Opentherm gateway and Vokera Unica HE
david_wallis
Post by david_wallis »
I have built the gateway and connected it to my boiler, at the moment I don't have an opentherm thermostat.. Seem to be in short supply in the UK at a sensible price.
My plan was to wire the original thermostat into the opentherm board initially, but allowing me to monitor when the boiler is coming on etc.
When connected the boiler it is recognised and its two seven segment displays change to ot
however Shorting the cables has no effect on firing the boiler up... (it does recognise it on the log.)
here is the log:
15:04:49.724397	R00110000	Read-Data 	Relative modulation level: 0.00
15:04:49.955178	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:04:49.956353	Command: PR=A
15:04:49.998094	PR: A=OpenTherm Gateway 4.0.1
15:04:50.775258	R00000000	Read-Data 	Status: 00000000 00000000
15:04:51.055294	BC0000000	Read-Ack  	Status: 00000000 00000000
15:04:51.825436	R801C0000	Read-Data 	Return water temperature: 0.00
15:04:52.048426	B401C3000	Read-Ack  	Return water temperature: 48.00
15:04:52.882543	R900E6400	Write-Data	Maximum relative modulation level: 100.00
15:04:53.152636	B500E6400	Write-Ack 	Maximum relative modulation level: 100.00
15:04:53.927693	R00000000	Read-Data 	Status: 00000000 00000000
15:04:54.154731	BC0000000	Read-Ack  	Status: 00000000 00000000
15:04:54.978674	R00000000	Read-Data 	Status: 00000000 00000000
15:04:55.258718	BC0000000	Read-Ack  	Status: 00000000 00000000
15:04:56.028807	R80190000	Read-Data 	Boiler water temperature: 0.00
15:04:56.255750	B40193300	Read-Ack  	Boiler water temperature: 51.00
15:04:57.078705	R10010A00	Write-Data	Control setpoint: 10.00
15:04:57.359640	BD0010A00	Write-Ack 	Control setpoint: 10.00
15:04:58.129760	R80380000	Read-Data 	DHW setpoint: 0.00
15:04:58.359785	BC0383700	Read-Ack  	DHW setpoint: 55.00
15:04:59.179956	R00390000	Read-Data 	Max CH water setpoint: 0.00
15:04:59.460060	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
15:05:00.240044	R00000000	Read-Data 	Status: 00000000 00000000
15:05:00.466018	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:01.290082	R00120000	Read-Data 	CH water pressure: 0.00
15:05:01.470114	Error 03
15:05:02.350106	R00120000	Read-Data 	CH water pressure: 0.00
15:05:02.577082	B60120000	Data-Inv  	CH water pressure: 0.00
15:05:03.400186	R00000000	Read-Data 	Status: 00000000 00000000
15:05:03.660202	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:04.461240	R80190000	Read-Data 	Boiler water temperature: 0.00
15:05:04.663234	B40193300	Read-Ack  	Boiler water temperature: 51.00
15:05:05.511333	R10010A00	Write-Data	Control setpoint: 10.00
15:05:05.769291	BD0010A00	Write-Ack 	Control setpoint: 10.00
15:05:06.561365	R00000000	Read-Data 	Status: 00000000 00000000
15:05:06.763380	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:07.606309	R00110000	Read-Data 	Relative modulation level: 0.00
15:05:07.866440	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:05:08.657481	R00000000	Read-Data 	Status: 00000000 00000000
15:05:08.867506	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:09.707532	R801C0000	Read-Data 	Return water temperature: 0.00
15:05:09.967559	B401C3000	Read-Ack  	Return water temperature: 48.00
15:05:10.767607	R900E6400	Write-Data	Maximum relative modulation level: 100.00
15:05:10.967553	B500E6400	Write-Ack 	Maximum relative modulation level: 100.00
15:05:11.812670	R00000000	Read-Data 	Status: 00000000 00000000
15:05:12.067744	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:12.867745	R00000000	Read-Data 	Status: 00000000 00000000
15:05:13.075783	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:13.917769	R80190000	Read-Data 	Boiler water temperature: 0.00
15:05:14.177795	B40193300	Read-Ack  	Boiler water temperature: 51.00
15:05:14.967729	R10010A00	Write-Data	Control setpoint: 10.00
15:05:15.177863	BD0010A00	Write-Ack 	Control setpoint: 10.00
15:05:16.018891	R80380000	Read-Data 	DHW setpoint: 0.00
15:05:16.278883	BC0383700	Read-Ack  	DHW setpoint: 55.00
15:05:17.067031	R00390000	Read-Data 	Max CH water setpoint: 0.00
15:05:17.279001	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
15:05:18.119039	R00000000	Read-Data 	Status: 00000000 00000000
15:05:18.379062	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:19.169146	R00120000	Read-Data 	CH water pressure: 0.00
15:05:19.379136	B60120000	Data-Inv  	CH water pressure: 0.00
15:05:20.219170	R00000000	Read-Data 	Status: 00000000 00000000
15:05:20.479196	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:21.269318	R80190000	Read-Data 	Boiler water temperature: 0.00
15:05:21.479249	B40193300	Read-Ack  	Boiler water temperature: 51.00
15:05:22.320262	R10010A00	Write-Data	Control setpoint: 10.00
15:05:22.579273	BD0010A00	Write-Ack 	Control setpoint: 10.00
15:05:23.380325	R00000000	Read-Data 	Status: 00000000 00000000
15:05:23.587277	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:24.430412	R00110000	Read-Data 	Relative modulation level: 0.00
15:05:24.680432	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:05:25.473478	R00000000	Read-Data 	Status: 00000000 00000000
15:05:25.680452	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:26.523524	R801C0000	Read-Data 	Return water temperature: 0.00
15:05:26.790569	B401C3000	Read-Ack  	Return water temperature: 48.00
15:05:27.582537	R900E6400	Write-Data	Maximum relative modulation level: 100.00
15:05:27.790642	B500E6400	Write-Ack 	Maximum relative modulation level: 100.00
15:05:28.630651	R00000000	Read-Data 	Status: 00000000 00000000
15:05:28.890653	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:29.685715	R00000000	Read-Data 	Status: 00000000 00000000
15:05:29.890704	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:30.727761	R80190000	Read-Data 	Boiler water temperature: 0.00
15:05:30.990662	B40193300	Read-Ack  	Boiler water temperature: 51.00
15:05:31.781799	R10010A00	Write-Data	Control setpoint: 10.00
15:05:31.991828	BD0010A00	Write-Ack 	Control setpoint: 10.00
15:05:32.828850	R80380000	Read-Data 	DHW setpoint: 0.00
15:05:33.091886	BC0383700	Read-Ack  	DHW setpoint: 55.00
15:05:33.881965	R00390000	Read-Data 	Max CH water setpoint: 0.00
15:05:34.088985	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
15:05:34.932052	R00000000	Read-Data 	Status: 00000000 00000000
15:05:35.192063	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:35.982098	R00120000	Read-Data 	CH water pressure: 0.00
15:05:36.192108	B60120000	Data-Inv  	CH water pressure: 0.00
15:05:37.032136	R00000000	Read-Data 	Status: 00000000 00000000
15:05:37.292204	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:38.092221	R80190000	Read-Data 	Boiler water temperature: 0.00
15:05:38.292211	B40193300	Read-Ack  	Boiler water temperature: 51.00
15:05:39.142272	R10010A00	Write-Data	Control setpoint: 10.00
15:05:39.392268	BD0010A00	Write-Ack 	Control setpoint: 10.00
15:05:40.193268	R00000000	Read-Data 	Status: 00000000 00000000
15:05:40.393288	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:41.243336	R00110000	Read-Data 	Relative modulation level: 0.00
15:05:41.503381	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:05:42.293510	R00000000	Read-Data 	Status: 00000000 00000000
15:05:42.495454	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:43.343522	R801C0000	Read-Data 	Return water temperature: 0.00
15:05:43.597539	B401C3000	Read-Ack  	Return water temperature: 48.00
15:05:44.414575	R900E6400	Write-Data	Maximum relative modulation level: 100.00
15:05:44.704599	B500E6400	Write-Ack 	Maximum relative modulation level: 100.00
15:05:45.464663	R00000000	Read-Data 	Status: 00000000 00000000
15:05:45.704645	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:46.514695	R00000000	Read-Data 	Status: 00000000 00000000
15:05:46.808702	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:47.564761	R80190000	Read-Data 	Boiler water temperature: 0.00
15:05:47.809792	B40193300	Read-Ack  	Boiler water temperature: 51.00
15:05:48.615759	R10010A00	Write-Data	Control setpoint: 10.00
15:05:48.905776	BD0010A00	Write-Ack 	Control setpoint: 10.00
15:05:49.665856	R80380000	Read-Data 	DHW setpoint: 0.00
15:05:49.905881	BC0383700	Read-Ack  	DHW setpoint: 55.00
15:05:50.715956	R00390000	Read-Data 	Max CH water setpoint: 0.00
15:05:51.009895	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
15:05:51.766014	R00000000	Read-Data 	Status: 00000000 00000000
15:05:52.009062	BC0000000	Read-Ack  	Status: 00000000 00000000
15:05:52.816095	R00120000	Read-Data 	CH water pressure: 0.00
15:05:53.116079	B60120000	Data-Inv  	CH water pressure: 0.00
15:05:53.866007	R00000000	Read-Data 	Status: 00000000 00000000
15:05:54.116039	BC0000000	Read-Ack  	Status: 00000000 00000000
what should I try next?
Thanks
David
Re: Opentherm gateway and Vokera Unica HE
david_wallis wrote:what should I try next?
Firmware 4.2
david_wallis
Thanks, I thought I was on the latest firmware, but looking at the release date, I was at the time when I last tried, so didnt think to check for another release..
Just upgraded to that and it still doesn't fire..
logs show the version change too.
10:58:12.228560	R00000000	Read-Data 	Status: 00000000 00000000
10:58:12.452384	BC0000000	Read-Ack  	Status: 00000000 00000000
10:58:12.453884	Command: PR=A
10:58:12.479337	SE
10:58:13.279355	R801C0000	Read-Data 	Return water temperature: 0.00
10:58:13.549400	B401C2700	Read-Ack  	Return water temperature: 39.00
10:58:13.550777	Command: PR=A
10:58:13.599390	PR: A=OpenTherm Gateway 4.0.1
10:58:14.325415	R900E6400	Write-Data	Maximum relative modulation level: 100.00
10:58:14.548629	B500E6400	Write-Ack 	Maximum relative modulation level: 100.00
10:58:15.375533	R00000000	Read-Data 	Status: 00000000 00000000
10:58:15.665519	BC0000000	Read-Ack  	Status: 00000000 00000000
10:58:16.440540	R00000000	Read-Data 	Status: 00000000 00000000
10:58:16.653579	BC0000000	Read-Ack  	Status: 00000000 00000000
10:58:17.481663	R80190000	Read-Data 	Boiler water temperature: 0.00
10:58:17.751557	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
10:58:18.526708	R10010A00	Write-Data	Control setpoint: 10.00
10:58:18.749702	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:58:19.582759	R80380000	Read-Data 	DHW setpoint: 0.00
10:58:19.856849	BC0383700	Read-Ack  	DHW setpoint: 55.00
10:58:20.632775	R00390000	Read-Data 	Max CH water setpoint: 0.00
10:58:20.860807	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
10:58:21.852635	R00000000	Read-Data 	Status: 00000000 00000000
10:58:22.640985	BC0000000	Read-Ack  	Status: 00000000 00000000
10:58:22.883729	R00120000	Read-Data 	CH water pressure: 0.00
10:58:22.961131	B60120000	Data-Inv  	CH water pressure: 0.00
10:58:23.788058	R00000000	Read-Data 	Status: 00000000 00000000
10:58:24.070125	BC0000000	Read-Ack  	Status: 00000000 00000000
10:58:24.833104	R80190000	Read-Data 	Boiler water temperature: 0.00
10:58:25.071234	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
10:58:25.885049	R10010A00	Write-Data	Control setpoint: 10.00
10:58:26.165238	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:58:27.180802	R00000000	Read-Data 	Status: 00000000 00000000
10:58:27.182649	BC0000000	Read-Ack  	Status: 00000000 00000000
10:58:27.995331	R00110000	Read-Data 	Relative modulation level: 0.00
10:58:28.272346	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:58:29.045329	R00000000	Read-Data 	Status: 00000000 00000000
10:58:29.269343	BC0000000	Read-Ack  	Status: 00000000 00000000
10:58:30.096354	R801C0000	Read-Data 	Return water temperature: 0.00
10:58:30.360474	B401C2700	Read-Ack  	Return water temperature: 39.00
10:58:58.878957	OpenTherm Gateway 4.2
10:58:58.909073	Thermostat disconnected
10:59:03.030296	R00000000	Read-Data 	Status: 00000000 00000000
10:59:04.047276	R00000000	Read-Data 	Status: 00000000 00000000
10:59:04.297435	BC0000000	Read-Ack  	Status: 00000000 00000000
10:59:05.104451	R80190000	Read-Data 	Boiler water temperature: 0.00
10:59:05.393476	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
10:59:06.152482	R10010A00	Write-Data	Control setpoint: 10.00
10:59:06.398495	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:59:07.208446	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
10:59:07.499497	BC0060303	Read-Ack  	Remote parameter flags: 00000011 00000011
10:59:08.258391	R00110000	Read-Data 	Relative modulation level: 0.00
10:59:08.493412	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:59:09.314530	R001B0000	Read-Data 	Outside temperature: 0.00
10:59:09.595545	BF01B0000	Unk-DataId	Outside temperature: 0.00
10:59:10.355624	R801C0000	Read-Data 	Return water temperature: 0.00
10:59:10.604660	B401C2700	Read-Ack  	Return water temperature: 39.00
10:59:11.405699	R900E6400	Write-Data	Maximum relative modulation level: 100.00
10:59:11.701709	B500E6400	Write-Ack 	Maximum relative modulation level: 100.00
10:59:12.465790	R00300000	Read-Data 	DHW setpoint boundaries: 0 0
10:59:12.705801	B40303C23	Read-Ack  	DHW setpoint boundaries: 60 35
10:59:13.515879	R00000000	Read-Data 	Status: 00000000 00000000
10:59:13.807861	BC0000000	Read-Ack  	Status: 00000000 00000000
10:59:14.566925	R80190000	Read-Data 	Boiler water temperature: 0.00
10:59:14.801921	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
10:59:15.615962	R10010A00	Write-Data	Control setpoint: 10.00
10:59:15.913982	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:59:16.673063	R80380000	Read-Data 	DHW setpoint: 0.00
10:59:16.908041	BC0383700	Read-Ack  	DHW setpoint: 55.00
10:59:17.712973	R00390000	Read-Data 	Max CH water setpoint: 0.00
10:59:18.021095	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
10:59:18.770134	R80310000	Read-Data 	Max CH setpoint boundaries: 0 0
10:59:19.013155	B40315028	Read-Ack  	Max CH setpoint boundaries: 80 40
10:59:19.819203	R00120000	Read-Data 	CH water pressure: 0.00
10:59:20.109220	B60120000	Data-Inv  	CH water pressure: 0.00
10:59:20.875275	R00000000	Read-Data 	Status: 00000000 00000000
10:59:21.108282	BC0000000	Read-Ack  	Status: 00000000 00000000
10:59:21.925344	R80190000	Read-Data 	Boiler water temperature: 0.00
10:59:22.210540	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
10:59:22.971485	R10010A00	Write-Data	Control setpoint: 10.00
10:59:23.214420	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:59:24.021467	R00740000	Read-Data 	Burner starts: 0
10:59:24.311477	BF0740000	Unk-DataId	Burner starts: 0
10:59:25.070521	R00110000	Read-Data 	Relative modulation level: 0.00
10:59:25.242547	Error 03
10:59:26.117581	R00110000	Read-Data 	Relative modulation level: 0.00
10:59:26.319616	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:59:27.155669	R001B0000	Read-Data 	Outside temperature: 0.00
10:59:27.358690	Error 03
10:59:28.175721	R001B0000	Read-Data 	Outside temperature: 0.00
10:59:28.420761	BF01B0000	Unk-DataId	Outside temperature: 0.00
10:59:28.492782	Error 03
10:59:29.241797	R801C0000	Read-Data 	Return water temperature: 0.00
10:59:29.515864	B401C2700	Read-Ack  	Return water temperature: 39.00
10:59:30.292808	R900E6400	Write-Data	Maximum relative modulation level: 100.00
10:59:30.515813	B500E6400	Write-Ack 	Maximum relative modulation level: 100.00
10:59:31.340991	R80750000	Read-Data 	CH pump starts: 0
10:59:31.621901	B70750000	Unk-DataId	CH pump starts: 0
10:59:32.397935	R80000100	Read-Data 	Status: 00000001 00000000
10:59:32.621931	B40000100	Read-Ack  	Status: 00000001 00000000
10:59:33.447979	R80190000	Read-Data 	Boiler water temperature: 0.00
10:59:33.717926	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
10:59:34.495085	R10015000	Write-Data	Control setpoint: 80.00
10:59:34.728037	BD0015000	Write-Ack 	Control setpoint: 80.00
10:59:35.554119	R80380000	Read-Data 	DHW setpoint: 0.00
10:59:35.825122	BC0383700	Read-Ack  	DHW setpoint: 55.00
10:59:36.599170	R00390000	Read-Data 	Max CH water setpoint: 0.00
10:59:36.834178	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
10:59:37.656265	R80760000	Read-Data 	DHW pump/valve starts: 0
10:59:37.930297	B70760000	Unk-DataId	DHW pump/valve starts: 0
10:59:38.706302	R00120000	Read-Data 	CH water pressure: 0.00
10:59:38.939296	B60120000	Data-Inv  	CH water pressure: 0.00
10:59:39.752258	R80000100	Read-Data 	Status: 00000001 00000000
10:59:40.026391	B40000100	Read-Ack  	Status: 00000001 00000000
10:59:40.812400	R80190000	Read-Data 	Boiler water temperature: 0.00
10:59:41.029400	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
10:59:41.852435	R10015000	Write-Data	Control setpoint: 80.00
10:59:42.132498	BD0015000	Write-Ack 	Control setpoint: 80.00
10:59:42.903558	R00770000	Read-Data 	DHW burner starts: 0
10:59:43.134549	BF0770000	Unk-DataId	DHW burner starts: 0
10:59:43.958627	R00110000	Read-Data 	Relative modulation level: 0.00
10:59:44.228612	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:59:45.010645	R001B0000	Read-Data 	Outside temperature: 0.00
10:59:45.231663	BF01B0000	Unk-DataId	Outside temperature: 0.00
10:59:46.054771	R801C0000	Read-Data 	Return water temperature: 0.00
10:59:46.334750	B401C2700	Read-Ack  	Return water temperature: 39.00
10:59:47.108787	R900E6400	Write-Data	Maximum relative modulation level: 100.00
10:59:47.337779	B500E6400	Write-Ack 	Maximum relative modulation level: 100.00
10:59:48.158832	R00780000	Read-Data 	Burner operation hours: 0
10:59:48.440853	BF0780000	Unk-DataId	Burner operation hours: 0
10:59:49.208905	R80000100	Read-Data 	Status: 00000001 00000000
10:59:49.433933	B40000100	Read-Ack  	Status: 00000001 00000000
10:59:50.264978	R80190000	Read-Data 	Boiler water temperature: 0.00
10:59:50.546987	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
10:59:51.315025	R10015000	Write-Data	Control setpoint: 80.00
10:59:51.540056	BD0015000	Write-Ack 	Control setpoint: 80.00
10:59:52.372070	R80380000	Read-Data 	DHW setpoint: 0.00
10:59:52.642344	BC0383700	Read-Ack  	DHW setpoint: 55.00
10:59:53.422162	R00390000	Read-Data 	Max CH water setpoint: 0.00
10:59:53.636166	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
10:59:54.488196	R80790000	Read-Data 	CH pump operation hours: 0
10:59:54.742196	B70790000	Unk-DataId	CH pump operation hours: 0
10:59:55.538248	R00120000	Read-Data 	CH water pressure: 0.00
10:59:55.741225	B60120000	Data-Inv  	CH water pressure: 0.00
10:59:56.584296	R00000000	Read-Data 	Status: 00000000 00000000
10:59:56.844351	BC0000000	Read-Ack  	Status: 00000000 00000000
10:59:57.634417	R80190000	Read-Data 	Boiler water temperature: 0.00
10:59:57.847369	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
10:59:58.690408	R10010A00	Write-Data	Control setpoint: 10.00
10:59:58.949431	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:59:59.739434	R807A0000	Read-Data 	DHW pump/valve operation hours: 0
10:59:59.952539	B707A0000	Unk-DataId	DHW pump/valve operation hours: 0
11:00:00.795572	R00110000	Read-Data 	Relative modulation level: 0.00
11:00:01.049583	BC0110000	Read-Ack  	Relative modulation level: 0.00
11:00:01.845609	R007B0000	Read-Data 	DHW burner operation hours: 0
11:00:02.058648	BF07B0000	Unk-DataId	DHW burner operation hours: 0
11:00:02.901662	R801C0000	Read-Data 	Return water temperature: 0.00
11:00:03.145684	B401C2700	Read-Ack  	Return water temperature: 39.00
11:00:03.941757	R900E6400	Write-Data	Maximum relative modulation level: 100.00
11:00:04.154793	B500E6400	Write-Ack 	Maximum relative modulation level: 100.00
11:00:05.000786	R00740000	Read-Data 	Burner starts: 0
11:00:05.251761	BF0740000	Unk-DataId	Burner starts: 0
11:00:06.057748	R80000100	Read-Data 	Status: 00000001 00000000
11:00:06.348741	B40000100	Read-Ack  	Status: 00000001 00000000
11:00:07.112781	R80190000	Read-Data 	Boiler water temperature: 0.00
11:00:07.356828	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
11:00:08.162877	R10015000	Write-Data	Control setpoint: 80.00
11:00:08.454917	BD0015000	Write-Ack 	Control setpoint: 80.00
11:00:09.218960	R80380000	Read-Data 	DHW setpoint: 0.00
11:00:09.452985	BC0383700	Read-Ack  	DHW setpoint: 55.00
11:00:10.271207	R00390000	Read-Data 	Max CH water setpoint: 0.00
11:00:10.561174	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
11:00:11.315200	R80750000	Read-Data 	CH pump starts: 0
11:00:11.559251	B70750000	Unk-DataId	CH pump starts: 0
11:00:12.365272	R00120000	Read-Data 	CH water pressure: 0.00
11:00:12.656332	B60120000	Data-Inv  	CH water pressure: 0.00
11:00:13.431311	R80000100	Read-Data 	Status: 00000001 00000000
11:00:13.665307	B40000100	Read-Ack  	Status: 00000001 00000000
11:00:14.471346	R80190000	Read-Data 	Boiler water temperature: 0.00
11:00:14.763378	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
11:00:15.527561	R10015000	Write-Data	Control setpoint: 80.00
11:00:15.761376	BD0015000	Write-Ack 	Control setpoint: 80.00
11:00:16.577456	R80760000	Read-Data 	DHW pump/valve starts: 0
11:00:16.867478	B70760000	Unk-DataId	DHW pump/valve starts: 0
11:00:17.627547	R00110000	Read-Data 	Relative modulation level: 0.00
11:00:17.861565	BC0110000	Read-Ack  	Relative modulation level: 0.00
11:00:18.673625	R00770000	Read-Data 	DHW burner starts: 0
11:00:18.963653	BF0770000	Unk-DataId	DHW burner starts: 0
11:00:19.722556	R801C0000	Read-Data 	Return water temperature: 0.00
11:00:19.967679	B401C2700	Read-Ack  	Return water temperature: 39.00
11:00:20.772675	R900E6400	Write-Data	Maximum relative modulation level: 100.00
11:00:21.069702	B500E6400	Write-Ack 	Maximum relative modulation level: 100.00
11:00:21.829890	R00780000	Read-Data 	Burner operation hours: 0
11:00:22.073820	BF0780000	Unk-DataId	Burner operation hours: 0
11:00:22.885815	R80000100	Read-Data 	Status: 00000001 00000000
11:00:23.166831	B40000100	Read-Ack  	Status: 00000001 00000000
11:00:23.935919	R80190000	Read-Data 	Boiler water temperature: 0.00
11:00:24.169920	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
11:00:24.991918	R10015000	Write-Data	Control setpoint: 80.00
11:00:25.271969	BD0015000	Write-Ack 	Control setpoint: 80.00
11:00:26.036067	R80380000	Read-Data 	DHW setpoint: 0.00
11:00:26.274801	BC0383700	Read-Ack  	DHW setpoint: 55.00
11:00:27.080173	R00390000	Read-Data 	Max CH water setpoint: 0.00
11:00:27.389079	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
11:00:28.511307	R80790000	Read-Data 	CH pump operation hours: 0
11:00:28.539157	B70790000	Unk-DataId	CH pump operation hours: 0
11:00:29.193195	R00120000	Read-Data 	CH water pressure: 0.00
11:00:29.475306	B60120000	Data-Inv  	CH water pressure: 0.00
11:00:30.235255	R80000100	Read-Data 	Status: 00000001 00000000
11:00:30.478381	B40000100	Read-Ack  	Status: 00000001 00000000
11:00:31.426296	R80190000	Read-Data 	Boiler water temperature: 0.00
11:00:31.579345	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
11:00:32.349422	R10015000	Write-Data	Control setpoint: 80.00
11:00:32.578563	BD0015000	Write-Ack 	Control setpoint: 80.00
11:00:33.398505	R807A0000	Read-Data 	DHW pump/valve operation hours: 0
11:00:33.685358	B707A0000	Unk-DataId	DHW pump/valve operation hours: 0
11:00:34.508655	R00110000	Read-Data 	Relative modulation level: 0.00
11:00:34.688591	BC0110000	Read-Ack  	Relative modulation level: 0.00
11:00:35.661856	R007B0000	Read-Data 	DHW burner operation hours: 0
11:00:35.683270	Command: PR=V
11:00:35.686357	Command: PR=T
11:00:35.691288	Command: PR=S
11:00:35.726048	PR: V=3
11:00:35.729138	PR: T=11
11:00:35.736274	PR: S=16.00
11:00:35.782048	BF07B0000	Unk-DataId	DHW burner operation hours: 0
11:00:36.547876	R801C0000	Read-Data 	Return water temperature: 0.00
11:00:36.787704	B401C2700	Read-Ack  	Return water temperature: 39.00
11:00:37.590690	R900E6400	Write-Data	Maximum relative modulation level: 100.00
11:00:37.882679	B500E6400	Write-Ack 	Maximum relative modulation level: 100.00
11:00:38.656777	R00740000	Read-Data 	Burner starts: 0
11:00:38.891776	BF0740000	Unk-DataId	Burner starts: 0
11:00:39.696811	R80000100	Read-Data 	Status: 00000001 00000000
11:00:39.986823	B40000100	Read-Ack  	Status: 00000001 00000000
11:00:40.746853	R80190000	Read-Data 	Boiler water temperature: 0.00
11:00:40.996883	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
11:00:41.802893	R10015000	Write-Data	Control setpoint: 80.00
11:00:42.092928	BD0015000	Write-Ack 	Control setpoint: 80.00
11:00:42.445106	Command: PR=W
11:00:42.477991	PR: W=A
11:00:42.851940	R80380000	Read-Data 	DHW setpoint: 0.00
11:00:43.092990	BC0383700	Read-Ack  	DHW setpoint: 55.00
11:00:43.898074	R00390000	Read-Data 	Max CH water setpoint: 0.00
11:00:44.190080	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
11:00:44.398051	Command: PR=L
11:00:44.400313	Command: PR=G
11:00:44.427080	PR: L=FXOMPC
11:00:44.429850	PR: G=00
11:00:44.958105	R80750000	Read-Data 	CH pump starts: 0
11:00:45.192101	B70750000	Unk-DataId	CH pump starts: 0
11:00:46.004162	R00120000	Read-Data 	CH water pressure: 0.00
11:00:46.296187	B60120000	Data-Inv  	CH water pressure: 0.00
11:00:47.054225	R80000100	Read-Data 	Status: 00000001 00000000
11:00:47.299214	B40000100	Read-Ack  	Status: 00000001 00000000
11:00:48.110251	R80190000	Read-Data 	Boiler water temperature: 0.00
11:00:48.392327	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
11:00:48.456828	Command: PR=M
11:00:48.490316	PR: M=G
11:00:49.160304	R10015000	Write-Data	Control setpoint: 80.00
11:00:49.395584	BD0015000	Write-Ack 	Control setpoint: 80.00
11:00:50.216393	R80760000	Read-Data 	DHW pump/valve starts: 0
11:00:50.403996	Command: GW=1
11:00:50.417717	GW: 1
11:00:50.498424	B70760000	Unk-DataId	DHW pump/valve starts: 0
11:00:51.256440	R00110000	Read-Data 	Relative modulation level: 0.00
11:00:51.502461	BC0110000	Read-Ack  	Relative modulation level: 0.00
11:00:52.311529	R00770000	Read-Data 	DHW burner starts: 0
11:00:52.604523	BF0770000	Unk-DataId	DHW burner starts: 0
11:00:53.362608	R801C0000	Read-Data 	Return water temperature: 0.00
11:00:53.606579	B401C2700	Read-Ack  	Return water temperature: 39.00
11:00:54.412649	R900E6400	Write-Data	Maximum relative modulation level: 100.00
11:00:54.710695	B500E6400	Write-Ack 	Maximum relative modulation level: 100.00
11:00:55.461680	R00780000	Read-Data 	Burner operation hours: 0
11:00:55.702689	BF0780000	Unk-DataId	Burner operation hours: 0
11:00:56.517767	R80000100	Read-Data 	Status: 00000001 00000000
11:00:56.803766	B40000100	Read-Ack  	Status: 00000001 00000000
11:00:57.564822	R80190000	Read-Data 	Boiler water temperature: 0.00
11:00:57.806819	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
11:00:58.623918	R10015000	Write-Data	Control setpoint: 80.00
11:00:58.904894	BD0015000	Write-Ack 	Control setpoint: 80.00
11:00:59.670899	R80380000	Read-Data 	DHW setpoint: 0.00
11:00:59.911588	BC0383700	Read-Ack  	DHW setpoint: 55.00
11:01:00.717981	R00390000	Read-Data 	Max CH water setpoint: 0.00
11:01:01.011033	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
11:01:01.764915	R80790000	Read-Data 	CH pump operation hours: 0
11:01:02.011018	B70790000	Unk-DataId	CH pump operation hours: 0
11:01:02.817112	R00120000	Read-Data 	CH water pressure: 0.00
11:01:03.107183	B60120000	Data-Inv  	CH water pressure: 0.00
11:01:03.871184	R80000100	Read-Data 	Status: 00000001 00000000
11:01:04.107161	B40000100	Read-Ack  	Status: 00000001 00000000
11:01:04.923233	R80190000	Read-Data 	Boiler water temperature: 0.00
11:01:05.219270	BC0192A00	Read-Ack  	Boiler water temperature: 42.00
11:01:05.972305	R10015000	Write-Data	Control setpoint: 80.00
11:01:06.209294	BD0015000	Write-Ack 	Control setpoint: 80.00
11:01:07.027356	R807A0000	Read-Data 	DHW pump/valve operation hours: 0
11:01:07.319392	B707A0000	Unk-DataId	DHW pump/valve operation hours: 0
11:01:08.078485	R00110000	Read-Data 	Relative modulation level: 0.00
11:01:08.311418	BC0110000	Read-Ack  	Relative modulation level: 0.00
11:01:09.124480	R007B0000	Read-Data 	DHW burner operation hours: 0
11:01:09.415472	BF07B0000	Unk-DataId	DHW burner operation hours: 0
11:01:10.173536	R801C0000	Read-Data 	Return water temperature: 0.00
11:01:10.417528	B401C2700	Read-Ack  	Return water temperature: 39.00
11:01:11.226968	R900E6400	Write-Data	Maximum relative modulation level: 100.00
11:01:11.515895	B500E6400	Write-Ack 	Maximum relative modulation level: 100.00
11:01:12.292076	R80750000	Read-Data 	CH pump starts: 0
11:01:12.523593	B70750000	Unk-DataId	CH pump starts: 0
11:01:13.335778	R80000100	Read-Data 	Status: 00000001 00000000
11:01:13.617694	B40000100	Read-Ack  	Status: 00000001 00000000
Looks to me like the gateway is now doing what it is supposed to do. Starting at 10:59:32 it sends the CH enable bit in the status message and a control setpoint of 80 degrees. According to the opentherm specification that should cause the boiler to start heating. But then at 10:59:56 it falls back to the idle state. At 11:00:06 it tells the boiler to start heating again. Did you manually short the wires, or did you use an actual thermostat?
Perhaps you need to give the system some time. If the boiler was heating just before you connected the OTGW, it may have some internal timers that prevent it from heating again within some set time after its previous cycle. According to the manual this is "at least 3-minutes after the set-point hysterisis (set-point + 5-deg)". The on/off/on cycle you did may have restarted the timer. So you may have to be a bit more patient.
The manual also shows that the boiler uses different connecting points for an on/off thermostat and an opentherm thermostat. Perhaps it sticks to one or the other once it has seen one. You could try to power-cycle the boiler and then make sure the on/off thermostat doesn't interact with the boiler (disconnect it, or set it very low).
Finally, if you're unlucky, the boiler may not properly follow the opentherm spec and will only work with a specific thermostat that sends some non-standard opentherm messages to make the boiler operate.
david_wallis
Tried Disconnecting std thermostat, power cycling boiler and leaving a while.. no luck.
Then your boiler wants to see something more/different from what the specs prescribe. Someone else reported that his boiler operates based on the current room temperature and the room setpoint. If you're up to it, you can try to use the interface firmware to send your own messages and figure out what the boiler wants to see.
You can also try to contact the manufacturer, but experience of several people shows that most of them are not able/willing to provide such details.