15:49:27.639545  B5081100E  Write-Ack   Message ID 129: 4110
15:49:28.316329  T80000200  Read-Data   Status: 00000010 00000000
15:49:28.636782  B40000200  Read-Ack    Status: 00000010 00000000
15:49:29.309902  T90100400  Write-Data  Room setpoint: 4.00
15:49:29.639500  B50100400  Write-Ack   Room setpoint: 4.00
15:49:30.259206  T10170400  Write-Data  Room Setpoint CH2: 4.00
15:49:30.633663  BD0170400  Write-Ack   Room Setpoint CH2: 4.00
15:49:31.253628  T90181938  Write-Data  Room temperature: 25.22
15:49:31.634838  B50181938  Write-Ack   Room temperature: 25.22
15:49:32.160012  PR: I=11
15:49:32.253326  T80800000  Read-Data   Message ID 128: 0
15:49:32.629320  BE0800000  Data-Inv    Message ID 128: 0
15:49:33.249692  T90821D41  Write-Data  Message ID 130: 7489
15:49:33.629878  B50821D41  Write-Ack   Message ID 130: 7489
15:49:34.247551  T80000200  Read-Data   Status: 00000010 00000000
15:49:34.630621  B40000200  Read-Ack    Status: 00000010 00000000
15:49:35.245919  T90010800  Write-Data  Control setpoint: 8.00
15:49:35.624746  B50010800  Write-Ack   Control setpoint: 8.00
15:49:36.242958  T90080800  Write-Data  Control setpoint 2: 8.00
15:49:36.627012  B50080800  Write-Ack   Control setpoint 2: 8.00
15:49:37.246147  T90383200  Write-Data  DHW setpoint: 50.00
15:49:37.619038  B50383200  Write-Ack   DHW setpoint: 50.00
15:49:38.240678  T80200000  Read-Data   DHW2 temperature: 0.00
15:49:38.616306  BE0200000  Data-Inv    DHW2 temperature: 0.00
15:49:39.242880  T801A0000  Read-Data   DHW temperature: 0.00
15:49:39.614499  BC01A3400  Read-Ack    DHW temperature: 52.00
15:49:40.235758  T80000200  Read-Data   Status: 00000010 00000000
15:49:40.617596  B40000200  Read-Ack    Status: 00000010 00000000
15:49:41.232785  T001B0000  Read-Data   Outside temperature: 0.00
15:49:41.652042  BC01B15F8  Read-Ack    Outside temperature: 21.97
15:49:42.189851  PR: I=11
15:49:42.230863  T80190000  Read-Data   Boiler water temperature: 0.00
15:49:42.611507  BC0191600  Read-Ack    Boiler water temperature: 22.00
15:49:43.257728  T801C0000  Read-Data   Return water temperature: 0.00
15:49:43.633190  BC01C15B4  Read-Ack    Return water temperature: 21.70
15:49:44.230588  T801F0000  Read-Data   Flow temperature CH2: 0.00
15:49:44.602995  BC01F16AC  Read-Ack    Flow temperature CH2: 22.67
15:49:45.231645  T00110000  Read-Data   Relative modulation level: 0.00
15:49:45.605900  BC0110000  Read-Ack    Relative modulation level: 0.00
15:49:46.255662  T80000200  Read-Data   Status: 00000010 00000000
15:49:46.619931  B40000200  Read-Ack    Status: 00000010 00000000
15:49:47.220316  T80130000  Read-Data   DHW flow rate: 0.00
15:49:47.609972  B70130000  Unk-DataId  DHW flow rate: 0.00
15:49:48.223290  T001D0000  Read-Data   Solar storage temperature: 0.00
15:49:48.618683  BF01D0000  Unk-DataId  Solar storage temperature: 0.00
15:49:49.217967  T001E0000  Read-Data   Solar collector temperature: 0.00
15:49:49.594118  BF01E0000  Unk-DataId  Solar collector temperature: 0.00
15:49:50.220133  T00210000  Read-Data   Exhaust temperature: 0
15:49:50.591676  BC0210021  Read-Ack    Exhaust temperature: 33
15:49:51.213251  T9081100E  Write-Data  Message ID 129: 4110
15:49:51.590199  B5081100E  Write-Ack   Message ID 129: 4110
15:49:52.220679  T80000200  Read-Data   Status: 00000010 00000000
15:49:52.224864  PR: I=11
15:49:52.589634  B40000200  Read-Ack    Status: 00000010 00000000
15:49:53.208457  T90100400  Write-Data  Room setpoint: 4.00
15:49:53.585329  B50100400  Write-Ack   Room setpoint: 4.00
15:49:54.209324  T10170400  Write-Data  Room Setpoint CH2: 4.00
15:49:54.583955  BD0170400  Write-Ack   Room Setpoint CH2: 4.00
15:49:55.204262  T90181938  Write-Data  Room temperature: 25.22
15:49:55.581477  B50181938  Write-Ack   Room temperature: 25.22
15:49:56.203438  T80800000  Read-Data   Message ID 128: 0
15:49:56.579472  BE0800000  Data-Inv    Message ID 128: 0
15:49:57.204047  T90821D41  Write-Data  Message ID 130: 7489
15:49:57.577580  B50821D41  Write-Ack   Message ID 130: 7489
15:49:58.197238  T90020004  Write-Data  Master configuration: 00000000 4
15:49:58.578598  B50020004  Write-Ack   Master configuration: 00000000 4
15:49:59.199495  T80000200  Read-Data   Status: 00000010 00000000
15:49:59.573825  B40000200  Read-Ack    Status: 00000010 00000000
15:50:00.193189  T90010800  Write-Data  Control setpoint: 8.00
15:50:00.574492  B50010800  Write-Ack   Control setpoint: 8.00
15:50:01.191252  T90080800  Write-Data  Control setpoint 2: 8.00
15:50:01.574849  B50080800  Write-Ack   Control setpoint 2: 8.00
15:50:02.193754  T90383200  Write-Data  DHW setpoint: 50.00
15:50:02.250690  PR: I=11
15:50:02.566018  B50383200  Write-Ack   DHW setpoint: 50.00
15:50:03.187404  T80200000  Read-Data   DHW2 temperature: 0.00
15:50:03.564068  BE0200000  Data-Inv    DHW2 temperature: 0.00
15:50:04.229925  T801A0000  Read-Data   DHW temperature: 0.00
15:50:04.563328  BC01A3400  Read-Ack    DHW temperature: 52.00
15:50:05.183609  T80000200  Read-Data   Status: 00000010 00000000
15:50:05.564570  B40000200  Read-Ack    Status: 00000010 00000000
15:50:06.180605  T001B0000  Read-Data   Outside temperature: 0.00
15:50:06.557852  BC01B15DC  Read-Ack    Outside temperature: 21.86
15:50:07.178146  T80190000  Read-Data   Boiler water temperature: 0.00
15:50:07.559229  BC0191600  Read-Ack    Boiler water temperature: 22.00
15:50:08.178338  T801C0000  Read-Data   Return water temperature: 0.00
15:50:08.554448  BC01C15B4  Read-Ack    Return water temperature: 21.70
15:50:09.174634  T801F0000  Read-Data   Flow temperature CH2: 0.00
15:50:09.554697  BC01F169C  Read-Ack    Flow temperature CH2: 22.61
15:50:10.173395  T00110000  Read-Data   Relative modulation level: 0.00
15:50:10.550578  BC0110000  Read-Ack    Relative modulation level: 0.00
15:50:11.170696  T80000200  Read-Data   Status: 00000010 00000000
15:50:11.548297  B40000200  Read-Ack    Status: 00000010 00000000
15:50:12.122467  T80130000  Read-Data   DHW flow rate: 0.00
15:50:12.289546  PR: I=11
15:50:12.413036  B70130000  Unk-DataId  DHW flow rate: 0.00
Attachments
MQTT Opentherm.jpg
MQTT Opentherm.jpg (76.75 KiB) Viewed 598 times
Screenshot 2024-06-03 155003.jpg
Screenshot 2024-06-03 155003.jpg (66.95 KiB) Viewed 598 times
Screenshot 2024-06-03 155412.jpg
Screenshot 2024-06-03 155412.jpg (64.91 KiB) Viewed 598 times
Screenshot 2024-06-03 155348.jpg
Screenshot 2024-06-03 155348.jpg (56.44 KiB) Viewed 598 times
Post Reply

Return to “Opentherm Gateway Forum”