Fibaro Relay 2x1.5kW with pulse switch?

Forum and Topics about Z-Wave devices.
Post Reply
DJF3
Advanced Member
Advanced Member
Posts: 895
Joined: Thu Jul 12, 2007 9:28 am
Contact:

Fibaro Relay 2x1.5kW with pulse switch?

Post by DJF3 »

Team,

When connected, the pulse switch switches on the light as long as I keep it pressed..
Fibaro Relay switch
Fibaro Relay switch
Fibaro-Relay-PastedGraphic-5.jpg (155.44 KiB) Viewed 8790 times
The white (split) cable going down is connected to a lamp
Fibaro: S1 goes into the switch
Fibaro: Q1 goes to the lamp
Fibaro: IN is connected with L
Fibaro: L & N to 230v
Switch: other connection to L

It feels like I have connected the switch the wrong way ;-)

Fibaro parameter 14 (0=momentary switch, 1=toggle switch) have been tested with both 0 and 1. Same result.

Any idea?


Cheers
Dirk
raymonvdm
Senior Member
Senior Member
Posts: 1153
Joined: Sun Dec 18, 2011 1:23 am

Re: Fibaro Relay 2x1.5kW with pulse switch?

Post by raymonvdm »

This should be the schematic you are using but i cannot figure this out using the picture. Are u using fixed cable or a wallplug so are u sure L1 is L1 and not Null because the wallplug is connected up side down?

If you measure the brown wire and ground do you measure 230Volt?

Image


I think parameter 14 should be 0 and it should work fine then
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s
DJF3
Advanced Member
Advanced Member
Posts: 895
Joined: Thu Jul 12, 2007 9:28 am
Contact:

Re: Fibaro Relay 2x1.5kW with pulse switch?

Post by DJF3 »

I think the problem may be in the Pulse Switch, of which I have no idea which cable should go where ;-)
The schematic you attached is the one I used to connect everything.

After measuring I found that connecting the wires as they are right now (in #11 and #14), clicking the switch would momentarily switch it on

Don't have any schematics or details on the Gira Pulse Switch (015500?)

DJ
raymonvdm
Senior Member
Senior Member
Posts: 1153
Joined: Sun Dec 18, 2011 1:23 am

Re: Fibaro Relay 2x1.5kW with pulse switch?

Post by raymonvdm »

Usually this is straightforward (RED / P / L) is the input and the outgoing arrow is the output.

When u remove the switch and use the naked wires (WATCH OUT HIGH VOLTAGE!!) and connect them for a second is the fibaro working as expected then?

Note: If you deassociate the fibaro al settings are lost (atleast for my fibaro versions) so are u sure that option 14 is still set correctly ?
Running HS3PRO on PC with Z-Wave / OpenTherm / Plugwise / RFXcom / MQTT / XAP400 / Logitech Media Server and Squeezelite on PI`s
DJF3
Advanced Member
Advanced Member
Posts: 895
Joined: Thu Jul 12, 2007 9:28 am
Contact:

Re: Fibaro Relay 2x1.5kW with pulse switch?

Post by DJF3 »

FYI

Think this is the schematics for the Gira 0155 00 pulse switch
Gira pulse switch schematics
Gira pulse switch schematics
BA4B1EA4-7274-4A8D-8EC3-2BF603FBD34B.png (15.06 KiB) Viewed 8691 times

Raymond: Using a wall plug and your "up side down" comment might be very smart ;-). I will check!
DJF3
Advanced Member
Advanced Member
Posts: 895
Joined: Thu Jul 12, 2007 9:28 am
Contact:

Re: Fibaro Relay 2x1.5kW with pulse switch?

Post by DJF3 »

raymonvdm wrote:Are u using fixed cable or a wallplug so are u sure L1 is L1 and not Null because the wallplug is connected up side down?
Brilliant... This solved the problem ;-)