AWB Boiler connectivity Error 03
Posted: Thu Feb 18, 2021 11:25 pm
I have the otgw running for some time, but Error 03 happens very frequent. about 50 per hour.
I have programmed the diagnostic to findout where it came from and it was the boiler, a AWB thermomaster 3HR 24T.
These seem normal:
The no.3 produce the error. 2 is okay.
Any clue what to do next? I used a oscilloscope to check the voltages, they are fine.
I'm using a standard otgw with a rs232 to lan module.
Code: Select all
2021-02-18 22:19:02.569 Status: OpenTherm: Error 03
2021-02-18 22:19:03.475 Status: OpenTherm: Error 03
2021-02-18 22:19:04.397 Status: OpenTherm: Error 03
2021-02-18 22:19:05.303 Status: OpenTherm: Error 03
2021-02-18 22:19:12.917 Status: OpenTherm: Error 03
2021-02-18 22:19:13.823 Status: OpenTherm: Error 03
2021-02-18 22:19:14.745 Status: OpenTherm: Error 04
2021-02-18 22:19:15.651 Status: OpenTherm: Error 03
2021-02-18 22:19:16.558 Status: OpenTherm: Error 04
2021-02-18 22:19:17.480 Status: OpenTherm: Error 03
2021-02-18 22:19:18.386 Status: OpenTherm: Error 03
These seem normal:
Code: Select all
Enter test number: 4
OK1A high-to-low: 10us
OK1A low-to-high: 22us
OK1B high-to-low: 5us
OK1B low-to-high: 6us
Enter test number: 5
Thermostat: 0.81, 2.14
Boiler: 0.00
Reference: 1.22
Enter test number: 6
B: 34.558
T: 443.939
Code: Select all
Enter test number: 3
506,1010,1032,992,507,506,507,505,526,487,505,505,509,511,500,504,507,507,505,508,522,487,508,504,507,505,509,523,487,505,507,506,510,502,507,504,507,505,508,521,491,504,1017,1010,524,485,509,504,508,504,506,527,485,509,505,504,517,495,507,505,1013.
40000200 Read-Ack Status: 00000010 00000000
504,1012,1012,1012,507,504,507,525,487,505,508,504,511,500,507,506,508,506,528,481,508,505,528,489,504,529,481,516,497,504,533,478,507,505,507,513,500,538,473,506,506,506,1012,1012,506,519,494,504,508,504,508,516,505,519,502,486,507,505,509,505,1034.
40000200 Read-Ack Status: 00000010 00000000
501,1011,1014,1012,506,525,487,506,505,506,508,504,525,486,508,504,509,514,497,504,510,503,506,507,525,486,506,507,507,504,507,524,488,504,509,505,512,499,506,505,507,507,1027,997,507,505,508,503,526,488,507,504,506,508,507,503,506,507,505,506,1013.
40000200 Read-Ack Status: 00000010 00000000
506,505,508,504,507,1011,1013,1012,507,524,488,506,507,504,508,506,505,504,507,507,505,517,496,506,506,506,507,504,1015,1010,506,506,506,525,487,506,1012,1014,1011,1011,518,512,488,507,505,505,511,503,505,507,505,507,506,531,482,504,1015.
D0010A00 Write-Ack Control setpoint: 10.00
504,1028,996,1011,508,504,526,485,507,506,508,521,490,504,508,506,505,506,520,491,1013,507,506,1031,486,508,1012,1011,525,486,506,507,1024,493,510,1009,506,506,526,485,507,505,508,503,509,525,487,504,507,505,514,497,508,505,507,505,1028.
40191800 Read-Ack Boiler water temperature: 24.00
504,504,508,517,496,1010,507,505,508,524,486,507,506,506,506,517,512,488,508,504,508,510,1034,984,507,504,526,489,1010,1014,504,530,484,504,507,506,521,491,507,503,509,504,543,470,505,508,504,509,503,507,505,531,481,535,477,505,509,504,507,504,1015.
C0110000 Read-Ack Relative modulation level: 0.00
2005,523,1013,1010,533,480,507,506,506,519,493,505,506,506,506,506,529,483,509,503,508,504,507,523,489,504,509,503,510,502,506,506,506,507,507,521,490,504,508,505,506,506,1013,1011,507,514,497,526,486,506,508,503,517,497,507,504,507,504,508,523,995.
Error 03
506,505,507,505,525,486,507,1012,517,494,508,504,509,503,507,524,489,504,507,507,1011,524,487,506,507,1016,503,506,505,506,506,505,522,490,1013,505,512,499,530,483,506,1012,512,499,507,507,506,505,507,517,495,506,506,506,509,501,527,485,508,505,1013.
E0383C00 Data-Inv DHW setpoint: 60.00
504,1013,1030,992,541,472,506,506,505,524,488,506,506,506,508,504,506,508,1011,504,533,480,506,1013,515,495,1013,1011,1036,989,505,508,1011,1011,507,508,1039,984,506,504,2025,75,432,503,508,522,490,506,506,504,508,505,1012.
Error 03
503,1014,1010,1011,508,505,508,1793,230,505,507,506,520,492,507,505,507,506,1034,483,506,505,507,1012,532,480,1014,1014,1009,1012,505,506,1013,1012,505,506,1034,990,508,506,505,506,526,485,508,504,508,515,496,506,508,503,1015.
Error 03
503.
722,1014,520,489,509,505,505,505,508,528,484,506,505,509,504,506,1011,507,507,505,509,1007,508,506,1012,1012,1012,1012,505,525,993,1012,508,503,1014,1011,506,514,498,506,507,504,508,506,524,486,507,505,507,505,1033.
Error 03
487,1011,1013,2023,508,505,511,501,532,480,507,504,518,507,493,507,507,503,1013,529,484,505,507,1010,507,526,992,1013,1012,1011,508,504,1026,997,508,503,1015,1010,507,506,505,507,507,523,488,506,507,505,517,496,505,504,1015.
Error 03
484,1011,1014,1035,481,1663,370,496,543,471,507,503,507,526,486,506,506,505,1013,529,483,505,507,1017,500,534,986,1010,1013,1011,507,504,1045,981,506,505,1012,1013,507,504,508,510,501,506,505,505,508,505,521,492,505,507,1012.
Error 03
503,1011,1013,1012,508,505,506,525,487,505,508,505,510,500,1625,399,507,522,996,505,508,504,507,1012,506,508,1014,1033,988,1012,520,491,1013,1033,485,506,1013,1012,532,479,506,505,509,512,499,575,438,504,507,505,512,499,1014.
Error 03
481,1010,1020,1026,485,1873,165,502,496,504,508,505,507,528,484,504,507,507,1011,529,483,504,507,1024,494,506,1012,1012,1013,1011,508,504,1033,991,506,506,1013,1013,505,506,507,516,496,506,506,504,509,503,527,485,507,507,1012.
Error 03
539,977,1012,1012,509,504,507,513,498,1638,385,507,526,486,507,505,507,504,1038,481,506,506,505,1012,507,506,1011,1033,991,1013,506,506,1013,1011,505,506,1031,994,505,507,514,497,507,505,508,503,507,523,490,504,508,506,1012.
Error 03
526.
659,1012,507,504,507,528,485,504,507,505,507,506,531,481,509,503,1020,498,507,507,504,1013,516,495,1012,1012,1031,994,507,504,1014,1010,507,506,1031,994,505,506,507,505,523,490,505,506,507,505,507,526,486,506,1012.
Error 03
503,1031,994,2023,531,481,507,505,508,506,506,531,479,506,506,507,518,496,1011,504,508,504,528,991,507,505,1014,1010,1012,1015,505,525,992,1012,518,494,1013,1014,505,523,488,506,506,505,508,504,527,485,507,505,509,511,1005.
Error 03
505,1036,987,1011,2010,75,446,505,507,522,491,505,506,505,508,506,531,479,1013,505,520,492,531,988,506,504,1017,1010,1012,1026,491,507,1010,1013,525,485,1013,1015,503,505,507,507,505,507,518,492,507,505,508,506,506,526,992.
Error 03
506,1013,1013,1010,505,504,509,530,482,507,504,1893,155,480,507,506,506,529,990,503,508,506,506,1012,505,505,1015,1034,988,1011,511,502,1012,1012,506,517,1000,1012,517,494,526,488,508,503,507,504,507,526,486,506,507,504,1013.
Error 03
505,1018,1029,2000,518,506,494,508,504,506,507,526,485,507,507,504,506,506,1012,505,507,505,515,1003,508,503,1014,1013,1012,1010,507,524,994,1012,506,505,1013,1012,506,512,500,505,506,506,507,505,524,487,507,507,505,507,1030.
Error 03
479,1014,1018,1003,507,506,1579,444,506,505,508,506,505,530,482,506,505,507,1013,529,482,504,508,1024,495,504,1013,1012,1012,1011,506,507,1031,995,505,504,1013,1011,507,505,508,517,494,507,506,503,508,504,528,484,508,505,1015.
Error 03
536,978,1011,1013,505,505,508,507,506,1631,392,505,519,492,507,505,508,505,1036,481,508,505,506,1010,532,481,1013,1025,998,1011,508,506,1011,1013,504,507,1032,992,506,505,507,504,526,488,507,504,507,513,498,506,507,505,1012.
Error 03
520,994,1013,1012,526,485,507,507,519,492,506,505,507,506,506,506,517,494,1013,505,507,506,525,991,507,506,1013,1010,1014,1018,500,504,1015,1010,522,489,1012,1012,509,522,487,507,505,506,512,499,507,507,506,505,507,519,1002.
40394900 Read-Ack Max CH water setpoint: 73.00
506,1011,1013,1012,505,509,504,504,508,506,505,505,520,492,507,504,508,504,509,523,488,504,507,506,505,506,527,485,507,504,507,515,497,507,506,504,507,506,526,485,507,507,1012,1030,486,505,507,506,512,499,507,506,505,507,506,521,491,508,503,506,1012.
40000200 Read-Ack Status: 00000010 00000000
503,531,483,504,507,1011,508,522,489,504,507,506,514,497,507,504,510,503,506,523,490,504,508,506,505,506,1012,1011,1018,1007,507,504,508,505,520,492,507,503,508,505,506,525,489,503,508,504,507,506,527,485,507,505,506,515,496,506,508,503,508,506,1013.
C0050000 Read-Ack Application-specific flags: 00000000 0
503,525,487,505,508,1016,1009,1011,505,506,522,489,507,504,509,505,507,525,486,504,508,505,508,504,506,506,506,507,1023,1001,505,506,507,504,526,488,1011,1013,1031,993,504,506,514,497,508,506,507,504,508,520,491,506,505,506,506,505,1013.
D0010A00 Write-Ack Control setpoint: 10.00
504,1011,1014,1015,502,508,505,506,506,505,520,492,506,506,507,504,508,524,488,506,1013,503,508,1011,507,505,1024,1000,507,506,506,506,1012,506,507,1012,506,528,484,504,507,506,513,499,507,504,509,503,506,521,492,506,506,505,508,506,1012.
40191800 Read-Ack Boiler water temperature: 24.00
494,1013,1012,1030,488,506,505,505,507,506,526,486,506,505,507,511,503,507,503,505,509,504,522,490,506,505,507,504,507,526,490,502,507,505,509,504,506,506,506,526,486,506,1011,1012,508,505,519,492,510,529,482,504,506,506,520,492,508,504,506,507,1039.
40000200 Read-Ack Status: 00000010 00000000
504,505,510,503,506,1012,506,505,507,507,509,520,489,504,508,506,516,495,507,504,507,505,1033,994,504,506,506,505,1012,1012,509,509,500,509,503,506,506,517,511,491,506,504,508,504,509,523,486,506,507,504,511,503,527,484,510,502,507,516,496,506,1012.
C0110000 Read-Ack Relative modulation level: 0.00
505,506,513,499,507,1011,506,506,524,487,507,506,506,509,504,524,488,505,506,506,510,514,1000,507,507,505,519,998,507,506,505,506,525,487,506,507,1013,504,527,992,506,506,1013,1012,506,505,507,523,490,503,507,506,505,506,526,485,508,507,1017.
C01C1900 Read-Ack Return water temperature: 25.00
503,1013,1011,1012,508,504,507,510,501,506,506,506,506,507,520,507,489,506,507,567,446,505,507,505,509,505,541,469,505,506,506,556,458,538,484,493,533,479,583,428,509,504,1014,1013,542,466,508,504,528,500,491,505,507,521,492,506,530,481,506,506,1025.
40000200 Read-Ack Status: 00000010 00000000
526,484,508,516,495,1012,1012,1012,509,522,487,508,504,506,506,505,528,485,507,505,507,511,502,503,507,506,507,504,1015,1010,506,507,507,523,489,521,995,1012,1012,1012,506,506,506,531,482,504,508,504,519,494,507,505,507,504,507,528,991.
D0010A00 Write-Ack Control setpoint: 10.00
507,1009,1013,1011,508,505,506,506,508,508,504,628,382,507,505,506,521,490,508,504,1013,505,532,986,507,504,1017,1008,508,504,506,577,941,507,507,1011,507,504,507,505,506,534,482,505,532,478,510,501,593,420,506,506,507,530,500,487,1012.
Error 01
506,503,527,485,507,1013,514,497,505,507,507,504,507,525,487,505,508,503,509,503,527,487,1015,502,512,500,506,1014,506,503,524,488,509,503,508,505,1032,485,508,1011,509,502,1012,1012,507,517,494,506,508,504,508,503,527,487,506,505,507,505,1032.
C01C1900 Read-Ack Return water temperature: 25.00
501,1012,1012,1012,507,503,507,517,494,506,507,506,505,506,526,485,508,504,507,506,507,523,489,506,505,505,515,508,496,504,507,505,509,520,491,504,507,505,506,507,526,485,1012,1017,502,505,506,506,508,504,521,490,507,509,505,504,507,524,487,505,1014.
40000200 Read-Ack Status: 00000010 00000000
505,506,531,479,508,1011,506,504,533,481,521,490,506,506,526,486,519,493,508,503,507,504,509,504,508,510,1020,997,1015,1009,518,494,523,489,507,506,505,505,508,505,506,518,493,524,489,505,506,508,506,503,1383,136,507,506,520,490,508,506,505,505,1036.
Error 03
518,1003,1038,983,506,504,534,479,507,507,505,513,499,504,508,504,509,503,534,478,507,507,505,514,499,504,507,1876,165,488,508,504,508,505,506,532,480,505,508,504,511,501,1012,1012,507,519,493,506,506,506,526,486,507,507,504,552,460,573,440,505,1012.
Error 03
519,493,505,506,506,506,505,1013,505,1568,457,530,481,506,506,505,521,492,507,505,1014,503,531,483,506,1010,506,506,532,481,505,506,506,510,1010,505,505,505,508,518,495,1011,505,505,506,526,488,508,503,506,506,504,528,484,507,505,507,516,496,505,1013.
Error 03
503.
399,505,515,497,532,986,505,507,523,487,509,503,507,505,507,530,484,504,1011,513,501,523,487,1012,507,511,500,506,505,506,508,503,1013,507,510,499,511,502,527,990,507,506,511,503,505,505,506,505,507,518,494,505,507,504,507,506,527,485,1012.
Error 01
506,504,506,521,494,502,508,1010,506,525,489,504,507,504,510,506,524,485,507,505,1023,495,505,505,508,1011,527,487,504,505,507,505,506,525,994,506,505,513,499,506,506,1012,508,519,490,509,503,506,506,505,526,485,507,509,504,510,502,504,506,507,1013.
E0383C00 Data-Inv DHW setpoint: 60.00
511,1007,1012,1010,521,492,505,506,507,504,507,525,488,509,503,506,505,504,1014,504,507,506,515,1003,505,506,1014,1010,1014,1009,507,525,994,1011,512,499,1012,1012,507,521,490,504,508,508,512,496,508,504,508,505,506,534,984.
40394900 Read-Ack Max CH water setpoint: 73.00
I'm using a standard otgw with a rs232 to lan module.