Opentherm gateway and Vokera Unica HE
Posted: Tue Jan 06, 2015 5:21 pm
Hi,
I have built the gateway and connected it to my boiler, at the moment I don't have an opentherm thermostat.. Seem to be in short supply in the UK at a sensible price.
My plan was to wire the original thermostat into the opentherm board initially, but allowing me to monitor when the boiler is coming on etc.
When connected the boiler it is recognised and its two seven segment displays change to ot
however Shorting the cables has no effect on firing the boiler up... (it does recognise it on the log.)
here is the log:
what should I try next?
Thanks
David
I have built the gateway and connected it to my boiler, at the moment I don't have an opentherm thermostat.. Seem to be in short supply in the UK at a sensible price.
My plan was to wire the original thermostat into the opentherm board initially, but allowing me to monitor when the boiler is coming on etc.
When connected the boiler it is recognised and its two seven segment displays change to ot
however Shorting the cables has no effect on firing the boiler up... (it does recognise it on the log.)
here is the log:
Code: Select all
15:04:49.724397 R00110000 Read-Data Relative modulation level: 0.00
15:04:49.955178 BC0110000 Read-Ack Relative modulation level: 0.00
15:04:49.956353 Command: PR=A
15:04:49.998094 PR: A=OpenTherm Gateway 4.0.1
15:04:50.775258 R00000000 Read-Data Status: 00000000 00000000
15:04:51.055294 BC0000000 Read-Ack Status: 00000000 00000000
15:04:51.825436 R801C0000 Read-Data Return water temperature: 0.00
15:04:52.048426 B401C3000 Read-Ack Return water temperature: 48.00
15:04:52.882543 R900E6400 Write-Data Maximum relative modulation level: 100.00
15:04:53.152636 B500E6400 Write-Ack Maximum relative modulation level: 100.00
15:04:53.927693 R00000000 Read-Data Status: 00000000 00000000
15:04:54.154731 BC0000000 Read-Ack Status: 00000000 00000000
15:04:54.978674 R00000000 Read-Data Status: 00000000 00000000
15:04:55.258718 BC0000000 Read-Ack Status: 00000000 00000000
15:04:56.028807 R80190000 Read-Data Boiler water temperature: 0.00
15:04:56.255750 B40193300 Read-Ack Boiler water temperature: 51.00
15:04:57.078705 R10010A00 Write-Data Control setpoint: 10.00
15:04:57.359640 BD0010A00 Write-Ack Control setpoint: 10.00
15:04:58.129760 R80380000 Read-Data DHW setpoint: 0.00
15:04:58.359785 BC0383700 Read-Ack DHW setpoint: 55.00
15:04:59.179956 R00390000 Read-Data Max CH water setpoint: 0.00
15:04:59.460060 BC0395000 Read-Ack Max CH water setpoint: 80.00
15:05:00.240044 R00000000 Read-Data Status: 00000000 00000000
15:05:00.466018 BC0000000 Read-Ack Status: 00000000 00000000
15:05:01.290082 R00120000 Read-Data CH water pressure: 0.00
15:05:01.470114 Error 03
15:05:02.350106 R00120000 Read-Data CH water pressure: 0.00
15:05:02.577082 B60120000 Data-Inv CH water pressure: 0.00
15:05:03.400186 R00000000 Read-Data Status: 00000000 00000000
15:05:03.660202 BC0000000 Read-Ack Status: 00000000 00000000
15:05:04.461240 R80190000 Read-Data Boiler water temperature: 0.00
15:05:04.663234 B40193300 Read-Ack Boiler water temperature: 51.00
15:05:05.511333 R10010A00 Write-Data Control setpoint: 10.00
15:05:05.769291 BD0010A00 Write-Ack Control setpoint: 10.00
15:05:06.561365 R00000000 Read-Data Status: 00000000 00000000
15:05:06.763380 BC0000000 Read-Ack Status: 00000000 00000000
15:05:07.606309 R00110000 Read-Data Relative modulation level: 0.00
15:05:07.866440 BC0110000 Read-Ack Relative modulation level: 0.00
15:05:08.657481 R00000000 Read-Data Status: 00000000 00000000
15:05:08.867506 BC0000000 Read-Ack Status: 00000000 00000000
15:05:09.707532 R801C0000 Read-Data Return water temperature: 0.00
15:05:09.967559 B401C3000 Read-Ack Return water temperature: 48.00
15:05:10.767607 R900E6400 Write-Data Maximum relative modulation level: 100.00
15:05:10.967553 B500E6400 Write-Ack Maximum relative modulation level: 100.00
15:05:11.812670 R00000000 Read-Data Status: 00000000 00000000
15:05:12.067744 BC0000000 Read-Ack Status: 00000000 00000000
15:05:12.867745 R00000000 Read-Data Status: 00000000 00000000
15:05:13.075783 BC0000000 Read-Ack Status: 00000000 00000000
15:05:13.917769 R80190000 Read-Data Boiler water temperature: 0.00
15:05:14.177795 B40193300 Read-Ack Boiler water temperature: 51.00
15:05:14.967729 R10010A00 Write-Data Control setpoint: 10.00
15:05:15.177863 BD0010A00 Write-Ack Control setpoint: 10.00
15:05:16.018891 R80380000 Read-Data DHW setpoint: 0.00
15:05:16.278883 BC0383700 Read-Ack DHW setpoint: 55.00
15:05:17.067031 R00390000 Read-Data Max CH water setpoint: 0.00
15:05:17.279001 BC0395000 Read-Ack Max CH water setpoint: 80.00
15:05:18.119039 R00000000 Read-Data Status: 00000000 00000000
15:05:18.379062 BC0000000 Read-Ack Status: 00000000 00000000
15:05:19.169146 R00120000 Read-Data CH water pressure: 0.00
15:05:19.379136 B60120000 Data-Inv CH water pressure: 0.00
15:05:20.219170 R00000000 Read-Data Status: 00000000 00000000
15:05:20.479196 BC0000000 Read-Ack Status: 00000000 00000000
15:05:21.269318 R80190000 Read-Data Boiler water temperature: 0.00
15:05:21.479249 B40193300 Read-Ack Boiler water temperature: 51.00
15:05:22.320262 R10010A00 Write-Data Control setpoint: 10.00
15:05:22.579273 BD0010A00 Write-Ack Control setpoint: 10.00
15:05:23.380325 R00000000 Read-Data Status: 00000000 00000000
15:05:23.587277 BC0000000 Read-Ack Status: 00000000 00000000
15:05:24.430412 R00110000 Read-Data Relative modulation level: 0.00
15:05:24.680432 BC0110000 Read-Ack Relative modulation level: 0.00
15:05:25.473478 R00000000 Read-Data Status: 00000000 00000000
15:05:25.680452 BC0000000 Read-Ack Status: 00000000 00000000
15:05:26.523524 R801C0000 Read-Data Return water temperature: 0.00
15:05:26.790569 B401C3000 Read-Ack Return water temperature: 48.00
15:05:27.582537 R900E6400 Write-Data Maximum relative modulation level: 100.00
15:05:27.790642 B500E6400 Write-Ack Maximum relative modulation level: 100.00
15:05:28.630651 R00000000 Read-Data Status: 00000000 00000000
15:05:28.890653 BC0000000 Read-Ack Status: 00000000 00000000
15:05:29.685715 R00000000 Read-Data Status: 00000000 00000000
15:05:29.890704 BC0000000 Read-Ack Status: 00000000 00000000
15:05:30.727761 R80190000 Read-Data Boiler water temperature: 0.00
15:05:30.990662 B40193300 Read-Ack Boiler water temperature: 51.00
15:05:31.781799 R10010A00 Write-Data Control setpoint: 10.00
15:05:31.991828 BD0010A00 Write-Ack Control setpoint: 10.00
15:05:32.828850 R80380000 Read-Data DHW setpoint: 0.00
15:05:33.091886 BC0383700 Read-Ack DHW setpoint: 55.00
15:05:33.881965 R00390000 Read-Data Max CH water setpoint: 0.00
15:05:34.088985 BC0395000 Read-Ack Max CH water setpoint: 80.00
15:05:34.932052 R00000000 Read-Data Status: 00000000 00000000
15:05:35.192063 BC0000000 Read-Ack Status: 00000000 00000000
15:05:35.982098 R00120000 Read-Data CH water pressure: 0.00
15:05:36.192108 B60120000 Data-Inv CH water pressure: 0.00
15:05:37.032136 R00000000 Read-Data Status: 00000000 00000000
15:05:37.292204 BC0000000 Read-Ack Status: 00000000 00000000
15:05:38.092221 R80190000 Read-Data Boiler water temperature: 0.00
15:05:38.292211 B40193300 Read-Ack Boiler water temperature: 51.00
15:05:39.142272 R10010A00 Write-Data Control setpoint: 10.00
15:05:39.392268 BD0010A00 Write-Ack Control setpoint: 10.00
15:05:40.193268 R00000000 Read-Data Status: 00000000 00000000
15:05:40.393288 BC0000000 Read-Ack Status: 00000000 00000000
15:05:41.243336 R00110000 Read-Data Relative modulation level: 0.00
15:05:41.503381 BC0110000 Read-Ack Relative modulation level: 0.00
15:05:42.293510 R00000000 Read-Data Status: 00000000 00000000
15:05:42.495454 BC0000000 Read-Ack Status: 00000000 00000000
15:05:43.343522 R801C0000 Read-Data Return water temperature: 0.00
15:05:43.597539 B401C3000 Read-Ack Return water temperature: 48.00
15:05:44.414575 R900E6400 Write-Data Maximum relative modulation level: 100.00
15:05:44.704599 B500E6400 Write-Ack Maximum relative modulation level: 100.00
15:05:45.464663 R00000000 Read-Data Status: 00000000 00000000
15:05:45.704645 BC0000000 Read-Ack Status: 00000000 00000000
15:05:46.514695 R00000000 Read-Data Status: 00000000 00000000
15:05:46.808702 BC0000000 Read-Ack Status: 00000000 00000000
15:05:47.564761 R80190000 Read-Data Boiler water temperature: 0.00
15:05:47.809792 B40193300 Read-Ack Boiler water temperature: 51.00
15:05:48.615759 R10010A00 Write-Data Control setpoint: 10.00
15:05:48.905776 BD0010A00 Write-Ack Control setpoint: 10.00
15:05:49.665856 R80380000 Read-Data DHW setpoint: 0.00
15:05:49.905881 BC0383700 Read-Ack DHW setpoint: 55.00
15:05:50.715956 R00390000 Read-Data Max CH water setpoint: 0.00
15:05:51.009895 BC0395000 Read-Ack Max CH water setpoint: 80.00
15:05:51.766014 R00000000 Read-Data Status: 00000000 00000000
15:05:52.009062 BC0000000 Read-Ack Status: 00000000 00000000
15:05:52.816095 R00120000 Read-Data CH water pressure: 0.00
15:05:53.116079 B60120000 Data-Inv CH water pressure: 0.00
15:05:53.866007 R00000000 Read-Data Status: 00000000 00000000
15:05:54.116039 BC0000000 Read-Ack Status: 00000000 00000000
Thanks
David