Connection to BRAHMA thermostat and "EMMETI" boiler

This Forum is about the Opentherm gateway (OTGW) from Schelte

Moderator: hvxl

mcasamento
Starting Member
Starting Member
Posts: 17
Joined: Fri Jan 03, 2020 6:14 pm

Connection to BRAHMA thermostat and "EMMETI" boiler

Post by mcasamento »

Hi,
I've bought the OTGW kit with a NodeMCU from Nodeshop but I'm only able to connect it in Monitor Mode thus receiving a lot of Error 03.
The thermostat is a BRAHMA KRONOS OT11 and if it can helo I've got a techincal document on my 1drive : https://1drv.ms/b/s!AineZF8jPblsisRctwD ... Q?e=XfE2lA
The boiler is an Emmeti Althea S that is very likely to be somthing rebranded, but I don't have any other techincal document about it.
I've found that there is another thread on this forum with the same boiler and the same thermostat, posted by @ilcalmo: viewtopic.php?f=75&t=10784&p=76588&hilit=emmeti#p76588 and I'm experiencing more or less the same behaviour, but unfortunately that thread has been abandoned and I'm not sure about what test should I do.

I've tried to set any possible reference voltage, but if I set a value under 1.042 or above 2.292 the thermostat will shut down, the values in between all give the same Error 03.
When in monitor mode it does returns some data:

Code: Select all

15:29:01.817527  Error 03
15:29:01.941722  T00000300  Read-Data   Status: 00000011 00000000
                               - CH enable: enabled (1)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
15:29:02.313402  rror 03
15:29:02.472321  T10101281  Write-Data  Room setpoint: 18.50
15:29:02.803894  Error 03
15:29:02.952177  T00110000  Read-Data   Relative modulation level: 0.00
15:29:03.471337  00120000
15:29:03.815348  Error 03
15:29:03.945892  T00140000  Read-Data   Day of week and time of day: Unk 00:00
15:29:04.319223  Error 03
15:29:04.854299  T80130000  Read-Data   DHW flow rate: 0.00
15:29:05.204917  Error 03
15:29:05.356545  T1018134D  Write-Data  Room temperature: 19.30
15:29:05.721436  Error 03
15:29:05.858484  T80190000  Read-Data   Boiler water temperature: 0.00
15:29:06.222383  Error 03
15:29:06.364653  T801A0000  Read-Data   DHW temperature: 0.00
15:29:06.725769  Error 03
15:29:06.848825  T001B0000  Read-Data   Outside temperature: 0.00
15:29:07.247142  Error 03
15:29:07.363161  T00110000  Read-Data   Relative modulation level: 0.00
15:29:07.748304  Error 03
15:29:07.951760  T00120000  Read-Data   CH water pressure: 0.00
15:29:08.345868  Error 03
15:29:08.561200  T801C0000  Read-Data   Return water temperature: 0.00
15:29:08.901867  Error 03
15:29:09.048542  T00210000  Read-Data   Exhaust temperature: 0.00
15:29:09.450935  Error 03
15:29:09.650637  T90382A00  Write-Data  DHW setpoint: 42.00
15:29:10.074477  Error 03
15:29:10.671123  rror 03
15:29:10.853282  T10010500  Write-Data  Control setpoint: 5.00
15:29:11.215412  Error 03
15:29:11.350799  T00000300  Read-Data   Status: 00000011 00000000
                               - CH enable: enabled (1)
                               - DHW enable: enabled (1)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
15:29:11.714738  rror 03
15:29:11.853830  T00000300  Read-Data   Status: 00000011 00000000
while when in monitoring mode it repetitively print:

Code: Select all

09:23:13.964157  1002011C
09:23:14.965397  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
09:23:15.965842  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
09:23:16.798778  Command: PR=M
09:23:16.936919  PR: M=G
09:23:16.942489  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
09:23:17.966690  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
09:23:18.966793  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
09:23:19.967947  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
09:23:20.967173  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
09:23:21.970215  1002011C
In the tech specs of the thermostat it does say:
The communication between the thermostat and the control
board of the boiler takes place by means of a two-wire
cable; the data are exchanged with the communication
protocol compatible OpenTherm ™ v3.0 Smart Power
Mode - Medium Power.
does that means I'd better give up ? :cry: or anyone have a hint to try fixing the problem ?

Thanks in advance
hvxl
Senior Member
Senior Member
Posts: 2034
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Connection to BRAHMA thermostat and "EMMETI" boiler

Post by hvxl »

Your logs show that the messages from the thermostat are received properly. The Error 03 are coming from the boiler side. Given that the reference voltage setting almost exclusively affects the reception from the thermostat, there is not much sense in messing with that.

You describe both logs as being in monitor mode. The second one appears to be in gateway mode, as revealed by the "PR: M=G" response.

The OTGW supports OpenTherm v3.0 Smart Power, both medium and high power. But it does expect the devices to follow the specs. This means that both thermostat and boiler should start in low power mode and then negotiate to switch to medium power. As the OTGW has its own power, it doesn't need the boiler to provide extra power. It will therefor not ask the boiler to switch to medium power. If the thermostat requests a higher power level (medium or high), the OTGW will provide it, without involving the boiler.

With the OTGW in gateway mode, the thermostat repeats the same message when it doesn't get a response. With the OTGW in monitor mode, the thermostat requests different message IDs, suggesting that it is happy with the response it gets from the boiler. Yet, the OTGW can't make heads or tails of it. Possibly the boiler is always operating in medium power mode, even without being asked to do so via the methods defined in the opentherm specification. The OTGW does not currently handle such a situation.

One way to confirm if this is the case is to run the command DP=9C. This will report the CMCON register after each message. At those moments the OT lines should be idle. So, bit 6 and bit 7 should both be 1. Normally you would see C3 in gateway mode and C6 in monitor mode. If my theory is correct, I expect you to see 43 or 46.

Interesting would be to see logs of when you power up the boiler and connect the thermostat. Combined with the DP=9C test results, that would confirm if your equipment is really compatible with OpenTherm v3.0, or if they skip some vital steps and go straight into medium power mode.
Schelte
mcasamento
Starting Member
Starting Member
Posts: 17
Joined: Fri Jan 03, 2020 6:14 pm

Re: Connection to BRAHMA thermostat and "EMMETI" boiler

Post by mcasamento »

Thanks for your prompt reply!
I've issued the DP=9C command and as you expected, I see 9C=43 in the log

Code: Select all

10:46:26.060352	Error 03
10:46:26.647251	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
10:46:27.032586	Command: DP=9C
10:46:27.042043	rror 03
10:46:27.144766	DP: 9C
10:46:27.180485	9C=43
10:46:27.645828	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
10:46:27.724847	9C=43
10:46:28.076281	Error 03
10:46:28.093093	9C=43
10:46:28.646539	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
10:46:28.699925	9C=43
I'm now going to:
1. disconnect thermostat
2. shutdown boiler
3. restart otgw and issue DP=9C
4. power up boiler
5. connect thermostat and then post logs here

thanks again for your assistance

Marco
mcasamento
Starting Member
Starting Member
Posts: 17
Joined: Fri Jan 03, 2020 6:14 pm

Re: Connection to BRAHMA thermostat and "EMMETI" boiler

Post by mcasamento »

Thanks for your prompt response
I've issued the "DP=9C" command and as you predicted the gateway started to return 9C=43

Code: Select all

10:46:27.032586  Command: DP=9C
10:46:27.042043  rror 03
10:46:27.144766  DP: 9C
10:46:27.180485  9C=43
10:46:27.645828  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
10:46:27.724847  9C=43
10:46:28.076281  Error 03
10:46:28.093093  9C=43
10:46:28.646539  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
10:46:28.699925  9C=43
10:46:29.040012  Error 03
10:46:29.069176  9C=43
10:46:29.649571  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
10:46:29.741316  9C=43
10:46:30.040200  Error 03
10:46:30.079540  9C=43
10:46:30.650593  1002011C
10:46:30.681969  9C=43
10:46:31.041528  Error 03
10:46:31.071098  9C=43
I've then:
1. disconnect the thermostat
2. shutdown the boiler
3. restart otgw
4. issued DP=9C
5. power up boiled
6. connected the thermostat

the relevant part of the logs are:

Code: Select all

10:54:40.025183  Command: DP=9C
10:54:40.197395  DP: 9C
10:54:40.229976  9C=83
10:54:40.277508  R00000000  Read-Data   Status: 00000000 00000000
                               - CH enable: disabled (0)
                               - DHW enable: disabled (0)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
then I've powered up the boiler and a minute after connected the thermostat

Code: Select all

10:55:04.375155  9C=83
10:55:05.165794  R00000000  Read-Data   Status: 00000000 00000000
                               - CH enable: disabled (0)
                               - DHW enable: disabled (0)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:55:05.362572  9C=83
10:55:06.161501  00000000
10:55:06.194755  9C=83
10:55:07.006209  rror 03
10:55:07.040038  9C=83
10:55:07.166445  R00000000  Read-Data   Status: 00000000 00000000
                               - CH enable: disabled (0)
                               - DHW enable: disabled (0)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:55:07.319975  9C=83
10:55:07.608005  BC0000000  Read-Ack    Status: 00000000 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:55:07.836490  Command: PR=A
10:55:07.849805  9C=83
10:55:07.911838  PR: A=OpenTherm Gateway 4.2.5
10:55:07.920357  Command: SC=10:55/6
10:55:07.931698  Command: SR=21:01,04
10:55:07.942153  Command: SR=22:7,228
10:55:07.951983  9C=83
10:55:08.036520  SC: 10:55/6
10:55:08.070410  9C=83
10:55:08.115881  SR: 21:1/4
10:55:08.159510  9C=83
10:55:08.183149  SR: 22:7/228
10:55:08.207105  9C=83
10:55:08.228991  R80190000  Read-Data   Boiler water temperature: 0.00
10:55:08.253351  9C=83
10:55:08.662798  B40191400  Read-Ack    Boiler water temperature: 20.00
10:55:08.694877  9C=83
10:55:09.476964  R10010A00  Write-Data  Control setpoint: 10.00
10:55:09.511354  9C=83
10:55:09.687646  BD0010A00  Write-Ack   Control setpoint: 10.00
10:55:09.723062  9C=83
10:55:10.298087  R00060000  Read-Data   Remote parameter flags: 00000000 00000000
10:55:10.332360  9C=83
10:55:10.604900  BC0060303  Read-Ack    Remote parameter flags: 00000011 00000011
                               - DHW setpoint transfer: enabled (1)
                               - max CH setpoint transfer: enabled (1)
                               - DHW setpoint: read/write (1)
                               - max CH setpoint: read/write (1)
10:55:10.765613  9C=83
10:55:11.307046  R00110000  Read-Data   Relative modulation level: 0.00
10:55:11.344389  9C=83
10:55:11.664130  BC0110000  Read-Ack    Relative modulation level: 0.00
10:55:11.696321  9C=83
10:55:12.342718  R001B0000  Read-Data   Outside temperature: 0.00
10:55:12.382984  9C=83
10:55:12.698272  BF01B0000  Unk-DataId  Outside temperature: 0.00
10:55:12.721959  9C=83
10:55:13.386517  R801C0000  Read-Data   Return water temperature: 0.00
10:55:13.424604  9C=83
10:55:13.716922  BC01C1F00  Read-Ack    Return water temperature: 31.00
10:55:13.753705  9C=83
10:55:14.414715  900E6400
10:55:14.451969  9C=83
10:55:14.741970  B700E0000  Unk-DataId  Maximum relative modulation level: 0.00
10:55:14.781495  9C=83
10:55:15.456057  00300000
10:55:15.505504  9C=83
10:55:15.750679  B40303C23  Read-Ack    DHW setpoint boundaries: 60 35
10:55:15.789642  9C=83
10:55:16.491883  R00000000  Read-Data   Status: 00000000 00000000
                               - CH enable: disabled (0)
                               - DHW enable: disabled (0)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:55:16.658634  9C=83
10:55:16.838956  BC0000000  Read-Ack    Status: 00000000 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:55:17.043956  9C=83
10:55:17.529341  R80190000  Read-Data   Boiler water temperature: 0.00
10:55:17.578252  9C=83
10:55:17.902027  BC0192600  Read-Ack    Boiler water temperature: 38.00
10:55:17.936070  9C=83
10:55:18.564100  R10010A00  Write-Data  Control setpoint: 10.00
10:55:18.594655  9C=83
10:55:18.965877  BD0010A00  Write-Ack   Control setpoint: 10.00
10:55:19.001586  9C=83
10:55:19.595529  R80380000  Read-Data   DHW setpoint: 0.00
10:55:19.640494  9C=83
10:55:19.975636  BC0382A00  Read-Ack    DHW setpoint: 42.00
10:55:20.013496  9C=83
10:55:20.626156  R00390000  Read-Data   Max CH water setpoint: 0.00
10:55:20.662041  9C=83
10:55:21.005246  B40393200  Read-Ack    Max CH water setpoint: 50.00
10:55:21.044489  9C=83
10:55:21.663415  R80310000  Read-Data   Max CH setpoint boundaries: 0 0
10:55:21.705724  9C=83
10:55:22.039436  B40315028  Read-Ack    Max CH setpoint boundaries: 80 40
10:55:22.074381  9C=83
10:55:22.710948  00120000
10:55:22.749662  9C=83
10:55:23.109792  BC0120186  Read-Ack    CH water pressure: 1.52
10:55:23.146994  9C=83
10:55:23.740753  00000000
10:55:23.777651  9C=83
10:55:24.125707  BC0000000  Read-Ack    Status: 00000000 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:55:24.330084  9C=83
10:55:24.776762  R80190000  Read-Data   Boiler water temperature: 0.00
10:55:24.830871  9C=83
10:55:25.146213  BC0192600  Read-Ack    Boiler water temperature: 38.00
10:55:25.183437  9C=83
10:55:25.805919  R10010A00  Write-Data  Control setpoint: 10.00
10:55:25.843342  9C=83
10:55:26.186890  BD0010A00  Write-Ack   Control setpoint: 10.00
10:55:26.224326  9C=83
10:55:26.862345  R00740000  Read-Data   Burner starts: 0
10:55:26.889505  9C=83
10:55:27.277050  BF0740000  Unk-DataId  Burner starts: 0
10:55:27.328262  9C=83
10:55:27.884160  R00110000  Read-Data   Relative modulation level: 0.00
10:55:27.914049  9C=83
10:55:28.272942  BC0110000  Read-Ack    Relative modulation level: 0.00
10:55:28.317857  9C=83
10:55:28.922445  R001B0000  Read-Data   Outside temperature: 0.00
10:55:28.946615  9C=83
10:55:29.302874  BF01B0000  Unk-DataId  Outside temperature: 0.00
10:55:29.338808  9C=83
10:55:29.956788  R801C0000  Read-Data   Return water temperature: 0.00
10:55:29.965582  9C=83
10:55:30.332543  BC01C1F00  Read-Ack    Return water temperature: 31.00
10:55:30.351001  9C=83
10:55:30.980391  900E6400
10:55:31.004748  9C=83
10:55:31.367926  B700E0000  Unk-DataId  Maximum relative modulation level: 0.00
10:55:31.413654  9C=83
10:55:32.012796  80750000
10:55:32.027428  9C=83
10:55:32.417575  B70750000  Unk-DataId  CH pump starts: 0
10:55:32.429035  9C=83
10:55:33.050993  R00000000  Read-Data   Status: 00000000 00000000
                               - CH enable: disabled (0)
                               - DHW enable: disabled (0)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:55:33.234294  9C=83
10:55:33.431858  BC0000000  Read-Ack    Status: 00000000 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:55:33.537566  9C=83
10:55:34.082872  R80190000  Read-Data   Boiler water temperature: 0.00
10:55:34.098063  9C=83
10:55:34.457923  BC0192600  Read-Ack    Boiler water temperature: 38.00
10:55:34.468627  9C=83
10:55:35.118340  R10010A00  Write-Data  Control setpoint: 10.00
10:55:35.150681  9C=83
10:55:35.493527  BD0010A00  Write-Ack   Control setpoint: 10.00
10:55:35.536437  9C=83
10:55:36.163781  R80380000  Read-Data   DHW setpoint: 0.00
10:55:36.200118  9C=83
10:55:36.530507  BC0382A00  Read-Ack    DHW setpoint: 42.00
10:55:36.556732  9C=83
10:55:37.192138  R00390000  Read-Data   Max CH water setpoint: 0.00
10:55:37.223962  9C=83
10:55:37.576216  B40393200  Read-Ack    Max CH water setpoint: 50.00
10:55:37.585024  9C=83
10:55:38.231323  R80760000  Read-Data   DHW pump/valve starts: 0
10:55:38.271545  9C=83
10:55:38.607861  B70760000  Unk-DataId  DHW pump/valve starts: 0
10:55:38.633571  9C=83
10:55:39.641876  C0120186
10:55:39.680186  9C=83
10:55:40.912724  00000000
10:55:40.949984  9C=83
10:55:40.991403  BC0000000  Read-Ack    Status: 00000000 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:55:41.126385  9C=83
10:55:41.630765  R80190000  Read-Data   Boiler water temperature: 0.00
10:55:41.670308  9C=83
10:55:41.935795  BC0192600  Read-Ack    Boiler water temperature: 38.00
10:55:41.948846  9C=83
10:55:42.360208  R10010A00  Write-Data  Control setpoint: 10.00
10:55:42.387164  9C=83
10:55:42.743276  BD0010A00  Write-Ack   Control setpoint: 10.00
10:55:42.781891  9C=83
10:55:43.393762  R00770000  Read-Data   DHW burner starts: 0
10:55:43.426962  9C=83
10:55:43.890850  BF0770000  Unk-DataId  DHW burner starts: 0
10:55:43.909963  9C=83
10:55:44.425957  R00110000  Read-Data   Relative modulation level: 0.00
10:55:44.438919  9C=83
10:55:44.818125  BC0110000  Read-Ack    Relative modulation level: 0.00
10:55:44.830634  9C=83
10:55:45.468110  R001B0000  Read-Data   Outside temperature: 0.00
10:55:45.494086  9C=83
10:55:45.878104  BF01B0000  Unk-DataId  Outside temperature: 0.00
10:55:45.919716  9C=83
10:55:46.506740  R801C0000  Read-Data   Return water temperature: 0.00
10:55:46.539230  9C=83
10:55:46.893760  BC01C1F00  Read-Ack    Return water temperature: 31.00
10:55:46.936834  9C=83
10:55:47.497595  9C=83
10:55:47.900849  B700E0000  Unk-DataId  Maximum relative modulation level: 0.00
10:55:47.935259  9C=83
10:55:48.002145  .2.5
10:55:48.034087  9C=83
10:55:48.549975  R00780000  Read-Data   Burner operation hours: 0
10:55:48.569172  9C=83
10:55:48.933881  BF0780000  Unk-DataId  Burner operation hours: 0
10:55:48.976024  9C=83
10:55:49.583355  R00000000  Read-Data   Status: 00000000 00000000
                               - CH enable: disabled (0)
                               - DHW enable: disabled (0)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:55:49.723372  9C=83
10:55:49.967090  BC0000000  Read-Ack    Status: 00000000 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:55:50.197583  9C=83
10:55:50.615468  R80190000  Read-Data   Boiler water temperature: 0.00
10:55:50.671294  9C=83
10:55:50.993360  BC0192600  Read-Ack    Boiler water temperature: 38.00
10:55:51.027214  9C=83
10:55:51.656156  R10010A00  Write-Data  Control setpoint: 10.00
10:55:51.705335  9C=83
10:55:52.010265  BD0010A00  Write-Ack   Control setpoint: 10.00
10:55:52.052191  9C=83
10:55:52.691673  R80380000  Read-Data   DHW setpoint: 0.00
10:55:52.741555  9C=83
10:55:53.064101  BC0382A00  Read-Ack    DHW setpoint: 42.00
10:55:53.112446  9C=83
10:55:53.731356  R00390000  Read-Data   Max CH water setpoint: 0.00
10:55:53.753696  9C=83
10:55:54.113881  B40393200  Read-Ack    Max CH water setpoint: 50.00
10:55:54.149921  9C=83
10:55:54.760920  R80790000  Read-Data   CH pump operation hours: 0
10:55:54.798750  9C=83
10:55:55.138991  B70790000  Unk-DataId  CH pump operation hours: 0
10:55:55.171298  9C=83
10:55:55.790225  00120000
10:55:55.813376  9C=83
10:55:56.198761  C0120186
10:55:56.209715  9C=83
10:55:56.842652  R00000000  Read-Data   Status: 00000000 00000000
                               - CH enable: disabled (0)
                               - DHW enable: disabled (0)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:55:57.023590  9C=83
10:55:57.214070  BC0000000  Read-Ack    Status: 00000000 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:55:57.349814  9C=83
10:55:57.863622  R80190000  Read-Data   Boiler water temperature: 0.00
10:55:57.895859  9C=83
10:55:58.247679  BC0192600  Read-Ack    Boiler water temperature: 38.00
10:55:58.275675  9C=83
10:55:58.892868  R10010A00  Write-Data  Control setpoint: 10.00
10:55:58.931711  9C=83
10:55:59.277249  BD0010A00  Write-Ack   Control setpoint: 10.00
10:55:59.308125  9C=83
10:55:59.927647  R807A0000  Read-Data   DHW pump/valve operation hours: 0
10:55:59.940083  9C=83
10:56:00.001388  Command: SC=10:56/6
10:56:00.146798  SC: 10:56/6
10:56:00.155828  9C=83
10:56:00.344163  B707A0000  Unk-DataId  DHW pump/valve operation hours: 0
10:56:00.365792  9C=83
10:56:00.959068  R00110000  Read-Data   Relative modulation level: 0.00
10:56:01.000248  9C=83
10:56:01.367862  BC0110000  Read-Ack    Relative modulation level: 0.00
10:56:01.395632  9C=83
10:56:02.018865  R007B0000  Read-Data   DHW burner operation hours: 0
10:56:02.060314  9C=83
10:56:02.379458  BF07B0000  Unk-DataId  DHW burner operation hours: 0
10:56:02.405552  9C=83
10:56:03.028542  R801C0000  Read-Data   Return water temperature: 0.00
10:56:03.055570  9C=83
10:56:03.403895  BC01C1F00  Read-Ack    Return water temperature: 31.00
10:56:03.437710  9C=83
10:56:04.439519  F0740000
10:56:04.471082  9C=83
10:56:05.107825  R80750000  Read-Data   CH pump starts: 0
10:56:05.141621  9C=83
10:56:05.511991  B70750000  Unk-DataId  CH pump starts: 0
10:56:05.567208  9C=83
10:56:06.145903  R00000000  Read-Data   Status: 00000000 00000000
                               - CH enable: disabled (0)
                               - DHW enable: disabled (0)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:56:06.334499  9C=83
10:56:06.446008  Error 03
10:56:06.505477  9C=C3
10:56:07.235526  R00000000  Read-Data   Status: 00000000 00000000
                               - CH enable: disabled (0)
                               - DHW enable: disabled (0)
                               - Cooling enable: disabled (0)
                               - OTC active: not active (0)
                               - CH2 enable: disabled (0)
                               - Summer/winter mode: winter (0)
                               - DHW blocking: unblocked (0)
10:56:07.433764  9C=C3
10:56:07.449325  Thermostat connected
10:56:07.635541  BC0000000  Read-Ack    Status: 00000000 00000000
                               - Fault indication: no fault (0)
                               - CH mode: not active (0)
                               - DHW mode: not active (0)
                               - Flame status: flame off (0)
                               - Cooling status: not active (0)
                               - CH2 mode: not active (0)
                               - Diagnostic indication: no diagnostics (0)
                               - Electricity production: not active (0)
10:56:07.925091  9C=C3
10:56:10.142480  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
10:56:10.226428  9C=C3
10:56:10.253040  Medium power
10:56:10.307418  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
10:56:10.331010  9C=C3
10:56:10.720795  Error 03
10:56:10.759501  9C=43
10:56:11.633837  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
10:56:11.694805  9C=43
10:56:12.043288  Error 03
10:56:12.079791  9C=43
10:56:12.451282  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
10:56:12.535327  9C=43
10:56:12.865012  Error 03
10:56:12.897973  9C=43
10:56:13.726332  rror 03
10:56:13.765500  9C=43
10:56:14.337103  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
10:56:14.399573  9C=43
10:56:14.725918  Error 03
10:56:14.765172  9C=43
10:56:15.339517  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
10:56:15.397017  9C=43
10:56:15.737059  Error 03
10:56:15.774925  9C=43
10:56:16.337257  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
10:56:16.415022  9C=43
10:56:16.749899  Error 03
10:56:16.790510  9C=43
10:56:17.340948  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
10:56:17.423424  9C=43
10:56:17.761947  Error 03
10:56:17.799589  9C=43
10:56:18.338032  T1002011C  Write-Data  Master configuration: 00000001 28
                               - Smart power: supported (1)
10:56:18.435547  9C=43
10:56:18.730031  Error 03
10:56:18.771163  9C=43
Am I wrong or the OTGW has been able to read data from the boiler til I connected the thermostat ? that's light up some hopes maybe :o
hvxl
Senior Member
Senior Member
Posts: 2034
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Connection to BRAHMA thermostat and "EMMETI" boiler

Post by hvxl »

It certainly looks that way. It also looks like the boiler is switching to Medium Power mode as soon as it receives the Master Configuration message that indicates the thermostat supports Smart Power. You could try configuring the OTGW not to pass this message on to the boiler (UI=2). Then disconnect the thermostat and get the OTGW and boiler communicating again. When you finally reconnect the thermostat, communication will hopefully continue to work.
Schelte
mcasamento
Starting Member
Starting Member
Posts: 17
Joined: Fri Jan 03, 2020 6:14 pm

Re: Connection to BRAHMA thermostat and "EMMETI" boiler

Post by mcasamento »

I've tried to:
1. disconnect thermostat
2. shutdown boiler and otgw
3. power up boiler
4. wait for connection (and I believe it connected succesfully)
5. Issue UI=2
6. connect thermostat
Unfortunately it doesn't seems to work, or maybe I've misunderstood you
I've tried the same thing with some (probably irrelevant) variant but I'm attaching the log that I believe is most similar to what you suggested.
May you help to understand what should I look in the log or from where can I start to study what's happening ?

EDIT: it seems I can't attach file, so I'm pasting the log as code inside here

Code: Select all

20:52:20.590693	C0000000
20:52:21.204837	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:21.601957	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:21.682673	Command: PR=A
20:52:21.825137	PR: A=OpenTherm Gateway 4.2.5
20:52:22.233244	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:22.608632	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:23.265513	R80190000	Read-Data 	Boiler water temperature: 0.00
20:52:23.633661	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:52:24.300226	R10010A00	Write-Data	Control setpoint: 10.00
20:52:24.673253	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:52:25.342167	R80380000	Read-Data 	DHW setpoint: 0.00
20:52:25.706630	B40382D00	Read-Ack  	DHW setpoint: 45.00
20:52:26.374051	R00390000	Read-Data 	Max CH water setpoint: 0.00
20:52:26.754915	B40393200	Read-Ack  	Max CH water setpoint: 50.00
20:52:27.405534	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:27.785455	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:28.434906	R00120000	Read-Data 	CH water pressure: 0.00
20:52:28.603632	Command: PR=M
20:52:28.730280	PR: M=G
20:52:28.824373	BC0120186	Read-Ack  	CH water pressure: 1.52
20:52:29.465772	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:29.848567	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:30.498913	R80190000	Read-Data 	Boiler water temperature: 0.00
20:52:30.911387	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:52:31.542033	R10010A00	Write-Data	Control setpoint: 10.00
20:52:31.918322	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:52:32.568868	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:32.946748	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:33.607796	R00110000	Read-Data 	Relative modulation level: 0.00
20:52:33.988493	BC0110000	Read-Ack  	Relative modulation level: 0.00
20:52:34.653223	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:35.013416	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:35.679010	R801C0000	Read-Data 	Return water temperature: 0.00
20:52:36.067587	B401C1D00	Read-Ack  	Return water temperature: 29.00
20:52:36.714926	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:36.825536	Command: PR=W
20:52:36.923757	PR: W=A
20:52:37.098271	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:37.744998	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:38.130716	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:38.778351	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:39.160062	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:39.808004	R80190000	Read-Data 	Boiler water temperature: 0.00
20:52:40.217330	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:52:40.849715	R10010A00	Write-Data	Control setpoint: 10.00
20:52:41.227516	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:52:41.877021	R80380000	Read-Data 	DHW setpoint: 0.00
20:52:42.260897	B40382D00	Read-Ack  	DHW setpoint: 45.00
20:52:42.909154	R00390000	Read-Data 	Max CH water setpoint: 0.00
20:52:43.281710	B40393200	Read-Ack  	Max CH water setpoint: 50.00
20:52:43.947874	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:44.361919	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:44.978742	R00120000	Read-Data 	CH water pressure: 0.00
20:52:45.337281	BC0120186	Read-Ack  	CH water pressure: 1.52
20:52:46.021494	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:46.396780	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:47.048201	R80190000	Read-Data 	Boiler water temperature: 0.00
20:52:47.410963	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:52:48.077646	R10010A00	Write-Data	Control setpoint: 10.00
20:52:48.456511	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:52:49.106681	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:49.520371	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:50.139092	R00110000	Read-Data 	Relative modulation level: 0.00
20:52:50.496412	BC0110000	Read-Ack  	Relative modulation level: 0.00
20:52:51.179387	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:51.553936	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:52.220491	R801C0000	Read-Data 	Return water temperature: 0.00
20:52:52.598253	B401C1D00	Read-Ack  	Return water temperature: 29.00
20:52:53.246178	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:53.416354	Command: SW=45.00
20:52:53.532201	SW: 45.00
20:52:53.627562	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:54.285361	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:54.687650	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:55.321210	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:52:55.702262	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:52:56.348409	R80190000	Read-Data 	Boiler water temperature: 0.00
20:52:56.736256	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:52:57.382565	R10010A00	Write-Data	Control setpoint: 10.00
20:52:57.772378	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:52:58.412258	R80380000	Read-Data 	DHW setpoint: 0.00
20:52:58.789075	B40382D00	Read-Ack  	DHW setpoint: 45.00
20:52:59.453816	R00390000	Read-Data 	Max CH water setpoint: 0.00
20:52:59.844539	B40393200	Read-Ack  	Max CH water setpoint: 50.00
20:53:00.493734	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:00.866205	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:01.530791	R00120000	Read-Data 	CH water pressure: 0.00
20:53:01.907723	BC0120186	Read-Ack  	CH water pressure: 1.52
20:53:02.572605	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:02.987858	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:03.604064	R80190000	Read-Data 	Boiler water temperature: 0.00
20:53:03.999671	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:53:04.630596	R10010A00	Write-Data	Control setpoint: 10.00
20:53:05.013210	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:53:05.661089	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:06.042424	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:06.692233	R00110000	Read-Data 	Relative modulation level: 0.00
20:53:06.705395	Command: HW=1
20:53:06.769380	HW: 1
20:53:07.074278	BC0110000	Read-Ack  	Relative modulation level: 0.00
20:53:07.723369	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:08.161936	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:08.455596	Command: SH=51.97
20:53:08.531753	SH: 51.97
20:53:08.759202	R801C0000	Read-Data 	Return water temperature: 0.00
20:53:09.157163	B401C1D00	Read-Ack  	Return water temperature: 29.00
20:53:09.793554	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:10.132061	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:10.828526	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:11.217722	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:11.866154	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:12.247427	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:12.894901	R80190000	Read-Data 	Boiler water temperature: 0.00
20:53:13.274019	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:53:13.922527	R10010A00	Write-Data	Control setpoint: 10.00
20:53:14.330620	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:53:14.965498	R80380000	Read-Data 	DHW setpoint: 0.00
20:53:15.346980	B40382D00	Read-Ack  	DHW setpoint: 45.00
20:53:15.996502	R00390000	Read-Data 	Max CH water setpoint: 0.00
20:53:16.381663	B40393200	Read-Ack  	Max CH water setpoint: 50.00
20:53:17.025860	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:17.407240	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:18.054701	R00120000	Read-Data 	CH water pressure: 0.00
20:53:18.437839	BC0120186	Read-Ack  	CH water pressure: 1.52
20:53:19.083307	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:19.502095	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:20.117738	R80190000	Read-Data 	Boiler water temperature: 0.00
20:53:20.511134	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:53:21.152984	R10010A00	Write-Data	Control setpoint: 10.00
20:53:21.534411	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:53:22.185240	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:22.562355	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:23.209684	R00110000	Read-Data 	Relative modulation level: 0.00
20:53:23.589960	BC0110000	Read-Ack  	Relative modulation level: 0.00
20:53:24.239337	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:24.655841	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:25.274269	R801C0000	Read-Data 	Return water temperature: 0.00
20:53:25.665713	B401C1D00	Read-Ack  	Return water temperature: 29.00
20:53:26.316813	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:26.695946	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:27.344337	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:27.728013	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:28.374679	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:28.797234	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:29.415016	R80190000	Read-Data 	Boiler water temperature: 0.00
20:53:29.818998	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:53:30.450294	R10010A00	Write-Data	Control setpoint: 10.00
20:53:30.834009	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:53:31.247323	Command: TC=22.00
20:53:31.331192	TC: 22.00
20:53:31.483087	R80380000	Read-Data 	DHW setpoint: 0.00
20:53:31.862515	B40382D00	Read-Ack  	DHW setpoint: 45.00
20:53:32.510860	R00390000	Read-Data 	Max CH water setpoint: 0.00
20:53:32.888732	B40393200	Read-Ack  	Max CH water setpoint: 50.00
20:53:33.537261	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:33.920390	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:34.567547	R00120000	Read-Data 	CH water pressure: 0.00
20:53:34.929266	BC0120186	Read-Ack  	CH water pressure: 1.52
20:53:35.613042	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:35.993177	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:36.647282	R80190000	Read-Data 	Boiler water temperature: 0.00
20:53:37.014976	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:53:37.680731	R10010A00	Write-Data	Control setpoint: 10.00
20:53:38.065426	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:53:38.718022	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:39.128283	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:39.747430	R00110000	Read-Data 	Relative modulation level: 0.00
20:53:40.092748	BC0110000	Read-Ack  	Relative modulation level: 0.00
20:53:40.774798	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:41.147899	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:41.811600	R801C0000	Read-Data 	Return water temperature: 0.00
20:53:42.196919	B401C1D00	Read-Ack  	Return water temperature: 29.00
20:53:42.846132	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:43.220243	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:43.881671	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:44.228140	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:44.913394	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:45.148935	Command: PR=L
20:53:45.157424	Command: PR=G
20:53:45.229297	PR: L=FXOMPC
20:53:45.278047	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:45.503831	PR: G=00
20:53:45.939488	R80190000	Read-Data 	Boiler water temperature: 0.00
20:53:46.138298	Command: PR=V
20:53:46.147470	Command: PR=T
20:53:46.159054	Command: PR=S
20:53:46.230063	PR: V=3
20:53:46.327584	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:53:46.434630	PR: T=11
20:53:46.472306	PR: S=16.00
20:53:46.974326	R10010A00	Write-Data	Control setpoint: 10.00
20:53:47.362393	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:53:48.033774	R80380000	Read-Data 	DHW setpoint: 0.00
20:53:48.391336	B40382D00	Read-Ack  	DHW setpoint: 45.00
20:53:49.037544	R00390000	Read-Data 	Max CH water setpoint: 0.00
20:53:49.451651	B40393200	Read-Ack  	Max CH water setpoint: 50.00
20:53:50.069847	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:50.460614	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:51.108236	R00120000	Read-Data 	CH water pressure: 0.00
20:53:51.488279	BC0120186	Read-Ack  	CH water pressure: 1.52
20:53:52.137058	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:52.514494	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:53.180752	R80190000	Read-Data 	Boiler water temperature: 0.00
20:53:53.599011	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:53:54.218282	R10010A00	Write-Data	Control setpoint: 10.00
20:53:54.610076	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:53:55.257154	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:55.635257	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:56.119565	Command: UI=2
20:53:56.225900	UI: 2
20:53:56.308916	R00110000	Read-Data 	Relative modulation level: 0.00
20:53:56.662783	BC0110000	Read-Ack  	Relative modulation level: 0.00
20:53:57.311026	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:57.687865	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:53:58.339230	R801C0000	Read-Data 	Return water temperature: 0.00
20:53:58.766525	B401C1D00	Read-Ack  	Return water temperature: 29.00
20:53:59.375643	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:53:59.785703	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:54:00.405854	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:54:00.793641	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:54:01.433879	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:54:01.812791	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:54:02.476925	R80190000	Read-Data 	Boiler water temperature: 0.00
20:54:02.858943	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:54:03.508253	R10010A00	Write-Data	Control setpoint: 10.00
20:54:03.930825	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:54:04.541621	R80380000	Read-Data 	DHW setpoint: 0.00
20:54:04.931026	B40382D00	Read-Ack  	DHW setpoint: 45.00
20:54:05.581146	R00390000	Read-Data 	Max CH water setpoint: 0.00
20:54:05.952502	B40393200	Read-Ack  	Max CH water setpoint: 50.00
20:54:06.616214	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:54:06.973525	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:54:07.655476	R00120000	Read-Data 	CH water pressure: 0.00
20:54:08.071614	BC0120186	Read-Ack  	CH water pressure: 1.52
20:54:08.683939	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:54:09.078835	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:54:09.725103	R80190000	Read-Data 	Boiler water temperature: 0.00
20:54:10.087525	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:54:10.768417	R10010A00	Write-Data	Control setpoint: 10.00
20:54:11.147177	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:54:11.821087	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:54:12.221511	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:54:12.855928	R00110000	Read-Data 	Relative modulation level: 0.00
20:54:13.233980	BC0110000	Read-Ack  	Relative modulation level: 0.00
20:54:13.896680	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:54:14.265692	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:54:14.928514	R801C0000	Read-Data 	Return water temperature: 0.00
20:54:15.347846	B401C1D00	Read-Ack  	Return water temperature: 29.00
20:54:15.964545	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:54:16.364976	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:54:17.002310	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:54:17.381993	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:54:18.038365	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:54:18.410227	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:54:19.061546	R80190000	Read-Data 	Boiler water temperature: 0.00
20:54:19.412426	BC0192500	Read-Ack  	Boiler water temperature: 37.00
20:54:20.094887	R10010A00	Write-Data	Control setpoint: 10.00
20:54:20.518248	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:54:21.135175	R80380000	Read-Data 	DHW setpoint: 0.00
20:54:21.526643	B40382D00	Read-Ack  	DHW setpoint: 45.00
20:54:22.174863	R00390000	Read-Data 	Max CH water setpoint: 0.00
20:54:22.555129	B40393200	Read-Ack  	Max CH water setpoint: 50.00
20:54:23.204073	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:54:23.581522	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:54:24.246286	R00120000	Read-Data 	CH water pressure: 0.00
20:54:24.665824	BC0120186	Read-Ack  	CH water pressure: 1.52
20:54:25.282735	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:54:25.674292	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:54:26.324596	R80190000	Read-Data 	Boiler water temperature: 0.00
20:54:26.699955	B40192400	Read-Ack  	Boiler water temperature: 36.00
20:54:27.365342	R10010A00	Write-Data	Control setpoint: 10.00
20:54:27.747873	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:54:28.402126	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
20:54:28.810613	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
20:54:29.209867	Thermostat connected
20:54:32.206589	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
20:54:32.277688	Medium power
20:54:33.610830	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
20:54:34.008283	Error 03
20:54:34.638033	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
20:54:35.035710	Error 03
20:54:35.638738	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
20:54:35.966218	Error 03
20:54:36.636952	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
20:54:37.035830	Error 03
20:54:37.637489	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
20:54:38.034432	Error 03
20:54:38.638964	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
20:54:39.041040	Error 03
20:54:39.639416	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
20:54:40.059092	Error 03
20:54:40.639711	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
20:54:41.024428	Error 03
20:54:41.643496	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
20:54:42.073309	Error 03
20:54:42.642979	T1002011C	Write-Data	Master configuration: 00000001 28
hvxl
Senior Member
Senior Member
Posts: 2034
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Connection to BRAHMA thermostat and "EMMETI" boiler

Post by hvxl »

The procedure is what I intended, but somehow the OTGW doesn't send an alternative message when it receives MsgID 2 from the thermostat. The only reason I can think of for that to happen is if the list of alternatives is empty. In that case the OTGW will still send the received message to the boiler. Did you happen to clear all alternative messages at some point?

Looking at the part of the log when it's just the OTGW talking to the boiler, it seems that way. The UserDefined slots in the message sequence are filled with status messages. That's what the OTGW does when there are no alternative messages available.

So, for the next try, first define an alternative message that your boiler supports, like the boiler water temperature (AA=25). The UI=2 command is stored in EEPROM, so it should not be necessary to repeat that, although it won't hurt either.
Schelte
mcasamento
Starting Member
Starting Member
Posts: 17
Joined: Fri Jan 03, 2020 6:14 pm

Re: Connection to BRAHMA thermostat and "EMMETI" boiler

Post by mcasamento »

Something has changed!!
I've issued AA=25 and restarted the boiler (it wouldn't connect to the OTGW without restarting).
Then I've connected the thermostat but the thermostat wouldn't connect, keep saying "Connecting...". After about a minute a button on the thermostat turned red, to indicate a faulty connection, I pressed it again, it tried to connect for a while with "Connecting..." on the display, but no success :-(
Follow the relevant log

Code: Select all

4:15:04.761809	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
14:15:05.377459	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:05.776614	BC0192900	Read-Ack  	Boiler water temperature: 41.00
14:15:06.418030	R10010A00	Write-Data	Control setpoint: 10.00
14:15:06.807632	BD0010A00	Write-Ack 	Control setpoint: 10.00
14:15:07.453397	R80380000	Read-Data 	DHW setpoint: 0.00
14:15:07.848085	B40382D00	Read-Ack  	DHW setpoint: 45.00
14:15:08.490520	R00390000	Read-Data 	Max CH water setpoint: 0.00
14:15:08.906092	B40393400	Read-Ack  	Max CH water setpoint: 52.00
14:15:09.525723	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:09.921745	BC0192900	Read-Ack  	Boiler water temperature: 41.00
14:15:10.556116	R00120000	Read-Data 	CH water pressure: 0.00
14:15:10.940471	B4012016C	Read-Ack  	CH water pressure: 1.42
14:15:11.586758	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
14:15:11.964418	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
14:15:12.628044	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:13.011204	BC0192900	Read-Ack  	Boiler water temperature: 41.00
14:15:13.658540	R10010A00	Write-Data	Control setpoint: 10.00
14:15:14.062519	BD0010A00	Write-Ack 	Control setpoint: 10.00
14:15:14.697795	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:15.029177	BC0192900	Read-Ack  	Boiler water temperature: 41.00
14:15:15.736135	R00110000	Read-Data 	Relative modulation level: 0.00
14:15:16.122127	BC0110000	Read-Ack  	Relative modulation level: 0.00
14:15:16.765707	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:17.149780	BC0192900	Read-Ack  	Boiler water temperature: 41.00
14:15:17.801400	R801C0000	Read-Data 	Return water temperature: 0.00
14:15:18.214838	B401C1D00	Read-Ack  	Return water temperature: 29.00
14:15:18.827659	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:19.228322	BC0192900	Read-Ack  	Boiler water temperature: 41.00
14:15:19.868016	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:20.245297	BC0192900	Read-Ack  	Boiler water temperature: 41.00
14:15:20.894215	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
14:15:21.202012	Error 03
14:15:21.986662	R80000200	Read-Data 	Status: 00000010 00000000
		   - CH enable: disabled (0)
		   - DHW enable: enabled (1)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
14:15:22.220264	Thermostat connected
14:15:22.370006	B40000200	Read-Ack  	Status: 00000010 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
14:15:24.905937	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
14:15:25.000772	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:25.028857	Medium power
14:15:25.096320	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
14:15:25.142726	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:25.503204	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:25.542540	AD002011C	Write-Ack 	Master configuration: 00000001 28
		   - Smart power: supported (1)
14:15:25.705914	T00030000	Read-Data 	Slave configuration: 00000000 0
14:15:26.107603	B40030100	Read-Ack  	Slave configuration: 00000001 0
		   - DHW: present (1)
		   - Control type: modulating (0)
		   - Cooling: not supported (0)
		   - DHW: instantaneous (0)
		   - Master pump control: allowed (0)
		   - CH2: not present (0)
		   - Remote water filling: available/unknown (0)
		   - Heat/cool mode control: heat (0)
14:15:26.373757	T00060000	Read-Data 	Remote parameter flags: 00000000 00000000
14:15:26.716638	BC0060303	Read-Ack  	Remote parameter flags: 00000011 00000011
		   - DHW setpoint transfer: enabled (1)
		   - max CH setpoint transfer: enabled (1)
		   - DHW setpoint: read/write (1)
		   - max CH setpoint: read/write (1)
14:15:27.304989	T00050000	Read-Data 	Application-specific flags: 00000000 0
14:15:27.726826	B40050100	Read-Ack  	Application-specific flags: 00000001 0
		   - Service request: yes (1)
		   - Lockout-reset: disabled (0)
		   - Low water pressure: no fault (0)
		   - Gas/flame fault: no fault (0)
		   - Air pressure fault: no fault (0)
		   - Water over-temperature: no fault (0)
14:15:27.921437	T000A0000	Read-Data 	Number of TSPs: 0
14:15:28.287313	BF00A0000	Unk-DataId	Number of TSPs: 0
14:15:28.507771	T000C0000	Read-Data 	Size of fault buffer: 0
14:15:28.880796	BF00C0000	Unk-DataId	Size of fault buffer: 0
14:15:29.107780	T00120000	Read-Data 	CH water pressure: 0.00
14:15:29.490121	B4012016C	Read-Ack  	CH water pressure: 1.42
14:15:29.707318	T00110000	Read-Data 	Relative modulation level: 0.00
14:15:30.087398	BC0110000	Read-Ack  	Relative modulation level: 0.00
14:15:30.301365	T00120000	Read-Data 	CH water pressure: 0.00
14:15:30.691969	B4012016C	Read-Ack  	CH water pressure: 1.42
14:15:30.901704	T80130000	Read-Data 	DHW flow rate: 0.00
14:15:31.284242	B70130000	Unk-DataId	DHW flow rate: 0.00
14:15:31.508344	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:31.885336	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
14:15:31.904684	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:32.105010	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:32.496831	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
14:15:32.521906	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:32.702573	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:33.095788	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
14:15:33.139373	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:33.303107	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:33.330373	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:33.703435	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:33.765241	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:33.904080	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:33.954820	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:34.262639	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:34.312276	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:34.505278	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:34.545428	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:34.919493	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:34.979656	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:35.105891	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:35.122362	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:35.523982	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:35.577402	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:35.707494	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:35.749608	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:36.131329	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:36.196841	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:36.313537	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:36.333109	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:36.688603	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:36.733785	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:37.309891	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:37.367379	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:37.699230	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:37.736788	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:37.913398	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:37.951712	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:38.277917	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:38.336035	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:38.513294	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:38.544231	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:38.891019	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:38.942265	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:39.115663	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:39.166692	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:39.488449	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:39.536580	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:39.713361	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:39.746279	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:40.099860	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:40.153422	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:40.310383	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:40.329025	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:40.646255	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:40.678539	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:40.913698	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:40.938007	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:41.294487	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:41.310604	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:41.517841	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:41.564944	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:41.907470	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:41.967419	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:42.114561	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:42.159255	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:42.521020	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:42.565246	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:42.715007	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:42.772322	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:43.129786	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:43.199604	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:43.317244	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:43.334359	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:43.732213	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:43.765048	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:43.910559	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:43.932361	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:44.334893	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:44.414405	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:44.515966	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:44.563896	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:44.935480	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:44.979979	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:45.117091	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:45.170654	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:45.499434	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:45.535445	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:45.716364	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:45.746811	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:46.104076	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:46.162783	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:46.317364	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:46.358275	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:46.706119	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:46.748126	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:47.323659	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:47.391793	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:47.702307	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:47.743515	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:47.918755	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:47.944728	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:48.304130	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:48.324455	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:48.520185	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:48.580364	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:48.907955	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:48.962745	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:49.122474	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:49.171551	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:49.505030	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:49.548127	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:49.719750	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:49.765089	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:50.115299	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:50.157874	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:50.316417	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:50.392004	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:50.720471	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:50.757920	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:50.922896	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:51.001039	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:51.320406	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:51.381943	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:51.522363	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:51.585026	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:51.925575	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:51.973783	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:52.117612	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:52.137384	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:52.534867	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:52.570805	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:52.722568	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:52.762885	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:53.135658	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:53.187712	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:53.317445	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:53.362193	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:53.706781	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:53.776943	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:53.918913	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:53.978745	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:54.299969	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:54.330316	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:54.518867	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:54.583626	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:54.898048	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:54.955577	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:55.124188	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:55.175086	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:55.498804	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:55.536835	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:55.723490	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:55.776453	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:56.109448	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:56.162655	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:56.326764	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:56.385450	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:56.705096	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:56.724372	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:57.326753	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:57.364191	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:57.711024	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:57.767901	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:57.924948	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:57.963382	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:58.306240	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:58.339332	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:58.521842	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:58.572075	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:58.922239	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:58.991155	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:59.127728	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:59.163921	R80190000	Read-Data 	Boiler water temperature: 0.00
14:15:59.522837	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:15:59.567950	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:15:59.726508	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:15:59.783240	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:00.128541	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:00.149719	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:00.330170	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:00.363277	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:00.743522	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:00.761618	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:00.928347	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:00.947003	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:01.345430	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:01.379421	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:01.526635	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:01.563037	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:01.942726	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:01.982317	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:02.123551	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:02.166835	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:02.518929	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:02.576386	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:02.728192	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:02.746026	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:03.120797	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:03.160805	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:03.329159	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:03.349393	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:03.710908	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:03.751368	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:03.924593	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:03.969786	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:04.312555	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:04.371013	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:04.531466	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:04.566460	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:04.910070	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:04.947808	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:05.125730	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:05.170416	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:05.508074	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:05.527869	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:05.733644	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:05.764014	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:06.148186	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:06.205429	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:06.331559	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:06.349080	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:06.722674	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:06.772371	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:07.334837	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:07.401098	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:07.726757	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:07.806082	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:07.932647	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:07.976532	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:08.291730	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:08.374693	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:08.533219	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:08.576465	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:08.940102	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:09.005984	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:09.130949	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:09.175206	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:09.545097	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:09.623693	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:09.732271	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:09.762216	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:10.154863	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:10.193138	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:10.332708	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:10.360488	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:10.715346	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:10.755313	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:10.935655	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:10.972590	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:11.318259	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:11.353167	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:11.535090	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:11.575534	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:11.887954	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:11.914286	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:12.134148	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:12.186981	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:12.507948	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:12.564889	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:12.737962	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:12.804838	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:13.119710	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:13.158374	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:13.333547	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:13.404860	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:13.715268	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:13.756528	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:13.942273	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:14.011086	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:14.320150	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:14.358353	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:14.538813	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:14.581217	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:14.920114	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:14.964510	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:15.140404	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:15.179934	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:15.521952	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:15.561378	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:15.738360	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:15.780632	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:18.283273	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:18.332322	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:18.381585	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:18.410546	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:18.437351	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:18.465421	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:18.494025	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:18.523073	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:18.552574	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:18.581945	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:18.612538	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:18.640743	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:18.670305	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:18.699180	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:18.728811	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:18.756752	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:18.961345	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:18.999412	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:19.137613	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:19.217950	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:19.562521	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:19.610210	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:19.746607	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:19.787822	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:20.115967	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:20.177858	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:20.345395	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:20.398288	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:20.722302	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:20.783160	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:20.942919	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:21.011191	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:21.329107	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:21.350279	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:21.541984	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:21.561191	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:21.926723	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:22.001688	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:22.139700	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:22.185160	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:22.529795	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:22.563355	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:22.741949	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:22.786483	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:23.127815	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:23.184756	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:23.344157	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:23.373938	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:23.732554	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:23.784419	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:23.940414	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:23.989102	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:24.336797	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:24.387283	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:24.541154	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:24.615235	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:24.943357	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:24.984690	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:25.145763	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:25.212226	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:25.546460	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:25.613337	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:25.748225	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:25.804359	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:26.148895	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:26.210030	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:26.342100	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:26.380657	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:26.753300	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:26.812683	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:27.348290	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:27.395197	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:27.714593	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:27.781104	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:27.945664	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:27.964884	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:28.327785	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:28.380181	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:28.542789	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:28.600341	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:28.932052	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:28.968267	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:29.148135	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:29.203949	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:29.528066	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:29.577917	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:29.749207	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:29.768391	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:30.133136	B40192800	Read-Ack  	Boiler water temperature: 40.00
14:16:30.156470	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:30.349636	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:30.388568	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:30.726028	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:30.778842	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:30.946439	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:30.964575	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:31.331794	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:31.403197	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:31.547808	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:31.590865	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:31.929981	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:31.981418	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:32.157119	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:32.216192	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:32.530491	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:32.566074	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:32.746041	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:32.786127	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:33.143207	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:33.217344	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:33.345748	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:33.409164	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:33.695690	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:33.776664	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:33.947870	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:34.006870	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:34.351141	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:34.405087	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:34.552588	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:34.590713	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:34.957517	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:34.996722	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:35.151145	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:35.169069	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:35.575869	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:35.603464	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:35.748206	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:35.809925	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:36.168806	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:36.210043	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:36.356145	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:36.418298	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:36.726447	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:36.773635	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:37.349529	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:37.401708	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:37.732183	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:37.768706	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:37.953444	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:37.999925	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:38.332814	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:38.398583	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:38.556621	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:38.602830	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:38.944368	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:38.990308	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:39.153951	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:39.202611	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:39.532260	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:39.574813	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:39.764732	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:39.803892	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:40.135702	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:40.169471	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:40.357352	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:40.405712	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:40.739803	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:40.771956	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:40.955946	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:41.005943	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:41.339643	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:41.356313	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:41.556751	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:41.573140	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:41.945853	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:42.017383	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:42.158309	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:42.210633	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:42.557870	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:16:42.595368	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:42.767081	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:42.799405	R80190000	Read-Data 	Boiler water temperature: 0.00
14:16:44.239645	OpenTherm Gateway 4.2.5
14:16:47.123328	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
14:16:47.198377	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
14:16:47.230368	Medium power
14:16:47.350544	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
14:16:47.453099	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
14:16:47.726485	BC0060303	Read-Ack  	Remote parameter flags: 00000011 00000011
		   - DHW setpoint transfer: enabled (1)
		   - max CH setpoint transfer: enabled (1)
		   - DHW setpoint: read/write (1)
		   - max CH setpoint: read/write (1)
14:16:47.928511	AD002011C	Write-Ack 	Master configuration: 00000001 28
		   - Smart power: supported (1)
14:16:47.987178	T00030000	Read-Data 	Slave configuration: 00000000 0
14:16:48.328767	B40030100	Read-Ack  	Slave configuration: 00000001 0
		   - DHW: present (1)
		   - Control type: modulating (0)
		   - Cooling: not supported (0)
		   - DHW: instantaneous (0)
		   - Master pump control: allowed (0)
		   - CH2: not present (0)
		   - Remote water filling: available/unknown (0)
		   - Heat/cool mode control: heat (0)
14:16:48.571278	T00060000	Read-Data 	Remote parameter flags: 00000000 00000000
14:16:48.946438	BC0060303	Read-Ack  	Remote parameter flags: 00000011 00000011
		   - DHW setpoint transfer: enabled (1)
		   - max CH setpoint transfer: enabled (1)
		   - DHW setpoint: read/write (1)
		   - max CH setpoint: read/write (1)
14:16:49.151422	T00050000	Read-Data 	Application-specific flags: 00000000 0
14:16:49.530235	B40050100	Read-Ack  	Application-specific flags: 00000001 0
		   - Service request: yes (1)
		   - Lockout-reset: disabled (0)
		   - Low water pressure: no fault (0)
		   - Gas/flame fault: no fault (0)
		   - Air pressure fault: no fault (0)
		   - Water over-temperature: no fault (0)
14:16:49.751061	T000A0000	Read-Data 	Number of TSPs: 0
14:16:50.136243	BF00A0000	Unk-DataId	Number of TSPs: 0
14:16:50.352098	T000C0000	Read-Data 	Size of fault buffer: 0
14:16:50.759408	BF00C0000	Unk-DataId	Size of fault buffer: 0
14:16:50.958161	T90101201	Write-Data	Room setpoint: 18.00
14:16:51.356022	B70100000	Unk-DataId	Room setpoint: 0.00
14:16:51.391178	AD0100000	Write-Ack 	Room setpoint: 0.00
14:16:51.553018	T90101201	Write-Data	Room setpoint: 18.00
14:16:51.960560	B70100000	Unk-DataId	Room setpoint: 0.00
14:16:51.993020	AD0100000	Write-Ack 	Room setpoint: 0.00
14:16:52.153036	T90101201	Write-Data	Room setpoint: 18.00
14:16:52.569455	B70100000	Unk-DataId	Room setpoint: 0.00
14:16:52.603722	AD0100000	Write-Ack 	Room setpoint: 0.00
14:16:52.755097	T90101201	Write-Data	Room setpoint: 18.00
14:16:52.800464	R00300000	Read-Data 	DHW setpoint boundaries: 0 0
14:16:53.172362	B40303C23	Read-Ack  	DHW setpoint boundaries: 60 35
14:16:53.203859	A50101201	Write-Ack 	Room setpoint: 18.00
14:16:53.358704	T00110000	Read-Data 	Relative modulation level: 0.00
14:16:53.778645	BC0110000	Read-Ack  	Relative modulation level: 0.00
14:16:53.956535	T00120000	Read-Data 	CH water pressure: 0.00
14:16:54.335703	B4012016C	Read-Ack  	CH water pressure: 1.42
14:16:54.554289	T80130000	Read-Data 	DHW flow rate: 0.00
14:16:54.938745	B70130000	Unk-DataId	DHW flow rate: 0.00
14:16:55.154293	T90101201	Write-Data	Room setpoint: 18.00
14:16:55.200698	R80310000	Read-Data 	Max CH setpoint boundaries: 0 0
14:16:55.540042	B40315028	Read-Ack  	Max CH setpoint boundaries: 80 40
14:16:55.573946	A50101201	Write-Ack 	Room setpoint: 18.00
14:16:55.756942	T00110000	Read-Data 	Relative modulation level: 0.00
14:16:56.137272	BC0110000	Read-Ack  	Relative modulation level: 0.00
14:16:56.358392	T00120000	Read-Data 	CH water pressure: 0.00
14:16:56.740072	B4012016C	Read-Ack  	CH water pressure: 1.42
14:16:57.358346	T80130000	Read-Data 	DHW flow rate: 0.00
14:16:57.737593	B70130000	Unk-DataId	DHW flow rate: 0.00
14:16:57.957078	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:58.344703	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
14:16:58.385169	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:58.559741	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:58.950653	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
14:16:58.988856	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:59.157382	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:59.518743	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
14:16:59.549032	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:16:59.758972	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:16:59.811397	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:00.163754	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:00.181694	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:00.360213	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:00.400339	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:00.725700	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:00.761568	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:00.959683	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:00.999393	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:01.378876	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:01.400228	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:01.561571	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:01.588790	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:01.936210	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:01.978731	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:02.160258	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:02.201450	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:02.544180	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:02.605089	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:02.762895	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:02.808375	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:03.144848	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:03.161546	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:03.359579	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:03.408464	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:03.749243	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:03.792136	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:03.960289	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:03.984445	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:04.325493	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:04.381033	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:04.563314	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:04.616511	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:04.946940	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:05.013130	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:05.162241	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:05.224401	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:05.531176	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:05.549001	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:05.763788	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:05.782412	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:06.139714	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:06.158211	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:06.361754	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:06.385200	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:06.748036	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:06.780425	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:07.364519	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:07.426995	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:07.753448	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:07.795528	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:07.966805	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:08.016906	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:08.367953	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:08.437846	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:08.564507	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:08.614515	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:08.977118	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:09.029586	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:09.165784	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:09.183943	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:10.168454	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:10.229929	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:10.585336	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:10.628567	AC0140000	Read-Ack  	Day of week and time of day: Unk 00:00
14:17:10.767849	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
14:17:10.806008	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:10.898679	High power
14:17:10.946397	Thermostat disconnected
14:17:10.966588	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
14:17:11.212131	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
14:17:11.974151	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:12.341921	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:13.005382	R10010A00	Write-Data	Control setpoint: 10.00
14:17:13.384622	BD0010A00	Write-Ack 	Control setpoint: 10.00
14:17:14.048606	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:14.439075	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:15.086463	R00110000	Read-Data 	Relative modulation level: 0.00
14:17:15.466146	BC0110000	Read-Ack  	Relative modulation level: 0.00
14:17:16.126845	R001B0000	Read-Data 	Outside temperature: 0.00
14:17:16.504552	BF01B0000	Unk-DataId	Outside temperature: 0.00
14:17:17.168891	R801C0000	Read-Data 	Return water temperature: 0.00
14:17:17.536975	B401C1D00	Read-Ack  	Return water temperature: 29.00
14:17:18.203523	R900E6400	Write-Data	Maximum relative modulation level: 100.00
14:17:18.548976	B700E0000	Unk-DataId	Maximum relative modulation level: 0.00
14:17:19.232624	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:19.609704	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:20.272786	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
14:17:20.655521	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
14:17:21.316599	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:21.727257	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:22.344522	R10010A00	Write-Data	Control setpoint: 10.00
14:17:22.745388	BD0010A00	Write-Ack 	Control setpoint: 10.00
14:17:23.374403	R80380000	Read-Data 	DHW setpoint: 0.00
14:17:23.756107	B40382D00	Read-Ack  	DHW setpoint: 45.00
14:17:24.403709	R00390000	Read-Data 	Max CH water setpoint: 0.00
14:17:24.776291	B40393400	Read-Ack  	Max CH water setpoint: 52.00
14:17:25.445273	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:25.820940	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:26.482069	R00120000	Read-Data 	CH water pressure: 0.00
14:17:26.850868	B4012016C	Read-Ack  	CH water pressure: 1.42
14:17:27.516053	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
14:17:27.860235	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
14:17:28.554209	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:28.920426	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:29.570663	R10010A00	Write-Data	Control setpoint: 10.00
14:17:29.953457	BD0010A00	Write-Ack 	Control setpoint: 10.00
14:17:30.604437	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:30.985378	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:31.632834	R00110000	Read-Data 	Relative modulation level: 0.00
14:17:32.050545	BC0110000	Read-Ack  	Relative modulation level: 0.00
14:17:32.669762	R001B0000	Read-Data 	Outside temperature: 0.00
14:17:33.064796	BF01B0000	Unk-DataId	Outside temperature: 0.00
14:17:33.700441	R801C0000	Read-Data 	Return water temperature: 0.00
14:17:34.077896	B401C1D00	Read-Ack  	Return water temperature: 29.00
14:17:34.725254	R900E6400	Write-Data	Maximum relative modulation level: 100.00
14:17:35.102340	B700E0000	Unk-DataId	Maximum relative modulation level: 0.00
14:17:35.771014	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:36.140284	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:36.802586	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
14:17:37.171135	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
14:17:37.835711	R80190000	Read-Data 	Boiler water temperature: 0.00
14:17:38.187910	B40192700	Read-Ack  	Boiler water temperature: 39.00
14:17:38.868021	R10010A00	Write-Data	Control setpoint: 10.00
14:17:39.241927	BD0010A00	Write-Ack 	Control setpoint: 10.00
14:17:39.904640	R80380000	Read-Data 	DHW setpoint: 0.00
14:17:40.273520	B40382D00	Read-Ack  	DHW setpoint: 45.00
14:17:40.949951	R00390000	Read-Data 	Max CH water setpoint: 0.00
14:17:41.314363	B40393400	Read-Ack  	Max CH water setpoint: 52.00

it has however practically stopped to send 03 Errors, we're making progress!
How can we try to understand what's needed to make the thermostat connect to OTGW ? Should I try to some how sniff communication in monitor mode ? If yes, should I first empty UI and AA messages ?

Thank you very much for your assistance!
hvxl
Senior Member
Senior Member
Posts: 2034
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Connection to BRAHMA thermostat and "EMMETI" boiler

Post by hvxl »

Ah, progress! Now the thermostat seems unhappy about the response to MsgID 20. Rather than responding Unk-DataId as the boiler does, the OTGW returns Read-Data, but with a day of week of 0. This is supposed to mean "no DoW info available", but the thermostat possibly considers it invalid. This may need to be changed in the firmware.

For now, try enabling the "Automatically update the gateway clock" setting in OTmonitor. That should cause the OTGW to return a valid day and time. As a bonus the thermostat will have the correct time, so you don't have to set that manually anymore.
Schelte
mcasamento
Starting Member
Starting Member
Posts: 17
Joined: Fri Jan 03, 2020 6:14 pm

Re: Connection to BRAHMA thermostat and "EMMETI" boiler

Post by mcasamento »

Changed again! Or at least it does look different to me. No more begging for date and time, but still the thermostat can't connect

Code: Select all

23:26:14.662944	Command: PR=M
23:26:18.696161	Command: GW=1
23:26:19.914307	Command: GW=0
23:26:22.248275	Command: GW=1
23:56:44.262625	80190000
23:56:44.781566	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:56:44.820989	Command: PR=A
23:56:44.962575	PR: A=OpenTherm Gateway 4.2.5
23:56:45.003300	Command: SC=23:56/4
23:56:45.193947	SC: 23:56/4
23:56:45.365658	R801C0000	Read-Data 	Return water temperature: 0.00
23:56:45.860878	B401C1B00	Read-Ack  	Return water temperature: 27.00
23:56:46.462025	R80190000	Read-Data 	Boiler water temperature: 0.00
23:56:46.663971	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:56:47.363987	R80190000	Read-Data 	Boiler water temperature: 0.00
23:56:47.863956	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:56:48.469561	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
23:56:49.090223	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
23:56:49.569219	R80190000	Read-Data 	Boiler water temperature: 0.00
23:56:49.899665	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:56:50.563858	R10010A00	Write-Data	Control setpoint: 10.00
23:56:50.862852	BD0010A00	Write-Ack 	Control setpoint: 10.00
23:56:51.588177	R80380000	Read-Data 	DHW setpoint: 0.00
23:56:51.873929	B40382D00	Read-Ack  	DHW setpoint: 45.00
23:56:52.564600	R00390000	Read-Data 	Max CH water setpoint: 0.00
23:56:52.885421	B40393400	Read-Ack  	Max CH water setpoint: 52.00
23:56:53.556548	R80190000	Read-Data 	Boiler water temperature: 0.00
23:56:53.663394	Command: PR=M
23:56:54.173647	PR: M=G
23:56:54.219158	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:56:54.603072	R00120000	Read-Data 	CH water pressure: 0.00
23:56:54.961904	B4012016C	Read-Ack  	CH water pressure: 1.42
23:56:55.627155	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
23:56:56.395819	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
23:56:57.231991	R80190000	Read-Data 	Boiler water temperature: 0.00
23:56:57.317973	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:56:57.856156	R10010A00	Write-Data	Control setpoint: 10.00
23:56:58.149707	BD0010A00	Write-Ack 	Control setpoint: 10.00
23:56:58.730331	R80190000	Read-Data 	Boiler water temperature: 0.00
23:56:59.104900	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:56:59.769501	R00110000	Read-Data 	Relative modulation level: 0.00
23:57:00.034333	Command: SC=23:57/4
23:57:00.151968	SC: 23:57/4
23:57:00.191361	BC0110000	Read-Ack  	Relative modulation level: 0.00
23:57:00.820558	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:01.181906	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:01.846034	R801C0000	Read-Data 	Return water temperature: 0.00
23:57:02.229220	B401C1B00	Read-Ack  	Return water temperature: 27.00
23:57:02.895399	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:03.291555	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:03.932510	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:04.284712	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:04.967003	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
23:57:05.349387	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
23:57:05.999642	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:06.381643	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:07.026782	R10010A00	Write-Data	Control setpoint: 10.00
23:57:07.445164	BD0010A00	Write-Ack 	Control setpoint: 10.00
23:57:08.067259	R80380000	Read-Data 	DHW setpoint: 0.00
23:57:08.458726	B40382D00	Read-Ack  	DHW setpoint: 45.00
23:57:09.106109	R00390000	Read-Data 	Max CH water setpoint: 0.00
23:57:09.482021	B40393400	Read-Ack  	Max CH water setpoint: 52.00
23:57:10.150011	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:10.524393	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:11.188604	R00120000	Read-Data 	CH water pressure: 0.00
23:57:11.595408	B4012016C	Read-Ack  	CH water pressure: 1.42
23:57:12.226490	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
23:57:12.600534	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
23:57:13.256470	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:13.636902	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:14.290234	R10010A00	Write-Data	Control setpoint: 10.00
23:57:14.667902	BD0010A00	Write-Ack 	Control setpoint: 10.00
23:57:15.314580	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:15.698648	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:16.349521	R00110000	Read-Data 	Relative modulation level: 0.00
23:57:16.753352	BC0110000	Read-Ack  	Relative modulation level: 0.00
23:57:17.392289	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:17.769828	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:18.417565	R801C0000	Read-Data 	Return water temperature: 0.00
23:57:18.791713	B401C1B00	Read-Ack  	Return water temperature: 27.00
23:57:19.457531	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:19.833282	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:20.498493	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:20.866210	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:21.530954	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
23:57:21.881545	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
23:57:22.555029	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:22.932475	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:23.600192	R10010A00	Write-Data	Control setpoint: 10.00
23:57:23.975604	BD0010A00	Write-Ack 	Control setpoint: 10.00
23:57:24.640595	R80380000	Read-Data 	DHW setpoint: 0.00
23:57:25.053531	B40382D00	Read-Ack  	DHW setpoint: 45.00
23:57:25.667652	R00390000	Read-Data 	Max CH water setpoint: 0.00
23:57:26.062804	B40393400	Read-Ack  	Max CH water setpoint: 52.00
23:57:26.715226	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:27.090049	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:27.752334	R00120000	Read-Data 	CH water pressure: 0.00
23:57:28.133557	B4012016C	Read-Ack  	CH water pressure: 1.42
23:57:28.792219	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
23:57:29.161625	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
23:57:29.824765	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:30.207696	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:30.862794	R10010A00	Write-Data	Control setpoint: 10.00
23:57:31.244170	BD0010A00	Write-Ack 	Control setpoint: 10.00
23:57:31.892439	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:32.272157	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:32.919421	R00110000	Read-Data 	Relative modulation level: 0.00
23:57:33.301890	BC0110000	Read-Ack  	Relative modulation level: 0.00
23:57:33.954181	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:34.364034	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:34.998061	R801C0000	Read-Data 	Return water temperature: 0.00
23:57:35.372320	B401C1B00	Read-Ack  	Return water temperature: 27.00
23:57:36.027072	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:36.404268	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:37.058039	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:37.434541	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:38.092355	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
23:57:38.457519	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
23:57:39.123541	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:39.518655	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:40.173657	R10010A00	Write-Data	Control setpoint: 10.00
23:57:40.551332	BD0010A00	Write-Ack 	Control setpoint: 10.00
23:57:41.202944	R80380000	Read-Data 	DHW setpoint: 0.00
23:57:41.587907	B40382D00	Read-Ack  	DHW setpoint: 45.00
23:57:42.228911	R00390000	Read-Data 	Max CH water setpoint: 0.00
23:57:42.616172	B40393400	Read-Ack  	Max CH water setpoint: 52.00
23:57:43.260278	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:43.675138	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:44.299303	R00120000	Read-Data 	CH water pressure: 0.00
23:57:44.684218	B4012016C	Read-Ack  	CH water pressure: 1.42
23:57:45.334255	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
23:57:45.705106	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
23:57:46.372220	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:46.755992	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:47.414902	R10010A00	Write-Data	Control setpoint: 10.00
23:57:47.781040	BD0010A00	Write-Ack 	Control setpoint: 10.00
23:57:48.449457	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:48.830834	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:49.474319	R00110000	Read-Data 	Relative modulation level: 0.00
23:57:49.866591	BC0110000	Read-Ack  	Relative modulation level: 0.00
23:57:50.516175	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:50.890277	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:51.538095	R801C0000	Read-Data 	Return water temperature: 0.00
23:57:51.925842	B401C1B00	Read-Ack  	Return water temperature: 27.00
23:57:52.583325	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:52.982181	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:53.613980	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:53.995298	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:54.472566	Error 03
23:57:54.707670	R00000000	Read-Data 	Status: 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
23:57:54.947708	Thermostat connected
23:57:55.103988	BC0000000	Read-Ack  	Status: 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
23:57:58.168595	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
23:57:58.234517	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:58.258514	Medium power
23:57:58.353397	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
23:57:58.388634	R80190000	Read-Data 	Boiler water temperature: 0.00
23:57:58.744213	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:57:58.787278	AD002011C	Write-Ack 	Master configuration: 00000001 28
		   - Smart power: supported (1)
23:57:58.956900	T00030000	Read-Data 	Slave configuration: 00000000 0
23:57:59.301681	B40030100	Read-Ack  	Slave configuration: 00000001 0
		   - DHW: present (1)
		   - Control type: modulating (0)
		   - Cooling: not supported (0)
		   - DHW: instantaneous (0)
		   - Master pump control: allowed (0)
		   - CH2: not present (0)
		   - Remote water filling: available/unknown (0)
		   - Heat/cool mode control: heat (0)
23:57:59.600163	T00060000	Read-Data 	Remote parameter flags: 00000000 00000000
23:57:59.965267	BC0060303	Read-Ack  	Remote parameter flags: 00000011 00000011
		   - DHW setpoint transfer: enabled (1)
		   - max CH setpoint transfer: enabled (1)
		   - DHW setpoint: read/write (1)
		   - max CH setpoint: read/write (1)
23:58:00.120172	Command: SC=23:58/4
23:58:00.139807	T00050000	Read-Data 	Application-specific flags: 00000000 0
23:58:00.242891	SC: 23:58/4
23:58:00.565562	B40050100	Read-Ack  	Application-specific flags: 00000001 0
		   - Service request: yes (1)
		   - Lockout-reset: disabled (0)
		   - Low water pressure: no fault (0)
		   - Gas/flame fault: no fault (0)
		   - Air pressure fault: no fault (0)
		   - Water over-temperature: no fault (0)
23:58:00.757935	T000A0000	Read-Data 	Number of TSPs: 0
23:58:01.175722	BF00A0000	Unk-DataId	Number of TSPs: 0
23:58:01.364782	T000C0000	Read-Data 	Size of fault buffer: 0
23:58:01.722209	BF00C0000	Unk-DataId	Size of fault buffer: 0
23:58:02.360789	T90100F01	Write-Data	Room setpoint: 15.00
23:58:02.731747	B70100000	Unk-DataId	Room setpoint: 0.00
23:58:02.766758	AD0100000	Write-Ack 	Room setpoint: 0.00
23:58:02.965610	T90100F01	Write-Data	Room setpoint: 15.00
23:58:03.328323	B70100000	Unk-DataId	Room setpoint: 0.00
23:58:03.384545	AD0100000	Write-Ack 	Room setpoint: 0.00
23:58:03.556406	T90100F01	Write-Data	Room setpoint: 15.00
23:58:03.941191	B70100000	Unk-DataId	Room setpoint: 0.00
23:58:04.003368	AD0100000	Write-Ack 	Room setpoint: 0.00
23:58:04.158508	T90100F01	Write-Data	Room setpoint: 15.00
23:58:04.214358	R80190000	Read-Data 	Boiler water temperature: 0.00
23:58:04.538713	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:58:04.578144	A50100F01	Write-Ack 	Room setpoint: 15.00
23:58:04.759877	T00110000	Read-Data 	Relative modulation level: 0.00
23:58:05.144492	BC0110000	Read-Ack  	Relative modulation level: 0.00
23:58:05.361628	T00120000	Read-Data 	CH water pressure: 0.00
23:58:05.691262	B4012016C	Read-Ack  	CH water pressure: 1.42
23:58:05.860603	T80130000	Read-Data 	DHW flow rate: 0.00
23:58:06.239404	B70130000	Unk-DataId	DHW flow rate: 0.00
23:58:06.472255	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:58:06.845067	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
23:58:06.896531	A4014973A	Read-Ack  	Day of week and time of day: Thu 23:58
23:58:07.064075	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:58:07.465928	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
23:58:07.520403	A4014973A	Read-Ack  	Day of week and time of day: Thu 23:58
23:58:07.669556	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:58:08.025396	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
23:58:08.077359	A4014973A	Read-Ack  	Day of week and time of day: Thu 23:58
23:58:08.267107	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:58:08.315766	R80190000	Read-Data 	Boiler water temperature: 0.00
23:58:08.626387	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:58:08.680183	A4014973A	Read-Ack  	Day of week and time of day: Thu 23:58
23:58:08.868735	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:58:08.918015	R80190000	Read-Data 	Boiler water temperature: 0.00
23:58:09.286245	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:58:09.347440	A4014973A	Read-Ack  	Day of week and time of day: Thu 23:58
23:58:09.460597	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:58:09.505458	R80190000	Read-Data 	Boiler water temperature: 0.00
23:58:09.841688	B40191E00	Read-Ack  	Boiler water temperature: 30.00
******LOG CUT BECAUSE message is too big and those messages are all the same***************
23:58:58.870017	A4014973A	Read-Ack  	Day of week and time of day: Thu 23:58
23:58:58.996365	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:58:59.013237	R80190000	Read-Data 	Boiler water temperature: 0.00
23:58:59.399374	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:58:59.461569	A4014973A	Read-Ack  	Day of week and time of day: Thu 23:58
23:58:59.601885	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:58:59.655160	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:00.002772	Command: SC=23:59/4
23:59:00.058466	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:00.087449	A4014973A	Read-Ack  	Day of week and time of day: Thu 23:58
23:59:00.115160	SC: 23:59/4
23:59:00.164915	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:00.211587	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:00.615920	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:00.669999	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:00.801680	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:00.837555	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:01.219872	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:01.259526	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:01.402739	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:01.458092	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:01.782997	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:01.818675	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:02.403594	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:02.465159	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:02.762340	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:02.778523	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:03.006556	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:03.040892	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:03.379378	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:03.436566	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:03.604369	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:03.647493	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:03.983041	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:04.045255	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:04.203244	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:04.255020	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:04.586128	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:04.645185	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:04.805852	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:04.866955	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:05.186273	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:05.205545	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:05.401426	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:05.451496	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:05.784960	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:05.844888	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:06.008656	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:06.047241	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:06.393360	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:06.447402	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:06.606151	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:06.641829	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:06.999393	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:07.052374	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:07.209505	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:07.240666	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:07.597695	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:07.641327	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:07.800181	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:07.838278	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:08.212030	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:08.282707	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:08.411727	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:08.451027	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:08.809896	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:08.897666	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:09.011119	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:09.065198	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:09.379526	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:09.438709	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:09.606914	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:09.663344	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:09.988937	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:10.047289	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:10.210317	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:10.265211	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:10.586110	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:10.667404	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:10.813075	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:10.871836	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:11.188789	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:11.243075	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:11.408506	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:11.480157	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:11.786664	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:11.827313	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:12.410671	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:12.446039	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:12.793164	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:12.809192	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:13.010947	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:13.030809	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:13.383347	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:13.412870	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:13.611310	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:13.649361	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:13.986586	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:14.037644	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:14.212245	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:14.265783	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:14.596519	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:14.642649	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:14.808360	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:14.876202	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:15.202834	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:15.246880	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:15.415119	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:15.481291	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:15.802815	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:15.863998	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:16.011682	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:16.052518	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:16.409623	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:16.448184	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:16.613861	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:16.655190	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:17.015758	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:17.061979	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:17.214083	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:17.262539	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:17.618265	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:17.653808	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:18.863666	OpenTherm Gateway 4.2.5
23:59:18.918902	Command: SC=23:59/4
23:59:18.950823	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
23:59:19.002538	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
23:59:19.027975	Medium power
23:59:19.053236	SC: 23:59/4
23:59:19.102205	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
23:59:19.141935	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
23:59:19.460474	BC0060303	Read-Ack  	Remote parameter flags: 00000011 00000011
		   - DHW setpoint transfer: enabled (1)
		   - max CH setpoint transfer: enabled (1)
		   - DHW setpoint: read/write (1)
		   - max CH setpoint: read/write (1)
23:59:19.639637	AD002011C	Write-Ack 	Master configuration: 00000001 28
		   - Smart power: supported (1)
23:59:19.686866	T00030000	Read-Data 	Slave configuration: 00000000 0
23:59:20.054071	B40030100	Read-Ack  	Slave configuration: 00000001 0
		   - DHW: present (1)
		   - Control type: modulating (0)
		   - Cooling: not supported (0)
		   - DHW: instantaneous (0)
		   - Master pump control: allowed (0)
		   - CH2: not present (0)
		   - Remote water filling: available/unknown (0)
		   - Heat/cool mode control: heat (0)
23:59:20.382531	T00060000	Read-Data 	Remote parameter flags: 00000000 00000000
23:59:20.619225	BC0060303	Read-Ack  	Remote parameter flags: 00000011 00000011
		   - DHW setpoint transfer: enabled (1)
		   - max CH setpoint transfer: enabled (1)
		   - DHW setpoint: read/write (1)
		   - max CH setpoint: read/write (1)
23:59:20.872002	T00050000	Read-Data 	Application-specific flags: 00000000 0
23:59:21.270155	B40050100	Read-Ack  	Application-specific flags: 00000001 0
		   - Service request: yes (1)
		   - Lockout-reset: disabled (0)
		   - Low water pressure: no fault (0)
		   - Gas/flame fault: no fault (0)
		   - Air pressure fault: no fault (0)
		   - Water over-temperature: no fault (0)
23:59:21.476830	T000A0000	Read-Data 	Number of TSPs: 0
23:59:21.869999	BF00A0000	Unk-DataId	Number of TSPs: 0
23:59:22.574532	T000C0000	Read-Data 	Size of fault buffer: 0
23:59:22.947090	BF00C0000	Unk-DataId	Size of fault buffer: 0
23:59:23.174444	T90100F01	Write-Data	Room setpoint: 15.00
23:59:23.551897	B70100000	Unk-DataId	Room setpoint: 0.00
23:59:23.591136	AD0100000	Write-Ack 	Room setpoint: 0.00
23:59:23.769302	T90100F01	Write-Data	Room setpoint: 15.00
23:59:24.151726	B70100000	Unk-DataId	Room setpoint: 0.00
23:59:24.229677	AD0100000	Write-Ack 	Room setpoint: 0.00
23:59:24.370560	T90100F01	Write-Data	Room setpoint: 15.00
23:59:24.742194	B70100000	Unk-DataId	Room setpoint: 0.00
23:59:24.785080	AD0100000	Write-Ack 	Room setpoint: 0.00
23:59:24.974120	T90100F01	Write-Data	Room setpoint: 15.00
23:59:25.001896	R00300000	Read-Data 	DHW setpoint boundaries: 0 0
23:59:25.349713	B40303C23	Read-Ack  	DHW setpoint boundaries: 60 35
23:59:25.407190	A50100F01	Write-Ack 	Room setpoint: 15.00
23:59:25.569869	T00110000	Read-Data 	Relative modulation level: 0.00
23:59:25.941100	BC0110000	Read-Ack  	Relative modulation level: 0.00
23:59:26.169728	T00120000	Read-Data 	CH water pressure: 0.00
23:59:26.540665	B4012016C	Read-Ack  	CH water pressure: 1.42
23:59:26.771654	T80130000	Read-Data 	DHW flow rate: 0.00
23:59:27.146720	B70130000	Unk-DataId	DHW flow rate: 0.00
23:59:27.369681	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:27.747571	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
23:59:27.778451	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:27.974236	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:28.352219	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
23:59:28.381578	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:28.572896	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:28.959712	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
23:59:29.025501	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:29.178557	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:29.240317	R80310000	Read-Data 	Max CH setpoint boundaries: 0 0
23:59:29.579245	B40315028	Read-Ack  	Max CH setpoint boundaries: 80 40
23:59:29.654430	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:29.776742	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:29.795386	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:30.134997	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:30.205106	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:30.378989	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:30.419865	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:30.749414	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:30.787267	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:30.978757	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:31.060993	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:31.388746	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:31.440784	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:32.080979	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:32.127513	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:32.450717	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:32.501275	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:32.680093	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:32.717914	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:33.056581	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:33.104035	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:33.279406	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:33.333262	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:33.655161	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:33.720404	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:33.882629	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:33.954688	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:34.261250	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:34.326334	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:34.481449	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:34.556173	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:34.854837	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:34.920991	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:35.081630	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:35.168265	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:35.463253	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:35.523634	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:35.677114	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:35.726872	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:36.059318	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:36.134990	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:36.277771	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:36.317161	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:36.665824	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:36.703604	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:36.877245	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:36.914192	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:37.226948	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:37.278448	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:37.487981	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:37.543783	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:37.876837	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:37.934782	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:38.083580	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:38.104186	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:38.479804	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:38.523756	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:38.683280	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:38.726833	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:39.086266	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:39.149186	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:39.285585	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:39.307907	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:39.689557	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:39.739855	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:39.884848	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:39.942416	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:40.265592	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:40.321846	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:40.486320	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:40.544805	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:40.863705	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:40.913054	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:41.084623	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:41.138541	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:41.468115	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:41.517969	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:42.188947	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:42.259477	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:42.563409	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:42.615315	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:42.789096	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:42.832918	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:43.169734	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:43.245255	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:43.389422	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:43.411452	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:43.758935	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:43.813961	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:43.984206	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:44.036642	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:44.365874	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:44.411500	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:44.587908	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:44.675022	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:44.964053	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:45.034143	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:45.190650	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:45.232892	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:45.594196	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:45.621472	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:45.783353	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:45.823533	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:46.178912	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:46.234440	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:46.390064	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:46.429138	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:46.783972	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:46.828690	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:46.992197	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:47.045695	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:47.388139	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:47.415140	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:47.586407	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:47.620261	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:47.994086	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:48.011642	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:48.190337	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:48.238483	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:48.568138	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:48.606523	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:48.789376	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:48.805735	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:49.168821	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:49.201770	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:49.391934	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:49.468375	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:49.770285	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:49.850493	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:49.988529	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:50.039867	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:50.375212	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:50.430782	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:50.592283	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:50.664488	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:50.970160	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:51.032145	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:51.191853	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:51.237381	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:51.563380	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:51.605369	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:52.192567	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:52.227782	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:52.573473	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:52.635022	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:52.793917	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:52.813614	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:53.178686	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:53.227609	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:53.393854	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:53.415878	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:53.769060	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:53.819727	AC014973B	Read-Ack  	Day of week and time of day: Thu 23:59
23:59:53.988972	Command: GW=0
23:59:54.005527	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
23:59:54.036625	R80190000	Read-Data 	Boiler water temperature: 0.00
23:59:54.098900	GW: 0
23:59:55.240230	Low power
23:59:55.287712	B40191E00	Read-Ack  	Boiler water temperature: 30.00
23:59:58.224913	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
23:59:58.314109	Medium power
23:59:58.900363	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
23:59:59.025064	Low power
23:59:59.581841	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
23:59:59.646347	Medium power
00:00:00.001383	Command: SC=00:00/5
00:00:00.103887	SC: 00:00/5
00:00:00.260222	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:00.323972	Low power
00:00:00.944690	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:01.010972	Medium power
00:00:01.627055	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:01.787239	Low power
00:00:02.304457	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:02.453261	Medium power
00:00:02.988499	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:03.120059	Low power
00:00:03.661610	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:03.778031	Medium power
00:00:04.347032	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:04.453523	Low power
00:00:05.025267	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:05.106025	Medium power
00:00:05.705306	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:05.772300	Low power
00:00:06.383882	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:06.463797	Medium power
00:00:07.064033	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:07.130867	Low power
00:00:07.747813	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:07.802076	Medium power
00:00:08.426725	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:08.484166	Low power
00:00:09.104610	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:09.183042	Medium power
00:00:09.790279	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:09.847019	Low power
00:00:10.470584	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:10.526298	Medium power
00:00:11.151880	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:11.198426	Low power
00:00:11.828695	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:11.885971	Medium power
00:00:12.508807	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:12.564419	Low power
00:00:13.192775	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:13.267951	Medium power
00:00:13.867063	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:13.935202	Low power
00:00:14.555502	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:14.595401	Medium power
00:00:15.230770	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:15.296661	Low power
00:00:15.909136	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:15.966163	Medium power
00:00:16.596723	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:16.671468	Low power
00:00:17.269166	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:17.352359	Medium power
00:00:17.954846	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:18.026504	Low power
00:00:18.636942	T1002011C	Write-Data	Master configuration: 00000001 28
		   - Smart power: supported (1)
00:00:18.706402	Medium power
The thermostat didn't connect to OTGW and I've switched it to Monitor mode but after a while it give up saying "Connect OT+ Slave".

I've then disconnected and reconnected the thermostat and it did connected to the OTGW (that in the meanwhile was left in monitor mode) but giving the usual Error 03 and the otgw only log "TXXXX.." messages.
For one I'd like to make use of that beautiful gateway but I'm also really curious to understand what's happening

Thanks for your support and explanation
hvxl
Senior Member
Senior Member
Posts: 2034
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Connection to BRAHMA thermostat and "EMMETI" boiler

Post by hvxl »

That's not correct. Look at the 'T' messages. At some point the thermostat gets stuck again, repeatedly asking for the "Day of week and time of day". Even though it now gets a correct answer. So I'm not really sure how to proceed. The only thing I can think of is to change the firmware to return Unk-DataId, like the boiler does, and see if that makes a difference. But that's a bit of work.

For future logs, please switch off the "Include details of bit fields" option. It makes the logs bigger and harder for me to read.

Did you notice that your boiler indicates that it has a problem? The "Application-specific flags" message response has the "Service request" bit active. Maybe because of the water pressure, which is quite low at 1.42 bar (although the low water pressure bit is not set).
Schelte
hvxl
Senior Member
Senior Member
Posts: 2034
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Connection to BRAHMA thermostat and "EMMETI" boiler

Post by hvxl »

Try the attached firmware (4.2.5.3). It sends Unk-DataId in response to a Read-Data request of MsgID 20 when no recent time information is available. So, switch off the "Automatically update the gateway clock" setting, if that is still on.
Attachments
gateway-4.2.5.3.zip
Debug firmware for mcasamento.
(9.24 KiB) Downloaded 424 times
Schelte
mcasamento
Starting Member
Starting Member
Posts: 17
Joined: Fri Jan 03, 2020 6:14 pm

Re: Connection to BRAHMA thermostat and "EMMETI" boiler

Post by mcasamento »

THANK YOU very much for your effort Schelte, is much appreciated!
I know I'm late with my reply, the seasonal flu hit my familiy, both my wife and daughter, I'm just waiting for my turn :-)

No, I didn't know the boiler have that service bit on, I'm still not able to decode those messages properly.
I've just uploaded the firmware and it didn't work on first attempt but I want to do another proper and carefully logged test, before I post the new logs. Just a question, I guess I should reissue UI=2 and AA=25, right ?
hvxl
Senior Member
Senior Member
Posts: 2034
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Connection to BRAHMA thermostat and "EMMETI" boiler

Post by hvxl »

If you didn't uncheck the "Transfer old EEPROM settings to the new firmware" box during the firmware upgrade, then those settings should have been copied. If your otmonitor is still running, you can check by opening the firmware upgrade window and clicking on the button with the magnifying glass. That will show which Alternative IDs and Blocked MessageIDs were transferred.

If that information is lost and you want to make sure, you can repeat the UI=2 command. I suggest to first run DA=25 before you repeat the AA=25 command, to avoid duplicates. Not that that would be a big deal.
Schelte
mcasamento
Starting Member
Starting Member
Posts: 17
Joined: Fri Jan 03, 2020 6:14 pm

Re: Connection to BRAHMA thermostat and "EMMETI" boiler

Post by mcasamento »

Good News first: IT WORKS maybe not everything but it started to work!! Thank you genius!!

Bad News then: I wasn't able to copy Alternative ID's with magnifying glass, so I went to the path you described, issuing:
DA=25
DA=25 (two times, just in case)
KI=2
KI=2 (two times, just in case)
UI=2
AA=25
BUT it seemed it didn't work, So I've turned down boiler and OTGW with thermostat disconnected, but nothing, event the connection to the boiler (that was working) stopped working.
Then I've repeated the step above and added a simple GW=R, while everything was up and connected (and thermostat keep saying connecting) and BUM! It started to flash green and thermostat got connected and OTMonitor start to print messages!
The bad News here is that for my own easy I run those command on a ubuntu laptop near the thermostat where I forgot to check "save log" :-(, so I didn't collected the exact log of what I did, but I'm pretty sure that was the sequence

What don't work, is the TT=xx or TC=xx, the boiler don't start whatever value i put, I've concluded that my thermostat don't support override, but maybe you have another idea :-)

Oh, and finally, if I set the OTGW in monitor mode, everything stop to works, and I only see a lot of error 03. I have to restart the boiler for it to works again, to me is seems like the boiler "learns" to communicate either in monitoring mode or in gateway mode.

Follows log of my try to override room temp

Code: Select all

15:50:45.606544	80130000
15:50:45.625123	R80190000	Read-Data 	Boiler water temperature: 0.00
15:50:45.987716	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:50:45.994338	Command: PR=A
15:50:46.001715	A70130000	Unk-DataId	DHW flow rate: 0.00
15:50:46.060321	PR: A=OpenTherm Gateway 4.2.5.3
15:50:46.205138	T80190000	Read-Data 	Boiler water temperature: 0.00
15:50:46.583429	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:50:46.807823	T801A0000	Read-Data 	DHW temperature: 0.00
15:50:47.191702	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:50:47.406613	T00000300	Read-Data 	Status: 00000011 00000000
15:50:47.789779	BC0000300	Read-Ack  	Status: 00000011 00000000
15:50:48.008563	T00110000	Read-Data 	Relative modulation level: 0.00
15:50:48.608585	00120000
15:50:48.996511	BC0120186	Read-Ack  	CH water pressure: 1.52
15:50:49.209653	T00000300	Read-Data 	Status: 00000011 00000000
15:50:49.614770	BC0000300	Read-Ack  	Status: 00000011 00000000
15:50:49.808646	T00000300	Read-Data 	Status: 00000011 00000000
15:50:50.221569	BC0000300	Read-Ack  	Status: 00000011 00000000
15:50:50.409142	T00000300	Read-Data 	Status: 00000011 00000000
15:50:50.831554	BC0000300	Read-Ack  	Status: 00000011 00000000
15:50:51.009661	T00000300	Read-Data 	Status: 00000011 00000000
15:50:51.441671	BC0000300	Read-Ack  	Status: 00000011 00000000
15:50:51.609480	T00000300	Read-Data 	Status: 00000011 00000000
15:50:51.993107	BC0000300	Read-Ack  	Status: 00000011 00000000
15:50:52.209504	T00000300	Read-Data 	Status: 00000011 00000000
15:50:52.614318	BC0000300	Read-Ack  	Status: 00000011 00000000
15:50:52.809203	T00110000	Read-Data 	Relative modulation level: 0.00
15:50:53.189808	C0110000
15:50:53.409791	T00120000	Read-Data 	CH water pressure: 0.00
15:50:53.800650	BC0120186	Read-Ack  	CH water pressure: 1.52
15:50:54.010875	T00000300	Read-Data 	Status: 00000011 00000000
15:50:54.396455	BC0000300	Read-Ack  	Status: 00000011 00000000
15:50:54.612475	T00000300	Read-Data 	Status: 00000011 00000000
15:50:54.994720	BC0000300	Read-Ack  	Status: 00000011 00000000
15:50:55.612149	T80130000	Read-Data 	DHW flow rate: 0.00
15:50:55.642384	R80190000	Read-Data 	Boiler water temperature: 0.00
15:50:56.003488	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:50:56.047300	A70130000	Unk-DataId	DHW flow rate: 0.00
15:50:56.213462	T80190000	Read-Data 	Boiler water temperature: 0.00
15:50:56.813718	801A0000
15:50:57.199861	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:50:57.411647	T00000300	Read-Data 	Status: 00000011 00000000
15:50:57.805244	BC0000300	Read-Ack  	Status: 00000011 00000000
15:50:58.018122	T00110000	Read-Data 	Relative modulation level: 0.00
15:50:58.416116	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:50:58.613803	T00120000	Read-Data 	CH water pressure: 0.00
15:50:59.022443	BC0120186	Read-Ack  	CH water pressure: 1.52
15:50:59.219174	T00000300	Read-Data 	Status: 00000011 00000000
15:50:59.627493	BC0000300	Read-Ack  	Status: 00000011 00000000
15:50:59.819059	T00000300	Read-Data 	Status: 00000011 00000000
15:51:00.233027	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:00.415052	T00000300	Read-Data 	Status: 00000011 00000000
15:51:00.844007	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:01.014771	T00000300	Read-Data 	Status: 00000011 00000000
15:51:01.398359	C0000300
15:51:01.615303	T00000300	Read-Data 	Status: 00000011 00000000
15:51:01.994666	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:02.220859	T00000300	Read-Data 	Status: 00000011 00000000
15:51:02.601461	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:02.820721	T00110000	Read-Data 	Relative modulation level: 0.00
15:51:03.196411	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:51:03.416701	T00120000	Read-Data 	CH water pressure: 0.00
15:51:03.804093	BC0120186	Read-Ack  	CH water pressure: 1.52
15:51:04.016805	T00000300	Read-Data 	Status: 00000011 00000000
15:51:04.401443	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:04.620169	T00000300	Read-Data 	Status: 00000011 00000000
15:51:04.744840	teway 4.2.5.3
15:51:05.003704	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:05.618955	T80130000	Read-Data 	DHW flow rate: 0.00
15:51:05.632703	R80190000	Read-Data 	Boiler water temperature: 0.00
15:51:06.009807	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:51:06.032251	A70130000	Unk-DataId	DHW flow rate: 0.00
15:51:06.231501	T80190000	Read-Data 	Boiler water temperature: 0.00
15:51:06.613779	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:51:06.825878	T801A0000	Read-Data 	DHW temperature: 0.00
15:51:07.224997	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:51:07.424333	T00000300	Read-Data 	Status: 00000011 00000000
15:51:07.830584	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:08.020620	T00110000	Read-Data 	Relative modulation level: 0.00
15:51:08.434325	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:51:08.620330	T00120000	Read-Data 	CH water pressure: 0.00
15:51:09.063974	BC0120186	Read-Ack  	CH water pressure: 1.52
15:51:09.641711	C0000300
15:51:09.824533	T00000300	Read-Data 	Status: 00000011 00000000
15:51:10.200083	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:10.423090	T00000300	Read-Data 	Status: 00000011 00000000
15:51:10.807564	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:11.022274	T00000300	Read-Data 	Status: 00000011 00000000
15:51:11.406448	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:11.623241	T00000300	Read-Data 	Status: 00000011 00000000
15:51:12.023654	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:12.230795	T00000300	Read-Data 	Status: 00000011 00000000
15:51:12.607740	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:12.732124	Gateway 4.2.5.3
15:51:12.827807	T00110000	Read-Data 	Relative modulation level: 0.00
15:51:13.205257	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:51:13.425817	T00120000	Read-Data 	CH water pressure: 0.00
15:51:13.810730	BC0120186	Read-Ack  	CH water pressure: 1.52
15:51:14.025924	T00000300	Read-Data 	Status: 00000011 00000000
15:51:14.441930	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:14.628174	T00000300	Read-Data 	Status: 00000011 00000000
15:51:15.015670	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:15.630500	T80130000	Read-Data 	DHW flow rate: 0.00
15:51:15.662048	R80190000	Read-Data 	Boiler water temperature: 0.00
15:51:16.017181	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:51:16.040066	A70130000	Unk-DataId	DHW flow rate: 0.00
15:51:16.225367	T80190000	Read-Data 	Boiler water temperature: 0.00
15:51:16.631164	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:51:16.828155	T801A0000	Read-Data 	DHW temperature: 0.00
15:51:17.234716	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:51:17.425818	00000300
15:51:17.838047	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:18.029616	T00110000	Read-Data 	Relative modulation level: 0.00
15:51:18.442532	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:51:18.626621	T00120000	Read-Data 	CH water pressure: 0.00
15:51:19.006897	BC0120186	Read-Ack  	CH water pressure: 1.52
15:51:19.228966	T00000300	Read-Data 	Status: 00000011 00000000
15:51:19.610093	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:19.827573	T00000300	Read-Data 	Status: 00000011 00000000
15:51:20.199672	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:20.429330	T00000300	Read-Data 	Status: 00000011 00000000
15:51:20.808141	B
15:51:21.031501	00000300
15:51:21.417395	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:21.631041	T00000300	Read-Data 	Status: 00000011 00000000
15:51:22.012898	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:22.234601	T00000300	Read-Data 	Status: 00000011 00000000
15:51:22.610406	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:22.831284	T00110000	Read-Data 	Relative modulation level: 0.00
15:51:23.220184	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:51:23.432004	T00120000	Read-Data 	CH water pressure: 0.00
15:51:23.818590	BC0120186	Read-Ack  	CH water pressure: 1.52
15:51:24.034064	T00000300	Read-Data 	Status: 00000011 00000000
15:51:24.420992	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:24.632640	T00000300	Read-Data 	Status: 00000011 00000000
15:51:25.027372	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:25.733302	80130000
15:51:25.774210	R80190000	Read-Data 	Boiler water temperature: 0.00
15:51:26.135055	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:51:26.146634	A70130000	Unk-DataId	DHW flow rate: 0.00
15:51:26.333474	T80190000	Read-Data 	Boiler water temperature: 0.00
15:51:26.742985	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:51:26.935463	T801A0000	Read-Data 	DHW temperature: 0.00
15:51:27.354494	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:51:27.533936	T00000300	Read-Data 	Status: 00000011 00000000
15:51:27.960383	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:28.135430	T00110000	Read-Data 	Relative modulation level: 0.00
15:51:28.518380	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:51:28.733627	T00120000	Read-Data 	CH water pressure: 0.00
15:51:29.118307	C0120186
15:51:29.335426	T00000300	Read-Data 	Status: 00000011 00000000
15:51:29.721702	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:29.935370	T00000300	Read-Data 	Status: 00000011 00000000
15:51:30.326573	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:30.537668	T00000300	Read-Data 	Status: 00000011 00000000
15:51:30.916661	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:31.135709	T00000300	Read-Data 	Status: 00000011 00000000
15:51:31.524397	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:31.736480	T00000300	Read-Data 	Status: 00000011 00000000
15:51:32.125860	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:32.339073	T00000300	Read-Data 	Status: 00000011 00000000
15:51:32.720743	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:32.945651	T90101201	Write-Data	Room setpoint: 18.00
15:51:32.962895	R80190000	Read-Data 	Boiler water temperature: 0.00
15:51:33.326641	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:51:33.335933	A50101201	Write-Ack 	Room setpoint: 18.00
15:51:33.880214	C0110000
15:51:34.139283	T00120000	Read-Data 	CH water pressure: 0.00
15:51:34.536800	BC0120186	Read-Ack  	CH water pressure: 1.52
15:51:35.238451	T80130000	Read-Data 	DHW flow rate: 0.00
15:51:35.244275	R80190000	Read-Data 	Boiler water temperature: 0.00
15:51:35.645345	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:51:35.658953	A70130000	Unk-DataId	DHW flow rate: 0.00
15:51:35.840427	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
15:51:35.852884	R80190000	Read-Data 	Boiler water temperature: 0.00
15:51:36.252478	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:51:36.265011	AF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
15:51:36.444187	T90181567	Write-Data	Room temperature: 21.40
15:51:36.470071	R80190000	Read-Data 	Boiler water temperature: 0.00
15:51:36.857012	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:51:36.877619	AF0181567	Unk-DataId	Room temperature: 21.40
15:51:37.463803	40192200
15:51:37.641047	T801A0000	Read-Data 	DHW temperature: 0.00
15:51:39.227284	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:51:39.250360	T00110000	Read-Data 	Relative modulation level: 0.00
15:51:39.292004	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:51:39.319625	T00120000	Read-Data 	CH water pressure: 0.00
15:51:39.339761	BC0120186	Read-Ack  	CH water pressure: 1.52
15:51:39.449305	T001B0000	Read-Data 	Outside temperature: 0.00
15:51:39.470598	R80190000	Read-Data 	Boiler water temperature: 0.00
15:51:39.822408	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:51:39.838956	AF01B0000	Unk-DataId	Outside temperature: 0.00
15:51:40.042437	T801C0000	Read-Data 	Return water temperature: 0.00
15:51:40.353228	BC01C1A00	Read-Ack  	Return water temperature: 26.00
15:51:40.543780	T00210000	Read-Data 	Exhaust temperature: 0.00
15:51:40.932772	BC0211B00	Read-Ack  	Exhaust temperature: 27.00
15:51:41.145135	T10382D00	Write-Data	DHW setpoint: 45.00
15:51:41.542955	BD0382D00	Write-Ack 	DHW setpoint: 45.00
15:51:42.142210	D0393400
15:51:42.344316	T10010000	Write-Data	Control setpoint: 0.00
15:51:42.726377	BD0010000	Write-Ack 	Control setpoint: 0.00
15:51:42.946164	T00110000	Read-Data 	Relative modulation level: 0.00
15:51:43.342363	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:51:43.544028	T00120000	Read-Data 	CH water pressure: 0.00
15:51:43.955384	BC0120186	Read-Ack  	CH water pressure: 1.52
15:51:44.145899	T00000300	Read-Data 	Status: 00000011 00000000
15:51:44.554569	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:45.610092	40192200
15:51:45.638317	A70130000	Unk-DataId	DHW flow rate: 0.00
15:51:45.849589	T80190000	Read-Data 	Boiler water temperature: 0.00
15:51:46.104594	Command: PR=M
15:51:46.236758	PR: M=G
15:51:46.249611	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:51:46.445622	T801A0000	Read-Data 	DHW temperature: 0.00
15:51:46.871268	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:51:47.048870	T00000300	Read-Data 	Status: 00000011 00000000
15:51:47.429794	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:47.647014	T00000300	Read-Data 	Status: 00000011 00000000
15:51:48.036752	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:48.250375	T00110000	Read-Data 	Relative modulation level: 0.00
15:51:48.631424	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:51:48.851439	T00120000	Read-Data 	CH water pressure: 0.00
15:51:49.228574	BC0120186	Read-Ack  	CH water pressure: 1.52
15:51:49.449222	T00000300	Read-Data 	Status: 00000011 00000000
15:51:50.051927	00000300
15:51:50.435554	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:50.653694	T00000300	Read-Data 	Status: 00000011 00000000
15:51:51.032385	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:51.252746	T00000300	Read-Data 	Status: 00000011 00000000
15:51:51.640257	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:51.854937	T00000300	Read-Data 	Status: 00000011 00000000
15:51:52.236943	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:52.452584	T00000300	Read-Data 	Status: 00000011 00000000
15:51:52.854210	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:53.051666	T00110000	Read-Data 	Relative modulation level: 0.00
15:51:53.661022	00120000
15:51:54.057982	BC0120186	Read-Ack  	CH water pressure: 1.52
15:51:54.250132	T00000300	Read-Data 	Status: 00000011 00000000
15:51:54.666922	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:55.353382	T80130000	Read-Data 	DHW flow rate: 0.00
15:51:55.397320	R80190000	Read-Data 	Boiler water temperature: 0.00
15:51:55.770019	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:51:55.792157	A70130000	Unk-DataId	DHW flow rate: 0.00
15:51:55.953487	T80190000	Read-Data 	Boiler water temperature: 0.00
15:51:56.378967	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:51:56.555252	T801A0000	Read-Data 	DHW temperature: 0.00
15:51:56.940030	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:51:57.154494	T00000300	Read-Data 	Status: 00000011 00000000
15:51:57.536990	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:57.760578	T00110000	Read-Data 	Relative modulation level: 0.00
15:51:58.144505	C0110000
15:51:58.354730	T00120000	Read-Data 	CH water pressure: 0.00
15:51:58.588020	Command: TT=27.14
15:51:58.736412	TT: 27.14
15:51:58.754685	BC0120186	Read-Ack  	CH water pressure: 1.52
15:51:58.954435	T00000300	Read-Data 	Status: 00000011 00000000
15:51:59.334419	BC0000300	Read-Ack  	Status: 00000011 00000000
15:51:59.553150	T00000300	Read-Data 	Status: 00000011 00000000
15:51:59.942441	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:00.156108	T00000300	Read-Data 	Status: 00000011 00000000
15:52:00.541077	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:00.758222	T00000300	Read-Data 	Status: 00000011 00000000
15:52:01.150386	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:01.357784	T00000300	Read-Data 	Status: 00000011 00000000
15:52:01.744780	C0000300
15:52:01.959586	T00000300	Read-Data 	Status: 00000011 00000000
15:52:02.352285	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:02.556234	T00000300	Read-Data 	Status: 00000011 00000000
15:52:02.969379	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:03.157612	T00110000	Read-Data 	Relative modulation level: 0.00
15:52:03.575950	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:52:03.759024	T00120000	Read-Data 	CH water pressure: 0.00
15:52:04.181531	BC0120186	Read-Ack  	CH water pressure: 1.52
15:52:04.357881	T00000300	Read-Data 	Status: 00000011 00000000
15:52:04.732342	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:05.360560	T80130000	Read-Data 	DHW flow rate: 0.00
15:52:05.414257	R80190000	Read-Data 	Boiler water temperature: 0.00
15:52:05.741863	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:52:05.802515	A70130000	Unk-DataId	DHW flow rate: 0.00
15:52:05.959216	T80190000	Read-Data 	Boiler water temperature: 0.00
15:52:06.331872	40192200
15:52:06.559587	T801A0000	Read-Data 	DHW temperature: 0.00
15:52:06.943744	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:52:07.162770	T00000300	Read-Data 	Status: 00000011 00000000
15:52:07.548516	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:07.761662	T00110000	Read-Data 	Relative modulation level: 0.00
15:52:08.139455	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:52:08.363522	T00120000	Read-Data 	CH water pressure: 0.00
15:52:08.752966	BC0120186	Read-Ack  	CH water pressure: 1.52
15:52:08.962511	T00000300	Read-Data 	Status: 00000011 00000000
15:52:09.344835	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:09.561874	T00000300	Read-Data 	Status: 00000011 00000000
15:52:09.944155	C0000300
15:52:10.163803	T00000300	Read-Data 	Status: 00000011 00000000
15:52:10.545470	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:10.766700	T00000300	Read-Data 	Status: 00000011 00000000
15:52:11.153701	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:11.363031	T00000300	Read-Data 	Status: 00000011 00000000
15:52:11.760822	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:11.964060	T00000300	Read-Data 	Status: 00000011 00000000
15:52:12.326004	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:12.565851	T00000300	Read-Data 	Status: 00000011 00000000
15:52:12.980192	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:13.166319	T00110000	Read-Data 	Relative modulation level: 0.00
15:52:13.586762	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:52:13.769489	T00120000	Read-Data 	CH water pressure: 0.00
15:52:14.194914	BC0120186	Read-Ack  	CH water pressure: 1.52
15:52:14.365769	00000300
15:52:14.753222	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:15.368446	T80130000	Read-Data 	DHW flow rate: 0.00
15:52:15.414088	R80190000	Read-Data 	Boiler water temperature: 0.00
15:52:15.746166	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:52:15.785264	A70130000	Unk-DataId	DHW flow rate: 0.00
15:52:15.964745	T80190000	Read-Data 	Boiler water temperature: 0.00
15:52:16.355230	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:52:16.570499	T801A0000	Read-Data 	DHW temperature: 0.00
15:52:16.955424	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:52:17.174404	T00000300	Read-Data 	Status: 00000011 00000000
15:52:17.550567	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:17.769334	T00110000	Read-Data 	Relative modulation level: 0.00
15:52:18.158398	C0110000
15:52:18.373168	T00120000	Read-Data 	CH water pressure: 0.00
15:52:18.752045	BC0120186	Read-Ack  	CH water pressure: 1.52
15:52:18.974880	T00000300	Read-Data 	Status: 00000011 00000000
15:52:19.360440	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:19.572435	T00000300	Read-Data 	Status: 00000011 00000000
15:52:19.966139	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:20.168479	T00000300	Read-Data 	Status: 00000011 00000000
15:52:20.573968	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:20.770164	T00000300	Read-Data 	Status: 00000011 00000000
15:52:21.180162	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:21.368829	T00000300	Read-Data 	Status: 00000011 00000000
15:52:21.785178	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:21.970299	T00000300	Read-Data 	Status: 00000011 00000000
15:52:22.392810	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:22.491569	3
15:52:22.534678	T00000300	Read-Data 	Status: 00000011 00000000
15:52:22.999363	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:23.171609	T00110000	Read-Data 	Relative modulation level: 0.00
15:52:23.597427	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:52:23.775404	T00120000	Read-Data 	CH water pressure: 0.00
15:52:24.156330	BC0120186	Read-Ack  	CH water pressure: 1.52
15:52:24.373355	T00000300	Read-Data 	Status: 00000011 00000000
15:52:24.756792	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:25.373775	T80130000	Read-Data 	DHW flow rate: 0.00
15:52:25.420122	R80190000	Read-Data 	Boiler water temperature: 0.00
15:52:25.754411	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:52:25.766441	A70130000	Unk-DataId	DHW flow rate: 0.00
15:52:25.974005	T80190000	Read-Data 	Boiler water temperature: 0.00
15:52:26.351789	40192200
15:52:26.574574	T801A0000	Read-Data 	DHW temperature: 0.00
15:52:26.959990	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:52:27.178631	T00000300	Read-Data 	Status: 00000011 00000000
15:52:27.556635	BC0000300	Read-Ack  	Status: 00000011 00000000
15:52:27.774050	T00110000	Read-Data 	Relative modulation level: 0.00
15:52:28.153510	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:52:28.374938	T00120000	Read-Data 	CH water pressure: 0.00
15:52:28.759924	BC0120186	Read-Ack  	CH water pressure: 1.52
15:52:28.975575	T00000300	Read-Data 	Status: 00000011 00000000
15:54:35.357326	45.00,52.00,0,0,0,0,0,0,0,0
15:55:03.642795	Command: PR=M
15:55:03.750572	PR: M=G
15:55:12.042132	Command: GW=R
15:55:13.269213	OpenTherm Gateway 4.2.5.3
15:55:13.329368	T1002011C	Write-Data	Master configuration: 00000001 28
15:55:13.453841	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
15:55:13.488453	Medium power
15:55:13.514440	T1002011C	Write-Data	Master configuration: 00000001 28
15:55:13.539159	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
15:55:13.880053	C0060303
15:55:13.918912	AD002011C	Write-Ack 	Master configuration: 00000001 28
15:55:14.142348	T00030000	Read-Data 	Slave configuration: 00000000 0
15:55:14.525890	B40030100	Read-Ack  	Slave configuration: 00000001 0
15:55:15.242378	T00060000	Read-Data 	Remote parameter flags: 00000000 00000000
15:55:15.627762	BC0060303	Read-Ack  	Remote parameter flags: 00000011 00000011
15:55:15.841600	T00050000	Read-Data 	Application-specific flags: 00000000 0
15:55:16.242603	B40050100	Read-Ack  	Application-specific flags: 00000001 0
15:55:16.446810	T000A0000	Read-Data 	Number of TSPs: 0
15:55:16.828142	BF00A0000	Unk-DataId	Number of TSPs: 0
15:55:17.042314	T000C0000	Read-Data 	Size of fault buffer: 0
15:55:17.429804	F00C0000
15:55:17.643391	T00120000	Read-Data 	CH water pressure: 0.00
15:55:18.034386	BC0120186	Read-Ack  	CH water pressure: 1.52
15:55:18.243205	T00110000	Read-Data 	Relative modulation level: 0.00
15:55:18.628794	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:55:18.852207	T00120000	Read-Data 	CH water pressure: 0.00
15:55:19.185627	BC0120186	Read-Ack  	CH water pressure: 1.52
15:55:19.450720	T80130000	Read-Data 	DHW flow rate: 0.00
15:55:19.840767	B70130000	Unk-DataId	DHW flow rate: 0.00
15:55:20.044957	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
15:55:20.449826	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
15:55:20.645026	T80190000	Read-Data 	Boiler water temperature: 0.00
15:55:21.055518	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:55:21.246712	T801A0000	Read-Data 	DHW temperature: 0.00
15:55:21.662220	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:55:22.267350	F01B0000
15:55:22.445583	T801C0000	Read-Data 	Return water temperature: 0.00
15:55:22.866487	BC01C1A00	Read-Ack  	Return water temperature: 26.00
15:55:23.046526	T00110000	Read-Data 	Relative modulation level: 0.00
15:55:23.508393	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:55:23.648781	T00120000	Read-Data 	CH water pressure: 0.00
15:55:24.051744	BC0120186	Read-Ack  	CH water pressure: 1.52
15:55:24.253454	T00210000	Read-Data 	Exhaust temperature: 0.00
15:55:24.632458	BC0211B00	Read-Ack  	Exhaust temperature: 27.00
15:55:25.735271	70130000
15:55:25.951801	T80190000	Read-Data 	Boiler water temperature: 0.00
15:55:26.331573	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:55:26.549246	T801A0000	Read-Data 	DHW temperature: 0.00
15:55:26.937420	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:55:27.151812	T00300000	Read-Data 	DHW setpoint boundaries: 0 0
15:55:27.535864	B40303C23	Read-Ack  	DHW setpoint boundaries: 60 35
15:55:27.753703	T00110000	Read-Data 	Relative modulation level: 0.00
15:55:28.133578	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:55:28.351084	T00120000	Read-Data 	CH water pressure: 0.00
15:55:28.741594	BC0120186	Read-Ack  	CH water pressure: 1.52
15:55:28.953119	T80310000	Read-Data 	Max CH setpoint boundaries: 0 0
15:55:29.352848	B40315028	Read-Ack  	Max CH setpoint boundaries: 80 40
15:55:29.552254	T80380000	Read-Data 	DHW setpoint: 0.00
15:55:29.956469	B40382D00	Read-Ack  	DHW setpoint: 45.00
15:55:30.152250	00390000
15:55:30.565372	B40393400	Read-Ack  	Max CH water setpoint: 52.00
15:55:30.754585	T80670000	Read-Data 	Solar storage config/memberid: 00000000 0
15:55:31.172708	B70670000	Unk-DataId	Solar storage config/memberid: 00000000 0
15:55:31.362549	T107C0300	Write-Data	OpenTherm version Master: 3.00
15:55:31.777409	B707C0000	Unk-DataId	OpenTherm version Master: 0.00
15:55:31.954430	T007D0000	Read-Data 	OpenTherm version Slave: 0.00
15:55:32.334798	BF07D0000	Unk-DataId	OpenTherm version Slave: 0.00
15:55:32.377532	AC07D0300	Read-Ack  	OpenTherm version Slave: 3.00
15:55:32.557116	T10010000	Write-Data	Control setpoint: 0.00
15:55:32.945937	BD0010000	Write-Ack 	Control setpoint: 0.00
15:55:33.049332	Command: TC=25.51
15:55:33.136706	TC: 25.51
15:55:33.148758	T90101201	Write-Data	Room setpoint: 18.00
15:55:33.759155	90101201
15:55:34.133503	B70100000	Unk-DataId	Room setpoint: 0.00
15:55:34.181961	AD0100000	Write-Ack 	Room setpoint: 0.00
15:55:34.355243	T90101201	Write-Data	Room setpoint: 18.00
15:55:34.742257	B70100000	Unk-DataId	Room setpoint: 0.00
15:55:34.790298	AD0100000	Write-Ack 	Room setpoint: 0.00
15:55:35.358826	T90101201	Write-Data	Room setpoint: 18.00
15:55:35.400960	R80190000	Read-Data 	Boiler water temperature: 0.00
15:55:35.732768	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:55:35.770121	A50101201	Write-Ack 	Room setpoint: 18.00
15:55:35.958623	T00110000	Read-Data 	Relative modulation level: 0.00
15:55:36.338380	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:55:36.558779	T00120000	Read-Data 	CH water pressure: 0.00
15:55:36.942992	BC0120186	Read-Ack  	CH water pressure: 1.52
15:55:37.157419	T80130000	Read-Data 	DHW flow rate: 0.00
15:55:37.543612	B70130000	Unk-DataId	DHW flow rate: 0.00
15:55:37.757033	T00110000	Read-Data 	Relative modulation level: 0.00
15:55:38.360912	00120000
15:55:38.714569	BC0120186	Read-Ack  	CH water pressure: 1.52
15:55:38.957459	T00140000	Read-Data 	Day of week and time of day: Unk 00:00
15:55:39.364206	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
15:55:39.561062	T90181567	Write-Data	Room temperature: 21.40
15:55:39.972168	BF0180000	Unk-DataId	Room temperature: 0.00
15:55:40.160687	T80190000	Read-Data 	Boiler water temperature: 0.00
15:55:40.579031	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:55:40.760431	T801A0000	Read-Data 	DHW temperature: 0.00
15:55:41.176453	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:55:41.362387	T001B0000	Read-Data 	Outside temperature: 0.00
15:55:41.960941	801C0000
15:55:42.351007	BC01C1A00	Read-Ack  	Return water temperature: 26.00
15:55:42.564620	T00210000	Read-Data 	Exhaust temperature: 0.00
15:55:42.944724	BC0211B00	Read-Ack  	Exhaust temperature: 27.00
15:55:43.163856	T00110000	Read-Data 	Relative modulation level: 0.00
15:55:43.550520	BC0110000	Read-Ack  	Relative modulation level: 0.00
15:55:43.763231	T00120000	Read-Data 	CH water pressure: 0.00
15:55:44.146520	BC0120186	Read-Ack  	CH water pressure: 1.52
15:55:44.368334	T80380000	Read-Data 	DHW setpoint: 0.00
15:55:44.734365	B40382D00	Read-Ack  	DHW setpoint: 45.00
15:55:45.362057	T80130000	Read-Data 	DHW flow rate: 0.00
15:55:45.409569	R80190000	Read-Data 	Boiler water temperature: 0.00
15:55:45.737409	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:55:45.776673	A70130000	Unk-DataId	DHW flow rate: 0.00
15:55:45.970100	T80190000	Read-Data 	Boiler water temperature: 0.00
15:55:46.297994	B40192200	Read-Ack  	Boiler water temperature: 34.00
15:55:46.409984	5.3
15:55:46.576227	T801A0000	Read-Data 	DHW temperature: 0.00
15:55:46.953191	BC01A1A00	Read-Ack  	DHW temperature: 26.00
15:55:47.164156	T00390000	Read-Data 	Max CH water setpoint: 0.00