This new thermostat sometimes jumps to it's maximum setpoint of 35 °C. (If I lower the maximum temperature on the thermostat to 32 °C for example, then that will be what it jumps to.)
I have determined that this happens after a reset of the PIC. I could trigger the behaviour when pulling the reset line low for 500ms while having a laptop connected to the serial lines. Therefore I can pretty much rule out it being triggered by an invalid command being sent or some other crash.
My setup is a V2 gateway from NodoShop (bought in 2017, revision 0.9.9.3), and I normally have it connected via a NodeMCU running custom firmware. The PIC is a P16F1847 running OpenTherm Gateway 6.5.
When running the thermostat without OTGW, it runs fine. I have even already replaced the thermostat thinking it was faulty, but that did not made any difference.
Below is a log I captured using otmonitor, with some data before the reset and after the setpoint:
Code: Select all
09:56:35.477828 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:56:35.652836 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:56:36.475827 T00390000 Read-Data Max CH water setpoint (MsgID=57): 0.00
09:56:36.500914 R00780000 Read-Data Burner operation hours (MsgID=120): 0
09:56:36.652813 B40783481 Read-Ack Burner operation hours (MsgID=120): 13441
09:56:36.676253 AC0395A00 Read-Ack Max CH water setpoint (MsgID=57): 90.00
09:56:37.473821 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:56:37.663824 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:56:38.471842 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:56:38.668848 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:56:39.469853 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:56:39.667842 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:56:40.468065 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:56:40.578852 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:56:41.465850 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
09:56:41.583846 B601B0000 Data-Inv Outside temperature (MsgID=27): 0.00
09:56:42.463851 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:56:42.583854 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:56:43.461863 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:56:43.593868 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:56:46.498924 OpenTherm Gateway 6.5
09:56:46.523602 Error 03
09:56:47.401920 T1002010D Write-Data Master configuration (MsgID=2): 00000001 13
09:56:47.514910 B7002010D Unk-DataId Master configuration (MsgID=2): 00000001 13
09:56:47.538841 AD002010D Write-Ack Master configuration (MsgID=2): 00000001 13
09:56:47.590901 High power
09:56:48.400927 T807F0000 Read-Data Slave product version (MsgID=127): 0 0
09:56:48.520935 B707F0000 Unk-DataId Slave product version (MsgID=127): 0 0
09:56:48.595125 Low power
09:56:48.658125 Medium power
09:56:49.398934 T907E010B Write-Data Master product version (MsgID=126): 1 11
09:56:49.525928 BF07E010B Unk-DataId Master product version (MsgID=126): 1 11
09:56:50.397150 T00060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
09:56:50.525955 BF0060000 Unk-DataId Remote parameter flags (MsgID=6): 00000000 00000000
09:56:50.547600 AC0060300 Read-Ack Remote parameter flags (MsgID=6): 00000011 00000000
09:56:51.394956 T00300000 Read-Data DHW setpoint boundaries (MsgID=48): 0 0
09:56:51.537137 BF0300000 Unk-DataId DHW setpoint boundaries (MsgID=48): 0 0
09:56:52.393169 T80310000 Read-Data Max CH setpoint boundaries (MsgID=49): 0 0
09:56:52.540997 B70310000 Unk-DataId Max CH setpoint boundaries (MsgID=49): 0 0
09:56:53.391029 T80380000 Read-Data DHW setpoint (MsgID=56): 0.00
09:56:53.542996 B70380000 Unk-DataId DHW setpoint (MsgID=56): 0.00
09:56:53.564985 A40385000 Read-Ack DHW setpoint (MsgID=56): 80.00
09:56:54.388992 T00390000 Read-Data Max CH water setpoint (MsgID=57): 0.00
09:56:54.552999 BF0390000 Unk-DataId Max CH water setpoint (MsgID=57): 0.00
09:56:54.576613 AC0395A00 Read-Ack Max CH water setpoint (MsgID=57): 90.00
09:56:55.386963 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
09:56:55.556969 B601B0000 Data-Inv Outside temperature (MsgID=27): 0.00
09:56:56.385006 T000A0000 Read-Data Number of TSPs (MsgID=10): 0
09:56:56.557996 BF00A0000 Unk-DataId Number of TSPs (MsgID=10): 0
09:56:57.384022 T000C0000 Read-Data Size of fault buffer (MsgID=12): 0
09:56:57.568021 BF00C0000 Unk-DataId Size of fault buffer (MsgID=12): 0
09:56:58.382022 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:56:58.573041 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:56:59.380033 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:56:59.572231 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:57:00.378052 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:57:00.484028 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:57:01.376066 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:57:01.489209 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:57:02.374253 T00050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
09:57:02.487088 BC00500FF Read-Ack Application-specific flags (MsgID=5): 00000000 255
09:57:03.372279 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:57:03.500079 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:57:04.370112 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:57:04.505102 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:57:05.369092 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:57:05.504274 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:57:06.367097 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:57:06.515204 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:57:07.364304 T00090000 Read-Data Remote override room setpoint (MsgID=9): 0.00
09:57:07.521284 BF0090000 Unk-DataId Remote override room setpoint (MsgID=9): 0.00
09:57:07.546487 AC0090000 Read-Ack Remote override room setpoint (MsgID=9): 0.00
09:57:08.363323 T00090000 Read-Data Remote override room setpoint (MsgID=9): 0.00
09:57:08.519327 BF0090000 Unk-DataId Remote override room setpoint (MsgID=9): 0.00
09:57:08.544269 AC0090000 Read-Ack Remote override room setpoint (MsgID=9): 0.00
09:57:09.361163 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:57:09.531144 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:57:10.359134 T00090000 Read-Data Remote override room setpoint (MsgID=9): 0.00
09:57:10.536336 BF0090000 Unk-DataId Remote override room setpoint (MsgID=9): 0.00
09:57:10.561046 AC0090000 Read-Ack Remote override room setpoint (MsgID=9): 0.00
09:57:11.357146 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:57:11.535209 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:57:12.355372 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:57:12.547308 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:57:13.353184 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:57:13.552331 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:57:14.352279 T900E6400 Write-Data Maximum relative modulation level (MsgID=14): 100.00
09:57:14.551168 BF00E6400 Unk-DataId Maximum relative modulation level (MsgID=14): 100.00
09:57:15.350389 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:57:15.462345 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:57:16.348351 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:57:16.467283 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:57:17.346396 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:57:17.466353 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:57:18.345421 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:57:18.478419 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:57:19.343235 T10101400 Write-Data Room setpoint (MsgID=16): 20.00
09:57:19.483439 B70101400 Unk-DataId Room setpoint (MsgID=16): 20.00
09:57:19.508620 AD0101400 Write-Ack Room setpoint (MsgID=16): 20.00
09:57:20.341458 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:57:20.482433 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:57:21.338481 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:57:21.493256 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:57:22.337252 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:57:22.498463 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:57:23.335286 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:57:23.504252 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:57:24.333174 T1018148C Write-Data Room temperature (MsgID=24): 20.55
09:57:24.509457 B7018148C Unk-DataId Room temperature (MsgID=24): 20.55
09:57:25.331506 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:57:25.509472 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:57:26.329471 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:57:26.520292 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:57:27.327291 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:57:27.525499 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:57:28.325345 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:57:28.527524 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:57:29.323534 T80310000 Read-Data Max CH setpoint boundaries (MsgID=49): 0 0
09:57:29.436341 B70310000 Unk-DataId Max CH setpoint boundaries (MsgID=49): 0 0
09:57:30.321512 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:57:30.441525 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:57:31.320545 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:57:31.443340 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:57:32.318354 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:57:32.452543 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:57:33.315383 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:57:33.457547 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:57:34.314549 T1002010D Write-Data Master configuration (MsgID=2): 00000001 13
09:57:34.457587 B7002010D Unk-DataId Master configuration (MsgID=2): 00000001 13
09:57:34.481344 AD002010D Write-Ack Master configuration (MsgID=2): 00000001 13
09:57:35.312420 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:57:35.467568 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:57:36.310600 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:57:36.473610 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:57:37.308598 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:57:37.471644 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:57:38.306598 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:57:38.483442 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:57:39.304603 T00030000 Read-Data Slave configuration (MsgID=3): 00000000 0
09:57:39.488430 BF0030000 Unk-DataId Slave configuration (MsgID=3): 00000000 0
09:57:40.303469 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:57:40.487427 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:57:41.301485 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:57:41.499447 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:57:42.299649 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:57:42.403440 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:57:43.297470 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:57:43.402467 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:57:44.295650 T00390000 Read-Data Max CH water setpoint (MsgID=57): 0.00
09:57:44.414661 BF0390000 Unk-DataId Max CH water setpoint (MsgID=57): 0.00
09:57:44.439148 AC0395A00 Read-Ack Max CH water setpoint (MsgID=57): 90.00
09:57:45.293493 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:57:45.419465 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:57:46.291699 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:57:46.418474 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:57:47.289687 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:57:47.430506 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:57:48.288509 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:57:48.435475 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:57:49.286729 T001B0000 Read-Data Outside temperature (MsgID=27): 0.00
09:57:49.434536 B601B0000 Data-Inv Outside temperature (MsgID=27): 0.00
09:57:50.284532 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:57:50.446746 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:57:51.282511 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:57:51.451697 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:57:52.280545 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:57:52.450528 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:57:53.279558 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:57:53.461554 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:57:54.277540 T00060000 Read-Data Remote parameter flags (MsgID=6): 00000000 00000000
09:57:54.466574 BF0060000 Unk-DataId Remote parameter flags (MsgID=6): 00000000 00000000
09:57:54.490247 AC0060300 Read-Ack Remote parameter flags (MsgID=6): 00000011 00000000
09:57:55.275571 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:57:55.466604 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:57:56.273860 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:57:56.478747 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:57:57.271596 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:57:57.382569 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:57:58.269602 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:57:58.381830 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:57:59.268832 T907E010B Write-Data Master product version (MsgID=126): 1 11
09:57:59.393616 BF07E010B Unk-DataId Master product version (MsgID=126): 1 11
09:58:00.266831 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:58:00.398626 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:58:01.264630 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:58:01.404628 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:58:02.262646 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:58:02.408666 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:58:03.260893 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:58:03.408901 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:58:04.258753 T807F0000 Read-Data Slave product version (MsgID=127): 0 0
09:58:04.419645 B707F0000 Unk-DataId Slave product version (MsgID=127): 0 0
09:58:05.257639 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:58:05.424740 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:58:06.255685 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:58:06.426665 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:58:07.253909 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:58:07.435649 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:58:08.251707 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:58:08.440696 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:58:09.250680 T80380000 Read-Data DHW setpoint (MsgID=56): 0.00
09:58:09.440689 B70380000 Unk-DataId DHW setpoint (MsgID=56): 0.00
09:58:09.463202 A40385000 Read-Ack DHW setpoint (MsgID=56): 80.00
09:58:10.248075 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:58:10.451718 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:58:11.246686 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:58:11.355739 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:58:12.244722 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:58:12.356760 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:58:13.241737 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:58:13.366752 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:58:14.240763 T00300000 Read-Data DHW setpoint boundaries (MsgID=48): 0 0
09:58:14.371733 BF0300000 Unk-DataId DHW setpoint boundaries (MsgID=48): 0 0
09:58:15.239834 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:58:15.370808 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:58:16.237763 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:58:16.696320 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:58:17.234793 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:58:17.386806 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:58:18.234004 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:58:18.386775 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:58:19.231813 T00120000 Read-Data CH water pressure (MsgID=18): 0.00
09:58:19.398807 B40120199 Read-Ack CH water pressure (MsgID=18): 1.60
09:58:20.229832 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:58:20.403838 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:58:21.228841 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:58:21.401826 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:58:22.225859 T80000200 Read-Data Status (MsgID=0): 00000010 00000000
09:58:22.413810 B40000200 Read-Ack Status (MsgID=0): 00000010 00000000
09:58:23.224866 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:58:23.418836 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:58:24.222869 T80130000 Read-Data DHW flow rate (MsgID=19): 0.00
09:58:24.418865 B70130000 Unk-DataId DHW flow rate (MsgID=19): 0.00
09:58:25.220872 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:58:25.330074 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:58:26.218858 T10010A00 Write-Data Control setpoint (MsgID=1): 10.00
09:58:26.335080 BD0010A00 Write-Ack Control setpoint (MsgID=1): 10.00
09:58:27.217889 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
09:58:27.333911 BC0000300 Read-Ack Status (MsgID=0): 00000011 00000000
09:58:28.217066 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:58:28.344909 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:58:29.214947 T801A0000 Read-Data DHW temperature (MsgID=26): 0.00
09:58:29.350131 B701A0000 Unk-DataId DHW temperature (MsgID=26): 0.00
09:58:30.214119 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:58:30.348905 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:58:31.212936 T10015A00 Write-Data Control setpoint (MsgID=1): 90.00
09:58:31.360947 BD0015A00 Write-Ack Control setpoint (MsgID=1): 90.00
09:58:32.210935 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
09:58:32.364927 B40000302 Read-Ack Status (MsgID=0): 00000011 00000010
09:58:33.208959 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
09:58:33.365938 B40000302 Read-Ack Status (MsgID=0): 00000011 00000010
09:58:34.208136 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:58:34.377966 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:58:35.207004 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
09:58:35.382961 BC000030A Read-Ack Status (MsgID=0): 00000011 00001010
09:58:36.206145 T801C0000 Read-Data Return water temperature (MsgID=28): 0.00
09:58:36.388961 B701C0000 Unk-DataId Return water temperature (MsgID=28): 0.00
09:58:37.204002 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
09:58:37.394156 BC000030A Read-Ack Status (MsgID=0): 00000011 00001010
09:58:38.203143 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:58:38.394006 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:58:39.201205 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
09:58:39.404988 BC000030A Read-Ack Status (MsgID=0): 00000011 00001010
09:58:40.200188 T10015A00 Write-Data Control setpoint (MsgID=1): 90.00
09:58:40.309195 BD0015A00 Write-Ack Control setpoint (MsgID=1): 90.00
09:58:41.199015 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
09:58:41.309044 BC000030A Read-Ack Status (MsgID=0): 00000011 00001010
09:58:42.197026 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:58:42.320040 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:58:43.196059 T000A0000 Read-Data Number of TSPs (MsgID=10): 0
09:58:43.326027 BF00A0000 Unk-DataId Number of TSPs (MsgID=10): 0
09:58:44.195040 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:58:44.327068 B40192800 Read-Ack Boiler water temperature (MsgID=25): 40.00
09:58:45.193085 T10015A00 Write-Data Control setpoint (MsgID=1): 90.00
09:58:45.337244 BD0015A00 Write-Ack Control setpoint (MsgID=1): 90.00
09:58:46.191248 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
09:58:46.341053 BC000030A Read-Ack Status (MsgID=0): 00000011 00001010
09:58:47.190275 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:58:47.341094 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:58:48.189095 T000C0000 Read-Data Size of fault buffer (MsgID=12): 0
09:58:48.352292 BF00C0000 Unk-DataId Size of fault buffer (MsgID=12): 0
09:58:49.187100 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:58:49.357314 BC0192900 Read-Ack Boiler water temperature (MsgID=25): 41.00
09:58:50.186285 T10015A00 Write-Data Control setpoint (MsgID=1): 90.00
09:58:50.355092 BD0015A00 Write-Ack Control setpoint (MsgID=1): 90.00
09:58:51.184107 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
09:58:51.368312 BC000030A Read-Ack Status (MsgID=0): 00000011 00001010
09:58:52.183351 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:58:52.373141 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:58:53.182120 T00050000 Read-Data Application-specific flags (MsgID=5): 00000000 0
09:58:53.371196 BC00500FF Read-Ack Application-specific flags (MsgID=5): 00000000 255
09:58:54.181156 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:58:54.384176 BC0192900 Read-Ack Boiler water temperature (MsgID=25): 41.00
09:58:55.179338 T10015A00 Write-Data Control setpoint (MsgID=1): 90.00
09:58:55.288170 BD0015A00 Write-Ack Control setpoint (MsgID=1): 90.00
09:58:56.178192 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
09:58:56.287214 BC000030A Read-Ack Status (MsgID=0): 00000011 00001010
09:58:57.176150 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:58:57.299358 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:58:58.175230 T00090000 Read-Data Remote override room setpoint (MsgID=9): 0.00
09:58:58.196518 R00630000 Read-Data Operating mode HC1, HC2, DHW (MsgID=99): 0 0 0 0000
09:58:58.304366 BF0630000 Unk-DataId Operating mode HC1, HC2, DHW (MsgID=99): 0 0 0 0000
09:58:58.324668 AC0090000 Read-Ack Remote override room setpoint (MsgID=9): 0.00
09:58:59.173260 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:58:59.303280 BC0192A00 Read-Ack Boiler water temperature (MsgID=25): 42.00
09:59:00.172378 T10015A00 Write-Data Control setpoint (MsgID=1): 90.00
09:59:00.315310 BD0015A00 Write-Ack Control setpoint (MsgID=1): 90.00
09:59:01.171309 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
09:59:01.320196 BC000030A Read-Ack Status (MsgID=0): 00000011 00001010
09:59:02.170371 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:59:02.319454 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:59:03.168438 T900E6400 Write-Data Maximum relative modulation level (MsgID=14): 100.00
09:59:03.331423 BF00E6400 Unk-DataId Maximum relative modulation level (MsgID=14): 100.00
09:59:04.167370 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:59:04.336459 B40192B00 Read-Ack Boiler water temperature (MsgID=25): 43.00
09:59:05.165452 T10015A00 Write-Data Control setpoint (MsgID=1): 90.00
09:59:05.335266 BD0015A00 Write-Ack Control setpoint (MsgID=1): 90.00
09:59:06.164479 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
09:59:06.347297 BC000030A Read-Ack Status (MsgID=0): 00000011 00001010
09:59:07.162503 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:59:07.352472 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:59:08.161484 T90102300 Write-Data Room setpoint (MsgID=16): 35.00
09:59:08.351518 BF0102300 Unk-DataId Room setpoint (MsgID=16): 35.00
09:59:08.373148 A50102300 Write-Ack Room setpoint (MsgID=16): 35.00
09:59:09.160467 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:59:09.363489 B40192B00 Read-Ack Boiler water temperature (MsgID=25): 43.00
09:59:10.158487 T10015A00 Write-Data Control setpoint (MsgID=1): 90.00
09:59:10.268306 BD0015A00 Write-Ack Control setpoint (MsgID=1): 90.00
09:59:11.157493 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
09:59:11.266490 BC000030A Read-Ack Status (MsgID=0): 00000011 00001010
09:59:12.155336 T00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:59:12.278539 BF0110000 Unk-DataId Relative modulation level (MsgID=17): 0.00
09:59:13.154509 T1018149E Write-Data Room temperature (MsgID=24): 20.62
09:59:13.283351 B7018149E Unk-DataId Room temperature (MsgID=24): 20.62
09:59:14.153523 T80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:59:14.290534 BC0192C00 Read-Ack Boiler water temperature (MsgID=25): 44.00
09:59:15.152539 T10015A00 Write-Data Control setpoint (MsgID=1): 90.00
09:59:15.294339 BD0015A00 Write-Ack Control setpoint (MsgID=1): 90.00
09:59:16.150366 T00000300 Read-Data Status (MsgID=0): 00000011 00000000
09:59:16.293532 BC000030A Read-Ack Status (MsgID=0): 00000011 00001010
Could you assist me with debugging?