The Remeha Tzerra Ace boiler has what they call an R-bus. This bus should be capable, according to the documentation, of running the OT protocol as well as some kind of specific Remeha protocol. The E-twist thermostat should also be able to talk Opentherm.
I have the Nodo shop opentherm gateway running and connected via Wifi to Openhab with the OpenTherm gateway binding installed, so far so good everything comes online as it should.
At the gateway side things are a bit more problematic. With only the thermostat connected and the reference set to 1.25V I am only seeing error 3 messages in the terminal and the thermostat does not connect.
When 1 set the reference to voltage to 0.625V (0) the error 3 message disappears and the thermostat keeps connecting disconnecting.
I am running version 4.2.5 firmwater.
I hooked up a scope to the Ot bus and that seems to look fine I have a base line of 6 volt and on that I have 10 volt pulses.
The thermostat sends out first 9 bits then a 6mSec pause followed by 18 bits this is then repeated every 500 mSec.
With nothing connected the gateway is sending out the following messages:
17:10:38.761797 R00000000 Read-Data Status: 00000000 00000000
- CH enable: disabled (0)
- DHW enable: disabled (0)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
I found nothing on-line about connecting the Tzerra ace (new version of the Tzerra plus) with Etwist to the openhab gateway so I might be the first to try this.
I am a bit stuck at this moment and was hoping that somebody could help me forward.
Kind regards Willem
I have the Nodo shop opentherm gateway running and connected via Wifi to Openhab with the OpenTherm gateway binding installed, so far so good everything comes online as it should.
At the gateway side things are a bit more problematic. With only the thermostat connected and the reference set to 1.25V I am only seeing error 3 messages in the terminal and the thermostat does not connect.
When 1 set the reference to voltage to 0.625V (0) the error 3 message disappears and the thermostat keeps connecting disconnecting.
I am running version 4.2.5 firmwater.
I hooked up a scope to the Ot bus and that seems to look fine I have a base line of 6 volt and on that I have 10 volt pulses.
The thermostat sends out first 9 bits then a 6mSec pause followed by 18 bits this is then repeated every 500 mSec.
With nothing connected the gateway is sending out the following messages:
17:10:38.761797 R00000000 Read-Data Status: 00000000 00000000
- CH enable: disabled (0)
- DHW enable: disabled (0)
- Cooling enable: disabled (0)
- OTC active: not active (0)
- CH2 enable: disabled (0)
- Summer/winter mode: winter (0)
- DHW blocking: unblocked (0)
I found nothing on-line about connecting the Tzerra ace (new version of the Tzerra plus) with Etwist to the openhab gateway so I might be the first to try this.
I am a bit stuck at this moment and was hoping that somebody could help me forward.
Kind regards Willem
Re: Otgw and Remeha tzerra ace with etwist thermostat
Had a better look at what the thermostat was sending out:
First it sends out 10 bits with a cycle time of 2 msecs if these are manchester coded then it would read 1111.1111.11
After this there is a 6msec wait followed by what looks like a manchester coded opentherm message with 34 bits of exactly 1msec:
1.1001.0000.0000.0010.0000.0000.0000.1011.1
The above is repeated every 500mSec.
The terminal program shows only error 03 messages with very rarely the following messages in between the errors:
23:46:39.651051 T9002000B Write-Data Master configuration: 00000000 11
- Smart power: not supported (0)
First it sends out 10 bits with a cycle time of 2 msecs if these are manchester coded then it would read 1111.1111.11
After this there is a 6msec wait followed by what looks like a manchester coded opentherm message with 34 bits of exactly 1msec:
1.1001.0000.0000.0010.0000.0000.0000.1011.1
The above is repeated every 500mSec.
The terminal program shows only error 03 messages with very rarely the following messages in between the errors:
23:46:39.651051 T9002000B Write-Data Master configuration: 00000000 11
- Smart power: not supported (0)
Re: Otgw and Remeha tzerra ace with etwist thermostat
The first 10 bits clearly do not match OpenTherm timings. This is why the OTGW reports error 03. The next issue is that the thermostat then only waits 6 ms before sending the OpenTherm message. The OpenTherm spec requires an interval of 20 to 400 ms between the message from the master and the response from the slave. So an idle time of 6 ms is much shorter than expected. Currently the OTGW wants to see the line idle for at least 10 ms before it looks for a new OpenTherm message. As a result, the actual OpenTherm message from the thermostat is considered to still be part of the garbage. Apparently sometimes the gap is just long enough and the OTGW manages to find an occasional message.
Dialing the reference voltage all the way down to 0.625V stops the error messages because then the OTGW doesn't detect any changes on the line anymore (the line voltage always stays above the threshold).
You can recompile the gateway firmware with a shorter idle time requirement. How that works is clearly documented in the sources. Look for the line "constant PRELOADT0=100". Change that to "constant PRELOADT0=178" to use a 5 ms idle timer. (PRELOADT0 is the start value for timer 0, which counts up to 256. So, to halve the time, you have to halve the difference between PRELOADT0 and 256.)
Dialing the reference voltage all the way down to 0.625V stops the error messages because then the OTGW doesn't detect any changes on the line anymore (the line voltage always stays above the threshold).
You can recompile the gateway firmware with a shorter idle time requirement. How that works is clearly documented in the sources. Look for the line "constant PRELOADT0=100". Change that to "constant PRELOADT0=178" to use a 5 ms idle timer. (PRELOADT0 is the start value for timer 0, which counts up to 256. So, to halve the time, you have to halve the difference between PRELOADT0 and 256.)
Schelte
Re: Otgw and Remeha tzerra ace with etwist thermostat
Unfortunately changing PRELOADT0 to 178 does not help for my setup. I'm getting the Error 03 about every second. In monitor mode (as well as in gateway mode) the display of the eTwist doesn't turn on. Is there a way to directly pass through the OT signal to see if without any software the setup is working?
With the diagnose firmware I get this results:
With the diagnose firmware I get this results:
Code: Select all
Enter test number: 2
921,1104,930,1105,931,1105,931,1105,930,1108,931,1107,930,1109,930,1108,932,1106,929,6674,424,593,423,1102,422,596,930,1104,421,598,419,596,421,598,420,598,419,597,421,598,420,599,418,598,419,598,932,1103,420,597,422,599,418,597,421,597,422,596,420,598,421,597,422,596,420,598,420,597,423,595,420,597,930,1106,931,596,420,598,420.
921,1104,929,1106,930,1106,930,1104,929,1105,930,1105,930,1107,928,1107,930,1104,930,6676,424,593,422,1103,422,596,930,1104,420,598,419,597,420,597,420,599,418,597,420,598,420,598,418,597,420,598,932,1103,421,597,422,599,417,598,420,597,422,595,420,597,422,596,423,595,420,597,421,597,423,595,420,598,929,1106,931,596,421,597,421.
922,1104,931,1107,931,1106,932,1106,931,1107,931,1108,931,1108,930,1109,931,1107,930,6685,425,593,425,1104,423,597,930,1105,422,598,420,596,421,598,420,599,419,598,420,599,420,599,417,598,419,598,933,1102,421,597,422,599,417,597,421,597,422,596,420,597,422,596,423,595,421,597,420,598,423,594,420,598,929,1106,931,597,420,598,421.
921,1104,929,1105,930,1105,930,1105,930,1106,930,1106,930,1107,928,1107,930,1106,930,6678,424,594,423,1102,422,596,930,1105,420,599,419,597,421,597,420,599,418,597,421,598,421,599,418,598,420,597,934,1102,421,598,421,600,417,597,421,596,423,595,420,598,421,597,423,595,420,598,420,598,423,595,420,599,929,1106,931,597,420,598,421.
921,1104,930,1106,930,1105,930,1105,929,1107,930,1106,930,1107,928,1108,929,1107,929,6678,424,594,422,1103,422,597,931,1104,422,598,419,597,421,598,420,599,419,598,420,599,420,600,418,598,420,597,933,1103,421,598,422,599,418,598,421,597,422,596,420,597,421,597,423,595,421,597,421,597,423,594,421,598,930,1107,931,597,419,598,420.
Code: Select all
Enter test number: 5
Thermostat: 0.66, 1.89
Boiler: 0.00
Reference: 1.21
Re: Otgw and Remeha tzerra ace with etwist thermostat
You clearly need the PRELOADT0 modification, and you should have seen a change. With the original value you would only get Error 03. After changing PRELOADT0 to 178 you should see both Error 03 and T9002000B.
But there is another problem. Both in monitor mode and with the diagnostic firmware, the OTGW does directly pass through the OT signal, incorrect timings and all. However, no response appears on the boiler interface, as can be seen from your test #5. On the boiler interface only 0V is measured. So most likely there is an issue on the boiler interface. Either the signal doesn't get out, or the response is not detected. While you have the diagnostic firmware loaded, you can run test #4 (with the OTGW interfaces looped). You can also check the Opentherm interfaces as described in the troubleshooting instructions.
But there is another problem. Both in monitor mode and with the diagnostic firmware, the OTGW does directly pass through the OT signal, incorrect timings and all. However, no response appears on the boiler interface, as can be seen from your test #5. On the boiler interface only 0V is measured. So most likely there is an issue on the boiler interface. Either the signal doesn't get out, or the response is not detected. While you have the diagnostic firmware loaded, you can run test #4 (with the OTGW interfaces looped). You can also check the Opentherm interfaces as described in the troubleshooting instructions.
Schelte
Re: Otgw and Remeha tzerra ace with etwist thermostat
I removed IC1 and connected X1 to X2.
When I connect IC1 pin 2 to pin 14 (VCC), the voltage on X2 changes and IC1 pin 17 changes.
When I connect IC1 pin 3 to pin 5 (GND), the current on X1 changes from 20,2 mA to 6,1 mA. IC1 pin 18 however stays all the time to 0,0V.
The connection to the thermostat is fully working. OTGW can send messages to the boiler, but can't receive messages from the boiler anymore. This problem occurs since yesterday.
The optocoupler is fine. Do you have some advice how to find out what is wrong?
When I connect IC1 pin 2 to pin 14 (VCC), the voltage on X2 changes and IC1 pin 17 changes.
When I connect IC1 pin 3 to pin 5 (GND), the current on X1 changes from 20,2 mA to 6,1 mA. IC1 pin 18 however stays all the time to 0,0V.
The connection to the thermostat is fully working. OTGW can send messages to the boiler, but can't receive messages from the boiler anymore. This problem occurs since yesterday.
The optocoupler is fine. Do you have some advice how to find out what is wrong?
Re: Otgw and Remeha tzerra ace with etwist thermostat
Something seems to be wrong with the boiler interface of your OTGW. With X1 still connected to X2 (IC1 pin 3 not grounded), measure the voltages across D9, R2, and R3. Expected values are something like: D9: 4.7V, R2: 1.1V, R3: 3.6V.
How did you establish that the optocoupler is fine?
How did you establish that the optocoupler is fine?
Schelte
Re: Otgw and Remeha tzerra ace with etwist thermostat
I reasoned that either Q1 or D9 should be the cause of the problems, since the problem was in the receiving part of the boiler interface. I replaced Q1 with a new one and the interface is working fine again.
Then I flashed the customized firmware, connected X1 to the eTwist and did not connect the boiler. Result is Error 03's again, and not the T9002000B.
I realised I have a 18V transformer in stead of a 15V one. Could that be a problem?
Then I flashed the customized firmware, connected X1 to the eTwist and did not connect the boiler. Result is Error 03's again, and not the T9002000B.
I realised I have a 18V transformer in stead of a 15V one. Could that be a problem?
Re: Otgw and Remeha tzerra ace with etwist thermostat
The higher transformer voltage might be what blew your Q1 when you connected X1 to X2. An 18V transformer will provide 18V under its nominal load. But when not fully loaded, it produces a higher voltage. Suppose it puts out 23V AC. After rectifying and smoothing, that results in a DC voltage above 30V, the absolute maximum Vceo for a BC548. Now there is some other circuitry in between, so I would still not expect Q1 to have to deal with a voltage above its maximum rating, but you may be getting close. However, the higher voltage has no effect on the timing of the code in the PIC.
Looking at the timings you provided earlier:
921,1104,930,1105,931,1105,931,1105,930,1108,931,1107,930,1109,930,1108,932,1106,929,6674,424,593,423,1102,422,
596,930,1104,421,598,419,596,421,598,420,598,419,597,421,598,420,599,418,598,419,598,932,1103,420,597,422,599,
418,597,421,597,422,596,420,598,421,597,422,596,420,598,420,597,423,595,420,597,930,1106,931,596,420,598,420.
The first 921 µs high level will immediately produce the Error 03, because a valid OT signal must always start with a high level of half a bit length (between 400 and 650 µs). After the OTGW detects an error, it waits for the line to be idle for some amount of time before it will try to match an OT signal again. By default this is 10ms. The data following the 6674 µs low level is a proper OT message 9002000B. So, if you correctly reduced the idle timer to 5ms, the OT message should have been detected.
Looking at the timings you provided earlier:
921,1104,930,1105,931,1105,931,1105,930,1108,931,1107,930,1109,930,1108,932,1106,929,6674,424,593,423,1102,422,
596,930,1104,421,598,419,596,421,598,420,598,419,597,421,598,420,599,418,598,419,598,932,1103,420,597,422,599,
418,597,421,597,422,596,420,598,421,597,422,596,420,598,420,597,423,595,420,597,930,1106,931,596,420,598,420.
The first 921 µs high level will immediately produce the Error 03, because a valid OT signal must always start with a high level of half a bit length (between 400 and 650 µs). After the OTGW detects an error, it waits for the line to be idle for some amount of time before it will try to match an OT signal again. By default this is 10ms. The data following the 6674 µs low level is a proper OT message 9002000B. So, if you correctly reduced the idle timer to 5ms, the OT message should have been detected.
Schelte
Re: Otgw and Remeha tzerra ace with etwist thermostat
I changed line 190 in gateway.asm from
to
The output results in almost the same firmware as 4.2.5 gateway.hex. Only line 185 changes from
to
The resulting gateway.hex can be found as attachment. I'm 100% sure that firmware is running on the OTGW.
Today I found the T9002000B in the log, directly after connecting the thermostat:
The Error 03's continue if I leave the connection to the thermostat intact.
A bit longer log from the diagnosis firmware:
And the log when I start without a thermostat connection and connect the thermostat after a few seconds:
Code: Select all
constant PRELOADT0=100
Code: Select all
constant PRELOADT0=178
Code: Select all
:100B3000DD01640891020630031C91028C106430C0
Code: Select all
:100B3000DD01640891020630031C91028C10B23072
Today I found the T9002000B in the log, directly after connecting the thermostat:
Code: Select all
17:23:57.955971 Thermostat connected
17:24:00.957499 Error 03
17:24:04.077589 Error 03
17:24:04.166622 T9002000B Write-Data Master configuration: 00000000 11
17:24:04.618150 Error 03
17:24:05.127118 Error 03
17:24:05.653598 Error 03
17:24:05.925314 Thermostat disconnected
17:24:06.755402 R00000000 Read-Data Status: 00000000 00000000
17:24:07.546045 Thermostat connected
17:24:10.617758 Error 03
17:24:10.651716 T9002000B Write-Data Master configuration: 00000000 11
17:24:11.178268 Error 03
17:24:11.657068 Error 03
17:24:12.163612 Error 03
17:24:12.677593 Error 03
17:24:13.182861 Error 03
17:24:13.678445 Error 03
17:24:14.210833 Error 03
17:24:14.702331 Error 03
17:24:15.196309 Error 03
17:24:15.707923 Error 03
17:24:16.223229 Error 03
17:24:16.718322 Error 03
17:24:17.272303 Error 03
17:24:17.491768 Thermostat disconnected
17:24:18.431856 R00000000 Read-Data Status: 00000000 00000000
17:24:18.878664 Thermostat connected
17:24:21.890070 Error 03
17:24:21.934223 T9002000B Write-Data Master configuration: 00000000 11
17:24:22.450623 Error 03
17:24:22.933456 Error 03
17:24:23.442339 Error 03
17:24:23.953955 Error 03
17:24:24.454074 Error 03
17:24:24.971875 Error 03
17:24:25.463319 Error 03
17:24:25.994969 Error 03
17:24:26.510293 Error 03
17:24:26.970879 Thermostat disconnected
17:24:27.887085 R00000000 Read-Data Status: 00000000 00000000
17:24:28.894887 R00000000 Read-Data Status: 00000000 00000000
17:24:29.885487 R00000000 Read-Data Status: 00000000 00000000
17:24:30.869626 R00000000 Read-Data Status: 00000000 00000000
17:24:31.683674 Thermostat connected
17:24:34.691185 Error 03
17:24:34.727720 T9002000B Write-Data Master configuration: 00000000 11
17:24:35.230482 Error 03
17:24:35.740873 Error 03
17:24:36.238491 Error 03
17:24:36.758749 Error 03
17:24:37.280206 Error 03
17:24:37.827096 Error 03
A bit longer log from the diagnosis firmware:
Code: Select all
Opentherm gateway diagnostics - Version 1.1
1. LED test
2. Bit timing thermostat
3. Bit timing boiler
4. Delay symmetry
5. Voltage levels
6. Idle times
Enter test number: 2
912,1114,922,1116,922,1118,921,1116,922,1120,918,1119,920,1119,921,1117,922,1117,922,6695,415,604,414,1114,412,606,923,1117,410,609,410,608,410,608,411,610,409,608,410,609,411,610,409,608,411,611,922,1114,411,608,412,611,407,609,410,608,412,609,407,609,413,607,414,610,409,609,412,609,414,607,411,610,921,1119,923,608,412,607,413.
913,1114,922,1119,919,1117,922,1116,921,1116,921,1117,921,1121,918,1117,921,1118,921,6692,415,604,413,1114,412,607,921,1116,412,608,412,609,411,610,409,609,410,607,412,608,411,610,408,608,411,607,924,1114,411,609,411,611,406,607,412,607,413,609,408,608,411,607,413,606,410,607,411,607,414,607,409,610,919,1116,921,608,410,608,411.
913,1114,921,1116,922,1115,922,1118,919,1116,923,1118,919,1118,921,1117,923,1121,919,6700,415,602,415,1116,411,606,923,1115,412,609,410,608,411,608,411,608,410,607,412,611,409,612,407,608,411,608,924,1115,410,608,412,610,408,608,412,607,413,612,406,609,410,607,414,606,411,608,411,609,412,606,410,609,921,1116,924,610,409,607,412.
913,1116,920,1115,923,1116,921,1115,921,1116,923,1120,918,1118,922,1117,921,1117,921,6693,416,603,414,1114,413,606,922,1118,409,611,408,607,412,608,411,609,410,608,411,609,411,609,409,608,411,608,925,1116,410,607,413,609,409,608,411,608,412,610,408,607,412,607,414,604,412,610,408,610,412,605,411,608,922,1117,921,608,410,607,412.
913,1115,921,1116,923,1119,920,1116,922,1118,921,1118,920,1119,922,1118,921,1117,922,6697,413,603,414,1114,412,608,921,1117,411,609,410,606,412,607,412,612,407,608,412,608,412,609,409,608,411,608,924,1114,412,607,414,608,409,610,410,607,413,609,408,608,412,607,412,607,410,608,410,609,413,605,411,610,920,1116,923,607,412,607,412.
912,1113,921,1116,922,1116,922,1115,922,1117,922,1117,921,1119,921,1118,923,1118,922,6698,416,603,415,1116,410,609,920,1115,412,608,411,607,411,608,411,609,409,607,412,608,412,612,407,610,409,608,926,1115,411,608,413,609,408,608,412,607,413,609,408,611,409,609,412,606,412,608,411,608,414,606,411,608,920,1117,922,607,412,610,409.
913,1116,920,1115,923,1116,922,1116,921,1117,922,1120,918,1118,922,1117,921,1117,921,6692,415,604,413,1114,412,607,921,1114,412,611,408,609,409,607,411,609,409,607,411,609,410,610,408,608,411,607,924,1117,408,609,411,609,408,607,411,608,413,609,407,608,411,607,412,606,411,606,412,610,411,607,409,608,920,1117,921,607,410,608,410.
912,1115,921,1116,922,1118,920,1115,922,1116,922,1117,920,1117,921,1120,919,1116,922,6692,415,606,411,1114,413,606,922,1115,411,608,410,607,411,607,411,608,410,610,408,610,409,609,408,607,411,607,923,1114,411,607,412,609,408,607,412,610,410,610,407,607,412,607,413,606,411,608,411,608,413,605,411,608,921,1120,920,607,412,607,412.
910,1113,922,1116,922,1116,921,1116,921,1119,918,1117,920,1117,921,1118,920,1117,921,6693,413,604,413,1113,413,606,922,1117,410,608,412,607,412,608,411,609,409,608,412,608,413,609,410,607,413,611,923,1115,412,608,413,610,407,609,411,607,413,609,407,608,412,607,413,608,409,607,411,608,413,604,411,608,921,1116,922,607,412,606,413.
913,1114,922,1118,920,1116,922,1117,923,1118,923,1118,922,1120,919,1116,921,1118,921,6693,416,603,414,1114,412,607,921,1115,412,608,410,605,413,610,409,609,410,608,411,609,410,610,408,609,410,608,924,1114,411,609,411,611,405,607,412,607,413,609,407,609,411,608,413,606,411,607,411,608,414,608,408,610,919,1117,922,608,411,608,410.
914,1115,921,1117,922,1116,922,1119,919,1116,921,1118,920,1118,921,1117,922,1119,919,5678,414,605,414,1114,412,609,920,1116,412,609,410,609,414,605,410,610,409,608,411,608,412,612,407,610,409,609,923,1115,410,610,410,610,408,609,410,608,413,609,409,611,409,611,409,610,408,608,411,609,412,610,407,609,921,1117,922,607,412,613,406.
913,1117,920,1115,922,1117,920,1118,921,1117,922,1119,920,1117,922,1118,921,1117,921,6695,414,605,413,1114,413,606,923,1118,409,609,410,607,411,608,411,609,410,608,411,608,411,609,410,607,412,608,924,1117,409,608,413,609,408,609,411,608,412,610,408,607,412,607,413,609,409,610,410,609,412,605,412,607,923,1117,920,608,411,607,412.
912,1115,921,1116,922,1117,921,1116,922,1119,920,1117,921,1117,922,1119,920,1117,921,6697,412,604,414,1113,414,607,921,1115,412,608,411,607,411,606,412,612,407,607,411,607,411,609,409,608,410,609,921,1115,410,607,412,609,409,610,408,608,413,609,408,607,412,607,413,610,407,608,412,607,413,605,412,607,922,1116,922,607,411,608,411.
912,1114,922,1117,920,1116,921,1116,923,1119,920,1117,922,1118,921,1117,921,1116,922,6694,414,604,414,1113,414,609,919,1115,412,608,411,607,411,608,411,609,410,607,411,608,411,612,407,610,409,609,924,1114,411,608,411,610,408,608,411,607,413,609,409,610,410,610,410,610,408,607,412,608,412,607,411,608,921,1117,922,608,411,610,409.
914,1115,924,1115,922,1116,923,1117,920,1118,922,1119,920,1116,923,1117,921,1117,922,6691,415,604,414,1114,412,606,921,1116,412,610,408,609,410,606,412,608,411,607,411,608,411,609,409,608,411,608,924,1116,408,610,410,609,409,607,412,607,413,610,407,609,411,607,413,605,411,608,412,609,411,607,410,608,921,1117,922,608,410,608,411.
914,1115,922,1115,921,1117,920,1116,920,1117,922,1117,921,1116,921,1118,918,1116,922,6695,413,606,412,1112,414,605,923,1115,411,609,410,607,411,608,411,608,411,610,409,610,409,610,408,608,410,609,923,1115,410,607,413,609,408,607,412,610,410,610,407,608,412,606,414,606,410,609,411,607,413,605,412,607,922,1119,920,608,411,608,410.
911,1114,924,1115,921,1117,922,1116,921,1121,919,1116,922,1117,922,1117,922,1116,922,6694,414,604,414,1113,413,605,923,1116,412,608,411,608,410,609,410,610,409,608,410,608,411,609,410,609,410,611,921,1115,411,607,413,610,409,608,410,608,413,609,408,608,412,609,411,609,408,608,412,607,413,606,411,608,921,1118,922,607,412,607,412.
912,1113,924,1118,919,1115,923,1117,920,1117,921,1116,921,1119,920,1116,921,1118,920,6694,415,605,413,1115,412,607,921,1115,412,608,410,610,409,610,409,609,411,608,411,608,411,610,409,608,410,610,923,1114,411,611,409,612,406,609,411,608,413,609,408,608,411,608,412,607,411,607,413,606,414,609,409,609,920,1118,923,608,410,609,410.
914,1115,922,1116,922,1116,922,1118,919,1117,922,1117,921,1117,921,1117,921,1120,919,6693,415,605,412,1115,411,606,922,1114,412,608,410,607,411,607,411,609,410,606,412,611,408,611,407,608,411,609,923,1115,410,608,412,609,408,608,411,608,413,611,406,609,410,607,413,606,411,608,411,608,413,606,411,607,921,1115,922,610,409,608,411.
913,1116,921,1116,923,1118,923,1116,921,1117,923,1118,921,1116,922,1117,920,1118,922,6692,414,605,413,1113,413,606,922,1118,409,608,410,608,411,608,410,610,410,607,410,609,410,609,409,608,411,610,922,1114,411,608,412,609,409,608,410,608,412,610,407,607,412,607,414,607,409,610,409,607,413,606,411,607,922,1117,921,607,411,607,412.
912,1115,922,1115,922,1117,922,1116,920,1118,921,1116,922,1117,920,1116,923,1116,922,6697,413,603,415,1113,413,606,921,1116,411,608,411,606,412,610,409,611,408,606,412,607,412,608,410,608,410,609,923,1114,411,607,413,611,407,610,409,608,412,610,408,608,411,608,413,606,410,608,412,607,413,605,412,610,920,1117,922,607,412,608,411.
913,1115,922,1117,920,1117,922,1120,918,1118,922,1118,923,1120,922,1119,923,1121,919,6691,415,603,414,1115,410,607,921,1114,412,608,410,607,411,608,410,609,410,608,412,607,412,611,407,609,409,609,923,1114,410,609,411,609,408,608,410,608,412,609,408,611,410,609,412,606,412,608,412,608,413,607,411,609,921,1119,923,611,409,611,409.
914,1116,920,1115,921,1117,922,1117,920,1117,922,1119,919,1117,921,1117,921,1118,921,6694,414,605,413,1114,412,607,921,1115,411,610,408,608,410,608,411,610,409,608,411,608,411,610,408,608,411,608,923,1117,409,607,413,609,409,607,411,608,412,610,407,608,412,606,414,605,411,608,412,609,411,605,412,607,922,1117,922,608,410,608,411.
913,1115,922,1115,920,1119,919,1117,920,1118,922,1117,921,1117,922,1119,919,1117,921,6696,413,605,413,1112,413,607,922,1118,411,610,410,608,412,609,411,613,408,610,410,609,412,610,410,609,411,611,924,1116,411,608,413,610,410,611,410,611,410,610,408,608,411,607,413,607,411,608,411,608,413,606,411,607,922,1119,921,607,412,608,411.
Code: Select all
Enter test number: 2
12277,176,2998,75.
59,1200,1096,87,898,963,75,303,191,7542,459,75,114,204,611,321,1416,1436,98,75,176,1964,217,75,616,427,10598,851,475,181,397,220,75,2903,75,709,75,42057,5147.
899,1123,954,1173,953.
906,1112,921,1113,921,1112,922,1111,922,1111,923,1110,923,1110,922,1110,922,1110,923,6674,419,598,416,1107,415,602,922,1110,414,603,412,602,414,602,415,604,411,603,414,602,416,603,411,603,414,602,923,1110,415,601,417,600,414,602,414,603,417,599,414,603,414,602,417,600,413,603,414,602,414,602,414,603,923,1110,925,601,414,603,415,3149.
917,1109,923,1110,923,1111,921,1111,922,1111,922,1111,922,1111,923,1111,922,1112,923,6673,417,599,417,1110,413,600,924,1109,415,602,414,602,416,599,415,602,414,602,417,600,414,603,413,603,418,599,924,1110,414,602,414,603,413,602,415,602,414,604,413,602,414,603,414,604,412,603,414,602,415,604,411,602,924,1114,920,603,413,604,412.
914,1108,924,1109,924,1110,922,1110,924,1110,923,1111,922,1111,923,1112,922,1112,921,6676,417,598,418,1108,414,601,924,1112,412,601,415,602,416,603,411,602,415,601,416,601,414,601,416,601,417,600,924,1109,418,599,414,603,413,603,417,599,413,604,413,602,414,602,415,603,414,602,414,602,414,604,413,603,924,1112,921,603,415,603,416.
917,1110,923,1110,923,1109,924,1110,923,1110,923,1111,923,1110,922,1111,923,1110,923,6677,417,599,417,1109,414,600,924,1112,412,602,414,602,416,603,412,602,415,602,416,600,415,602,415,602,417,600,924,1110,417,599,415,603,413,602,415,602,415,603,413,602,414,603,414,604,413,602,414,603,414,604,412,603,924,1111,921,603,414,604,416.
917,1108,924,1110,922,1111,923,1109,923,1111,921,1112,922,1111,923,1110,923,1110,923,6671,417,599,416,1109,413,601,924,1111,412,601,416,600,417,599,415,602,414,602,416,600,414,602,415,602,417,599,925,1109,417,599,414,603,413,602,414,602,414,604,413,602,414,602,414,604,414,602,415,604,415,604,412,602,923,1113,921,603,413,604,416.
918,1108,923,1109,924,1110,923,1111,924,1112,923,1111,922,1110,920,1111,923,1110,923,6673,417,599,416,1110,413,601,924,1109,414,602,416,600,417,599,415,601,415,602,417,599,415,602,414,602,417,599,925,1109,414,602,414,603,413,602,413,603,414,603,413,602,415,603,413,604,412,603,414,603,413,604,412,603,923,1113,920,603,414,604,412.
916,1109,923,1109,924,1110,922,1110,923,1110,923,1110,922,1110,923,1111,921,1111,923,6674,418,599,416,1110,413,600,924,1108,415,602,414,602,417,600,414,602,415,602,417,600,414,603,414,603,417,599,925,1110,414,602,415,603,413,603,414,603,414,603,413,602,414,603,415,604,412,602,415,602,415,604,412,602,924,1112,920,603,414,604,413.
915,1109,924,1110,923,1111,921,1109,922,1111,923,1111,923,1110,923,1110,923,1111,922,6678,418,599,417,1108,414,601,924,1112,412,601,416,601,416,604,411,602,415,601,416,600,415,602,415,601,416,600,924,1109,417,599,414,603,414,602,417,599,414,603,413,602,414,602,414,603,413,603,414,603,414,603,412,602,924,1110,922,602,414,603,416.
917,1108,924,1110,921,1110,923,1110,923,1111,923,1110,923,1111,923,1110,923,1111,923,6677,417,599,416,1110,413,600,925,1112,411,602,415,602,416,604,411,602,415,602,416,600,415,601,415,602,417,599,924,1110,418,599,414,603,413,602,414,603,414,603,413,602,415,602,414,604,414,602,414,603,414,603,412,603,925,1111,922,602,414,
- Attachments
-
- gateway-eTwist.zip
- (8.79 KiB) Downloaded 469 times
Re: Otgw and Remeha tzerra ace with etwist thermostat
I created an scl file from the timings you reported. Running that through the simulator, I also see only Error 03. Closer inspection revealed that my expectation that the initial pulse of around 912 µs would cause an error was incorrect. The first signal that the OTGW doesn't like is the 6600 µs gap between the rubbish and the actual Opentherm signal.
By the time the firmware concludes that the gap duration exceeds a valid Opentherm bit, 2ms have already passed. So only 4.5 ms of idle time remains by the time timer T0 is started. This explains why the workaround to reduce the timer to 5ms doesn't work for you, except on very rare occasions. You will have to reduce the idle line detection time even further. To make it 4 ms, set PRELOADT0 to 194. If that still misses too many messages, set PRELOADT0 to 201, for 3.5 ms.
By the time the firmware concludes that the gap duration exceeds a valid Opentherm bit, 2ms have already passed. So only 4.5 ms of idle time remains by the time timer T0 is started. This explains why the workaround to reduce the timer to 5ms doesn't work for you, except on very rare occasions. You will have to reduce the idle line detection time even further. To make it 4 ms, set PRELOADT0 to 194. If that still misses too many messages, set PRELOADT0 to 201, for 3.5 ms.
- Attachments
-
- stimulus.zip
- Simulator stimulus file
- (3.46 KiB) Downloaded 417 times
Schelte
Re: Otgw and Remeha tzerra ace with etwist thermostat
Thanks for the analysis!
Unfortunately with the new firmware (PRELOADT0=201) and the eTwist my OTGW broke again. I'm afraid the thermostat asks the boiler for a bigger current/voltage the OTGW can handle. This is the log with the (last) communication:
After this the boiler doesn't respond anymore, and the T9002000B continues together with the Error 03.
Is message ID 135 a OpenTherm 3.0 message? I can't find any documentation about OpenTherm 3.0, except the Wikipedia article which describes OpenTherm Smart Power is added in OpenTherm 3.0.
Unfortunately with the new firmware (PRELOADT0=201) and the eTwist my OTGW broke again. I'm afraid the thermostat asks the boiler for a bigger current/voltage the OTGW can handle. This is the log with the (last) communication:
Code: Select all
05:37:53.662526 Error 03
05:37:53.691515 T9002000B Write-Data Master configuration: 00000000 11
05:37:54.156821 Error 03
05:37:54.199709 T9002000B Write-Data Master configuration: 00000000 11
05:37:54.670997 Error 03
05:37:54.703824 T9002000B Write-Data Master configuration: 00000000 11
05:37:54.805242 B5002000B Write-Ack Master configuration: 00000000 11
05:37:55.166802 Error 03
05:37:55.212233 T80870B00 Read-Data Message ID 135: 2816
05:37:55.311015 BE0870B00 Data-Inv Message ID 135: 2816
05:37:58.387838 Error 03
05:37:58.428135 T9002000B Write-Data Master configuration: 00000000 11
05:37:58.518367 B5002000B Write-Ack Master configuration: 00000000 11
05:37:58.702158 Error 03
05:37:58.743448 T80870B00 Read-Data Message ID 135: 2816
05:37:58.906282 BE0870B00 Data-Inv Message ID 135: 2816
05:38:01.987844 Error 03
05:38:02.029229 T9002000B Write-Data Master configuration: 00000000 11
05:38:02.115765 B5002000B Write-Ack Master configuration: 00000000 11
05:38:02.238481 Error 03
05:38:02.278962 T80870B00 Read-Data Message ID 135: 2816
05:38:02.404192 B4087000B Read-Ack Message ID 135: 11
05:38:05.490665 Error 03
05:38:05.533388 T9002000B Write-Data Master configuration: 00000000 11
05:38:05.787525 Error 03
05:38:06.020407 T9002000B Write-Data Master configuration: 00000000 11
05:38:06.284252 Error 03
05:38:06.502000 T9002000B Write-Data Master configuration: 00000000 11
05:38:06.784753 Error 03
05:38:06.985018 T9002000B Write-Data Master configuration: 00000000 11
05:38:07.295253 Error 03
05:38:07.483102 T9002000B Write-Data Master configuration: 00000000 11
05:38:07.794623 Error 03
05:38:07.958779 T9002000B Write-Data Master configuration: 00000000 11
05:38:08.303900 Error 03
05:38:08.442894 T9002000B Write-Data Master configuration: 00000000 11
05:38:08.810668 Error 03
05:38:08.932422 T9002000B Write-Data Master configuration: 00000000 11
05:38:09.319904 Error 03
Is message ID 135 a OpenTherm 3.0 message? I can't find any documentation about OpenTherm 3.0, except the Wikipedia article which describes OpenTherm Smart Power is added in OpenTherm 3.0.
Re: Otgw and Remeha tzerra ace with etwist thermostat
It's a Data-ID above 127 so is most likely a manufacturers (Remeha) message for test & diagnostic purposes. Here some Remeha meesages I recorded in 2017:dimplou wrote: Is message ID 135 a OpenTherm 3.0 message? I can't find any documentation about OpenTherm 3.0, except the Wikipedia article which describes OpenTherm Smart Power is added in OpenTherm 3.0.
ID 131: {u8 u8} "Remeha dF-/dU-codes"
ID 132: {u8 u8} "Remeha Servicemessage"
ID 133: {u8 u8} "Remeha detection connected SCU’s"
Perhaps there is a Data-ID 134 too. More info about thermostat Data-ID's: http://otgw.tclcode.com/matrix.cgi#thermostats
Last edited by Templar on Wed Dec 16, 2020 11:52 pm, edited 1 time in total.
Re: Otgw and Remeha tzerra ace with etwist thermostat
The Opentherm spec only defines messages up to 127: "Id’s 0 .. 127 are reserved for OpenTherm pre-defined information, while id’s from 128 .. 255 can be used by manufacturers (members of the association) for test & diagnostic purposes only. The MemberID codes of the master and slave can be used to handshake between two compatible devices and enable the use of the Test & Diagnostic-Area data-items."
So, message ID 135 is a manufacturer specific message, not an OT 3.0 message. The text quoted above also hints at a possible way out: Modify the message ID 3 response to pretend that you have a Daalderop boiler instead of a Remeha Tzerra Ace (SR=3:1,29). If that doesn't do the trick, you can try to mark message IDs 2 or 3 as unknown (UI=2, UI=3). The best solution would be if you could prevent message ID 135 from getting to the boiler. But unfortunately, the OTGW currently does not support marking message IDs above 127 as unknown. There is not enough space to track all 256 messages individually. But maybe it would be possible to add a way to mark all "test & diagnostic" messages as unknown.
So, message ID 135 is a manufacturer specific message, not an OT 3.0 message. The text quoted above also hints at a possible way out: Modify the message ID 3 response to pretend that you have a Daalderop boiler instead of a Remeha Tzerra Ace (SR=3:1,29). If that doesn't do the trick, you can try to mark message IDs 2 or 3 as unknown (UI=2, UI=3). The best solution would be if you could prevent message ID 135 from getting to the boiler. But unfortunately, the OTGW currently does not support marking message IDs above 127 as unknown. There is not enough space to track all 256 messages individually. But maybe it would be possible to add a way to mark all "test & diagnostic" messages as unknown.
Schelte
Re: Otgw and Remeha tzerra ace with etwist thermostat
I've been following this subject as Calenta Ace could be similar to Tzerra ace.
Today I tested the following setup:
From: This Setup is Working No Error: 03 events just missing Outside Temperature, DHW Setpoint and DHW temperature in OTMonitor running FW 4.2.5
PR: V=3 / PR: T=11 / PR: S=17.99 / PR: G=00 PR: I=00 PR: O=T20.00
So inspired by etwist advertisements I tried this setup. However now the etwist thermostat does not light up.
So, removed the OTGW (not what I want ofcourse...) That seems to work.
Could that be related to the ideas mentioned in this topic?
Today I tested the following setup:
From: This Setup is Working No Error: 03 events just missing Outside Temperature, DHW Setpoint and DHW temperature in OTMonitor running FW 4.2.5
PR: V=3 / PR: T=11 / PR: S=17.99 / PR: G=00 PR: I=00 PR: O=T20.00
So inspired by etwist advertisements I tried this setup. However now the etwist thermostat does not light up.
So, removed the OTGW (not what I want ofcourse...) That seems to work.
Could that be related to the ideas mentioned in this topic?