Overriding temperature setpoint with OTG and iSense
Re: Overriding temperature setpoint with OTG and iSense
Digit wrote:TC works, no experience with TT yet.
I will do some tests asap.
- Remeha Calenta, Honeywell Chronotherm IV, no go.
- same boiler, with a new Chronotherm Touch Modulation (for the looks 8) ), same result.
- TC is dropped after approx. 4 minutes.
I can provide logfiles if needed.
bus147
Post by bus147 »
Digit,
perhaps you should consider building your own thermostat/controller. You've got most of the building blocks already present. You could build your own controller by using the OTG to send commands to your boiler and a JeeNode or SimpleCortex as controller. Or buy a commercial gui-less thermostat/controller, like the cenvax line from Itho or a panther from Honeywell. And use use your tablet as GUI for instance.
The only thing missing is a room temperature sensor, which is currently built-in your chronotherm. But all other components are there: you can read the outdoor temperature, you can interface with the boiler and you can program. Formulate your own heating strategy and burn it into a microcontroller. You can make another nice blog series about this project. I'm also looking into such a setup myself. Yes, you loose the nice looking thermostat but by separating the GUI from the controller you can create any interface you like on any device. (Just as in your latest blog entry) In terms risk, I think such a project is acceptable. I've got a separate set of JeeNodes and a sms gateway to monitor certain faults (loss of main power, too low room temperatures) and alert me in such a case. Your boiler could also fail and so can fuses for example. Not all faults are caused by our (own) hobby projects. If the heating fails during winter I risk frozen pipes and radiators which will cause massive damage. I've got ancient plaster ceilings so imagine what happens to that if water starts leaking onto that. Yes my own built controller could fail, but so can a lot of other things. Ever since that helicopter crashed into a electricity tower, december 2007, and I had no electricity for 4 days I think different about failure(modes). (Our town was one off the last to got power restored) Fortunately it wasn't freezing and I was at home but it was a valuable lesson.
To conclude, my proposal is is to build our own heating controller either by using the OTG or by something like the Jeenode shield Jaagpad built. And interface the heating controller via a GUI on webpage, smartphone app or on whatever you like.
Regards
Yeah, maybe I can in terms of tools available, but I don't think I will.
I can already use tablets & smart phones to set the thermostat (OK, there's a small issue to be resolved yet, see previous post) so that's taken care of.
The point is, the Opentherm Gateway suits my needs perfectly and I don't really think I can do better than a regular thermostat. Well, maybe after a few years I can get close?
And there are too many other things I like to do besides Opentherm - a heavy focus on this would mean I'd have to drop other things and that's just not worth it.
bus147
Post by bus147 »
@digit,
Time, that's a very scarce resource indeed.
Most of our thermostats do their work well and as advertised. But the unadvertised features ( as possible in the OpenTherm specs) don't live up to the expectations. My frustration is that devices are fixed for life. Unless an advertised feature is broken the manufacturer won't update it. Probably motived by cost and liability none of these devices are field updateable. My entire boiler mainboard was simply swapped because off a little firmware bug. Understandable but still annoying if you know that some of these bugs could easy be fixed.
Depending on the outcome of a test firmware for the OTG I'll give this project a shot next year.
bus147 wrote:Looking forward to a test firmware with only the second bit set.
http://www.tclcode.com/download/isense147.hex
bus147
Post by bus147 »
@hvxl,
thanks. I've downloaded the firmware. Will apply it shortly, next program change is at 2230h. Current setpoint is stable, I'll raise the setpoint by 0.5 degrees. Before the update some stats from the last three days:
  • error 01 39
  • error 02 4
  • error 03 3373
  • error 04 2
Update applied. Firmware applied, OpenTherm Gateway 3.3.1. Remote room temperature setpoint accepted. The hand symbol appeared on the iSense. And after a few minutes the special bitmask appeared. Unfortunately the WDT reset occured. I'll try again tomorrow.
Digit wrote: - Remeha Calenta, Honeywell Chronotherm IV, no go.
After disabling the TELE contact (in the User config menu of the thermostat) my problems were gone.
However I have the same thing as the 'iSense' guys - I have to go via TC=0 before I can set a new TC temperature, i.e. from TC=x to TC=y where both x and y are <> 0.
If I don't, the thermostat starts behaving very strange, e.g. jumping to temperature setpoints I can't explain (did not set).
But that's something I can live with/work around.
I'll do some tests with TT as well later this week, just to be sure.
Tested with Honeywell Chronotherm Touch and Remeha Calenta.
bus147
Post by bus147 »
The beta/test firmware, with the special bitmask, does seem to solve the problem on the iSense. I've managed to let the iSense continue the program after an override. Last night the tests were inclusive because of the the resets (The resets are not caused by the firmware but is a local problem) Use cases I haven't tested are:
  • manually overriding the temperature on the iSense after setting a remote room temperature setpoint
  • manually resuming the program on the iSense after setting a remote room temperature setpoint
  • testing the constant remote temperature setpoint by issuing a TC command
I'll test this some more. Perhaps bwired can also test this firmware.
Here's a log fragment, the program resumed at 1500h leaving no traces on the iSense
14:36:58.288343 T10101200 Write-Data Room setpoint: 18.00
14:36:58.378443 BD0101200 Write-Ack  Room setpoint: 18.00
14:37:00.291291 T10012980 Write-Data Control setpoint: 41.50
14:37:00.461372 BD0012980 Write-Ack  Control setpoint: 41.50
14:37:05.308572 T10012980 Write-Data Control setpoint: 41.50
14:37:05.458914 BD0012980 Write-Ack  Control setpoint: 41.50
14:37:08.312943 T00090000 Read-Data  Remote override room setpoint: 0.00
14:37:08.670711 AC0090000 Read-Ack   Remote override room setpoint: 0.00
14:37:10.315705 T10012980 Write-Data Control setpoint: 41.50
14:37:10.455829 BD0012980 Write-Ack  Control setpoint: 41.50
14:37:15.342895 T10012980 Write-Data Control setpoint: 41.50
14:37:15.453015 BD0012980 Write-Ack  Control setpoint: 41.50
14:37:20.350195 T10012980 Write-Data Control setpoint: 41.50
14:37:20.450199 BD0012980 Write-Ack  Control setpoint: 41.50
14:37:25.377417 T10012980 Write-Data Control setpoint: 41.50
14:37:25.467380 BD0012980 Write-Ack  Control setpoint: 41.50
14:37:30.394697 T10012980 Write-Data Control setpoint: 41.50
14:37:30.555284 BD0012980 Write-Ack  Control setpoint: 41.50
14:37:35.411739 T10012980 Write-Data Control setpoint: 41.50
14:37:35.552577 BD0012980 Write-Ack  Control setpoint: 41.50
14:37:38.426123 T10101200 Write-Data Room setpoint: 18.00
14:37:38.555232 BD0101200 Write-Ack  Room setpoint: 18.00
14:37:40.429038 T10012980 Write-Data Control setpoint: 41.50
14:37:40.564435 BD0012980 Write-Ack  Control setpoint: 41.50
14:37:45.436375 T10012980 Write-Data Control setpoint: 41.50
14:37:45.546373 BD0012980 Write-Ack  Control setpoint: 41.50
14:37:48.450674 T00090000 Read-Data  Remote override room setpoint: 0.00
14:37:48.761303 AC0090000 Read-Ack   Remote override room setpoint: 0.00
14:37:50.463336 T10012980 Write-Data Control setpoint: 41.50
14:37:50.553467 BD0012980 Write-Ack  Control setpoint: 41.50
14:37:55.480694 T10012980 Write-Data Control setpoint: 41.50
14:37:55.641044 BD0012980 Write-Ack  Control setpoint: 41.50
14:38:00.498013 T10012980 Write-Data Control setpoint: 41.50
14:38:00.648627 BD0012980 Write-Ack  Control setpoint: 41.50
14:38:05.515021 T10012980 Write-Data Control setpoint: 41.50
14:38:05.637375 BD0012980 Write-Ack  Control setpoint: 41.50
14:38:10.532264 T10012980 Write-Data Control setpoint: 41.50
14:38:10.642717 BD0012980 Write-Ack  Control setpoint: 41.50
14:38:15.539464 T10012980 Write-Data Control setpoint: 41.50
14:38:15.639687 BD0012980 Write-Ack  Control setpoint: 41.50
14:38:18.544400 T10101200 Write-Data Room setpoint: 18.00
14:38:18.644136 BD0101200 Write-Ack  Room setpoint: 18.00
14:38:20.546601 T10012980 Write-Data Control setpoint: 41.50
14:38:20.646917 BD0012980 Write-Ack  Control setpoint: 41.50
14:38:25.563931 T10012980 Write-Data Control setpoint: 41.50
14:38:25.664431 BD0012980 Write-Ack  Control setpoint: 41.50
14:38:28.578412 T00090000 Read-Data  Remote override room setpoint: 0.00
14:38:28.939067 AC0090000 Read-Ack   Remote override room setpoint: 0.00
14:38:30.581276 T10012980 Write-Data Control setpoint: 41.50
14:38:30.741483 BD0012980 Write-Ack  Control setpoint: 41.50
14:38:35.598349 T10012980 Write-Data Control setpoint: 41.50
14:38:35.738728 BD0012980 Write-Ack  Control setpoint: 41.50
14:38:40.615429 T10012980 Write-Data Control setpoint: 41.50
14:38:40.735847 BD0012980 Write-Ack  Control setpoint: 41.50
14:38:45.650901 T10012980 Write-Data Control setpoint: 41.50
14:38:45.745401 BD0012980 Write-Ack  Control setpoint: 41.50
14:38:50.660313 T10012980 Write-Data Control setpoint: 41.50
14:38:50.749074 BD0012980 Write-Ack  Control setpoint: 41.50
14:38:55.677411 T10012980 Write-Data Control setpoint: 41.50
14:38:55.825137 BD0012980 Write-Ack  Control setpoint: 41.50
14:38:58.681963 T10101200 Write-Data Room setpoint: 18.00
14:38:58.828572 BD0101200 Write-Ack  Room setpoint: 18.00
14:39:00.684738 T10012980 Write-Data Control setpoint: 41.50
14:39:00.831770 BD0012980 Write-Ack  Control setpoint: 41.50
14:39:05.691853 T10012980 Write-Data Control setpoint: 41.50
14:39:05.837706 BD0012980 Write-Ack  Control setpoint: 41.50
14:39:08.707137 T00090000 Read-Data  Remote override room setpoint: 0.00
14:39:08.946491 AC0090000 Read-Ack   Remote override room setpoint: 0.00
14:39:10.709128 T10012980 Write-Data Control setpoint: 41.50
14:39:10.819131 BD0012980 Write-Ack  Control setpoint: 41.50
14:39:15.726306 T10012980 Write-Data Control setpoint: 41.50
14:39:15.817745 BD0012980 Write-Ack  Control setpoint: 41.50
14:39:20.744036 T10012980 Write-Data Control setpoint: 41.50
14:39:20.831520 BD0012980 Write-Ack  Control setpoint: 41.50
14:39:25.751554 T10012980 Write-Data Control setpoint: 41.50
14:39:25.851510 BD0012980 Write-Ack  Control setpoint: 41.50
14:39:30.767840 T10012980 Write-Data Control setpoint: 41.50
14:39:30.917877 BD0012980 Write-Ack  Control setpoint: 41.50
14:39:35.775112 T10012980 Write-Data Control setpoint: 41.50
14:39:35.925211 BD0012980 Write-Ack  Control setpoint: 41.50
14:39:38.779681 T10101200 Write-Data Room setpoint: 18.00
14:39:38.920488 BD0101200 Write-Ack  Room setpoint: 18.00
14:39:40.782890 T10012980 Write-Data Control setpoint: 41.50
14:39:40.913100 BD0012980 Write-Ack  Control setpoint: 41.50
14:39:45.800177 T10012980 Write-Data Control setpoint: 41.50
14:39:45.919961 BD0012980 Write-Ack  Control setpoint: 41.50
14:39:48.803677 T00090000 Read-Data  Remote override room setpoint: 0.00
14:39:49.033998 AC0090000 Read-Ack   Remote override room setpoint: 0.00
14:39:50.806687 T10012980 Write-Data Control setpoint: 41.50
14:39:50.917250 BD0012980 Write-Ack  Control setpoint: 41.50
14:39:55.833912 T10012980 Write-Data Control setpoint: 41.50
14:39:55.931868 BD0012980 Write-Ack  Control setpoint: 41.50
14:40:00.841350 T10012980 Write-Data Control setpoint: 41.50
14:40:01.011652 BD0012980 Write-Ack  Control setpoint: 41.50
14:40:01.356308 Command: TT=18.5
14:40:01.375275 OK
14:40:05.858706 T10012980 Write-Data Control setpoint: 41.50
14:40:06.018542 BD0012980 Write-Ack  Control setpoint: 41.50
14:40:10.885681 T10012980 Write-Data Control setpoint: 41.50
14:40:11.025878 BD0012980 Write-Ack  Control setpoint: 41.50
14:40:15.883910 T10012980 Write-Data Control setpoint: 41.50
14:40:16.003382 BD0012980 Write-Ack  Control setpoint: 41.50
14:40:18.907917 T10101200 Write-Data Room setpoint: 18.00
14:40:19.008017 BD0101200 Write-Ack  Room setpoint: 18.00
14:40:20.901065 T10012980 Write-Data Control setpoint: 41.50
14:40:21.000915 BD0012980 Write-Ack  Control setpoint: 41.50
14:40:25.928739 T10012980 Write-Data Control setpoint: 41.50
14:40:26.017631 BD0012980 Write-Ack  Control setpoint: 41.50
14:40:28.921770 T00090000 Read-Data  Remote override room setpoint: 0.00
14:40:29.312403 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:40:29.933715 T00090000 Read-Data  Remote override room setpoint: 0.00
14:40:30.223283 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:40:30.925383 T00090000 Read-Data  Remote override room setpoint: 0.00
14:40:31.224903 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:40:32.928182 T10012980 Write-Data Control setpoint: 41.50
14:40:33.028144 BD0012980 Write-Ack  Control setpoint: 41.50
14:40:37.955148 T10012F80 Write-Data Control setpoint: 47.50
14:40:38.095129 BD0012F80 Write-Ack  Control setpoint: 47.50
14:40:42.961978 T10012F80 Write-Data Control setpoint: 47.50
14:40:43.101898 BD0012F80 Write-Ack  Control setpoint: 47.50
14:40:47.985190 T10012F80 Write-Data Control setpoint: 47.50
14:40:48.108838 BD0012F80 Write-Ack  Control setpoint: 47.50
14:40:52.993292 T10012F80 Write-Data Control setpoint: 47.50
14:40:53.116691 BD0012F80 Write-Ack  Control setpoint: 47.50
14:40:58.000763 T10012F80 Write-Data Control setpoint: 47.50
14:40:58.103948 BD0012F80 Write-Ack  Control setpoint: 47.50
14:41:01.008281 T90101280 Write-Data Room setpoint: 18.50
14:41:01.108310 B50101280 Write-Ack  Room setpoint: 18.50
14:41:03.020569 T10012F80 Write-Data Control setpoint: 47.50
14:41:03.108758 BD0012F80 Write-Ack  Control setpoint: 47.50
14:41:08.038254 T10012F80 Write-Data Control setpoint: 47.50
14:41:08.139753 BD0012F80 Write-Ack  Control setpoint: 47.50
14:41:11.052617 T00090000 Read-Data  Remote override room setpoint: 0.00
14:41:11.302411 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:41:13.046111 T10012F80 Write-Data Control setpoint: 47.50
14:41:13.185730 BD0012F80 Write-Ack  Control setpoint: 47.50
14:41:18.062782 T10012F80 Write-Data Control setpoint: 47.50
14:41:18.192804 BD0012F80 Write-Ack  Control setpoint: 47.50
14:41:21.087795 T80640000 Read-Data  Remote override function: 00000000
14:41:21.447173 AC0640002 Read-Ack   Remote override function: 00000010
14:41:23.080126 T10012F80 Write-Data Control setpoint: 47.50
14:41:23.179939 BD0012F80 Write-Ack  Control setpoint: 47.50
14:41:28.097289 T10012F80 Write-Data Control setpoint: 47.50
14:41:28.186529 BD0012F80 Write-Ack  Control setpoint: 47.50
14:41:33.104895 T10012F80 Write-Data Control setpoint: 47.50
14:41:33.204049 BD0012F80 Write-Ack  Control setpoint: 47.50
14:41:38.131803 T10012F80 Write-Data Control setpoint: 47.50
14:41:38.285039 BD0012F80 Write-Ack  Control setpoint: 47.50
14:41:41.145932 T90101280 Write-Data Room setpoint: 18.50
14:41:41.326070 B50101280 Write-Ack  Room setpoint: 18.50
14:41:43.138796 T10012F80 Write-Data Control setpoint: 47.50
14:41:43.289255 BD0012F80 Write-Ack  Control setpoint: 47.50
14:41:48.166484 T10012F80 Write-Data Control setpoint: 47.50
14:41:48.325898 BD0012F80 Write-Ack  Control setpoint: 47.50
14:41:51.170446 T00090000 Read-Data  Remote override room setpoint: 0.00
14:41:51.510933 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:41:53.173594 T10012F80 Write-Data Control setpoint: 47.50
14:41:53.342835 BD0012F80 Write-Ack  Control setpoint: 47.50
14:41:58.200581 T10012F80 Write-Data Control setpoint: 47.50
14:41:58.410106 BD0012F80 Write-Ack  Control setpoint: 47.50
14:42:03.199066 T10012F80 Write-Data Control setpoint: 47.50
14:42:03.357254 BD0012F80 Write-Ack  Control setpoint: 47.50
14:42:08.213064 T10012F80 Write-Data Control setpoint: 47.50
14:42:08.385632 BD0012F80 Write-Ack  Control setpoint: 47.50
14:42:13.231806 T10012F80 Write-Data Control setpoint: 47.50
14:42:13.391791 BD0012F80 Write-Ack  Control setpoint: 47.50
14:42:18.240273 T10012F80 Write-Data Control setpoint: 47.50
14:42:18.388950 BD0012F80 Write-Ack  Control setpoint: 47.50
14:42:21.263765 T90101280 Write-Data Room setpoint: 18.50
14:42:21.414278 B50101280 Write-Ack  Room setpoint: 18.50
14:42:23.266766 T10012F80 Write-Data Control setpoint: 47.50
14:42:23.477092 BD0012F80 Write-Ack  Control setpoint: 47.50
14:42:28.344573 T10012F80 Write-Data Control setpoint: 47.50
14:42:28.484675 BD0012F80 Write-Ack  Control setpoint: 47.50
14:42:31.278370 T00090000 Read-Data  Remote override room setpoint: 0.00
14:42:31.517680 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:42:33.290437 T10012F80 Write-Data Control setpoint: 47.50
14:42:33.491098 BD0012F80 Write-Ack  Control setpoint: 47.50
14:42:38.369043 T10012F80 Write-Data Control setpoint: 47.50
14:42:38.508444 BD0012F80 Write-Ack  Control setpoint: 47.50
14:42:43.315800 T10012F80 Write-Data Control setpoint: 47.50
14:42:43.496758 BD0012F80 Write-Ack  Control setpoint: 47.50
14:42:48.383339 T10012F80 Write-Data Control setpoint: 47.50
14:42:48.552384 BD0012F80 Write-Ack  Control setpoint: 47.50
14:42:53.390556 T10012F80 Write-Data Control setpoint: 47.50
14:42:53.484787 BD0012F80 Write-Ack  Control setpoint: 47.50
14:42:58.386780 T10012F80 Write-Data Control setpoint: 47.50
14:42:58.527359 BD0012F80 Write-Ack  Control setpoint: 47.50
14:43:01.390958 T90101280 Write-Data Room setpoint: 18.50
14:43:01.531106 B50101280 Write-Ack  Room setpoint: 18.50
14:43:03.404820 T10012F80 Write-Data Control setpoint: 47.50
14:43:03.544266 BD0012F80 Write-Ack  Control setpoint: 47.50
14:43:08.410989 T10012F80 Write-Data Control setpoint: 47.50
14:43:08.505105 BD0012F80 Write-Ack  Control setpoint: 47.50
14:43:11.375066 T00090000 Read-Data  Remote override room setpoint: 0.00
14:43:11.675711 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:43:13.378092 T10012F80 Write-Data Control setpoint: 47.50
14:43:13.534126 BD0012F80 Write-Ack  Control setpoint: 47.50
14:43:18.457197 T10012F80 Write-Data Control setpoint: 47.50
14:43:18.535398 BD0012F80 Write-Ack  Control setpoint: 47.50
14:43:23.452579 T10012F80 Write-Data Control setpoint: 47.50
14:43:23.556257 BD0012F80 Write-Ack  Control setpoint: 47.50
14:43:28.571103 T10012F80 Write-Data Control setpoint: 47.50
14:43:28.705889 BD0012F80 Write-Ack  Control setpoint: 47.50
14:43:33.447718 T10012F80 Write-Data Control setpoint: 47.50
14:43:33.569542 BD0012F80 Write-Ack  Control setpoint: 47.50
14:43:38.455705 T10012F80 Write-Data Control setpoint: 47.50
14:43:38.608373 BD0012F80 Write-Ack  Control setpoint: 47.50
14:43:41.478715 T90101280 Write-Data Room setpoint: 18.50
14:43:41.560754 B50101280 Write-Ack  Room setpoint: 18.50
14:43:43.472735 T10012F80 Write-Data Control setpoint: 47.50
14:43:43.579184 BD0012F80 Write-Ack  Control setpoint: 47.50
14:43:48.479231 T10012F80 Write-Data Control setpoint: 47.50
14:43:48.609408 BD0012F80 Write-Ack  Control setpoint: 47.50
14:43:51.483425 T00090000 Read-Data  Remote override room setpoint: 0.00
14:43:51.753350 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:43:53.486306 T10012F80 Write-Data Control setpoint: 47.50
14:43:53.690599 BD0012F80 Write-Ack  Control setpoint: 47.50
14:43:58.553395 T10012F80 Write-Data Control setpoint: 47.50
14:43:58.663152 BD0012F80 Write-Ack  Control setpoint: 47.50
14:44:03.520320 T10012F80 Write-Data Control setpoint: 47.50
14:44:03.660452 BD0012F80 Write-Ack  Control setpoint: 47.50
14:44:08.548415 T10012F80 Write-Data Control setpoint: 47.50
14:44:08.667573 BD0012F80 Write-Ack  Control setpoint: 47.50
14:44:13.554662 T10012F80 Write-Data Control setpoint: 47.50
14:44:13.645953 BD0012F80 Write-Ack  Control setpoint: 47.50
14:44:18.602970 T10012F80 Write-Data Control setpoint: 47.50
14:44:18.682624 BD0012F80 Write-Ack  Control setpoint: 47.50
14:44:21.586828 T90101280 Write-Data Room setpoint: 18.50
14:44:21.671711 B50101280 Write-Ack  Room setpoint: 18.50
14:44:23.579202 T10012F80 Write-Data Control setpoint: 47.50
14:44:23.782559 BD0012F80 Write-Ack  Control setpoint: 47.50
14:44:28.606033 T10012F80 Write-Data Control setpoint: 47.50
14:44:28.756100 BD0012F80 Write-Ack  Control setpoint: 47.50
14:44:31.610630 T00090000 Read-Data  Remote override room setpoint: 0.00
14:44:31.950639 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:44:33.603884 T10012F80 Write-Data Control setpoint: 47.50
14:44:33.743735 BD0012F80 Write-Ack  Control setpoint: 47.50
14:44:38.620863 T10012F80 Write-Data Control setpoint: 47.50
14:44:38.756765 BD0012F80 Write-Ack  Control setpoint: 47.50
14:44:43.637927 T10012F80 Write-Data Control setpoint: 47.50
14:44:43.777979 BD0012F80 Write-Ack  Control setpoint: 47.50
14:44:48.655320 T10012F80 Write-Data Control setpoint: 47.50
14:44:48.795878 BD0012F80 Write-Ack  Control setpoint: 47.50
14:44:53.682581 T10012F80 Write-Data Control setpoint: 47.50
14:44:53.793278 BD0012F80 Write-Ack  Control setpoint: 47.50
14:44:58.679663 T10012F80 Write-Data Control setpoint: 47.50
14:44:58.833717 BD0012F80 Write-Ack  Control setpoint: 47.50
14:45:01.693980 T90101280 Write-Data Room setpoint: 18.50
14:45:01.836590 B50101280 Write-Ack  Room setpoint: 18.50
14:45:03.696930 T10012F80 Write-Data Control setpoint: 47.50
14:45:03.837329 BD0012F80 Write-Ack  Control setpoint: 47.50
14:45:08.724095 T10012F80 Write-Data Control setpoint: 47.50
14:45:08.834049 BD0012F80 Write-Ack  Control setpoint: 47.50
14:45:11.728501 T00090000 Read-Data  Remote override room setpoint: 0.00
14:45:12.048489 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:45:13.741262 T10012F80 Write-Data Control setpoint: 47.50
14:45:13.871879 BD0012F80 Write-Ack  Control setpoint: 47.50
14:45:18.748277 T10012F80 Write-Data Control setpoint: 47.50
14:45:18.869115 BD0012F80 Write-Ack  Control setpoint: 47.50
14:45:23.766045 T10012F80 Write-Data Control setpoint: 47.50
14:45:23.874918 BD0012F80 Write-Ack  Control setpoint: 47.50
14:45:28.773003 T10012F80 Write-Data Control setpoint: 47.50
14:45:28.932838 BD0012F80 Write-Ack  Control setpoint: 47.50
14:45:33.790194 T10012F80 Write-Data Control setpoint: 47.50
14:45:33.938650 BD0012F80 Write-Ack  Control setpoint: 47.50
14:45:39.808680 T10015A00 Write-Data Control setpoint: 90.00
14:45:39.934499 BD0015A00 Write-Ack  Control setpoint: 90.00
14:45:42.812849 T90101280 Write-Data Room setpoint: 18.50
14:45:42.936477 B50101280 Write-Ack  Room setpoint: 18.50
14:45:47.840122 T10015A00 Write-Data Control setpoint: 90.00
14:45:47.930696 BD0015A00 Write-Ack  Control setpoint: 90.00
14:45:52.847366 T10015A00 Write-Data Control setpoint: 90.00
14:45:52.939038 BD0015A00 Write-Ack  Control setpoint: 90.00
14:45:55.881663 T00090000 Read-Data  Remote override room setpoint: 0.00
14:45:56.042067 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:45:57.884506 T10015A00 Write-Data Control setpoint: 90.00
14:45:58.024524 BD0015A00 Write-Ack  Control setpoint: 90.00
14:46:02.881887 T10015A00 Write-Data Control setpoint: 90.00
14:46:03.021523 BD0015A00 Write-Ack  Control setpoint: 90.00
14:46:07.898960 T10015A00 Write-Data Control setpoint: 90.00
14:46:08.029010 BD0015A00 Write-Ack  Control setpoint: 90.00
14:46:12.926304 T10015A00 Write-Data Control setpoint: 90.00
14:46:13.026323 BD0015A00 Write-Ack  Control setpoint: 90.00
14:46:17.933490 T10015A00 Write-Data Control setpoint: 90.00
14:46:18.023596 BD0015A00 Write-Ack  Control setpoint: 90.00
14:46:22.940530 T10015A00 Write-Data Control setpoint: 90.00
14:46:23.040678 BD0015A00 Write-Ack  Control setpoint: 90.00
14:46:25.954892 T90101280 Write-Data Room setpoint: 18.50
14:46:26.115195 B50101280 Write-Ack  Room setpoint: 18.50
14:46:27.958007 T10015A00 Write-Data Control setpoint: 90.00
14:46:28.117842 BD0015A00 Write-Ack  Control setpoint: 90.00
14:46:32.975581 T10015A00 Write-Data Control setpoint: 90.00
14:46:33.115141 BD0015A00 Write-Ack  Control setpoint: 90.00
14:46:35.979092 T00090000 Read-Data  Remote override room setpoint: 0.00
14:46:36.319857 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:46:37.992246 T10015A00 Write-Data Control setpoint: 90.00
14:46:38.112341 BD0015A00 Write-Ack  Control setpoint: 90.00
14:46:42.999845 T10015A00 Write-Data Control setpoint: 90.00
14:46:43.109705 BD0015A00 Write-Ack  Control setpoint: 90.00
14:46:48.006712 T10015A00 Write-Data Control setpoint: 90.00
14:46:48.106416 BD0015A00 Write-Ack  Control setpoint: 90.00
14:46:53.023708 T10015A00 Write-Data Control setpoint: 90.00
14:46:53.113957 BD0015A00 Write-Ack  Control setpoint: 90.00
14:46:58.040705 T10015A00 Write-Data Control setpoint: 90.00
14:46:58.131171 BD0015A00 Write-Ack  Control setpoint: 90.00
14:47:03.058314 T10015A00 Write-Data Control setpoint: 90.00
14:47:03.219141 BD0015A00 Write-Ack  Control setpoint: 90.00
14:47:06.072535 T90101280 Write-Data Room setpoint: 18.50
14:47:06.203091 B50101280 Write-Ack  Room setpoint: 18.50
14:47:08.075651 T10015A00 Write-Data Control setpoint: 90.00
14:47:08.205399 BD0015A00 Write-Ack  Control setpoint: 90.00
14:47:13.082454 T10015A00 Write-Data Control setpoint: 90.00
14:47:13.202676 BD0015A00 Write-Ack  Control setpoint: 90.00
14:47:16.097310 T00090000 Read-Data  Remote override room setpoint: 0.00
14:47:16.417601 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:47:18.099810 T10015A00 Write-Data Control setpoint: 90.00
14:47:18.199782 BD0015A00 Write-Ack  Control setpoint: 90.00
14:47:23.116903 T10015A00 Write-Data Control setpoint: 90.00
14:47:23.207175 BD0015A00 Write-Ack  Control setpoint: 90.00
14:47:28.144487 T10015A00 Write-Data Control setpoint: 90.00
14:47:28.225366 BD0015A00 Write-Ack  Control setpoint: 90.00
14:47:33.141314 T10015A00 Write-Data Control setpoint: 90.00
14:47:33.301380 BD0015A00 Write-Ack  Control setpoint: 90.00
14:47:38.158540 T10015A00 Write-Data Control setpoint: 90.00
14:47:38.298559 BD0015A00 Write-Ack  Control setpoint: 90.00
14:47:43.166097 T10015A00 Write-Data Control setpoint: 90.00
14:47:43.306213 BD0015A00 Write-Ack  Control setpoint: 90.00
14:47:46.180561 T90101280 Write-Data Room setpoint: 18.50
14:47:46.300614 B50101280 Write-Ack  Room setpoint: 18.50
14:47:48.183442 T10015A00 Write-Data Control setpoint: 90.00
14:47:48.303331 BD0015A00 Write-Ack  Control setpoint: 90.00
14:47:53.190298 T10015A00 Write-Data Control setpoint: 90.00
14:47:53.290612 BD0015A00 Write-Ack  Control setpoint: 90.00
14:47:56.195157 T00090000 Read-Data  Remote override room setpoint: 0.00
14:47:56.404597 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:47:58.197835 T10015A00 Write-Data Control setpoint: 90.00
14:47:58.297955 BD0015A00 Write-Ack  Control setpoint: 90.00
14:48:03.224704 T10015A00 Write-Data Control setpoint: 90.00
14:48:03.305151 BD0015A00 Write-Ack  Control setpoint: 90.00
14:48:08.221964 T10015A00 Write-Data Control setpoint: 90.00
14:48:08.402940 BD0015A00 Write-Ack  Control setpoint: 90.00
14:48:13.238806 T10015A00 Write-Data Control setpoint: 90.00
14:48:13.389369 BD0015A00 Write-Ack  Control setpoint: 90.00
14:48:18.256399 T10015A00 Write-Data Control setpoint: 90.00
14:48:18.386349 BD0015A00 Write-Ack  Control setpoint: 90.00
14:48:23.263655 T10015A00 Write-Data Control setpoint: 90.00
14:48:23.383873 BD0015A00 Write-Ack  Control setpoint: 90.00
14:48:26.278050 T90101280 Write-Data Room setpoint: 18.50
14:48:26.398318 B50101280 Write-Ack  Room setpoint: 18.50
14:48:28.280614 T10015A00 Write-Data Control setpoint: 90.00
14:48:28.391187 BD0015A00 Write-Ack  Control setpoint: 90.00
14:48:33.297697 T10015A00 Write-Data Control setpoint: 90.00
14:48:33.388372 BD0015A00 Write-Ack  Control setpoint: 90.00
14:48:36.312437 T00090000 Read-Data  Remote override room setpoint: 0.00
14:48:36.593589 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:48:38.315201 T10015A00 Write-Data Control setpoint: 90.00
14:48:38.405337 BD0015A00 Write-Ack  Control setpoint: 90.00
14:48:43.333467 T10015A00 Write-Data Control setpoint: 90.00
14:48:43.482894 BD0015A00 Write-Ack  Control setpoint: 90.00
14:48:48.340269 T10015A00 Write-Data Control setpoint: 90.00
14:48:48.490084 BD0015A00 Write-Ack  Control setpoint: 90.00
14:48:53.367678 T10015A00 Write-Data Control setpoint: 90.00
14:48:53.487794 BD0015A00 Write-Ack  Control setpoint: 90.00
14:48:55.370176 T10012F80 Write-Data Control setpoint: 47.50
14:48:55.489995 BD0012F80 Write-Ack  Control setpoint: 47.50
14:49:00.377620 T10012F80 Write-Data Control setpoint: 47.50
14:49:00.487815 BD0012F80 Write-Ack  Control setpoint: 47.50
14:49:05.394966 T10012F80 Write-Data Control setpoint: 47.50
14:49:05.485898 BD0012F80 Write-Ack  Control setpoint: 47.50
14:49:08.418470 T90101280 Write-Data Room setpoint: 18.50
14:49:08.578728 B50101280 Write-Ack  Room setpoint: 18.50
14:49:10.411663 T10012F80 Write-Data Control setpoint: 47.50
14:49:10.571304 BD0012F80 Write-Ack  Control setpoint: 47.50
14:49:15.428829 T10012F80 Write-Data Control setpoint: 47.50
14:49:15.568975 BD0012F80 Write-Ack  Control setpoint: 47.50
14:49:18.442614 T00090000 Read-Data  Remote override room setpoint: 0.00
14:49:18.794200 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:49:20.446218 T10012F80 Write-Data Control setpoint: 47.50
14:49:20.576170 BD0012F80 Write-Ack  Control setpoint: 47.50
14:49:25.463716 T10012F80 Write-Data Control setpoint: 47.50
14:49:25.573507 BD0012F80 Write-Ack  Control setpoint: 47.50
14:49:30.471245 T10012F80 Write-Data Control setpoint: 47.50
14:49:30.570305 BD0012F80 Write-Ack  Control setpoint: 47.50
14:49:35.487923 T10012F80 Write-Data Control setpoint: 47.50
14:49:35.578106 BD0012F80 Write-Ack  Control setpoint: 47.50
14:49:40.504925 T10012F80 Write-Data Control setpoint: 47.50
14:49:40.665571 BD0012F80 Write-Ack  Control setpoint: 47.50
14:49:45.522209 T10012F80 Write-Data Control setpoint: 47.50
14:49:45.662656 BD0012F80 Write-Ack  Control setpoint: 47.50
14:49:48.536424 T90101280 Write-Data Room setpoint: 18.50
14:49:48.677052 B50101280 Write-Ack  Room setpoint: 18.50
14:49:50.539515 T10012F80 Write-Data Control setpoint: 47.50
14:49:50.669594 BD0012F80 Write-Ack  Control setpoint: 47.50
14:49:55.546952 T10012F80 Write-Data Control setpoint: 47.50
14:49:55.667480 BD0012F80 Write-Ack  Control setpoint: 47.50
14:49:58.551348 T00090000 Read-Data  Remote override room setpoint: 0.00
14:49:58.881447 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:50:00.564108 T10012F80 Write-Data Control setpoint: 47.50
14:50:00.664350 BD0012F80 Write-Ack  Control setpoint: 47.50
14:50:05.570736 T10012F80 Write-Data Control setpoint: 47.50
14:50:05.660544 BD0012F80 Write-Ack  Control setpoint: 47.50
14:50:10.588308 T10012F80 Write-Data Control setpoint: 47.50
14:50:10.678410 BD0012F80 Write-Ack  Control setpoint: 47.50
14:50:15.616520 T10012F80 Write-Data Control setpoint: 47.50
14:50:15.775705 BD0012F80 Write-Ack  Control setpoint: 47.50
14:50:20.612811 T10012F80 Write-Data Control setpoint: 47.50
14:50:20.762976 BD0012F80 Write-Ack  Control setpoint: 47.50
14:50:25.629343 T10012F80 Write-Data Control setpoint: 47.50
14:50:25.770402 BD0012F80 Write-Ack  Control setpoint: 47.50
14:50:28.644447 T90101280 Write-Data Room setpoint: 18.50
14:50:28.764520 B50101280 Write-Ack  Room setpoint: 18.50
14:50:30.647444 T10012F80 Write-Data Control setpoint: 47.50
14:50:30.767461 BD0012F80 Write-Ack  Control setpoint: 47.50
14:50:35.664758 T10012F80 Write-Data Control setpoint: 47.50
14:50:35.754453 BD0012F80 Write-Ack  Control setpoint: 47.50
14:50:38.678981 T00090000 Read-Data  Remote override room setpoint: 0.00
14:50:38.969592 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:50:40.681795 T10012F80 Write-Data Control setpoint: 47.50
14:50:40.771317 BD0012F80 Write-Ack  Control setpoint: 47.50
14:50:45.698970 T10012F80 Write-Data Control setpoint: 47.50
14:50:45.845907 BD0012F80 Write-Ack  Control setpoint: 47.50
14:50:50.705995 T10012F80 Write-Data Control setpoint: 47.50
14:50:50.852251 BD0012F80 Write-Ack  Control setpoint: 47.50
14:50:55.722552 T10012F80 Write-Data Control setpoint: 47.50
14:50:55.860836 BD0012F80 Write-Ack  Control setpoint: 47.50
14:51:00.740285 T10012F80 Write-Data Control setpoint: 47.50
14:51:00.851122 BD0012F80 Write-Ack  Control setpoint: 47.50
14:51:05.758366 T10012F80 Write-Data Control setpoint: 47.50
14:51:05.848177 BD0012F80 Write-Ack  Control setpoint: 47.50
14:51:08.761750 T90101280 Write-Data Room setpoint: 18.50
14:51:08.862525 B50101280 Write-Ack  Room setpoint: 18.50
14:51:10.765540 T10012F80 Write-Data Control setpoint: 47.50
14:51:10.882549 BD0012F80 Write-Ack  Control setpoint: 47.50
14:51:15.782166 T10012F80 Write-Data Control setpoint: 47.50
14:51:15.953606 BD0012F80 Write-Ack  Control setpoint: 47.50
14:51:18.796314 T00090000 Read-Data  Remote override room setpoint: 0.00
14:51:19.146687 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:51:20.809763 T10012F80 Write-Data Control setpoint: 47.50
14:51:20.949727 BD0012F80 Write-Ack  Control setpoint: 47.50
14:51:25.826352 T10012F80 Write-Data Control setpoint: 47.50
14:51:25.946833 BD0012F80 Write-Ack  Control setpoint: 47.50
14:51:30.844226 T10012F80 Write-Data Control setpoint: 47.50
14:51:30.932431 BD0012F80 Write-Ack  Control setpoint: 47.50
14:51:35.861559 T10012F80 Write-Data Control setpoint: 47.50
14:51:35.954648 BD0012F80 Write-Ack  Control setpoint: 47.50
14:51:40.878479 T90012F99 Write-Data Control setpoint: 47.60
14:51:41.038771 B50012F99 Write-Ack  Control setpoint: 47.60
14:51:45.885556 T90012F99 Write-Data Control setpoint: 47.60
14:51:46.045679 B50012F99 Write-Ack  Control setpoint: 47.60
14:51:48.890283 T90101280 Write-Data Room setpoint: 18.50
14:51:49.051115 B50101280 Write-Ack  Room setpoint: 18.50
14:51:50.903225 T90012F99 Write-Data Control setpoint: 47.60
14:51:51.044154 B50012F99 Write-Ack  Control setpoint: 47.60
14:51:55.909470 T90012F99 Write-Data Control setpoint: 47.60
14:51:56.040514 B50012F99 Write-Ack  Control setpoint: 47.60
14:51:58.913477 T00090000 Read-Data  Remote override room setpoint: 0.00
14:51:59.247682 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:52:00.927434 T90012F99 Write-Data Control setpoint: 47.60
14:52:01.032142 B50012F99 Write-Ack  Control setpoint: 47.60
14:52:05.944559 T90012F99 Write-Data Control setpoint: 47.60
14:52:06.036047 B50012F99 Write-Ack  Control setpoint: 47.60
14:52:10.951962 T90012F99 Write-Data Control setpoint: 47.60
14:52:11.051133 B50012F99 Write-Ack  Control setpoint: 47.60
14:52:15.974584 T90012F99 Write-Data Control setpoint: 47.60
14:52:16.119131 B50012F99 Write-Ack  Control setpoint: 47.60
14:52:20.982301 T90012F99 Write-Data Control setpoint: 47.60
14:52:21.116686 B50012F99 Write-Ack  Control setpoint: 47.60
14:52:26.002543 T90012F99 Write-Data Control setpoint: 47.60
14:52:26.252784 B50012F99 Write-Ack  Control setpoint: 47.60
14:52:29.007033 T90101280 Write-Data Room setpoint: 18.50
14:52:29.127721 B50101280 Write-Ack  Room setpoint: 18.50
14:52:31.009742 T90012F99 Write-Data Control setpoint: 47.60
14:52:31.130675 B50012F99 Write-Ack  Control setpoint: 47.60
14:52:36.027809 T90012F99 Write-Data Control setpoint: 47.60
14:52:36.137622 B50012F99 Write-Ack  Control setpoint: 47.60
14:52:39.032609 T00090000 Read-Data  Remote override room setpoint: 0.00
14:52:39.361924 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:52:41.055073 T10012F80 Write-Data Control setpoint: 47.50
14:52:41.140806 BD0012F80 Write-Ack  Control setpoint: 47.50
14:52:46.051760 T10012F80 Write-Data Control setpoint: 47.50
14:52:46.152443 BD0012F80 Write-Ack  Control setpoint: 47.50
14:52:51.079691 T10012F80 Write-Data Control setpoint: 47.50
14:52:51.299315 BD0012F80 Write-Ack  Control setpoint: 47.50
14:52:56.096684 T10012F80 Write-Data Control setpoint: 47.50
14:52:56.226243 BD0012F80 Write-Ack  Control setpoint: 47.50
14:53:01.103678 T10012F80 Write-Data Control setpoint: 47.50
14:53:01.243534 BD0012F80 Write-Ack  Control setpoint: 47.50
14:53:06.110976 T10012F80 Write-Data Control setpoint: 47.50
14:53:06.211664 BD0012F80 Write-Ack  Control setpoint: 47.50
14:53:09.125697 T90101280 Write-Data Room setpoint: 18.50
14:53:09.213569 B50101280 Write-Ack  Room setpoint: 18.50
14:53:11.119790 T10012F80 Write-Data Control setpoint: 47.50
14:53:11.217438 BD0012F80 Write-Ack  Control setpoint: 47.50
14:53:16.135352 T10012F80 Write-Data Control setpoint: 47.50
14:53:16.223512 BD0012F80 Write-Ack  Control setpoint: 47.50
14:53:19.149572 T00090000 Read-Data  Remote override room setpoint: 0.00
14:53:19.369209 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:53:21.142604 T10012F80 Write-Data Control setpoint: 47.50
14:53:21.242890 BD0012F80 Write-Ack  Control setpoint: 47.50
14:53:26.170212 T10012F80 Write-Data Control setpoint: 47.50
14:53:26.331637 BD0012F80 Write-Ack  Control setpoint: 47.50
14:53:29.174193 T80640000 Read-Data  Remote override function: 00000000
14:53:29.424039 AC0640002 Read-Ack   Remote override function: 00000010
14:53:31.167486 T10012F80 Write-Data Control setpoint: 47.50
14:53:31.310935 BD0012F80 Write-Ack  Control setpoint: 47.50
14:53:36.175653 T10012F80 Write-Data Control setpoint: 47.50
14:53:36.423974 BD0012F80 Write-Ack  Control setpoint: 47.50
14:53:41.201514 T90012F99 Write-Data Control setpoint: 47.60
14:53:41.342297 B50012F99 Write-Ack  Control setpoint: 47.60
14:53:46.208710 T90012F99 Write-Data Control setpoint: 47.60
14:53:46.367920 B50012F99 Write-Ack  Control setpoint: 47.60
14:53:49.223811 T90101280 Write-Data Room setpoint: 18.50
14:53:49.373172 B50101280 Write-Ack  Room setpoint: 18.50
14:53:51.226166 T90012F99 Write-Data Control setpoint: 47.60
14:53:51.386037 B50012F99 Write-Ack  Control setpoint: 47.60
14:53:56.232885 T90012F99 Write-Data Control setpoint: 47.60
14:53:56.422582 B50012F99 Write-Ack  Control setpoint: 47.60
14:53:59.237502 T00090000 Read-Data  Remote override room setpoint: 0.00
14:53:59.617380 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:54:01.260386 T90012F99 Write-Data Control setpoint: 47.60
14:54:01.430342 B50012F99 Write-Ack  Control setpoint: 47.60
14:54:06.267599 T90012F99 Write-Data Control setpoint: 47.60
14:54:06.417111 B50012F99 Write-Ack  Control setpoint: 47.60
14:54:11.284987 T90012F99 Write-Data Control setpoint: 47.60
14:54:11.434083 B50012F99 Write-Ack  Control setpoint: 47.60
14:54:16.281351 T90012F99 Write-Data Control setpoint: 47.60
14:54:16.441367 B50012F99 Write-Ack  Control setpoint: 47.60
14:54:21.299300 T90012F99 Write-Data Control setpoint: 47.60
14:54:21.409737 B50012F99 Write-Ack  Control setpoint: 47.60
14:54:26.335902 T90012F99 Write-Data Control setpoint: 47.60
14:54:26.486024 B50012F99 Write-Ack  Control setpoint: 47.60
14:54:29.371403 T90101280 Write-Data Room setpoint: 18.50
14:54:29.501063 B50101280 Write-Ack  Room setpoint: 18.50
14:54:31.323654 T90012F99 Write-Data Control setpoint: 47.60
14:54:31.472916 B50012F99 Write-Ack  Control setpoint: 47.60
14:54:36.330817 T90012F99 Write-Data Control setpoint: 47.60
14:54:36.490646 B50012F99 Write-Ack  Control setpoint: 47.60
14:54:39.369968 T00090000 Read-Data  Remote override room setpoint: 0.00
14:54:39.624831 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:54:41.337648 T90012F99 Write-Data Control setpoint: 47.60
14:54:41.567496 B50012F99 Write-Ack  Control setpoint: 47.60
14:54:46.365156 T90012F99 Write-Data Control setpoint: 47.60
14:54:46.505443 B50012F99 Write-Ack  Control setpoint: 47.60
14:54:51.381869 T90012F99 Write-Data Control setpoint: 47.60
14:54:51.512449 B50012F99 Write-Ack  Control setpoint: 47.60
14:54:56.429236 T90012F99 Write-Data Control setpoint: 47.60
14:54:56.599303 B50012F99 Write-Ack  Control setpoint: 47.60
14:55:01.396865 T90012F99 Write-Data Control setpoint: 47.60
14:55:01.539572 B50012F99 Write-Ack  Control setpoint: 47.60
14:55:06.443502 T90012F99 Write-Data Control setpoint: 47.60
14:55:06.529081 B50012F99 Write-Ack  Control setpoint: 47.60
14:55:09.489071 T90101280 Write-Data Room setpoint: 18.50
14:55:09.588024 B50101280 Write-Ack  Room setpoint: 18.50
14:55:11.451942 T90012F99 Write-Data Control setpoint: 47.60
14:55:11.590942 B50012F99 Write-Ack  Control setpoint: 47.60
14:55:16.448006 T90012F99 Write-Data Control setpoint: 47.60
14:55:16.587997 B50012F99 Write-Ack  Control setpoint: 47.60
14:55:19.482368 T00090000 Read-Data  Remote override room setpoint: 0.00
14:55:19.723380 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:55:21.455143 T90012F99 Write-Data Control setpoint: 47.60
14:55:21.605207 B50012F99 Write-Ack  Control setpoint: 47.60
14:55:26.512436 T90012F99 Write-Data Control setpoint: 47.60
14:55:26.604065 B50012F99 Write-Ack  Control setpoint: 47.60
14:55:31.489488 T90012F99 Write-Data Control setpoint: 47.60
14:55:31.590503 B50012F99 Write-Ack  Control setpoint: 47.60
14:55:36.506986 T90012F99 Write-Data Control setpoint: 47.60
14:55:36.606631 B50012F99 Write-Ack  Control setpoint: 47.60
14:55:41.514099 T10012FB3 Write-Data Control setpoint: 47.70
14:55:41.734141 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:55:46.542269 T10012FB3 Write-Data Control setpoint: 47.70
14:55:46.696673 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:55:49.545310 T90101280 Write-Data Room setpoint: 18.50
14:55:49.669006 B50101280 Write-Ack  Room setpoint: 18.50
14:55:51.548340 T10012FB3 Write-Data Control setpoint: 47.70
14:55:51.668405 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:55:56.597546 T10012FB3 Write-Data Control setpoint: 47.70
14:55:56.736886 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:55:59.579625 T00090000 Read-Data  Remote override room setpoint: 0.00
14:55:59.780568 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:56:01.592895 T10012FB3 Write-Data Control setpoint: 47.70
14:56:01.702687 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:56:06.589785 T10012FB3 Write-Data Control setpoint: 47.70
14:56:06.730568 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:56:11.607296 T10012FB3 Write-Data Control setpoint: 47.70
14:56:11.807592 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:56:16.624178 T10012FB3 Write-Data Control setpoint: 47.70
14:56:16.790615 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:56:21.641298 T10012FB3 Write-Data Control setpoint: 47.70
14:56:21.771740 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:56:26.668698 T10012FB3 Write-Data Control setpoint: 47.70
14:56:26.769464 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:56:29.682971 T90101280 Write-Data Room setpoint: 18.50
14:56:29.773216 B50101280 Write-Ack  Room setpoint: 18.50
14:56:31.655873 T10012FB3 Write-Data Control setpoint: 47.70
14:56:31.776054 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:56:36.683162 T10012FB3 Write-Data Control setpoint: 47.70
14:56:36.823212 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:56:39.727663 T00090000 Read-Data  Remote override room setpoint: 0.00
14:56:39.967954 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:56:41.690232 T10012FB3 Write-Data Control setpoint: 47.70
14:56:41.846942 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:56:46.727662 T10012FB3 Write-Data Control setpoint: 47.70
14:56:46.847516 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:56:51.724976 T10012FB3 Write-Data Control setpoint: 47.70
14:56:51.904754 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:56:56.752953 T10012FB3 Write-Data Control setpoint: 47.70
14:56:56.842910 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:57:01.760357 T10012FB3 Write-Data Control setpoint: 47.70
14:57:01.844357 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:57:06.786490 T10012FB3 Write-Data Control setpoint: 47.70
14:57:06.862592 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:57:09.800753 T90101280 Write-Data Room setpoint: 18.50
14:57:09.879299 B50101280 Write-Ack  Room setpoint: 18.50
14:57:11.794047 T10012FB3 Write-Data Control setpoint: 47.70
14:57:11.897640 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:57:16.800966 T10012FB3 Write-Data Control setpoint: 47.70
14:57:16.956232 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:57:19.805351 T00090000 Read-Data  Remote override room setpoint: 0.00
14:57:20.155260 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:57:21.808175 T10012FB3 Write-Data Control setpoint: 47.70
14:57:21.948288 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:57:26.815197 T10012FB3 Write-Data Control setpoint: 47.70
14:57:26.945814 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:57:31.842420 T10012FB3 Write-Data Control setpoint: 47.70
14:57:31.942250 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:57:36.839628 T10012FB3 Write-Data Control setpoint: 47.70
14:57:36.944818 BD0012FB3 Write-Ack  Control setpoint: 47.70
14:57:41.856761 T90012FCC Write-Data Control setpoint: 47.80
14:57:41.943167 B50012FCC Write-Ack  Control setpoint: 47.80
14:57:46.874172 T90012FCC Write-Data Control setpoint: 47.80
14:57:46.953839 B50012FCC Write-Ack  Control setpoint: 47.80
14:57:49.878559 T90101280 Write-Data Room setpoint: 18.50
14:57:49.958703 B50101280 Write-Ack  Room setpoint: 18.50
14:57:51.871530 T90012FCC Write-Data Control setpoint: 47.80
14:57:51.961755 B50012FCC Write-Ack  Control setpoint: 47.80
14:57:56.888526 T90012FCC Write-Data Control setpoint: 47.80
14:57:57.088695 B50012FCC Write-Ack  Control setpoint: 47.80
14:57:59.902584 T00090000 Read-Data  Remote override room setpoint: 0.00
14:58:00.253071 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:58:01.905782 T90012FCC Write-Data Control setpoint: 47.80
14:58:02.046018 B50012FCC Write-Ack  Control setpoint: 47.80
14:58:06.911117 T90012FCC Write-Data Control setpoint: 47.80
14:58:07.031758 B50012FCC Write-Ack  Control setpoint: 47.80
14:58:11.930175 T90012FCC Write-Data Control setpoint: 47.80
14:58:12.035631 B50012FCC Write-Ack  Control setpoint: 47.80
14:58:16.944276 T90012FCC Write-Data Control setpoint: 47.80
14:58:17.027372 B50012FCC Write-Ack  Control setpoint: 47.80
14:58:21.954695 T90012FCC Write-Data Control setpoint: 47.80
14:58:22.038665 B50012FCC Write-Ack  Control setpoint: 47.80
14:58:26.961822 T90012FCC Write-Data Control setpoint: 47.80
14:58:27.062422 B50012FCC Write-Ack  Control setpoint: 47.80
14:58:29.966861 T90101280 Write-Data Room setpoint: 18.50
14:58:30.062308 B50101280 Write-Ack  Room setpoint: 18.50
14:58:31.968855 T90012FCC Write-Data Control setpoint: 47.80
14:58:32.138992 B50012FCC Write-Ack  Control setpoint: 47.80
14:58:36.985893 T90012FCC Write-Data Control setpoint: 47.80
14:58:37.136732 B50012FCC Write-Ack  Control setpoint: 47.80
14:58:40.000454 T00090000 Read-Data  Remote override room setpoint: 0.00
14:58:40.240487 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:58:42.003403 T90012FCC Write-Data Control setpoint: 47.80
14:58:42.123224 B50012FCC Write-Ack  Control setpoint: 47.80
14:58:47.010512 T90012FCC Write-Data Control setpoint: 47.80
14:58:47.120299 B50012FCC Write-Ack  Control setpoint: 47.80
14:58:52.017550 T90012FCC Write-Data Control setpoint: 47.80
14:58:52.117947 B50012FCC Write-Ack  Control setpoint: 47.80
14:58:57.045124 T90012FCC Write-Data Control setpoint: 47.80
14:58:57.125226 B50012FCC Write-Ack  Control setpoint: 47.80
14:59:02.044765 T90012FCC Write-Data Control setpoint: 47.80
14:59:02.132000 B50012FCC Write-Ack  Control setpoint: 47.80
14:59:07.058386 T90012FCC Write-Data Control setpoint: 47.80
14:59:07.219626 B50012FCC Write-Ack  Control setpoint: 47.80
14:59:10.063448 T90101280 Write-Data Room setpoint: 18.50
14:59:10.213858 B50101280 Write-Ack  Room setpoint: 18.50
14:59:12.076891 T90012FCC Write-Data Control setpoint: 47.80
14:59:12.216718 B50012FCC Write-Ack  Control setpoint: 47.80
14:59:17.083571 T90012FCC Write-Data Control setpoint: 47.80
14:59:17.213881 B50012FCC Write-Ack  Control setpoint: 47.80
14:59:20.098793 T00090000 Read-Data  Remote override room setpoint: 0.00
14:59:20.429172 A40091280 Read-Ack   Remote override room setpoint: 18.50
14:59:22.100951 T90012FCC Write-Data Control setpoint: 47.80
14:59:22.210775 B50012FCC Write-Ack  Control setpoint: 47.80
14:59:27.108488 T90012FCC Write-Data Control setpoint: 47.80
14:59:27.218193 B50012FCC Write-Ack  Control setpoint: 47.80
14:59:32.135541 T90012FCC Write-Data Control setpoint: 47.80
14:59:32.240607 B50012FCC Write-Ack  Control setpoint: 47.80
14:59:37.135737 T90012FCC Write-Data Control setpoint: 47.80
14:59:37.233310 B50012FCC Write-Ack  Control setpoint: 47.80
14:59:42.158880 T90012FCC Write-Data Control setpoint: 47.80
14:59:42.310097 B50012FCC Write-Ack  Control setpoint: 47.80
14:59:47.167148 T90012FCC Write-Data Control setpoint: 47.80
14:59:47.307033 B50012FCC Write-Ack  Control setpoint: 47.80
14:59:50.181119 T90101280 Write-Data Room setpoint: 18.50
14:59:50.301461 B50101280 Write-Ack  Room setpoint: 18.50
14:59:52.183821 T90012FCC Write-Data Control setpoint: 47.80
14:59:52.314306 B50012FCC Write-Ack  Control setpoint: 47.80
14:59:57.202000 T90012FCC Write-Data Control setpoint: 47.80
14:59:57.301588 B50012FCC Write-Ack  Control setpoint: 47.80
15:00:00.215294 T00090000 Read-Data  Remote override room setpoint: 0.00
15:00:00.507387 A40091280 Read-Ack   Remote override room setpoint: 18.50
15:00:02.218702 T90012FCC Write-Data Control setpoint: 47.80
15:00:02.308697 B50012FCC Write-Ack  Control setpoint: 47.80
15:00:07.225537 T90012FCC Write-Data Control setpoint: 47.80
15:00:07.325710 B50012FCC Write-Ack  Control setpoint: 47.80
15:00:12.252771 T90012FCC Write-Data Control setpoint: 47.80
15:00:12.402817 B50012FCC Write-Ack  Control setpoint: 47.80
15:00:17.260496 T90012FCC Write-Data Control setpoint: 47.80
15:00:17.400186 B50012FCC Write-Ack  Control setpoint: 47.80
15:00:22.267225 T90012FCC Write-Data Control setpoint: 47.80
15:00:22.407358 B50012FCC Write-Ack  Control setpoint: 47.80
15:00:27.295252 T90012FCC Write-Data Control setpoint: 47.80
15:00:27.394676 B50012FCC Write-Ack  Control setpoint: 47.80
15:00:30.309030 T90101280 Write-Data Room setpoint: 18.50
15:00:30.399032 B50101280 Write-Ack  Room setpoint: 18.50
15:00:32.308389 T90012FCC Write-Data Control setpoint: 47.80
15:00:32.392347 B50012FCC Write-Ack  Control setpoint: 47.80
15:00:37.322407 T90012FCC Write-Data Control setpoint: 47.80
15:00:37.409549 B50012FCC Write-Ack  Control setpoint: 47.80
15:00:43.337598 T00090000 Read-Data  Remote override room setpoint: 0.00
15:00:43.704131 A40091280 Read-Ack   Remote override room setpoint: 18.50
15:00:45.350465 T900129CC Write-Data Control setpoint: 41.80
15:00:45.490735 B500129CC Write-Ack  Control setpoint: 41.80
15:00:52.370536 T900129CC Write-Data Control setpoint: 41.80
15:00:52.491363 B500129CC Write-Ack  Control setpoint: 41.80
15:00:57.387795 T900129CC Write-Data Control setpoint: 41.80
15:00:57.488506 B500129CC Write-Ack  Control setpoint: 41.80
15:01:02.406401 T900129CC Write-Data Control setpoint: 41.80
15:01:02.495656 B500129CC Write-Ack  Control setpoint: 41.80
15:01:09.425850 T900129CC Write-Data Control setpoint: 41.80
15:01:09.585506 B500129CC Write-Ack  Control setpoint: 41.80
15:01:14.442627 T900129CC Write-Data Control setpoint: 41.80
15:01:14.582730 B500129CC Write-Ack  Control setpoint: 41.80
15:01:17.457125 T10101200 Write-Data Room setpoint: 18.00
15:01:17.587122 BD0101200 Write-Ack  Room setpoint: 18.00
15:01:19.446656 T900129CC Write-Data Control setpoint: 41.80
15:01:19.576656 B500129CC Write-Ack  Control setpoint: 41.80
15:01:24.466627 T900129CC Write-Data Control setpoint: 41.80
15:01:24.576809 B500129CC Write-Ack  Control setpoint: 41.80
15:01:27.470361 T00090000 Read-Data  Remote override room setpoint: 0.00
15:01:27.792832 AC0090000 Read-Ack   Remote override room setpoint: 0.00
15:01:29.484340 T900129CC Write-Data Control setpoint: 41.80
15:01:29.573749 B500129CC Write-Ack  Control setpoint: 41.80
15:01:34.501355 T900129CC Write-Data Control setpoint: 41.80
15:01:34.591521 B500129CC Write-Ack  Control setpoint: 41.80
15:01:39.508322 T900129CC Write-Data Control setpoint: 41.80
15:01:39.679282 B500129CC Write-Ack  Control setpoint: 41.80
15:01:44.535765 T900129CC Write-Data Control setpoint: 41.80
15:01:44.678070 B500129CC Write-Ack  Control setpoint: 41.80
15:01:49.543262 T900129CC Write-Data Control setpoint: 41.80
15:01:49.673838 B500129CC Write-Ack  Control setpoint: 41.80
15:01:54.560467 T900129CC Write-Data Control setpoint: 41.80
15:01:54.670992 B500129CC Write-Ack  Control setpoint: 41.80
15:01:57.564729 T10101200 Write-Data Room setpoint: 18.00
15:01:57.675110 BD0101200 Write-Ack  Room setpoint: 18.00
15:01:59.567534 T900129CC Write-Data Control setpoint: 41.80
15:01:59.667771 B500129CC Write-Ack  Control setpoint: 41.80
15:02:04.574692 T900129CC Write-Data Control setpoint: 41.80
15:02:04.664309 B500129CC Write-Ack  Control setpoint: 41.80
15:02:07.588602 T00090000 Read-Data  Remote override room setpoint: 0.00
15:02:07.879912 AC0090000 Read-Ack   Remote override room setpoint: 0.00
15:02:09.591469 T900129CC Write-Data Control setpoint: 41.80
15:02:09.692244 B500129CC Write-Ack  Control setpoint: 41.80
15:02:14.619271 T900129CC Write-Data Control setpoint: 41.80
15:02:14.769419 B500129CC Write-Ack  Control setpoint: 41.80
15:02:19.626439 T900129CC Write-Data Control setpoint: 41.80
15:02:19.767414 B500129CC Write-Ack  Control setpoint: 41.80
15:02:24.643700 T900129CC Write-Data Control setpoint: 41.80
15:02:24.785155 B500129CC Write-Ack  Control setpoint: 41.80
15:02:29.650629 T900129CC Write-Data Control setpoint: 41.80
15:02:29.770962 B500129CC Write-Ack  Control setpoint: 41.80
15:02:34.647761 T900129CC Write-Data Control setpoint: 41.80
15:02:34.768213 B500129CC Write-Ack  Control setpoint: 41.80
15:02:37.651348 T10101200 Write-Data Room setpoint: 18.00
15:02:37.753088 BD0101200 Write-Ack  Room setpoint: 18.00
15:02:39.654828 T900129CC Write-Data Control setpoint: 41.80
15:02:39.755731 B500129CC Write-Ack  Control setpoint: 41.80
15:02:44.682417 T900129CC Write-Data Control setpoint: 41.80
15:02:44.772550 B500129CC Write-Ack  Control setpoint: 41.80
15:02:47.676338 T00090000 Read-Data  Remote override room setpoint: 0.00
15:02:47.987634 AC0090000 Read-Ack   Remote override room setpoint: 0.00
15:02:49.709979 T900129CC Write-Data Control setpoint: 41.80
15:02:49.860219 B500129CC Write-Ack  Control setpoint: 41.80
15:02:54.716582 T900129CC Write-Data Control setpoint: 41.80
15:02:54.857304 B500129CC Write-Ack  Control setpoint: 41.80
15:02:59.723643 T900129CC Write-Data Control setpoint: 41.80
15:02:59.864323 B500129CC Write-Ack  Control setpoint: 41.80
15:03:04.721352 T900129CC Write-Data Control setpoint: 41.80
15:03:04.872472 B500129CC Write-Ack  Control setpoint: 41.80
15:03:09.738625 T900129CC Write-Data Control setpoint: 41.80
15:03:09.868859 B500129CC Write-Ack  Control setpoint: 41.80
15:03:14.755428 T900129CC Write-Data Control setpoint: 41.80
15:03:14.855828 B500129CC Write-Ack  Control setpoint: 41.80
15:03:17.770246 T10101200 Write-Data Room setpoint: 18.00
15:03:17.871043 BD0101200 Write-Ack  Room setpoint: 18.00
15:03:19.762705 T900129CC Write-Data Control setpoint: 41.80
15:03:19.862698 B500129CC Write-Ack  Control setpoint: 41.80
15:03:24.779798 T900129CC Write-Data Control setpoint: 41.80
15:03:24.869775 B500129CC Write-Ack  Control setpoint: 41.80
15:03:27.783984 T00090000 Read-Data  Remote override room setpoint: 0.00
15:03:28.064385 AC0090000 Read-Ack   Remote override room setpoint: 0.00
15:03:29.786868 T900129CC Write-Data Control setpoint: 41.80
15:03:29.941789 B500129CC Write-Ack  Control setpoint: 41.80
15:03:34.803945 T900129CC Write-Data Control setpoint: 41.80
15:03:34.949018 B500129CC Write-Ack  Control setpoint: 41.80
15:03:39.811232 T900129CC Write-Data Control setpoint: 41.80
15:03:39.941422 B500129CC Write-Ack  Control setpoint: 41.80
15:03:44.818471 T900129CC Write-Data Control setpoint: 41.80
15:03:44.938629 B500129CC Write-Ack  Control setpoint: 41.80
15:03:49.835637 T900129CC Write-Data Control setpoint: 41.80
15:03:49.945819 B500129CC Write-Ack  Control setpoint: 41.80
15:03:54.839542 T900129CC Write-Data Control setpoint: 41.80
15:03:54.953373 B500129CC Write-Ack  Control setpoint: 41.80
15:03:57.847340 T10101200 Write-Data Room setpoint: 18.00
15:03:57.942550 BD0101200 Write-Ack  Room setpoint: 18.00
15:03:59.850249 T900129CC Write-Data Control setpoint: 41.80
15:03:59.944934 B500129CC Write-Ack  Control setpoint: 41.80
15:04:04.868193 T900129CC Write-Data Control setpoint: 41.80
15:04:04.952368 B500129CC Write-Ack  Control setpoint: 41.80
15:04:07.882446 T00090000 Read-Data  Remote override room setpoint: 0.00
15:04:08.293258 AC0090000 Read-Ack   Remote override room setpoint: 0.00
15:04:09.885287 T900129CC Write-Data Control setpoint: 41.80
15:04:09.974587 B500129CC Write-Ack  Control setpoint: 41.80
15:04:14.892611 T900129CC Write-Data Control setpoint: 41.80
15:04:15.032964 B500129CC Write-Ack  Control setpoint: 41.80
15:04:19.899909 T900129CC Write-Data Control setpoint: 41.80
15:04:20.040077 B500129CC Write-Ack  Control setpoint: 41.80
15:04:24.906971 T900129CC Write-Data Control setpoint: 41.80
15:04:25.035989 B500129CC Write-Ack  Control setpoint: 41.80
15:04:29.924044 T900129CC Write-Data Control setpoint: 41.80
15:04:30.030832 B500129CC Write-Ack  Control setpoint: 41.80
15:04:34.931463 T900129CC Write-Data Control setpoint: 41.80
15:04:35.024392 B500129CC Write-Ack  Control setpoint: 41.80
15:04:37.945128 T10101200 Write-Data Room setpoint: 18.00
15:04:38.029819 BD0101200 Write-Ack  Room setpoint: 18.00
15:04:39.938307 T900129CC Write-Data Control setpoint: 41.80
15:04:40.031795 B500129CC Write-Ack  Control setpoint: 41.80
15:04:44.965147 T900129CC Write-Data Control setpoint: 41.80
15:04:45.064648 B500129CC Write-Ack  Control setpoint: 41.80
15:04:47.957736 T00090000 Read-Data  Remote override room setpoint: 0.00
15:04:48.348120 AC0090000 Read-Ack   Remote override room setpoint: 0.00
15:04:49.962262 T900129CC Write-Data Control setpoint: 41.80
15:04:50.121490 B500129CC Write-Ack  Control setpoint: 41.80
15:04:54.990304 T900129CC Write-Data Control setpoint: 41.80
15:04:55.120458 B500129CC Write-Ack  Control setpoint: 41.80
15:04:59.987252 T900129CC Write-Data Control setpoint: 41.80
15:05:00.138916 B500129CC Write-Ack  Control setpoint: 41.80
15:05:05.004642 T900129CC Write-Data Control setpoint: 41.80
15:05:05.124419 B500129CC Write-Ack  Control setpoint: 41.80
15:05:10.012139 T900129CC Write-Data Control setpoint: 41.80
15:05:10.132314 B500129CC Write-Ack  Control setpoint: 41.80
15:05:15.041015 T900129CC Write-Data Control setpoint: 41.80
15:05:15.132075 B500129CC Write-Ack  Control setpoint: 41.80
15:05:18.044391 T10101200 Write-Data Room setpoint: 18.00
15:05:18.135714 BD0101200 Write-Ack  Room setpoint: 18.00
15:05:20.046106 T900129CC Write-Data Control setpoint: 41.80
15:05:20.136436 B500129CC Write-Ack  Control setpoint: 41.80
15:05:25.053025 T900129CC Write-Data Control setpoint: 41.80
15:05:25.222431 B500129CC Write-Ack  Control setpoint: 41.80
15:05:28.058169 T00090000 Read-Data  Remote override room setpoint: 0.00
15:05:28.387660 AC0090000 Read-Ack   Remote override room setpoint: 0.00
15:05:30.061245 T900129CC Write-Data Control setpoint: 41.80
15:05:30.220095 B500129CC Write-Ack  Control setpoint: 41.80
15:05:35.088065 T900129CC Write-Data Control setpoint: 41.80
15:05:35.227975 B500129CC Write-Ack  Control setpoint: 41.80
15:05:38.091947 T80640000 Read-Data  Remote override function: 00000000
15:05:38.361413 A40640000 Read-Ack   Remote override function: 00000000
15:05:40.095715 T900129CC Write-Data Control setpoint: 41.80
15:05:40.214380 B500129CC Write-Ack  Control setpoint: 41.80
15:05:45.100813 T900129CC Write-Data Control setpoint: 41.80
15:05:45.221050 B500129CC Write-Ack  Control setpoint: 41.80
15:05:50.109704 T900129CC Write-Data Control setpoint: 41.80
15:05:50.209726 B500129CC Write-Ack  Control setpoint: 41.80
15:05:55.116894 T900129CC Write-Data Control setpoint: 41.80
15:05:55.207619 B500129CC Write-Ack  Control setpoint: 41.80
15:05:58.131198 T10101200 Write-Data Room setpoint: 18.00
15:05:58.220060 BD0101200 Write-Ack  Room setpoint: 18.00
15:06:00.141877 T900129CC Write-Data Control setpoint: 41.80
15:06:00.232173 B500129CC Write-Ack  Control setpoint: 41.80
15:06:05.140947 T900129CC Write-Data Control setpoint: 41.80
15:06:05.300907 B500129CC Write-Ack  Control setpoint: 41.80
15:06:08.155451 T00090000 Read-Data  Remote override room setpoint: 0.00
15:06:08.515602 AC0090000 Read-Ack   Remote override room setpoint: 0.00
15:06:10.149542 T900129CC Write-Data Control setpoint: 41.80
15:06:10.298103 B500129CC Write-Ack  Control setpoint: 41.80
15:06:15.165562 T900129CC Write-Data Control setpoint: 41.80
15:06:15.305466 B500129CC Write-Ack  Control setpoint: 41.80
15:06:20.189684 T900129CC Write-Data Control setpoint: 41.80
15:06:20.303084 B500129CC Write-Ack  Control setpoint: 41.80
15:06:25.195805 T900129CC Write-Data Control setpoint: 41.80
15:06:25.310026 B500129CC Write-Ack  Control setpoint: 41.80
15:06:30.217276 T900129CC Write-Data Control setpoint: 41.80
15:06:30.302550 B500129CC Write-Ack  Control setpoint: 41.80
15:06:35.234662 T900129CC Write-Data Control setpoint: 41.80
15:06:35.322675 B500129CC Write-Ack  Control setpoint: 41.80
15:06:38.238593 T10101200 Write-Data Room setpoint: 18.00
15:06:38.337376 BD0101200 Write-Ack  Room setpoint: 18.00
15:06:40.231296 T900129CC Write-Data Control setpoint: 41.80
15:06:40.328859 B500129CC Write-Ack  Control setpoint: 41.80
15:06:45.247917 T900129CC Write-Data Control setpoint: 41.80
15:06:45.384154 B500129CC Write-Ack  Control setpoint: 41.80
15:06:48.253389 T00090000 Read-Data  Remote override room setpoint: 0.00
Re: Overriding temperature setpoint with OTG and iSense
Testing now :)
One problem solved!
If i make a temp setpoint (TT) this will be set. Then the program on the thermostat takes over according schedule. :)
But im still not able to make a new setpoint after setting the first, this will not be accepted. Override will go to 0 again.
still examining which set-point is taken after this?
bus147
Post by bus147 »
Now that setting TT works, I'll test some other scenarios as well:
  • Override temperature via TT and wait till next program change and program setting resumes. Then issue a new TT. Check if that gets accepted and program will resume after program change
  • Override temperature via TT. Manually resume program on the iSense. Then issue a new TT. Check if that gets accepted and program will resume after program change.
I'll look if I can figure out how one can see that the program resumes for example, based on the messages exchanged via the OTG.
One interesting question remains: how should this fix be implemented? Not, and only via a special build made available. Via, a new command eg TP. Or allow the user to configure the bitmask. But first more testing, which is rather time consuming.
Sorry, I updated the above post, I was setting the TT and not TC :oops:
I checked many times now, after setting TT, program pick up again according schedule, so that problem looks solved
Still Setting a TT while ID9 is <> 0 is a problem, this does not work, and thermostat resumes with scheduled program, not the last (current TT)
bus147
Post by bus147 »
That's great to read Bwired! Could describe why you want to set another TT? Is it something like: let's raise the temperature 0.5 degC above program. Wait sometime. Mmm, still too cold let's raise the temp another 0.5 degC. If the program/device forgot that a previous TT had been set. Isn't this detectable by looking at MsgId 9 and circumventable by issuing a TT=0 first. What's needed is a state diagram and some notes about timing. Because all these state transition can take minutes. At first I issues commands vary rapidly (a TT per 30 secs or minute) but the iSense didn't like that. With regard to determining the state, is there some command to query the thermostat? For example: are you running from program? Or when does the next program start? Because if you miss some responses you might not reliable determine the state the system is is. Also need to look more carefully at the allowed setpoint values. The iSense control allow for half degree resolution but internally up one hundredth of a degree is used. Can we set that as well or will it mess up the iSense somehow.
Yes i can check ID9 first if its <> 0, but its better when its working :-)
And yes if you raise 0.5 and later again with 2.0 the heating up increases a lot.
Like told before setting override to 0 will immedately activate the scheduld program and can start the hvac
But i think its not a big problem, we can live with it :-)
Good suggestion of you regarding the new firmware!
And thanks to schelte for making it
steelrv
Post by steelrv »
Here my findings with the new isense.hex.
I have a Remeha Calenta 40c with isense sw v19.
Just build my OTG this weekend.
- same conclusion as above, TT=x and then TT=y will only be accepted if first TT=0 is given. Should be nice if it can be solved, otherwise it's just a thing to remember when setting new temporary temperatures.
- however, something different then above, when I have set a TT=x the standard program will NOT resume when it should at a specific configured time. The overridden temperature stays active. Don't know with the other guys, but I also see a difference with a temporary override on the iSense itself and with the temporary override with OTG.
When I do the temporary override on the iSense it shows the until time on the left bottom, e.g.
Tot:
16:00
25/12/2012
When I override it with the OTG it doesn't show an until value.
Here some logging.
Configuration in iSense
08:30 19,5 degrees
16:00 15,0 degrees
TT=18 done at 15:55.
Should expect that program goes to 15 degrees at 16:00. It just doesn't happen. If I do a TT=0 it does go to 15 degrees (see 16:02:55). My first impression is that there is no difference between the 'TT' and the 'TC' in my configuration.
If you want more info, please let me know and I will give it.
15:55:12.364175 T80190000 Read-Data  Boiler water temperature: 0.00
15:55:12.484904 B4019417D Read-Ack   Boiler water temperature: 65.49
15:55:13.366172 T00090000 Read-Data  Remote override room setpoint: 0.00
15:55:13.396581 R80750000 Read-Data  CH pump starts: 0
15:55:13.696446 BC0757180 Read-Ack   CH pump starts: 29056
15:55:13.728529 AC0090000 Read-Ack   Remote override room setpoint: 0.00
15:55:14.367375 T80000200 Read-Data  Status: 00000010 00000000
15:55:14.487767 B40000200 Read-Ack   Status: 00000010 00000000
15:55:15.368622 T80000200 Read-Data  Status: 00000010 00000000
15:55:15.489033 B40000200 Read-Ack   Status: 00000010 00000000
15:55:16.369963 T80000200 Read-Data  Status: 00000010 00000000
15:55:16.483439 B40000200 Read-Ack   Status: 00000010 00000000
15:55:17.371695 T10011100 Write-Data Control setpoint: 17.00
15:55:17.481495 BD0011100 Write-Ack  Control setpoint: 17.00
15:55:18.372651 T00110000 Read-Data  Relative modulation level: 0.00
15:55:18.483149 BC0110000 Read-Ack   Relative modulation level: 0.00
15:55:19.373994 T80190000 Read-Data  Boiler water temperature: 0.00
15:55:19.484550 B401942E8 Read-Ack   Boiler water temperature: 66.91
15:55:20.375307 T00630000 Read-Data  Message ID 99: 0
15:55:20.410979 R80760000 Read-Data  DHW pump/valve starts: 0
15:55:20.586047 B407639B8 Read-Ack   DHW pump/valve starts: 14776
15:55:20.619950 AF0630000 Unk-DataId Message ID 99: 0
15:55:21.377374 T80000200 Read-Data  Status: 00000010 00000000
15:55:21.488099 B40000200 Read-Ack   Status: 00000010 00000000
15:55:22.378523 T10011100 Write-Data Control setpoint: 17.00
15:55:22.488274 BD0011100 Write-Ack  Control setpoint: 17.00
15:55:23.379562 T00110000 Read-Data  Relative modulation level: 0.00
15:55:23.480031 BC0110000 Read-Ack   Relative modulation level: 0.00
15:55:24.397456 T80190000 Read-Data  Boiler water temperature: 0.00
15:55:24.481386 B4019431C Read-Ack   Boiler water temperature: 67.11
15:55:25.382178 T80700000 Read-Data  Message ID 112: 0
15:55:25.418710 R00770000 Read-Data  DHW burner starts: 0
15:55:25.683186 B40774120 Read-Ack   DHW burner starts: 16672
15:55:25.754152 A70700000 Unk-DataId Message ID 112: 0
15:55:26.384110 T80000200 Read-Data  Status: 00000010 00000000
15:55:26.484378 B40000200 Read-Ack   Status: 00000010 00000000
15:55:27.385330 T10011100 Write-Data Control setpoint: 17.00
15:55:27.485052 BD0011100 Write-Ack  Control setpoint: 17.00
15:55:28.386434 T00110000 Read-Data  Relative modulation level: 0.00
15:55:28.486791 BC0110000 Read-Ack   Relative modulation level: 0.00
15:55:29.383416 T80190000 Read-Data  Boiler water temperature: 0.00
15:55:29.488755 B40194380 Read-Ack   Boiler water temperature: 67.50
15:55:30.389476 T00050000 Read-Data  Application-specific flags: 00000000 0
15:55:30.479627 BC00500FF Read-Ack   Application-specific flags: 00000000 255
15:55:31.390499 T80000200 Read-Data  Status: 00000010 00000000
15:55:31.480975 B40000200 Read-Ack   Status: 00000010 00000000
15:55:32.392185 T10011100 Write-Data Control setpoint: 17.00
15:55:32.491990 BD0011100 Write-Ack  Control setpoint: 17.00
15:55:32.866540 Command: TT=18.00
15:55:32.902723 OK
15:55:33.393127 T00110000 Read-Data  Relative modulation level: 0.00
15:55:33.493755 BC0110000 Read-Ack   Relative modulation level: 0.00
15:55:34.394533 T80190000 Read-Data  Boiler water temperature: 0.00
15:55:34.486352 BC0194399 Read-Ack   Boiler water temperature: 67.60
15:55:35.395900 T001B0ACC Read-Data  Outside temperature: 10.80
15:55:35.488550 BC01B0A99 Read-Ack   Outside temperature: 10.60
15:55:36.397395 T80000200 Read-Data  Status: 00000010 00000000
15:55:36.488624 B40000200 Read-Ack   Status: 00000010 00000000
15:55:37.402749 T10011100 Write-Data Control setpoint: 17.00
15:55:37.559272 BD0011100 Write-Ack  Control setpoint: 17.00
15:55:38.400419 T00110000 Read-Data  Relative modulation level: 0.00
15:55:38.490796 BC0110000 Read-Ack   Relative modulation level: 0.00
15:55:39.401354 T80190000 Read-Data  Boiler water temperature: 0.00
15:55:39.491879 B401943B3 Read-Ack   Boiler water temperature: 67.70
15:55:40.403273 T900E6400 Write-Data Maximum relative modulation level: 100.00
15:55:40.492909 B500E6400 Write-Ack  Maximum relative modulation level: 100.00
15:55:41.404223 T80000200 Read-Data  Status: 00000010 00000000
15:55:41.494564 B40000200 Read-Ack   Status: 00000010 00000000
15:55:42.405845 T10011100 Write-Data Control setpoint: 17.00
15:55:42.495864 BD0011100 Write-Ack  Control setpoint: 17.00
15:55:43.406809 T00110000 Read-Data  Relative modulation level: 0.00
15:55:43.497258 BC0110000 Read-Ack   Relative modulation level: 0.00
15:55:44.408173 T80190000 Read-Data  Boiler water temperature: 0.00
15:55:44.499650 BC01943CC Read-Ack   Boiler water temperature: 67.80
15:55:45.409913 T10101380 Write-Data Room setpoint: 19.50
15:55:45.499567 BD0101380 Write-Ack  Room setpoint: 19.50
15:55:46.411062 T80000200 Read-Data  Status: 00000010 00000000
15:55:46.501475 B40000200 Read-Ack   Status: 00000010 00000000
15:55:47.412720 T10011100 Write-Data Control setpoint: 17.00
15:55:47.502340 BD0011100 Write-Ack  Control setpoint: 17.00
15:55:48.454107 T00110000 Read-Data  Relative modulation level: 0.00
15:55:48.584500 BC0110000 Read-Ack   Relative modulation level: 0.00
15:55:49.415037 T80190000 Read-Data  Boiler water temperature: 0.00
15:55:49.505517 BC01943CC Read-Ack   Boiler water temperature: 67.80
15:55:50.416793 T901813E3 Write-Data Room temperature: 19.89
15:55:50.506507 B501813E3 Write-Ack  Room temperature: 19.89
15:55:51.407931 T80000200 Read-Data  Status: 00000010 00000000
15:55:51.508372 B40000200 Read-Ack   Status: 00000010 00000000
15:55:52.410200 T10011100 Write-Data Control setpoint: 17.00
15:55:52.509257 BD0011100 Write-Ack  Control setpoint: 17.00
15:55:53.410509 T00110000 Read-Data  Relative modulation level: 0.00
15:55:53.510954 BC0110000 Read-Ack   Relative modulation level: 0.00
15:55:54.411904 T80190000 Read-Data  Boiler water temperature: 0.00
15:55:54.512322 BC01943CC Read-Ack   Boiler water temperature: 67.80
15:55:55.413327 T00090000 Read-Data  Remote override room setpoint: 0.00
15:55:55.449241 R00780000 Read-Data  Burner operation hours: 0
15:55:55.683872 BC0780EDA Read-Ack   Burner operation hours: 3802
15:55:55.719684 AC0091200 Read-Ack   Remote override room setpoint: 18.00
15:55:56.414654 T00090000 Read-Data  Remote override room setpoint: 0.00
15:55:56.451460 R80790000 Read-Data  CH pump operation hours: 0
15:55:56.585147 BC0791126 Read-Ack   CH pump operation hours: 4390
15:55:56.621985 AC0091200 Read-Ack   Remote override room setpoint: 18.00
15:55:57.416076 T00090000 Read-Data  Remote override room setpoint: 0.00
15:55:57.454835 R807A0000 Read-Data  DHW pump/valve operation hours: 0
15:55:57.686614 B407A5BB0 Read-Ack   DHW pump/valve operation hours: 23472
15:55:57.721963 AC0091200 Read-Ack   Remote override room setpoint: 18.00
15:55:58.417425 T80000200 Read-Data  Status: 00000010 00000000
15:55:58.507964 B40000200 Read-Ack   Status: 00000010 00000000
15:55:59.419267 T10010600 Write-Data Control setpoint: 6.00
15:55:59.579108 BD0010600 Write-Ack  Control setpoint: 6.00
15:56:00.420064 T00110000 Read-Data  Relative modulation level: 0.00
15:56:00.580788 BC0110000 Read-Ack   Relative modulation level: 0.00
15:56:01.421481 T80190000 Read-Data  Boiler water temperature: 0.00
15:56:01.582725 BC01943CC Read-Ack   Boiler water temperature: 67.80
15:56:02.423081 T00630000 Read-Data  Message ID 99: 0
15:56:02.459383 R007B0000 Read-Data  DHW burner operation hours: 0
15:56:02.683759 BC07B019B Read-Ack   DHW burner operation hours: 411
15:56:02.707016 AF0630000 Unk-DataId Message ID 99: 0
15:56:03.424144 T80000200 Read-Data  Status: 00000010 00000000
15:56:03.584727 B40000200 Read-Ack   Status: 00000010 00000000
15:56:04.425766 T10010600 Write-Data Control setpoint: 6.00
15:56:04.595587 BD0010600 Write-Ack  Control setpoint: 6.00
15:56:05.426848 T00110000 Read-Data  Relative modulation level: 0.00
15:56:05.587502 BC0110000 Read-Ack   Relative modulation level: 0.00
15:56:06.428208 T80190000 Read-Data  Boiler water temperature: 0.00
15:56:06.588970 B401943B3 Read-Ack   Boiler water temperature: 67.70
15:56:07.432367 T1002010B Write-Data Master configuration: 00000001 11
15:56:07.580145 BD002010B Write-Ack  Master configuration: 00000001 11
15:56:08.431101 T80000200 Read-Data  Status: 00000010 00000000
15:56:08.581776 B40000200 Read-Ack   Status: 00000010 00000000
15:56:09.432596 T10010600 Write-Data Control setpoint: 6.00
15:56:09.583267 BD0010600 Write-Ack  Control setpoint: 6.00
15:56:10.413569 T00110000 Read-Data  Relative modulation level: 0.00
15:56:10.504054 BC0110000 Read-Ack   Relative modulation level: 0.00
15:56:11.414971 T80190000 Read-Data  Boiler water temperature: 0.00
15:56:11.505508 BC0194399 Read-Ack   Boiler water temperature: 67.60
15:56:12.416491 T00050000 Read-Data  Application-specific flags: 00000000 0
15:56:12.507008 BC00500FF Read-Ack   Application-specific flags: 00000000 255
15:56:13.417907 T80000200 Read-Data  Status: 00000010 00000000
15:56:13.509567 B40000200 Read-Ack   Status: 00000010 00000000
15:56:14.419557 T10010600 Write-Data Control setpoint: 6.00
15:56:14.589427 BD0010600 Write-Ack  Control setpoint: 6.00
15:56:15.420725 T00110000 Read-Data  Relative modulation level: 0.00
15:56:15.581241 BC0110000 Read-Ack   Relative modulation level: 0.00
15:56:16.422109 T80190000 Read-Data  Boiler water temperature: 0.00
15:56:16.582556 BC0194399 Read-Ack   Boiler water temperature: 67.60
15:56:17.423237 T001B0ACC Read-Data  Outside temperature: 10.80
15:56:17.583935 BC01B0A99 Read-Ack   Outside temperature: 10.60
15:56:18.425021 T80000200 Read-Data  Status: 00000010 00000000
15:56:18.585292 B40000200 Read-Ack   Status: 00000010 00000000
15:56:19.426363 T10010600 Write-Data Control setpoint: 6.00
15:56:19.586209 BD0010600 Write-Ack  Control setpoint: 6.00
15:56:20.427342 T00110000 Read-Data  Relative modulation level: 0.00
15:56:20.587923 BC0110000 Read-Ack   Relative modulation level: 0.00
15:56:21.428699 T80190000 Read-Data  Boiler water temperature: 0.00
15:56:21.589312 B40194380 Read-Ack   Boiler water temperature: 67.50
15:56:22.430523 T900E6400 Write-Data Maximum relative modulation level: 100.00
15:56:22.581210 B500E6400 Write-Ack  Maximum relative modulation level: 100.00
15:56:23.441894 T80000200 Read-Data  Status: 00000010 00000000
15:56:23.582215 B40000200 Read-Ack   Status: 00000010 00000000
15:56:24.433238 T10010600 Write-Data Control setpoint: 6.00
15:56:24.583373 BD0010600 Write-Ack  Control setpoint: 6.00
15:56:25.434237 T00110000 Read-Data  Relative modulation level: 0.00
15:56:25.585200 BC0110000 Read-Ack   Relative modulation level: 0.00
15:56:26.435560 T80190000 Read-Data  Boiler water temperature: 0.00
15:56:26.586518 B40194380 Read-Ack   Boiler water temperature: 67.50
15:56:27.437403 T10101200 Write-Data Room setpoint: 18.00
15:56:27.588305 BD0101200 Write-Ack  Room setpoint: 18.00
15:56:28.438551 T80000200 Read-Data  Status: 00000010 00000000
15:56:28.589041 B40000200 Read-Ack   Status: 00000010 00000000
15:56:29.440205 T10010600 Write-Data Control setpoint: 6.00
15:56:29.580157 BD0010600 Write-Ack  Control setpoint: 6.00
15:56:30.441157 T00110000 Read-Data  Relative modulation level: 0.00
15:56:30.581908 BC0110000 Read-Ack   Relative modulation level: 0.00
15:56:31.442549 T80190000 Read-Data  Boiler water temperature: 0.00
15:56:31.583210 B40194380 Read-Ack   Boiler water temperature: 67.50
15:56:32.444325 T101813E1 Write-Data Room temperature: 19.88
15:56:32.584192 BD01813E1 Write-Ack  Room temperature: 19.88
15:56:33.445299 T80000200 Read-Data  Status: 00000010 00000000
15:56:33.585939 B40000200 Read-Ack   Status: 00000010 00000000
15:56:34.446957 T10010600 Write-Data Control setpoint: 6.00
15:56:34.586865 BD0010600 Write-Ack  Control setpoint: 6.00
15:56:35.447896 T00110000 Read-Data  Relative modulation level: 0.00
15:56:35.588678 BC0110000 Read-Ack   Relative modulation level: 0.00
15:56:36.449258 T80190000 Read-Data  Boiler water temperature: 0.00
15:56:36.589972 B40194380 Read-Ack   Boiler water temperature: 67.50
15:56:37.450729 T00090000 Read-Data  Remote override room setpoint: 0.00
15:56:37.486120 R00740000 Read-Data  Burner starts: 0
15:56:37.791671 BC0745238 Read-Ack   Burner starts: 21048
15:56:37.826223 AC0091200 Read-Ack   Remote override room setpoint: 18.00
15:56:38.452114 T80000200 Read-Data  Status: 00000010 00000000
15:56:38.583771 B40000200 Read-Ack   Status: 00000010 00000000
15:56:39.453809 T10010600 Write-Data Control setpoint: 6.00
15:56:39.583820 BD0010600 Write-Ack  Control setpoint: 6.00
15:56:40.454805 T00110000 Read-Data  Relative modulation level: 0.00
15:56:40.585656 BC0110000 Read-Ack   Relative modulation level: 0.00
15:56:41.456116 T80190000 Read-Data  Boiler water temperature: 0.00
15:56:41.586960 B40194380 Read-Ack   Boiler water temperature: 67.50
15:56:42.457327 T00630000 Read-Data  Message ID 99: 0
15:56:42.492646 R80750000 Read-Data  CH pump starts: 0
15:56:42.798518 BC0757180 Read-Ack   CH pump starts: 29056
15:56:42.833836 AF0630000 Unk-DataId Message ID 99: 0
15:56:43.529216 T80000200 Read-Data  Status: 00000010 00000000
15:56:43.700064 B40000200 Read-Ack   Status: 00000010 00000000
15:56:44.480690 T10010600 Write-Data Control setpoint: 6.00
15:56:44.580492 BD0010600 Write-Ack  Control setpoint: 6.00
15:56:45.481693 T00110000 Read-Data  Relative modulation level: 0.00
15:56:45.582224 BC0110000 Read-Ack   Relative modulation level: 0.00
15:56:46.483041 T80190000 Read-Data  Boiler water temperature: 0.00
15:56:46.583537 BC0194363 Read-Ack   Boiler water temperature: 67.39
15:56:47.484667 T00030000 Read-Data  Slave configuration: 00000000 0
15:56:47.587176 B4003410B Read-Ack   Slave configuration: 01000001 11
15:56:48.485847 T80000200 Read-Data  Status: 00000010 00000000
15:56:48.586329 B40000200 Read-Ack   Status: 00000010 00000000
15:56:49.487920 T10010600 Write-Data Control setpoint: 6.00
15:56:49.587289 BD0010600 Write-Ack  Control setpoint: 6.00
15:56:50.478639 T00110000 Read-Data  Relative modulation level: 0.00
15:56:50.589041 BC0110000 Read-Ack   Relative modulation level: 0.00
15:56:51.480004 T80190000 Read-Data  Boiler water temperature: 0.00
15:56:51.590420 B4019434C Read-Ack   Boiler water temperature: 67.30
15:56:52.491347 T00050000 Read-Data  Application-specific flags: 00000000 0
15:56:52.582052 BC00500FF Read-Ack   Application-specific flags: 00000000 255
15:56:53.492737 T80000200 Read-Data  Status: 00000010 00000000
15:56:53.583215 B40000200 Read-Ack   Status: 00000010 00000000
15:56:54.484475 T10010600 Write-Data Control setpoint: 6.00
15:56:54.584283 BD0010600 Write-Ack  Control setpoint: 6.00
15:56:55.485669 T00110000 Read-Data  Relative modulation level: 0.00
15:56:55.585824 BC0110000 Read-Ack   Relative modulation level: 0.00
15:56:56.486661 T80190000 Read-Data  Boiler water temperature: 0.00
15:56:56.587103 BC0194333 Read-Ack   Boiler water temperature: 67.20
15:56:57.488085 T001B0ACC Read-Data  Outside temperature: 10.80
15:56:57.588469 BC01B0A99 Read-Ack   Outside temperature: 10.60
15:56:58.489565 T80000200 Read-Data  Status: 00000010 00000000
15:56:58.589942 B40000200 Read-Ack   Status: 00000010 00000000
15:56:59.491229 T10010600 Write-Data Control setpoint: 6.00
15:56:59.581048 BD0010600 Write-Ack  Control setpoint: 6.00
15:57:00.492225 T00110000 Read-Data  Relative modulation level: 0.00
15:57:00.582772 BC0110000 Read-Ack   Relative modulation level: 0.00
15:57:01.493657 T80190000 Read-Data  Boiler water temperature: 0.00
15:57:01.584207 BC0194333 Read-Ack   Boiler water temperature: 67.20
15:57:02.495362 T900E6400 Write-Data Maximum relative modulation level: 100.00
15:57:02.585189 B500E6400 Write-Ack  Maximum relative modulation level: 100.00
15:57:03.496428 T80000200 Read-Data  Status: 00000010 00000000
15:57:03.586940 B40000200 Read-Ack   Status: 00000010 00000000
15:57:04.498036 T10010600 Write-Data Control setpoint: 6.00
15:57:04.587898 BD0010600 Write-Ack  Control setpoint: 6.00
15:57:05.500111 T00110000 Read-Data  Relative modulation level: 0.00
15:57:05.589615 BC0110000 Read-Ack   Relative modulation level: 0.00
15:57:06.500843 T80190000 Read-Data  Boiler water temperature: 0.00
15:57:06.590981 BC0194333 Read-Ack   Boiler water temperature: 67.20
15:57:07.502136 T10101200 Write-Data Room setpoint: 18.00
15:57:07.591935 BD0101200 Write-Ack  Room setpoint: 18.00
15:57:08.503243 T80000200 Read-Data  Status: 00000010 00000000
15:57:08.593846 B40000200 Read-Ack   Status: 00000010 00000000
15:57:09.504931 T10010600 Write-Data Control setpoint: 6.00
15:57:09.594684 BD0010600 Write-Ack  Control setpoint: 6.00
15:57:10.505888 T00110000 Read-Data  Relative modulation level: 0.00
15:57:10.596369 BC0110000 Read-Ack   Relative modulation level: 0.00
15:57:11.507277 T80190000 Read-Data  Boiler water temperature: 0.00
15:57:11.597754 B40194326 Read-Ack   Boiler water temperature: 67.15
15:57:12.509005 T101813E1 Write-Data Room temperature: 19.88
15:57:12.598932 BD01813E1 Write-Ack  Room temperature: 19.88
15:57:13.540464 T80000200 Read-Data  Status: 00000010 00000000
15:57:13.680940 B40000200 Read-Ack   Status: 00000010 00000000
15:57:14.511909 T10010600 Write-Data Control setpoint: 6.00
15:57:14.601601 BD0010600 Write-Ack  Control setpoint: 6.00
15:57:15.513448 T00110000 Read-Data  Relative modulation level: 0.00
15:57:15.603686 BC0110000 Read-Ack   Relative modulation level: 0.00
15:57:16.514151 T80190000 Read-Data  Boiler water temperature: 0.00
15:57:16.604682 BC019430F Read-Ack   Boiler water temperature: 67.06
15:57:17.515733 T00090000 Read-Data  Remote override room setpoint: 0.00
15:57:17.549880 R80760000 Read-Data  DHW pump/valve starts: 0
15:57:17.796579 B407639B8 Read-Ack   DHW pump/valve starts: 14776
15:57:17.832226 AC0091200 Read-Ack   Remote override room setpoint: 18.00
15:57:18.516995 T80000200 Read-Data  Status: 00000010 00000000
15:57:18.607404 B40000200 Read-Ack   Status: 00000010 00000000
15:57:19.518595 T10010600 Write-Data Control setpoint: 6.00
15:57:19.608424 BD0010600 Write-Ack  Control setpoint: 6.00
15:57:20.519607 T00110000 Read-Data  Relative modulation level: 0.00
15:57:20.690326 BC0110000 Read-Ack   Relative modulation level: 0.00
15:57:21.520974 T80190000 Read-Data  Boiler water temperature: 0.00
15:57:21.681635 BC0194300 Read-Ack   Boiler water temperature: 67.00
15:57:22.522528 T00630000 Read-Data  Message ID 99: 0
15:57:22.563130 R00770000 Read-Data  DHW burner starts: 0
15:57:22.883258 B40774120 Read-Ack   DHW burner starts: 16672
15:57:22.917915 AF0630000 Unk-DataId Message ID 99: 0
15:57:23.523783 T80000200 Read-Data  Status: 00000010 00000000
15:57:23.684307 B40000200 Read-Ack   Status: 00000010 00000000
15:57:24.525630 T10010600 Write-Data Control setpoint: 6.00
15:57:24.686121 BD0010600 Write-Ack  Control setpoint: 6.00
<removed>
15:59:23.024040 AF0630000 Unk-DataId Message ID 99: 0
15:59:23.678385 T80000200 Read-Data  Status: 00000010 00000000
15:59:23.798648 B40000200 Read-Ack   Status: 00000010 00000000
15:59:24.679810 T10010600 Write-Data Control setpoint: 6.00
15:59:24.799601 BD0010600 Write-Ack  Control setpoint: 6.00
15:59:25.681991 T00110000 Read-Data  Relative modulation level: 0.00
15:59:25.791443 BC0110000 Read-Ack   Relative modulation level: 0.00
15:59:26.682397 T80190000 Read-Data  Boiler water temperature: 0.00
15:59:26.793054 BC0194219 Read-Ack   Boiler water temperature: 66.10
15:59:27.684440 T00300000 Read-Data  DHW setpoint boundaries: 0 0
15:59:27.796655 BC0304128 Read-Ack   DHW setpoint boundaries: 65 40
15:59:28.675094 T80000200 Read-Data  Status: 00000010 00000000
15:59:28.795537 B40000200 Read-Ack   Status: 00000010 00000000
15:59:29.676789 T10010600 Write-Data Control setpoint: 6.00
15:59:29.796885 BD0010600 Write-Ack  Control setpoint: 6.00
15:59:30.677737 T00110000 Read-Data  Relative modulation level: 0.00
15:59:30.798181 BC0110000 Read-Ack   Relative modulation level: 0.00
15:59:31.689012 T80190000 Read-Data  Boiler water temperature: 0.00
15:59:31.799976 BC0194219 Read-Ack   Boiler water temperature: 66.10
15:59:32.680524 T00050000 Read-Data  Application-specific flags: 00000000 0
15:59:32.791094 BC00500FF Read-Ack   Application-specific flags: 00000000 255
15:59:33.681830 T80000200 Read-Data  Status: 00000010 00000000
15:59:33.792483 B40000200 Read-Ack   Status: 00000010 00000000
15:59:34.683594 T10010600 Write-Data Control setpoint: 6.00
15:59:34.793327 BD0010600 Write-Ack  Control setpoint: 6.00
15:59:35.684525 T00110000 Read-Data  Relative modulation level: 0.00
15:59:35.794973 BC0110000 Read-Ack   Relative modulation level: 0.00
15:59:36.685827 T80190000 Read-Data  Boiler water temperature: 0.00
15:59:36.796377 BC0194219 Read-Ack   Boiler water temperature: 66.10
15:59:37.687228 T001B0ACC Read-Data  Outside temperature: 10.80
15:59:37.797785 BC01B0A99 Read-Ack   Outside temperature: 10.60
15:59:38.688703 T80000200 Read-Data  Status: 00000010 00000000
15:59:38.799184 B40000200 Read-Ack   Status: 00000010 00000000
15:59:39.690643 T10010600 Write-Data Control setpoint: 6.00
15:59:39.800172 BD0010600 Write-Ack  Control setpoint: 6.00
15:59:40.691361 T00110000 Read-Data  Relative modulation level: 0.00
15:59:40.791951 BC0110000 Read-Ack   Relative modulation level: 0.00
15:59:41.692865 T80190000 Read-Data  Boiler water temperature: 0.00
15:59:41.793294 BC0194219 Read-Ack   Boiler water temperature: 66.10
15:59:42.694557 T900E6400 Write-Data Maximum relative modulation level: 100.00
15:59:42.794256 B500E6400 Write-Ack  Maximum relative modulation level: 100.00
15:59:43.695934 T80000200 Read-Data  Status: 00000010 00000000
15:59:43.796060 B40000200 Read-Ack   Status: 00000010 00000000
15:59:44.697274 T10010600 Write-Data Control setpoint: 6.00
15:59:44.797024 BD0010600 Write-Ack  Control setpoint: 6.00
15:59:45.688450 T00110000 Read-Data  Relative modulation level: 0.00
15:59:45.798736 BC0110000 Read-Ack   Relative modulation level: 0.00
15:59:46.689821 T80190000 Read-Data  Boiler water temperature: 0.00
15:59:46.800142 B40194200 Read-Ack   Boiler water temperature: 66.00
15:59:47.691776 T10101200 Write-Data Room setpoint: 18.00
15:59:47.792157 BD0101200 Write-Ack  Room setpoint: 18.00
15:59:48.692610 T80000200 Read-Data  Status: 00000010 00000000
15:59:48.793009 B40000200 Read-Ack   Status: 00000010 00000000
15:59:49.694221 T10010600 Write-Data Control setpoint: 6.00
15:59:49.793916 BD0010600 Write-Ack  Control setpoint: 6.00
15:59:50.695156 T00110000 Read-Data  Relative modulation level: 0.00
15:59:50.796082 BC0110000 Read-Ack   Relative modulation level: 0.00
15:59:51.696550 T80190000 Read-Data  Boiler water temperature: 0.00
15:59:51.797057 B40194200 Read-Ack   Boiler water temperature: 66.00
15:59:52.698393 T101813DE Write-Data Room temperature: 19.87
15:59:52.798084 BD01813DE Write-Ack  Room temperature: 19.87
15:59:53.703586 T90143000 Write-Data Day of week and time of day: Mon 16:00
15:59:53.739929 R80760000 Read-Data  DHW pump/valve starts: 0
15:59:53.890122 B407639B8 Read-Ack   DHW pump/valve starts: 14776
15:59:53.926778 A50143000 Write-Ack  Day of week and time of day: Mon 16:00
15:59:54.703614 T101607DC Write-Data Year: 2012
15:59:54.740922 R00770000 Read-Data  DHW burner starts: 0
15:59:54.891431 B40774120 Read-Ack   DHW burner starts: 16672
15:59:54.931958 A701607DC Unk-DataId Year: 2012
15:59:55.705480 T10150C18 Write-Data Date: 12 24
15:59:55.743119 R00780000 Read-Data  Burner operation hours: 0
15:59:55.992872 BC0780EDA Read-Ack   Burner operation hours: 3802
15:59:56.035506 A70150C18 Unk-DataId Date: 12 24
15:59:56.703486 T80000200 Read-Data  Status: 00000010 00000000
15:59:56.793999 B40000200 Read-Ack   Status: 00000010 00000000
15:59:57.705125 T10010600 Write-Data Control setpoint: 6.00
15:59:57.794714 BD0010600 Write-Ack  Control setpoint: 6.00
15:59:58.706050 T00110000 Read-Data  Relative modulation level: 0.00
15:59:58.796441 BC0110000 Read-Ack   Relative modulation level: 0.00
15:59:59.707461 T80190000 Read-Data  Boiler water temperature: 0.00
15:59:59.797847 B40194200 Read-Ack   Boiler water temperature: 66.00
16:00:00.708977 T00090000 Read-Data  Remote override room setpoint: 0.00
16:00:00.746755 R80790000 Read-Data  CH pump operation hours: 0
16:00:00.889448 BC0791126 Read-Ack   CH pump operation hours: 4390
16:00:00.928686 AC0091200 Read-Ack   Remote override room setpoint: 18.00
16:00:01.710373 T80000200 Read-Data  Status: 00000010 00000000
16:00:01.800661 B40000200 Read-Ack   Status: 00000010 00000000
16:00:02.712007 T10010600 Write-Data Control setpoint: 6.00
16:00:02.801593 BD0010600 Write-Ack  Control setpoint: 6.00
16:00:03.713348 T00110000 Read-Data  Relative modulation level: 0.00
16:00:03.803388 BC0110000 Read-Ack   Relative modulation level: 0.00
16:00:04.714319 T80190000 Read-Data  Boiler water temperature: 0.00
16:00:04.804771 BC01941E6 Read-Ack   Boiler water temperature: 65.90
16:00:05.715526 T00630000 Read-Data  Message ID 99: 0
16:00:05.753202 R807A0000 Read-Data  DHW pump/valve operation hours: 0
16:00:05.886605 B407A5BB0 Read-Ack   DHW pump/valve operation hours: 23472
16:00:05.925242 AF0630000 Unk-DataId Message ID 99: 0
16:00:06.717282 T80000200 Read-Data  Status: 00000010 00000000
16:00:06.807608 B40000200 Read-Ack   Status: 00000010 00000000
16:00:07.718849 T10010600 Write-Data Control setpoint: 6.00
16:00:07.808466 BD0010600 Write-Ack  Control setpoint: 6.00
16:00:08.709860 T00110000 Read-Data  Relative modulation level: 0.00
16:00:08.810258 BC0110000 Read-Ack   Relative modulation level: 0.00
16:00:09.711327 T80190000 Read-Data  Boiler water temperature: 0.00
16:00:09.802947 BC01941E6 Read-Ack   Boiler water temperature: 65.90
16:00:10.712683 T80310000 Read-Data  Max CH setpoint boundaries: 0 0
16:00:10.815742 BC0314614 Read-Ack   Max CH setpoint boundaries: 70 20
16:00:11.713968 T80000200 Read-Data  Status: 00000010 00000000
16:00:11.804487 B40000200 Read-Ack   Status: 00000010 00000000
16:00:12.715645 T10010600 Write-Data Control setpoint: 6.00
16:00:12.805751 BD0010600 Write-Ack  Control setpoint: 6.00
16:00:13.716556 T00110000 Read-Data  Relative modulation level: 0.00
16:00:13.817043 BC0110000 Read-Ack   Relative modulation level: 0.00
16:00:14.717921 T80190000 Read-Data  Boiler water temperature: 0.00
16:00:14.818402 BC01941E6 Read-Ack   Boiler water temperature: 65.90
16:00:15.719385 T00050000 Read-Data  Application-specific flags: 00000000 0
16:00:15.819914 BC00500FF Read-Ack   Application-specific flags: 00000000 255
16:00:16.720732 T80000200 Read-Data  Status: 00000010 00000000
16:00:16.821285 B40000200 Read-Ack   Status: 00000010 00000000
16:00:17.722413 T10010600 Write-Data Control setpoint: 6.00
16:00:17.822137 BD0010600 Write-Ack  Control setpoint: 6.00
16:00:18.723409 T00110000 Read-Data  Relative modulation level: 0.00
16:00:18.823918 BC0110000 Read-Ack   Relative modulation level: 0.00
16:00:19.724784 T80190000 Read-Data  Boiler water temperature: 0.00
16:00:19.825245 BC01941E6 Read-Ack   Boiler water temperature: 65.90
16:00:20.726121 T801B0AB3 Read-Data  Outside temperature: 10.70
16:00:20.826634 BC01B0A99 Read-Ack   Outside temperature: 10.60
16:00:21.717639 T80000200 Read-Data  Status: 00000010 00000000
16:00:21.827974 B40000200 Read-Ack   Status: 00000010 00000000
16:00:22.719263 T10010600 Write-Data Control setpoint: 6.00
16:00:22.829168 BD0010600 Write-Ack  Control setpoint: 6.00
16:00:23.720527 T00110000 Read-Data  Relative modulation level: 0.00
16:00:23.830774 BC0110000 Read-Ack   Relative modulation level: 0.00
16:00:24.721742 T80190000 Read-Data  Boiler water temperature: 0.00
16:00:24.813871 B401941CC Read-Ack   Boiler water temperature: 65.80
16:00:25.723232 T900E6400 Write-Data Maximum relative modulation level: 100.00
16:00:25.814513 B500E6400 Write-Ack  Maximum relative modulation level: 100.00
16:00:26.724232 T80000200 Read-Data  Status: 00000010 00000000
16:00:26.816217 B40000200 Read-Ack   Status: 00000010 00000000
16:00:27.725966 T10010600 Write-Data Control setpoint: 6.00
16:00:27.817316 BD0010600 Write-Ack  Control setpoint: 6.00
16:00:28.727015 T00110000 Read-Data  Relative modulation level: 0.00
16:00:28.819154 BC0110000 Read-Ack   Relative modulation level: 0.00
16:00:29.728307 T80190000 Read-Data  Boiler water temperature: 0.00
16:00:29.820365 B401941CC Read-Ack   Boiler water temperature: 65.80
16:00:30.729913 T10101200 Write-Data Room setpoint: 18.00
16:00:30.821174 BD0101200 Write-Ack  Room setpoint: 18.00
16:00:31.731055 T80000200 Read-Data  Status: 00000010 00000000
16:00:31.823001 B40000200 Read-Ack   Status: 00000010 00000000
16:00:32.732848 T10010600 Write-Data Control setpoint: 6.00
16:00:32.824158 BD0010600 Write-Ack  Control setpoint: 6.00
16:00:33.744030 T00110000 Read-Data  Relative modulation level: 0.00
16:00:33.826011 BC0110000 Read-Ack   Relative modulation level: 0.00
16:00:34.735645 T80190000 Read-Data  Boiler water temperature: 0.00
16:00:34.827382 BC01941B3 Read-Ack   Boiler water temperature: 65.70
16:00:35.737115 T101813DE Write-Data Room temperature: 19.87
16:00:35.828284 BD01813DE Write-Ack  Room temperature: 19.87
16:00:36.728319 T80000200 Read-Data  Status: 00000010 00000000
16:00:36.830280 B40000200 Read-Ack   Status: 00000010 00000000
16:00:37.730277 T10010600 Write-Data Control setpoint: 6.00
16:00:37.831136 BD0010600 Write-Ack  Control setpoint: 6.00
16:00:38.731007 T00110000 Read-Data  Relative modulation level: 0.00
16:00:38.891386 BC0110000 Read-Ack   Relative modulation level: 0.00
16:00:39.732225 T80190000 Read-Data  Boiler water temperature: 0.00
16:00:39.822891 BC01941B3 Read-Ack   Boiler water temperature: 65.70
16:00:40.733726 T00090000 Read-Data  Remote override room setpoint: 0.00
16:00:40.770431 R007B0000 Read-Data  DHW burner operation hours: 0
16:00:41.084567 BC07B019B Read-Ack   DHW burner operation hours: 411
16:00:41.121047 AC0091200 Read-Ack   Remote override room setpoint: 18.00
16:00:41.735403 T80000200 Read-Data  Status: 00000010 00000000
16:00:41.885613 B40000200 Read-Ack   Status: 00000010 00000000
16:00:42.736770 T10010600 Write-Data Control setpoint: 6.00
16:00:42.887394 BD0010600 Write-Ack  Control setpoint: 6.00
16:00:43.737672 T00110000 Read-Data  Relative modulation level: 0.00
16:00:43.888264 BC0110000 Read-Ack   Relative modulation level: 0.00
16:00:44.739142 T80190000 Read-Data  Boiler water temperature: 0.00
16:00:44.889765 B40194187 Read-Ack   Boiler water temperature: 65.53
16:00:45.740201 T00630000 Read-Data  Message ID 99: 0
16:00:45.776871 R00740000 Read-Data  Burner starts: 0
16:00:46.091160 BC0745238 Read-Ack   Burner starts: 21048
16:00:46.127996 AF0630000 Unk-DataId Message ID 99: 0
16:00:46.741938 T80000200 Read-Data  Status: 00000010 00000000
16:00:46.892414 B40000200 Read-Ack   Status: 00000010 00000000
16:00:47.743523 T10010600 Write-Data Control setpoint: 6.00
16:00:47.883439 BD0010600 Write-Ack  Control setpoint: 6.00
16:00:48.744641 T00110000 Read-Data  Relative modulation level: 0.00
16:00:48.885178 BC0110000 Read-Ack   Relative modulation level: 0.00
16:00:49.745920 T80190000 Read-Data  Boiler water temperature: 0.00
16:00:49.896405 BC0194180 Read-Ack   Boiler water temperature: 65.50
16:00:50.750559 T10383C00 Write-Data DHW setpoint: 60.00
16:00:50.887983 BD0383C00 Write-Ack  DHW setpoint: 60.00
16:00:51.739175 T80000200 Read-Data  Status: 00000010 00000000
16:00:51.889266 B40000200 Read-Ack   Status: 00000010 00000000
16:00:52.740632 T10010600 Write-Data Control setpoint: 6.00
16:00:52.891041 BD0010600 Write-Ack  Control setpoint: 6.00
16:00:53.741578 T00110000 Read-Data  Relative modulation level: 0.00
16:00:53.891891 BC0110000 Read-Ack   Relative modulation level: 0.00
16:00:54.742919 T80190000 Read-Data  Boiler water temperature: 0.00
16:00:54.883462 BC0194180 Read-Ack   Boiler water temperature: 65.50
16:00:55.744316 T00050000 Read-Data  Application-specific flags: 00000000 0
16:00:55.884835 BC00500FF Read-Ack   Application-specific flags: 00000000 255
16:00:56.745597 T80000200 Read-Data  Status: 00000010 00000000
16:00:56.886165 B40000200 Read-Ack   Status: 00000010 00000000
16:00:57.747509 T10010600 Write-Data Control setpoint: 6.00
16:00:57.887072 BD0010600 Write-Ack  Control setpoint: 6.00
16:00:58.748335 T00110000 Read-Data  Relative modulation level: 0.00
16:00:58.888827 BC0110000 Read-Ack   Relative modulation level: 0.00
16:00:59.749643 T80190000 Read-Data  Boiler water temperature: 0.00
16:00:59.890221 BC0194180 Read-Ack   Boiler water temperature: 65.50
16:01:00.760963 T801B0AB3 Read-Data  Outside temperature: 10.70
16:01:00.892038 BC01B0A99 Read-Ack   Outside temperature: 10.60
16:01:01.752591 T80000200 Read-Data  Status: 00000010 00000000
16:01:01.893036 B40000200 Read-Ack   Status: 00000010 00000000
16:01:02.754477 T10010600 Write-Data Control setpoint: 6.00
16:01:02.884132 BD0010600 Write-Ack  Control setpoint: 6.00
16:01:03.755414 T00110000 Read-Data  Relative modulation level: 0.00
16:01:03.885921 BC0110000 Read-Ack   Relative modulation level: 0.00
16:01:04.756460 T80190000 Read-Data  Boiler water temperature: 0.00
16:01:04.887217 BC0194180 Read-Ack   Boiler water temperature: 65.50
16:01:05.758251 T900E6400 Write-Data Maximum relative modulation level: 100.00
16:01:05.888194 B500E6400 Write-Ack  Maximum relative modulation level: 100.00
16:01:06.759333 T80000200 Read-Data  Status: 00000010 00000000
16:01:06.889917 B40000200 Read-Ack   Status: 00000010 00000000
16:01:07.760998 T10010600 Write-Data Control setpoint: 6.00
16:01:07.890939 BD0010600 Write-Ack  Control setpoint: 6.00
16:01:08.761942 T00110000 Read-Data  Relative modulation level: 0.00
16:01:08.892685 BC0110000 Read-Ack   Relative modulation level: 0.00
16:01:09.763452 T80190000 Read-Data  Boiler water temperature: 0.00
16:01:09.883980 BC0194180 Read-Ack   Boiler water temperature: 65.50
16:01:10.765052 T10101200 Write-Data Room setpoint: 18.00
16:01:10.885718 BD0101200 Write-Ack  Room setpoint: 18.00
16:01:11.766121 T80000200 Read-Data  Status: 00000010 00000000
16:01:11.896985 B40000200 Read-Ack   Status: 00000010 00000000
16:01:12.767829 T10010600 Write-Data Control setpoint: 6.00
16:01:12.897821 BD0010600 Write-Ack  Control setpoint: 6.00
16:01:13.768823 T00110000 Read-Data  Relative modulation level: 0.00
16:01:13.899941 BC0110000 Read-Ack   Relative modulation level: 0.00
16:01:14.770188 T80190000 Read-Data  Boiler water temperature: 0.00
16:01:14.900850 BC0194180 Read-Ack   Boiler water temperature: 65.50
16:01:15.771968 T101813DE Write-Data Room temperature: 19.87
16:01:15.901931 BD01813DE Write-Ack  Room temperature: 19.87
16:01:16.763034 T80000200 Read-Data  Status: 00000010 00000000
16:01:16.885101 B40000200 Read-Ack   Status: 00000010 00000000
16:01:17.764652 T10010600 Write-Data Control setpoint: 6.00
16:01:17.885872 BD0010600 Write-Ack  Control setpoint: 6.00
16:01:18.765682 T00110000 Read-Data  Relative modulation level: 0.00
16:01:18.887681 BC0110000 Read-Ack   Relative modulation level: 0.00
16:01:19.767034 T80190000 Read-Data  Boiler water temperature: 0.00
16:01:19.889054 B40194166 Read-Ack   Boiler water temperature: 65.40
16:01:20.768455 T00090000 Read-Data  Remote override room setpoint: 0.00
16:01:20.805862 R80750000 Read-Data  CH pump starts: 0
16:01:20.988934 BC0757180 Read-Ack   CH pump starts: 29056
16:01:21.026564 AC0091200 Read-Ack   Remote override room setpoint: 18.00
16:01:21.769747 T80000200 Read-Data  Status: 00000010 00000000
16:01:21.891692 B40000200 Read-Ack   Status: 00000010 00000000
16:01:22.771418 T10010600 Write-Data Control setpoint: 6.00
16:01:22.892611 BD0010600 Write-Ack  Control setpoint: 6.00
16:01:23.772545 T00110000 Read-Data  Relative modulation level: 0.00
16:01:23.894394 BC0110000 Read-Ack   Relative modulation level: 0.00
16:01:24.771323 T80190000 Read-Data  Boiler water temperature: 0.00
16:01:24.884464 B40194166 Read-Ack   Boiler water temperature: 65.40
16:01:25.775840 T00630000 Read-Data  Message ID 99: 0
16:01:25.813484 R80760000 Read-Data  DHW pump/valve starts: 0
16:01:26.086151 B407639B8 Read-Ack   DHW pump/valve starts: 14776
16:01:26.122807 AF0630000 Unk-DataId Message ID 99: 0
16:01:26.776622 T80000200 Read-Data  Status: 00000010 00000000
16:01:26.887103 B40000200 Read-Ack   Status: 00000010 00000000
16:01:27.778237 T10010600 Write-Data Control setpoint: 6.00
16:01:27.888070 BD0010600 Write-Ack  Control setpoint: 6.00
16:01:28.779267 T00110000 Read-Data  Relative modulation level: 0.00
16:01:28.889897 BC0110000 Read-Ack   Relative modulation level: 0.00
16:01:29.780646 T80190000 Read-Data  Boiler water temperature: 0.00
16:01:29.891203 BC019414C Read-Ack   Boiler water temperature: 65.30
16:01:30.785234 T90395A00 Write-Data Max CH water setpoint: 90.00
16:01:30.895750 BE0394600 Data-Inv   Max CH water setpoint: 70.00
16:01:30.935900 AD0394600 Write-Ack  Max CH water setpoint: 70.00
16:01:31.783469 T80000200 Read-Data  Status: 00000010 00000000
16:01:31.884418 B40000200 Read-Ack   Status: 00000010 00000000
16:01:32.785178 T10010600 Write-Data Control setpoint: 6.00
16:01:32.884948 BD0010600 Write-Ack  Control setpoint: 6.00
16:01:33.786120 T00110000 Read-Data  Relative modulation level: 0.00
16:01:33.886658 BC0110000 Read-Ack   Relative modulation level: 0.00
16:01:34.787487 T80190000 Read-Data  Boiler water temperature: 0.00
16:01:34.888066 BC019414C Read-Ack   Boiler water temperature: 65.30
16:01:35.789012 T00050000 Read-Data  Application-specific flags: 00000000 0
16:01:35.889403 BC00500FF Read-Ack   Application-specific flags: 00000000 255
16:01:36.790264 T80000200 Read-Data  Status: 00000010 00000000
16:01:36.890747 B40000200 Read-Ack   Status: 00000010 00000000
16:01:37.792194 T10010600 Write-Data Control setpoint: 6.00
16:01:37.891857 BD0010600 Write-Ack  Control setpoint: 6.00
16:01:38.793087 T00110000 Read-Data  Relative modulation level: 0.00
16:01:38.893631 BC0110000 Read-Ack   Relative modulation level: 0.00
16:01:39.794540 T80190000 Read-Data  Boiler water temperature: 0.00
16:01:39.894869 BC019414C Read-Ack   Boiler water temperature: 65.30
16:01:40.795838 T801B0AB3 Read-Data  Outside temperature: 10.70
16:01:40.906248 BC01B0A99 Read-Ack   Outside temperature: 10.60
16:01:41.797227 T80000200 Read-Data  Status: 00000010 00000000
16:01:41.897646 B40000200 Read-Ack   Status: 00000010 00000000
16:01:42.798929 T10010600 Write-Data Control setpoint: 6.00
16:01:42.898653 BD0010600 Write-Ack  Control setpoint: 6.00
16:01:43.809905 T00110000 Read-Data  Relative modulation level: 0.00
16:01:43.900319 BC0110000 Read-Ack   Relative modulation level: 0.00
16:01:44.801346 T80190000 Read-Data  Boiler water temperature: 0.00
16:01:44.901785 BC019414C Read-Ack   Boiler water temperature: 65.30
16:01:45.803057 T900E6400 Write-Data Maximum relative modulation level: 100.00
16:01:45.902718 B500E6400 Write-Ack  Maximum relative modulation level: 100.00
16:01:46.814142 T80000200 Read-Data  Status: 00000010 00000000
16:01:46.904626 B40000200 Read-Ack   Status: 00000010 00000000
16:01:47.815779 T10010600 Write-Data Control setpoint: 6.00
16:01:47.905482 BD0010600 Write-Ack  Control setpoint: 6.00
16:01:48.816754 T00110000 Read-Data  Relative modulation level: 0.00
16:01:48.907273 BC0110000 Read-Ack   Relative modulation level: 0.00
16:01:49.818244 T80190000 Read-Data  Boiler water temperature: 0.00
16:01:49.909165 B40194135 Read-Ack   Boiler water temperature: 65.21
16:01:50.819850 T10101200 Write-Data Room setpoint: 18.00
16:01:50.909639 BD0101200 Write-Ack  Room setpoint: 18.00
16:01:51.820985 T80000200 Read-Data  Status: 00000010 00000000
16:01:51.911399 B40000200 Read-Ack   Status: 00000010 00000000
16:01:52.823095 T10010600 Write-Data Control setpoint: 6.00
16:01:52.926558 BD0010600 Write-Ack  Control setpoint: 6.00
16:01:53.823790 T00110000 Read-Data  Relative modulation level: 0.00
16:01:53.913981 BC0110000 Read-Ack   Relative modulation level: 0.00
16:01:54.825191 T80190000 Read-Data  Boiler water temperature: 0.00
16:01:54.915378 B40194133 Read-Ack   Boiler water temperature: 65.20
16:01:55.826753 T901813DC Write-Data Room temperature: 19.86
16:01:55.987500 B501813DC Write-Ack  Room temperature: 19.86
16:01:56.828028 T80000200 Read-Data  Status: 00000010 00000000
16:01:56.918200 B40000200 Read-Ack   Status: 00000010 00000000
16:01:57.829438 T10010600 Write-Data Control setpoint: 6.00
16:01:57.990120 BD0010600 Write-Ack  Control setpoint: 6.00
16:01:58.830494 T00110000 Read-Data  Relative modulation level: 0.00
16:01:58.990925 BC0110000 Read-Ack   Relative modulation level: 0.00
16:01:59.831807 T80190000 Read-Data  Boiler water temperature: 0.00
16:01:59.992772 B40194133 Read-Ack   Boiler water temperature: 65.20
16:02:00.837767 T00090000 Read-Data  Remote override room setpoint: 0.00
16:02:00.875899 R00770000 Read-Data  DHW burner starts: 0
16:02:01.093771 B40774120 Read-Ack   DHW burner starts: 16672
16:02:01.131564 AC0091200 Read-Ack   Remote override room setpoint: 18.00
16:02:01.834642 T80000200 Read-Data  Status: 00000010 00000000
16:02:01.985163 B40000200 Read-Ack   Status: 00000010 00000000
16:02:02.836488 T10010600 Write-Data Control setpoint: 6.00
16:02:02.986090 BD0010600 Write-Ack  Control setpoint: 6.00
16:02:03.837331 T00110000 Read-Data  Relative modulation level: 0.00
16:02:03.987795 BC0110000 Read-Ack   Relative modulation level: 0.00
16:02:04.838950 T80190000 Read-Data  Boiler water temperature: 0.00
16:02:04.989340 B40194133 Read-Ack   Boiler water temperature: 65.20
16:02:05.839949 T00630000 Read-Data  Message ID 99: 0
16:02:05.876512 R00780000 Read-Data  Burner operation hours: 0
16:02:06.190916 BC0780EDA Read-Ack   Burner operation hours: 3802
16:02:06.227523 AF0630000 Unk-DataId Message ID 99: 0
16:02:06.831624 T80000200 Read-Data  Status: 00000010 00000000
16:02:06.992055 B40000200 Read-Ack   Status: 00000010 00000000
16:02:07.833267 T10010600 Write-Data Control setpoint: 6.00
16:02:07.993927 BD0010600 Write-Ack  Control setpoint: 6.00
16:02:08.834533 T00110000 Read-Data  Relative modulation level: 0.00
16:02:08.994802 BC0110000 Read-Ack   Relative modulation level: 0.00
16:02:09.825637 T80190000 Read-Data  Boiler water temperature: 0.00
16:02:09.916083 B40194133 Read-Ack   Boiler water temperature: 65.20
16:02:10.827214 T80640000 Read-Data  Remote override function: 00000000
16:02:10.864958 R80790000 Read-Data  CH pump operation hours: 0
16:02:11.087827 BC0791126 Read-Ack   CH pump operation hours: 4390
16:02:11.129244 AC0640002 Read-Ack   Remote override function: 00000010
16:02:11.828474 T80000200 Read-Data  Status: 00000010 00000000
16:02:11.989111 B40000200 Read-Ack   Status: 00000010 00000000
16:02:12.830393 T10010600 Write-Data Control setpoint: 6.00
16:02:12.991010 BD0010600 Write-Ack  Control setpoint: 6.00
16:02:13.831141 T00110000 Read-Data  Relative modulation level: 0.00
16:02:13.991823 BC0110000 Read-Ack   Relative modulation level: 0.00
16:02:14.832507 T80190000 Read-Data  Boiler water temperature: 0.00
16:02:14.993230 B40194133 Read-Ack   Boiler water temperature: 65.20
16:02:15.834251 T00050000 Read-Data  Application-specific flags: 00000000 0
16:02:15.994574 BC00500FF Read-Ack   Application-specific flags: 00000000 255
16:02:16.845557 T80000200 Read-Data  Status: 00000010 00000000
16:02:16.986120 B40000200 Read-Ack   Status: 00000010 00000000
16:02:17.848043 T10010600 Write-Data Control setpoint: 6.00
16:02:17.987227 BD0010600 Write-Ack  Control setpoint: 6.00
16:02:18.848447 T00110000 Read-Data  Relative modulation level: 0.00
16:02:18.988669 BC0110000 Read-Ack   Relative modulation level: 0.00
16:02:19.849518 T80190000 Read-Data  Boiler water temperature: 0.00
16:02:20.119527 B4019412E Read-Ack   Boiler water temperature: 65.18
16:02:20.851961 T801B0AB3 Read-Data  Outside temperature: 10.70
16:02:20.993644 BC01B0A99 Read-Ack   Outside temperature: 10.60
16:02:21.854124 T80000200 Read-Data  Status: 00000010 00000000
16:02:21.994833 B40000200 Read-Ack   Status: 00000010 00000000
16:02:22.853840 T10010600 Write-Data Control setpoint: 6.00
16:02:23.003861 BD0010600 Write-Ack  Control setpoint: 6.00
16:02:23.958121 T00110000 Read-Data  Relative modulation level: 0.00
16:02:23.985724 BC0110000 Read-Ack   Relative modulation level: 0.00
16:02:24.857734 T80190000 Read-Data  Boiler water temperature: 0.00
16:02:24.987513 BC0194119 Read-Ack   Boiler water temperature: 65.10
16:02:25.858298 T900E6400 Write-Data Maximum relative modulation level: 100.00
16:02:25.998530 B500E6400 Write-Ack  Maximum relative modulation level: 100.00
16:02:26.859416 T80000200 Read-Data  Status: 00000010 00000000
16:02:26.999892 B40000200 Read-Ack   Status: 00000010 00000000
16:02:27.860977 T10010600 Write-Data Control setpoint: 6.00
16:02:28.000872 BD0010600 Write-Ack  Control setpoint: 6.00
16:02:28.862043 T00110000 Read-Data  Relative modulation level: 0.00
16:02:29.002708 BC0110000 Read-Ack   Relative modulation level: 0.00
16:02:29.863422 T80190000 Read-Data  Boiler water temperature: 0.00
16:02:30.004032 BC0194119 Read-Ack   Boiler water temperature: 65.10
16:02:30.865213 T10101200 Write-Data Room setpoint: 18.00
16:02:30.986534 BD0101200 Write-Ack  Room setpoint: 18.00
16:02:31.856404 T80000200 Read-Data  Status: 00000010 00000000
16:02:31.988569 B40000200 Read-Ack   Status: 00000010 00000000
16:02:32.867954 T10010600 Write-Data Control setpoint: 6.00
16:02:32.989554 BD0010600 Write-Ack  Control setpoint: 6.00
16:02:33.868947 T00110000 Read-Data  Relative modulation level: 0.00
16:02:33.991042 BC0110000 Read-Ack   Relative modulation level: 0.00
16:02:34.870383 T80190000 Read-Data  Boiler water temperature: 0.00
16:02:34.992411 BC0194119 Read-Ack   Boiler water temperature: 65.10
16:02:35.872343 T901813DC Write-Data Room temperature: 19.86
16:02:35.993458 B501813DC Write-Ack  Room temperature: 19.86
16:02:36.863355 T80000200 Read-Data  Status: 00000010 00000000
16:02:36.995675 B40000200 Read-Ack   Status: 00000010 00000000
16:02:37.864997 T10010600 Write-Data Control setpoint: 6.00
16:02:37.996421 BD0010600 Write-Ack  Control setpoint: 6.00
16:02:38.866361 T00110000 Read-Data  Relative modulation level: 0.00
16:02:38.998229 BC0110000 Read-Ack   Relative modulation level: 0.00
16:02:39.867635 T80190000 Read-Data  Boiler water temperature: 0.00
16:02:39.988328 B40194100 Read-Ack   Boiler water temperature: 65.00
16:02:40.868983 T00090000 Read-Data  Remote override room setpoint: 0.00
16:02:40.906462 R807A0000 Read-Data  DHW pump/valve operation hours: 0
16:02:41.089559 B407A5BB0 Read-Ack   DHW pump/valve operation hours: 23472
16:02:41.127304 AC0091200 Read-Ack   Remote override room setpoint: 18.00
16:02:41.870318 T80000200 Read-Data  Status: 00000010 00000000
16:02:41.990721 B40000200 Read-Ack   Status: 00000010 00000000
16:02:42.872070 T10010600 Write-Data Control setpoint: 6.00
16:02:42.991747 BD0010600 Write-Ack  Control setpoint: 6.00
16:02:43.872994 T00110000 Read-Data  Relative modulation level: 0.00
16:02:43.993436 BC0110000 Read-Ack   Relative modulation level: 0.00
16:02:44.874377 T80190000 Read-Data  Boiler water temperature: 0.00
16:02:44.994896 B40194100 Read-Ack   Boiler water temperature: 65.00
16:02:45.885578 T00630000 Read-Data  Message ID 99: 0
16:02:45.928554 R007B0000 Read-Data  DHW burner operation hours: 0
16:02:46.196913 BC07B019B Read-Ack   DHW burner operation hours: 411
16:02:46.239620 AF0630000 Unk-DataId Message ID 99: 0
16:02:46.877223 T80000200 Read-Data  Status: 00000010 00000000
16:02:46.987726 B40000200 Read-Ack   Status: 00000010 00000000
16:02:47.878885 T10010600 Write-Data Control setpoint: 6.00
16:02:47.988627 BD0010600 Write-Ack  Control setpoint: 6.00
16:02:48.879964 T00110000 Read-Data  Relative modulation level: 0.00
16:02:48.990744 BC0110000 Read-Ack   Relative modulation level: 0.00
16:02:49.881709 T80190000 Read-Data  Boiler water temperature: 0.00
16:02:49.991749 B40194100 Read-Ack   Boiler water temperature: 65.00
16:02:50.795677 Command: TT=0
16:02:50.833234 OK
16:02:50.890311 T00740000 Read-Data  Burner starts: 0
16:02:51.093221 BC0745238 Read-Ack   Burner starts: 21048
16:02:51.884123 T80000200 Read-Data  Status: 00000010 00000000
16:02:51.994544 B40000200 Read-Ack   Status: 00000010 00000000
16:02:52.885781 T10010600 Write-Data Control setpoint: 6.00
16:02:52.995561 BD0010600 Write-Ack  Control setpoint: 6.00
16:02:53.886970 T00110000 Read-Data  Relative modulation level: 0.00
16:02:53.997262 BC0110000 Read-Ack   Relative modulation level: 0.00
16:02:54.888188 T80190000 Read-Data  Boiler water temperature: 0.00
16:02:54.988674 B40194100 Read-Ack   Boiler water temperature: 65.00
16:02:55.889621 T00050000 Read-Data  Application-specific flags: 00000000 0
16:02:55.990114 BC00500FF Read-Ack   Application-specific flags: 00000000 255
16:02:56.891039 T80000200 Read-Data  Status: 00000010 00000000
16:02:56.991618 B40000200 Read-Ack   Status: 00000010 00000000
16:02:57.892815 T10010600 Write-Data Control setpoint: 6.00
16:02:57.992536 BD0010600 Write-Ack  Control setpoint: 6.00
16:02:58.893739 T00110000 Read-Data  Relative modulation level: 0.00
16:02:58.994267 BC0110000 Read-Ack   Relative modulation level: 0.00
16:02:59.895478 T80190000 Read-Data  Boiler water temperature: 0.00
16:02:59.995719 B40194100 Read-Ack   Boiler water temperature: 65.00
16:03:00.897732 T801B0AB3 Read-Data  Outside temperature: 10.70
16:03:00.997080 BC01B0A99 Read-Ack   Outside temperature: 10.60
16:03:01.898390 T80000200 Read-Data  Status: 00000010 00000000
16:03:01.998855 B40000200 Read-Ack   Status: 00000010 00000000
16:03:02.899770 T10010600 Write-Data Control setpoint: 6.00
16:03:02.989467 BD0010600 Write-Ack  Control setpoint: 6.00
16:03:03.900689 T00110000 Read-Data  Relative modulation level: 0.00
16:03:03.991156 BC0110000 Read-Ack   Relative modulation level: 0.00
16:03:04.902067 T80190000 Read-Data  Boiler water temperature: 0.00
16:03:04.992518 BC01940CC Read-Ack   Boiler water temperature: 64.80
16:03:05.904248 T900E6400 Write-Data Maximum relative modulation level: 100.00
16:03:05.993796 B500E6400 Write-Ack  Maximum relative modulation level: 100.00
16:03:06.904965 T80000200 Read-Data  Status: 00000010 00000000
16:03:06.995420 B40000200 Read-Ack   Status: 00000010 00000000
16:03:07.906546 T10010600 Write-Data Control setpoint: 6.00
16:03:07.996256 BD0010600 Write-Ack  Control setpoint: 6.00
16:03:08.907523 T00110000 Read-Data  Relative modulation level: 0.00
16:03:09.008029 BC0110000 Read-Ack   Relative modulation level: 0.00
16:03:09.909011 T80190000 Read-Data  Boiler water temperature: 0.00
16:03:09.999434 BC01940CC Read-Ack   Boiler water temperature: 64.80
16:03:10.910809 T10101200 Write-Data Room setpoint: 18.00
16:03:11.000511 BD0101200 Write-Ack  Room setpoint: 18.00
16:03:11.911921 T80000200 Read-Data  Status: 00000010 00000000
16:03:12.002724 B40000200 Read-Ack   Status: 00000010 00000000
16:03:12.913744 T10010600 Write-Data Control setpoint: 6.00
16:03:13.003288 BD0010600 Write-Ack  Control setpoint: 6.00
16:03:13.914580 T00110000 Read-Data  Relative modulation level: 0.00
16:03:14.005071 BC0110000 Read-Ack   Relative modulation level: 0.00
16:03:14.915988 T80190000 Read-Data  Boiler water temperature: 0.00
16:03:15.006461 BC01940CC Read-Ack   Boiler water temperature: 64.80
16:03:15.917817 T101813D7 Write-Data Room temperature: 19.84
16:03:16.096804 BD01813D7 Write-Ack  Room temperature: 19.84
16:03:16.918884 T80000200 Read-Data  Status: 00000010 00000000
16:03:17.009289 B40000200 Read-Ack   Status: 00000010 00000000
16:03:17.920532 T10010600 Write-Data Control setpoint: 6.00
16:03:18.010672 BD0010600 Write-Ack  Control setpoint: 6.00
16:03:18.911663 T00110000 Read-Data  Relative modulation level: 0.00
16:03:19.012031 BC0110000 Read-Ack   Relative modulation level: 0.00
16:03:19.913002 T80190000 Read-Data  Boiler water temperature: 0.00
16:03:20.013657 B401940B3 Read-Ack   Boiler water temperature: 64.70
16:03:20.924592 T00090000 Read-Data  Remote override room setpoint: 0.00
16:03:20.955448 R00740000 Read-Data  Burner starts: 0
16:03:21.096559 BC0745238 Read-Ack   Burner starts: 21048
16:03:21.128456 AC0090000 Read-Ack   Remote override room setpoint: 0.00
16:03:21.915812 T00090000 Read-Data  Remote override room setpoint: 0.00
16:03:21.953355 R80750000 Read-Data  CH pump starts: 0
16:03:22.196469 BC0757180 Read-Ack   CH pump starts: 29056
16:03:22.236916 AC0090000 Read-Ack   Remote override room setpoint: 0.00
16:03:22.917225 T00090000 Read-Data  Remote override room setpoint: 0.00
16:03:22.954479 R80760000 Read-Data  DHW pump/valve starts: 0
16:03:23.097694 B407639B8 Read-Ack   DHW pump/valve starts: 14776
16:03:23.135844 AC0090000 Read-Ack   Remote override room setpoint: 0.00
16:03:23.918995 T00000000 Read-Data  Status: 00000000 00000000
16:03:24.019142 BC0000000 Read-Ack   Status: 00000000 00000000
16:03:24.930326 T10010600 Write-Data Control setpoint: 6.00
16:03:25.063495 BD0010600 Write-Ack  Control setpoint: 6.00
16:03:25.921347 T00110000 Read-Data  Relative modulation level: 0.00
16:03:26.021766 BC0110000 Read-Ack   Relative modulation level: 0.00
16:03:26.932671 T80190000 Read-Data  Boiler water temperature: 0.00
16:03:27.023200 B401940B3 Read-Ack   Boiler water temperature: 64.70
16:03:27.934087 T00630000 Read-Data  Message ID 99: 0
16:03:27.971946 R00770000 Read-Data  DHW burner starts: 0
16:03:28.295049 B40774120 Read-Ack   DHW burner starts: 16672
16:03:28.332906 AF0630000 Unk-DataId Message ID 99: 0
16:03:28.925803 T00000000 Read-Data  Status: 00000000 00000000
16:03:29.096111 BC0000000 Read-Ack   Status: 00000000 00000000
16:03:29.927264 T10010600 Write-Data Control setpoint: 6.00
16:03:30.095402 BD0010600 Write-Ack  Control setpoint: 6.00
16:03:30.928321 T00110000 Read-Data  Relative modulation level: 0.00
16:03:31.098860 BC0110000 Read-Ack   Relative modulation level: 0.00
16:03:31.929673 T80190000 Read-Data  Boiler water temperature: 0.00
16:03:32.090409 B401940B3 Read-Ack   Boiler water temperature: 64.70
16:03:32.950941 T00770000 Read-Data  DHW burner starts: 0
16:03:33.191804 B40774120 Read-Ack   DHW burner starts: 16672
16:03:33.933164 T00000000 Read-Data  Status: 00000000 00000000
16:03:34.093005 BC0000000 Read-Ack   Status: 00000000 00000000
16:03:34.934753 T10010600 Write-Data Control setpoint: 6.00
16:03:35.096071 BD0010600 Write-Ack  Control setpoint: 6.00
16:03:35.935172 T00110000 Read-Data  Relative modulation level: 0.00
16:03:36.095749 BC0110000 Read-Ack   Relative modulation level: 0.00
16:03:36.936893 T80190000 Read-Data  Boiler water temperature: 0.00
16:03:37.097181 B401940B3 Read-Ack   Boiler water temperature: 64.70
16:03:37.938032 T00050000 Read-Data  Application-specific flags: 00000000 0
16:03:38.098562 BC00500FF Read-Ack   Application-specific flags: 00000000 255
16:03:38.939460 T00000000 Read-Data  Status: 00000000 00000000
16:03:39.090160 BC0000000 Read-Ack   Status: 00000000 00000000
16:03:39.941163 T10010600 Write-Data Control setpoint: 6.00
16:03:40.090902 BD0010600 Write-Ack  Control setpoint: 6.00
16:03:40.942171 T00110000 Read-Data  Relative modulation level: 0.00
16:03:41.102785 BC0110000 Read-Ack   Relative modulation level: 0.00
16:03:41.943566 T80190000 Read-Data  Boiler water temperature: 0.00
16:03:42.104275 B401940B3 Read-Ack   Boiler water temperature: 64.70
16:03:42.944965 T801B0AB3 Read-Data  Outside temperature: 10.70
16:03:43.105491 BC01B0A99 Read-Ack   Outside temperature: 10.60
16:03:43.946391 T00000000 Read-Data  Status: 00000000 00000000
16:03:44.106912 BC0000000 Read-Ack   Status: 00000000 00000000
16:03:44.948199 T10010600 Write-Data Control setpoint: 6.00
16:03:45.105506 BD0010600 Write-Ack  Control setpoint: 6.00
16:03:45.949233 T00110000 Read-Data  Relative modulation level: 0.00
16:03:46.091313 BC0110000 Read-Ack   Relative modulation level: 0.00
16:03:46.950450 T80190000 Read-Data  Boiler water temperature: 0.00
16:03:47.092690 B401940B3 Read-Ack   Boiler water temperature: 64.70
16:03:47.952235 T900E6400 Write-Data Maximum relative modulation level: 100.00
16:03:48.093638 B500E6400 Write-Ack  Maximum relative modulation level: 100.00
16:03:48.953589 T00000000 Read-Data  Status: 00000000 00000000
16:03:49.095590 BC0000000 Read-Ack   Status: 00000000 00000000
16:03:49.955351 T10010600 Write-Data Control setpoint: 6.00
16:03:50.106477 BD0010600 Write-Ack  Control setpoint: 6.00
16:03:50.956564 T00110000 Read-Data  Relative modulation level: 0.00
16:03:51.098098 BC0110000 Read-Ack   Relative modulation level: 0.00
16:03:51.957853 T80190000 Read-Data  Boiler water temperature: 0.00
16:03:52.099948 BC0194099 Read-Ack   Boiler water temperature: 64.60
16:03:52.959220 T10100F00 Write-Data Room setpoint: 15.00
16:03:53.100593 BD0100F00 Write-Ack  Room setpoint: 15.00
16:03:53.960201 T00000000 Read-Data  Status: 00000000 00000000
16:03:54.091103 BC0000000 Read-Ack   Status: 00000000 00000000
16:03:54.961887 T10010600 Write-Data Control setpoint: 6.00
16:03:55.112803 BD0010600 Write-Ack  Control setpoint: 6.00
16:03:55.962942 T00110000 Read-Data  Relative modulation level: 0.00
16:03:56.093766 BC0110000 Read-Ack   Relative modulation level: 0.00
16:03:56.964353 T80190000 Read-Data  Boiler water temperature: 0.00