I have bought a GW from the NODO shop and installed it. I see you can put it on gateway or monitor. Is there a big difference between the 2 functions ?
Grts
Patrick
OTGW /Remeha Initia/Honeywell T6
Moderator: hvxl
Re: OTGW /Remeha Initia/Honeywell T6
In monitor mode you can only observe the communication between the thermostat and the boiler. Gateway mode allows you to obtain additional information from the boiler that the thermostat may not request. Setting the time and changing the setpoint on the thermostat (if supported by the thermostat) or providing an outside temperature is also only possible in gateway mode. Finally, gateway mode is necessary for the more advanced features, such as controlling when the boiler will keep some amount of tap water heated, changing the maximum central heating water setpoint, or even interfering with the heating control algorithm.
Schelte
Re: OTGW /Remeha Initia/Honeywell T6
Ok I need only the monitoring part then. I want to look why the T6 is not controlling my brandnew remeha initia boiler. I set the demand room temp set to 25° (it is at 20°) but the boiler does nothing. When i use a old Isense thermostat all is working fine. ( same wiring and setup)
Re: OTGW /Remeha Initia/Honeywell T6
How can i post a GW log over her ?
Re: OTGW /Remeha Initia/Honeywell T6
You can attach it to a post in gzipped (or zipped) format using the "Upload attachment" tab.
Schelte