micro lamp module with flashing problems
I have a plcbus II R2263DE One Load Lamp modules installed. Some times the lamps gone flashing.
I installed a filter (PLCBUS 4821) and thats no solution for the flashing problems.
Anyone a solution for this?
I installed a filter (PLCBUS 4821) and thats no solution for the flashing problems.
Anyone a solution for this?
micro lamp module with flashing problems
No, i dont have any solution. Sorry to say tho...
Supplier told me to buy a filter, so guess thats not a option.
Can you have a look or you also got a pattern in flashing. Here it happends at whole and halve hours.
I dont have any timmer equiped stuff that could interfear at these times.
I got 3 (hallogens) 220v spots connected to each dimmer.
Hope we can sort something out!
Supplier told me to buy a filter, so guess thats not a option.
Can you have a look or you also got a pattern in flashing. Here it happends at whole and halve hours.
I dont have any timmer equiped stuff that could interfear at these times.
I got 3 (hallogens) 220v spots connected to each dimmer.
Hope we can sort something out!
-
- Member
- Posts: 140
- Joined: Thu Jul 16, 2009 12:04 pm
- Location: Netherlands
micro lamp module with flashing problems
I can't find a pattern. But most times when the light on the street goes on i think the problem is bigger (more flashes). So i think its a problem from outside my installation.
micro lamp module with flashing problems
The problem is the PLC-BUS itself!
You can test it.
Always, when a controller checks the PLC-BUS like "Get ON ID Pulse" or sending an additional ON Command to 2263 while ON, the light is flashing.
You can test it.
Always, when a controller checks the PLC-BUS like "Get ON ID Pulse" or sending an additional ON Command to 2263 while ON, the light is flashing.
micro lamp module with flashing problems
Hello Letitbe and welcome,
Do i understand you right that the plc controller itself is causing this problem ?
I guess thats easy yo check and put the dimmer on and disconnect the controller at one of those moments.
Thanks for your sugestion.
Thanks for the sugestion
Do i understand you right that the plc controller itself is causing this problem ?
I guess thats easy yo check and put the dimmer on and disconnect the controller at one of those moments.
Thanks for your sugestion.
Thanks for the sugestion
micro lamp module with flashing problems
Hello r_255,
I found a new German Forum; here you can find information about this problem. If I understand it correct, there is a communication problem with PLCBUS II R2263D.
http://www.plc-bus.info/viewtopic.php?f=11&t=5
The German PLC-BUS shop does not sell PLCBUS II R2263D any more.
I think there is something wrong with PLCBUS II R2263D.
http://www.ruvitec.de
I found a new German Forum; here you can find information about this problem. If I understand it correct, there is a communication problem with PLCBUS II R2263D.
http://www.plc-bus.info/viewtopic.php?f=11&t=5
The German PLC-BUS shop does not sell PLCBUS II R2263D any more.
I think there is something wrong with PLCBUS II R2263D.
http://www.ruvitec.de
micro lamp module with flashing problems
<blockquote id="quote"><font size="1" face="Verdana, Arial, Helvetica" id="quote">quote:<hr height="1" noshade id="quote"><i>Originally posted by letitbe</i>
<br />Hello r_255,
I found a new German Forum; here you can find information about this problem. If I understand it correct, there is a communication problem with PLCBUS II R2263D.
http://www.plc-bus.info/viewtopic.php?f=11&t=5
The German PLC-BUS shop does not sell PLCBUS II R2263D any more.
I think there is something wrong with PLCBUS II R2263D.
http://www.ruvitec.de
<hr height="1" noshade id="quote"></font id="quote"></blockquote id="quote">
Hello letitbe ,
Can you give me the serial number on your PLCBUSII-R2263D ?
I try to check with factory for what problem on this module.
Thanks
Kevin Lo
<br />Hello r_255,
I found a new German Forum; here you can find information about this problem. If I understand it correct, there is a communication problem with PLCBUS II R2263D.
http://www.plc-bus.info/viewtopic.php?f=11&t=5
The German PLC-BUS shop does not sell PLCBUS II R2263D any more.
I think there is something wrong with PLCBUS II R2263D.
http://www.ruvitec.de
<hr height="1" noshade id="quote"></font id="quote"></blockquote id="quote">
Hello letitbe ,
Can you give me the serial number on your PLCBUSII-R2263D ?
I try to check with factory for what problem on this module.
Thanks
Kevin Lo
-
- Member
- Posts: 140
- Joined: Thu Jul 16, 2009 12:04 pm
- Location: Netherlands
micro lamp module with flashing problems
<blockquote id="quote"><font size="1" face="Verdana, Arial, Helvetica" id="quote">quote:<hr height="1" noshade id="quote"><i>Originally posted by kevinlo</i>
<br /><blockquote id="quote"><font size="1" face="Verdana, Arial, Helvetica" id="quote">quote:<hr height="1" noshade id="quote"><i>Originally posted by letitbe</i>
<br />Hello r_255,
I found a new German Forum; here you can find information about this problem. If I understand it correct, there is a communication problem with PLCBUS II R2263D.
http://www.plc-bus.info/viewtopic.php?f=11&t=5
The German PLC-BUS shop does not sell PLCBUS II R2263D any more.
I think there is something wrong with PLCBUS II R2263D.
http://www.ruvitec.de
<hr height="1" noshade id="quote"></font id="quote"></blockquote id="quote">
Hello letitbe ,
Can you give me the serial number on your PLCBUSII-R2263D ?
I try to check with factory for what problem on this module.
Thanks
Kevin Lo
<hr height="1" noshade id="quote"></font id="quote"></blockquote id="quote">
Hello, is have the same problem with this module, i can find the following numbers:
on module: P2263GF27B020
on case: 6 933211 322637
<br /><blockquote id="quote"><font size="1" face="Verdana, Arial, Helvetica" id="quote">quote:<hr height="1" noshade id="quote"><i>Originally posted by letitbe</i>
<br />Hello r_255,
I found a new German Forum; here you can find information about this problem. If I understand it correct, there is a communication problem with PLCBUS II R2263D.
http://www.plc-bus.info/viewtopic.php?f=11&t=5
The German PLC-BUS shop does not sell PLCBUS II R2263D any more.
I think there is something wrong with PLCBUS II R2263D.
http://www.ruvitec.de
<hr height="1" noshade id="quote"></font id="quote"></blockquote id="quote">
Hello letitbe ,
Can you give me the serial number on your PLCBUSII-R2263D ?
I try to check with factory for what problem on this module.
Thanks
Kevin Lo
<hr height="1" noshade id="quote"></font id="quote"></blockquote id="quote">
Hello, is have the same problem with this module, i can find the following numbers:
on module: P2263GF27B020
on case: 6 933211 322637
micro lamp module with flashing problems
What is the exact model number on the module ?
Thanks
Kevin Lo
Thanks
Kevin Lo
micro lamp module with flashing problems
OK , I got the answer from R&D.
In some situation , when the PLCBUS II - 2263D receive the command and send back the ACK feedback , the light will flash.(ON - OFF - ON within 10ms )
The problem is like this :
Controller send A1 ON (need ACK feedback)
2263 receive it , then send ACK feedback <--- at this moment , it will NOT flash
Next time Controller send A1 ON ( need ACK feedback )
2263 receive it , then send ACK feedback <--- at this time , it will flash
But if the command no need ACK feedback , like ALL ON , it will not case this problem.
The problem is depend on the powerline environment . That mean even you have problem on this 2263 , but you give this 2263 to your friend , your friend may not have this problem.
R&D explain to me is the 2263 send ACK feedback command , it activate the Triac in the dimmer module .
For the solution , you can install a Noise Absorber ( 4820 ) at the L and N of 2263.
This Noise Absorber will absorb the Noise and PLCBUS signal for make the ACK feedback signal weaker for prevent this problem.
To letitbe , if you find the problem is cause by ACK feedback . you should install a 4820 at the 2263 , not at the distribution box. Then problem should solve.
To gjniewenhuijse , you need to check the problem is cause by Outside Noise or ACK feedback.
Actually 4820 is a 5uf capacitor , you should find in locally , otherwise , leave me a message .
In some situation , when the PLCBUS II - 2263D receive the command and send back the ACK feedback , the light will flash.(ON - OFF - ON within 10ms )
The problem is like this :
Controller send A1 ON (need ACK feedback)
2263 receive it , then send ACK feedback <--- at this moment , it will NOT flash
Next time Controller send A1 ON ( need ACK feedback )
2263 receive it , then send ACK feedback <--- at this time , it will flash
But if the command no need ACK feedback , like ALL ON , it will not case this problem.
The problem is depend on the powerline environment . That mean even you have problem on this 2263 , but you give this 2263 to your friend , your friend may not have this problem.
R&D explain to me is the 2263 send ACK feedback command , it activate the Triac in the dimmer module .
For the solution , you can install a Noise Absorber ( 4820 ) at the L and N of 2263.
This Noise Absorber will absorb the Noise and PLCBUS signal for make the ACK feedback signal weaker for prevent this problem.
To letitbe , if you find the problem is cause by ACK feedback . you should install a 4820 at the 2263 , not at the distribution box. Then problem should solve.
To gjniewenhuijse , you need to check the problem is cause by Outside Noise or ACK feedback.
Actually 4820 is a 5uf capacitor , you should find in locally , otherwise , leave me a message .
-
- Member
- Posts: 140
- Joined: Thu Jul 16, 2009 12:04 pm
- Location: Netherlands
micro lamp module with flashing problems
<blockquote id="quote"><font size="1" face="Verdana, Arial, Helvetica" id="quote">quote:<hr height="1" noshade id="quote"><i>Originally posted by kevinlo</i>
<br />
To gjniewenhuijse , you need to check the problem is cause by Outside Noise or ACK feedback.
Actually 4820 is a 5uf capacitor , you should find in locally , otherwise , leave me a message .
<hr height="1" noshade id="quote"></font id="quote"></blockquote id="quote">
My problem is not the ACK feedback, but a noise generated by another device or something else.
i try to install a capacitor and let you know if it works (or not).
<br />
To gjniewenhuijse , you need to check the problem is cause by Outside Noise or ACK feedback.
Actually 4820 is a 5uf capacitor , you should find in locally , otherwise , leave me a message .
<hr height="1" noshade id="quote"></font id="quote"></blockquote id="quote">
My problem is not the ACK feedback, but a noise generated by another device or something else.
i try to install a capacitor and let you know if it works (or not).
micro lamp module with flashing problems
I get definitely flashes by ACK. Always I send command from controller I get a flash.
@ kevinlo I think there must be a bug in firmware.
I also use 2026 plug-in module. This plug-in module works fine, no flashes!
4820 is not a solution for me, it is too big.[:(] I do not have the space for 4820 near 2263!
I had problems to get 2263 behind switch. It is impossible to put 2263 together with 4820 behind wall switch! I need other solution.
@ kevinlo I think there must be a bug in firmware.
I also use 2026 plug-in module. This plug-in module works fine, no flashes!
4820 is not a solution for me, it is too big.[:(] I do not have the space for 4820 near 2263!
I had problems to get 2263 behind switch. It is impossible to put 2263 together with 4820 behind wall switch! I need other solution.
micro lamp module with flashing problems
To letitbe , just got the message from R&D , will have new firmware (ready in this week) for solve this problem.
You can ask your supplier for change the unit.
If you find difficulty , leave a message to me. I can exchange to you. ( If you don't mind to send your unit to Hong Kong )
Kevin Lo
http://www.x10-hk.com
You can ask your supplier for change the unit.
If you find difficulty , leave a message to me. I can exchange to you. ( If you don't mind to send your unit to Hong Kong )
Kevin Lo
http://www.x10-hk.com
micro lamp module with flashing problems
I disconnected my controller from the powerline when the flashing started and the flashing did not stop, so it must be generated by something else on the line.
i also got 2 plc plugin dimmer and 2 switches who work perfectly. They 2263 must be more sensitive some how for these signals. I also noticed the devices locked up while flashing and are not controllable. And like letitbe, i think most of us have problems fitting in the module incombination with the original switch. So also mounting a filter wil be impossible without breaking up walls.
please dont get me wrong but with the prices of these filters zwave can be a good replacement and solve the problem as good as any filter can do for me.
but again, thanx for the efforts of posting.
Robin
thanx for your efforts!
i also got 2 plc plugin dimmer and 2 switches who work perfectly. They 2263 must be more sensitive some how for these signals. I also noticed the devices locked up while flashing and are not controllable. And like letitbe, i think most of us have problems fitting in the module incombination with the original switch. So also mounting a filter wil be impossible without breaking up walls.
please dont get me wrong but with the prices of these filters zwave can be a good replacement and solve the problem as good as any filter can do for me.
but again, thanx for the efforts of posting.
Robin
thanx for your efforts!