Thermostat: iSense (v19. external input allowed)
With a manual of Domoticz command SW=62, I am able to change the Domestic Hot Water Setpoint to 62 degrees. This is in OTMonitor visible in both the 'Summary' and 'Status page'. However, in the PS=1 string, and therefore also in Domoticz, I still see the old setpoint, as set by the iSense: 59'C. The iSense itself is also still at 59. Please see the piece of the OT messages at the point where I did the manual / Domoticz override:
Code: Select all
[b]13:14:05.441816 Command (via relay server, from 127.0.0.1:48214): SW=62.0
13:14:05.473613 SW: 62.00[/b]
13:14:05.503507 Command (via relay server, from 127.0.0.1:48214): PR=G
13:14:05.506578 Command (via relay server, from 127.0.0.1:48214): PR=I
13:14:05.510997 Command (via relay server, from 127.0.0.1:48214): PR=O
13:14:05.519177 Command (via relay server, from 127.0.0.1:48214): PS=1
13:14:05.545469 PR: G=00
13:14:05.572440 PR: I=11
13:14:05.595323 PR: O=N
13:14:05.621135 PS: 1
13:14:05.723893 00000000/00000000,6.90,00000001/00000001,100.00,0/0,17.50,0.00,0.00,18.33,22.00,0.00,3.80,21.00,75/20,45/0,[b]59.00[/b],0.00,23970,0,0,12150,30230,4482,1057,4629
13:14:05.734354 Command (via relay server, from 127.0.0.1:48214): PS=0
13:14:05.758500 PS: 0
13:14:05.834997 BC0000000 Read-Ack Status: 00000000 00000000
13:14:06.662679 T90010700 Write-Data Control setpoint: 7.00
13:14:06.841803 B50010700 Write-Ack Control setpoint: 7.00
13:14:07.664694 T00110000 Read-Data Relative modulation level: 0.00
13:14:07.844461 BC0110000 Read-Ack Relative modulation level: 0.00
13:14:08.669331 T80190000 Read-Data Boiler water temperature: 0.00
13:14:08.850636 BC0191600 Read-Ack Boiler water temperature: 22.00
13:14:09.675638 T90101180 Write-Data Room setpoint: 17.50
13:14:09.856790 B50101180 Write-Ack Room setpoint: 17.50
13:14:10.680807 T00000000 Read-Data Status: 00000000 00000000
13:14:10.863018 BC0000000 Read-Ack Status: 00000000 00000000
13:14:11.690923 T90010700 Write-Data Control setpoint: 7.00
13:14:11.867882 B50010700 Write-Ack Control setpoint: 7.00
13:14:12.785370 T00110000 Read-Data Relative modulation level: 0.00
13:14:12.877853 BC0110000 Read-Ack Relative modulation level: 0.00
13:14:13.857413 T80190000 Read-Data Boiler water temperature: 0.00
13:14:14.046559 BC0191600 Read-Ack Boiler water temperature: 22.00
13:14:14.705819 T1018124F Write-Data Room temperature: 18.31
13:14:14.886787 BD018124F Write-Ack Room temperature: 18.31
13:14:15.709942 T00000000 Read-Data Status: 00000000 00000000
13:14:15.890537 BC0000000 Read-Ack Status: 00000000 00000000
13:14:16.729307 T90010700 Write-Data Control setpoint: 7.00
13:14:16.896298 B50010700 Write-Ack Control setpoint: 7.00
13:14:17.721603 T00110000 Read-Data Relative modulation level: 0.00
13:14:17.902582 BC0110000 Read-Ack Relative modulation level: 0.00
13:14:18.727586 T80190000 Read-Data Boiler water temperature: 0.00
13:14:18.907351 BC0191600 Read-Ack Boiler water temperature: 22.00
13:14:19.732587 T00090000 Read-Data Remote override room setpoint: 0.00
13:14:19.744745 R90383E00 Write-Data DHW setpoint: 62.00
13:14:19.942502 B50383E00 Write-Ack DHW setpoint: 62.00
13:14:19.953080 AC0090000 Read-Ack Remote override room setpoint: 0.00
13:14:19.981372 Command (via relay server, from 127.0.0.1:48214): OT=3.8
13:14:20.009733 OT: 3.80
13:14:20.019365 Command (via relay server, from 127.0.0.1:48214): SC=13:14/1
13:14:20.022057 Command (via relay server, from 127.0.0.1:48214): PR=G
13:14:20.024761 Command (via relay server, from 127.0.0.1:48214): PR=I
13:14:20.027159 Command (via relay server, from 127.0.0.1:48214): PR=O
13:14:20.029996 Command (via relay server, from 127.0.0.1:48214): PS=1
13:14:20.053257 SC: 13:14/1
13:14:20.058061 PR: G=00
13:14:20.067003 PR: I=11
13:14:20.076638 PR: O=N
13:14:20.093104 PS: 1
13:14:20.252394 00000000/00000000,7.00,00000001/00000001,100.00,0/0,17.50,0.00,0.00,18.31,22.00,0.00,3.80,21.00,75/20,45/0,[b]59.00[/b],0.00,23970,0,0,12150,30230,4482,1057,4629
Is it normal that the iSense is not updated with the new DHW Setpoint? It does react well on changing the Thermostat Setpoint.