OTGW not working: where to start debugging
Bobsled0935
Post by Bobsled0935 »
A while ago I installed an OTGW in a holiday home, but unfortunately I haven't got it working yet. I'm not sure where to look for the problem/solution: the OTGW itself, the settings, or the thermostat? It concerns a Nefit Proline C110 boiler and a Nefit Moduline 2000 thermostat. These will continue to work with each other if the gateway is in between. A piece of log file is attached. In it a number of times 'Error03' (in recent months this has increased to thousands of errors). The temperature readings that come through don't seem realistic either. Where do I start looking?
20:11:46.259373  T80000200  Read-Data   Status: 00000010 00000000
20:11:47.259427  T80000200  Read-Data   Status: 00000010 00000000
20:11:49.259960  T80000200  Read-Data   Status: 00000010 00000000
20:11:50.258656  T80000200  Read-Data   Status: 00000010 00000000
20:11:50.348842  B40000200  Read-Ack    Status: 00000010 00000000
20:11:51.261662  T80000200  Read-Data   Status: 00000010 00000000
20:11:54.212056  T801A0000  Read-Data   DHW temperature: 0.00
20:11:56.254138  T80000200  Read-Data   Status: 00000010 00000000
20:11:56.319667  B40000200  Read-Ack    Status: 00000010 00000000
20:11:57.254644  T80000200  Read-Data   Status: 00000010 00000000
20:11:57.376548  B40000200  Read-Ack    Status: 00000010 00000000
20:11:58.257592  T80000200  Read-Data   Status: 00000010 00000000
20:11:58.363258  B40000200  Read-Ack    Status: 00000010 00000000
20:11:59.400351  T80000200  Read-Data   Status: 00000010 00000000
20:11:59.403760  B40000200  Read-Ack    Status: 00000010 00000000
20:12:00.254387  T80000200  Read-Data   Status: 00000010 00000000
20:12:00.329266  B40000200  Read-Ack    Status: 00000010 00000000
20:12:01.253751  T80000200  Read-Data   Status: 00000010 00000000
20:12:01.316753  B40000200  Read-Ack    Status: 00000010 00000000
20:12:05.292592  T80000200  Read-Data   Status: 00000010 00000000
20:12:05.326331  B40000200  Read-Ack    Status: 00000010 00000000
20:12:06.249106  T80000200  Read-Data   Status: 00000010 00000000
20:12:06.386466  Error 03
20:12:07.249712  T80000200  Read-Data   Status: 00000010 00000000
20:12:13.254742  T80000200  Read-Data   Status: 00000010 00000000
20:12:15.246923  T80000200  Read-Data   Status: 00000010 00000000
20:12:15.306980  B40000200  Read-Ack    Status: 00000010 00000000
20:12:16.248511  T80000200  Read-Data   Status: 00000010 00000000
20:12:16.360424  B40000200  Read-Ack    Status: 00000010 00000000
20:12:17.247118  T80000200  Read-Data   Status: 00000010 00000000
20:12:23.246436  T80000200  Read-Data   Status: 00000010 00000000
20:12:23.321304  B40000200  Read-Ack    Status: 00000010 00000000
20:12:27.240112  T80000200  Read-Data   Status: 00000010 00000000
20:12:27.329362  B40000200  Read-Ack    Status: 00000010 00000000
20:12:30.240635  T80000200  Read-Data   Status: 00000010 00000000
20:12:31.241041  T80000200  Read-Data   Status: 00000010 00000000
20:12:31.340760  B40000200  Read-Ack    Status: 00000010 00000000
20:12:32.238414  T80000200  Read-Data   Status: 00000010 00000000
20:12:32.321213  B40000200  Read-Ack    Status: 00000010 00000000
20:12:33.238778  T80000200  Read-Data   Status: 00000010 00000000
20:12:34.237920  T80000200  Read-Data   Status: 00000010 00000000
20:12:34.359961  B40000200  Read-Ack    Status: 00000010 00000000
20:12:35.237482  TBFFC0200  Reserved    Message ID 252: 512
20:12:36.239322  T80000200  Read-Data   Status: 00000010 00000000
20:12:38.236971  T803C0200  Read-Data   Remote parameter 5: 2.00
20:12:41.234531  T80000200  Read-Data   Status: 00000010 00000000
20:12:41.326005  B40000200  Read-Ack    Status: 00000010 00000000
20:12:43.235539  T80000200  Read-Data   Status: 00000010 00000000
20:12:44.238747  T80000200  Read-Data   Status: 00000010 00000000
20:12:44.346589  B40000200  Read-Ack    Status: 00000010 00000000
20:12:45.237443  T80F00200  Read-Data   Message ID 240: 512
20:12:45.326423  B40000200  Read-Ack    Status: 00000010 00000000
20:12:49.231335  T80000200  Read-Data   Status: 00000010 00000000
20:12:50.233438  T800FC200  Read-Data   Boiler capacity and modulation limits: 194 0
20:12:52.231782  T80000200  Read-Data   Status: 00000010 00000000
20:12:52.291945  B40000200  Read-Ack    Status: 00000010 00000000
20:12:52.435408  T10010000  Write-Data  Control setpoint: 0.00
20:12:52.549425  BD0010000  Write-Ack   Control setpoint: 0.00
20:12:53.414822  T801A0000  Read-Data   DHW temperature: 0.00
20:12:53.484777  B401A0000  Read-Ack    DHW temperature: 0.00
20:12:54.774799  T80000200  Read-Data   Status: 00000010 00000000
20:12:54.893841  B40000200  Read-Ack    Status: 00000010 00000000
20:12:55.228901  T80000200  Read-Data   Status: 00000010 00000000
20:12:55.313578  B40000200  Read-Ack    Status: 00000010 00000000
20:12:58.230842  T80000200  Read-Data   Status: 00000010 00000000
20:12:58.336779  B40000200  Read-Ack    Status: 00000010 00000000
20:12:59.228418  T80000200  Read-Data   Status: 00000010 00000000
20:12:59.320729  B40000200  Read-Ack    Status: 00000010 00000000
20:13:01.226231  T80000200  Read-Data   Status: 00000010 00000000
20:13:01.292520  B40000200  Read-Ack    Status: 00000010 00000000
20:13:02.226796  T80000200  Read-Data   Status: 00000010 00000000
20:13:02.347818  B40000200  Read-Ack    Status: 00000010 00000000
20:13:05.517315  T80000200  Read-Data   Status: 00000010 00000000
20:13:06.229133  T80000200  Read-Data   Status: 00000010 00000000
20:13:06.282910  B40000200  Read-Ack    Status: 00000010 00000000
20:13:07.222371  T80000200  Read-Data   Status: 00000010 00000000
20:13:07.349192  B40000200  Read-Ack    Status: 00000010 00000000
20:13:08.223017  T80000200  Read-Data   Status: 00000010 00000000
20:13:08.321046  B40000200  Read-Ack    Status: 00000010 00000000
20:13:09.226782  T80000200  Read-Data   Status: 00000010 00000000
20:13:09.305133  B40000200  Read-Ack    Status: 00000010 00000000
20:13:10.221796  T80000200  Read-Data   Status: 00000010 00000000
20:13:10.291482  B40000200  Read-Ack    Status: 00000010 00000000
20:13:11.227316  T9FF80200  Write-Data  Message ID 248: 512
20:13:12.222090  T80000200  Read-Data   Status: 00000010 00000000
20:13:12.323394  B40000200  Read-Ack    Status: 00000010 00000000
20:13:14.224249  T80000200  Read-Data   Status: 00000010 00000000
20:13:15.220797  T80000200  Read-Data   Status: 00000010 00000000
20:13:17.220110  T80000200  Read-Data   Status: 00000010 00000000
20:13:20.216895  T80000200  Read-Data   Status: 00000010 00000000
20:13:27.215095  T80000200  Read-Data   Status: 00000010 00000000
20:13:27.307164  B40000200  Read-Ack    Status: 00000010 00000000
20:13:28.215464  T80000200  Read-Data   Status: 00000010 00000000
20:13:29.215138  T80000200  Read-Data   Status: 00000010 00000000
20:13:29.273100  B40000200  Read-Ack    Status: 00000010 00000000
20:13:30.218653  T80000200  Read-Data   Status: 00000010 00000000
20:13:30.330432  B40000200  Read-Ack    Status: 00000010 00000000
20:13:31.214289  T80000200  Read-Data   Status: 00000010 00000000
20:13:31.312316  B40000200  Read-Ack    Status: 00000010 00000000
20:13:32.212379  T80000200  Read-Data   Status: 00000010 00000000
20:13:32.300740  B40000200  Read-Ack    Status: 00000010 00000000
20:13:33.213312  T80000200  Read-Data   Status: 00000010 00000000
20:13:33.282046  B40000200  Read-Ack    Status: 00000010 00000000
20:13:35.224942  T80000200  Read-Data   Status: 00000010 00000000
20:13:35.318997  B40000200  Read-Ack    Status: 00000010 00000000
20:13:37.212644  T80000200  Read-Data   Status: 00000010 00000000
20:13:37.288541  B40000200  Read-Ack    Status: 00000010 00000000
20:13:38.211626  T80000200  Read-Data   Status: 00000010 00000000
20:13:38.273003  B40000200  Read-Ack    Status: 00000010 00000000
20:13:46.209600  T80000200  Read-Data   Status: 00000010 00000000
20:13:48.206246  T80000200  Read-Data   Status: 00000010 00000000
20:13:48.330091  B40000200  Read-Ack    Status: 00000010 00000000
20:13:50.485852  T80000200  Read-Data   Status: 00000010 00000000
20:13:50.489696  B40000200  Read-Ack    Status: 00000010 00000000
20:13:52.779329  T10010000  Write-Data  Control setpoint: 0.00
20:13:52.899305  BD0010000  Write-Ack   Control setpoint: 0.00
20:13:53.822377  T801A0000  Read-Data   DHW temperature: 0.00
20:13:53.883113  B401A0000  Read-Ack    DHW temperature: 0.00
20:13:54.594132  T80000200  Read-Data   Status: 00000010 00000000
20:13:55.205490  T80000200  Read-Data   Status: 00000010 00000000
20:13:55.298912  Error 03
20:13:56.202734  T80000200  Read-Data   Status: 00000010 00000000
20:13:57.202778  T80000200  Read-Data   Status: 00000010 00000000
20:13:57.332165  B40000200  Read-Ack    Status: 00000010 00000000
20:13:58.202573  T80000200  Read-Data   Status: 00000010 00000000
20:13:58.312022  B40000200  Read-Ack    Status: 00000010 00000000
20:14:04.200724  T80000200  Read-Data   Status: 00000010 00000000
20:14:04.288627  B40000200  Read-Ack    Status: 00000010 00000000
20:14:05.197368  T80000200  Read-Data   Status: 00000010 00000000
20:14:05.273791  B40000200  Read-Ack    Status: 00000010 00000000
20:14:07.198503  TBFFF7A00  Reserved    Message ID 255: 31232
20:14:10.197645  T80000200  Read-Data   Status: 00000010 00000000
20:14:10.266777  B40000200  Read-Ack    Status: 00000010 00000000
20:14:12.198337  T80000200  Read-Data   Status: 00000010 00000000
20:14:12.306355  B40000200  Read-Ack    Status: 00000010 00000000
20:14:13.196848  T80000200  Read-Data   Status: 00000010 00000000
20:14:14.193997  T80000200  Read-Data   Status: 00000010 00000000
20:14:14.446863  B40000200  Read-Ack    Status: 00000010 00000000
20:14:15.196302  T80000200  Read-Data   Status: 00000010 00000000
20:14:16.198203  T80000200  Read-Data   Status: 00000010 00000000
20:14:16.308119  B40000200  Read-Ack    Status: 00000010 00000000
20:14:18.195818  T80000200  Read-Data   Status: 00000010 00000000
20:14:18.281730  B40000200  Read-Ack    Status: 00000010 00000000
20:14:19.194191  T80000200  Read-Data   Status: 00000010 00000000
20:14:19.269040  B40000200  Read-Ack    Status: 00000010 00000000
20:14:20.196273  T80000200  Read-Data   Status: 00000010 00000000
20:14:20.251009  B40000200  Read-Ack    Status: 00000010 00000000
20:14:21.193359  T80000200  Read-Data   Status: 00000010 00000000
20:14:21.301096  B40000200  Read-Ack    Status: 00000010 00000000
20:14:22.192237  T80000200  Read-Data   Status: 00000010 00000000
20:14:22.290017  B40000200  Read-Ack    Status: 00000010 00000000
20:14:26.189461  T80000200  Read-Data   Status: 00000010 00000000
20:14:28.188788  T80000200  Read-Data   Status: 00000010 00000000
20:14:28.266522  B40000200  Read-Ack    Status: 00000010 00000000
20:14:29.187194  T80000200  Read-Data   Status: 00000010 00000000
20:14:29.250236  B40000200  Read-Ack    Status: 00000010 00000000
20:14:30.187876  T80000200  Read-Data   Status: 00000010 00000000
20:14:30.313944  Error 03
20:14:31.185562  T80000200  Read-Data   Status: 00000010 00000000
20:14:31.290520  B40000200  Read-Ack    Status: 00000010 00000000
20:14:32.186121  T80000200  Read-Data   Status: 00000010 00000000
20:14:32.389004  B40000200  Read-Ack    Status: 00000010 00000000
20:14:34.185978  T80000200  Read-Data   Status: 00000010 00000000
20:14:34.312967  B40000200  Read-Ack    Status: 00000010 00000000
20:14:35.185740  T80000200  Read-Data   Status: 00000010 00000000
20:14:35.297171  B40000200  Read-Ack    Status: 00000010 00000000
20:14:37.188896  T87FE0200  Read-Data   Message ID 254: 512
20:14:39.185745  T80000200  Read-Data   Status: 00000010 00000000
20:14:40.184785  T80000200  Read-Data   Status: 00000010 00000000
20:14:40.288255  B40000200  Read-Ack    Status: 00000010 00000000
20:14:41.182126  T80000200  Read-Data   Status: 00000010 00000000
20:14:41.272935  B40000200  Read-Ack    Status: 00000010 00000000
20:14:42.183256  T80000200  Read-Data   Status: 00000010 00000000
20:14:42.257927  B40000200  Read-Ack    Status: 00000010 00000000
20:14:48.180568  T80000200  Read-Data   Status: 00000010 00000000
20:14:48.309310  Error 03
20:14:49.180505  T80000200  Read-Data   Status: 00000010 00000000
20:14:49.288145  B40000200  Read-Ack    Status: 00000010 00000000
20:14:52.179015  T80000200  Read-Data   Status: 00000010 00000000
20:14:53.902963  T80190000  Read-Data   Boiler water temperature: 0.00
20:14:53.999599  B40193000  Read-Ack    Boiler water temperature: 48.00
20:15:00.179020  T80000200  Read-Data   Status: 00000010 00000000
20:15:00.258644  B40000200  Read-Ack    Status: 00000010 00000000
20:15:04.232774  T80000200  Read-Data   Status: 00000010 00000000
20:15:06.170770  T80000200  Read-Data   Status: 00000010 00000000
20:15:06.234780  B40000200  Read-Ack    Status: 00000010 00000000
20:15:07.174220  T80000200  Read-Data   Status: 00000010 00000000
20:15:07.291646  B40000200  Read-Ack    Status: 00000010 00000000
20:15:08.177358  T80000200  Read-Data   Status: 00000010 00000000
20:15:09.171469  T80003200  Read-Data   Status: 00110010 00000000
20:15:11.170296  T80000200  Read-Data   Status: 00000010 00000000
20:15:11.293934  B40000200  Read-Ack    Status: 00000010 00000000
20:15:13.169998  T80000200  Read-Data   Status: 00000010 00000000
20:15:13.266166  B40000200  Read-Ack    Status: 00000010 00000000
20:15:16.167980  T80000200  Read-Data   Status: 00000010 00000000
20:15:16.287179  B40000200  Read-Ack    Status: 00000010 00000000
20:15:17.167676  T80000200  Read-Data   Status: 00000010 00000000
20:15:17.280175  B40000200  Read-Ack    Status: 00000010 00000000
20:15:18.171370  T80000200  Read-Data   Status: 00000010 00000000
20:15:18.255815  B40000200  Read-Ack    Status: 00000010 00000000
20:15:20.165196  T80000200  Read-Data   Status: 00000010 00000000
20:15:22.165157  T80000200  Read-Data   Status: 00000010 00000000
20:15:22.264626  B40000200  Read-Ack    Status: 00000010 00000000
20:15:24.166912  T80000200  Read-Data   Status: 00000010 00000000
20:15:24.236352  B40000200  Read-Ack    Status: 00000010 00000000
20:15:26.164918  T80000200  Read-Data   Status: 00000010 00000000
20:15:27.167704  T80000200  Read-Data   Status: 00000010 00000000
20:15:30.166215  T80000200  Read-Data   Status: 00000010 00000000
20:15:30.279920  B40000200  Read-Ack    Status: 00000010 00000000
20:15:32.160412  T80000200  Read-Data   Status: 00000010 00000000
20:15:32.249130  B40000200  Read-Ack    Status: 00000010 00000000
20:15:33.169018  T80000200  Read-Data   Status: 00000010 00000000
20:15:33.234116  B40000200  Read-Ack    Status: 00000010 00000000
20:15:34.160918  T80000200  Read-Data   Status: 00000010 00000000
20:15:34.221924  B40000200  Read-Ack    Status: 00000010 00000000
20:15:35.159996  T80000200  Read-Data   Status: 00000010 00000000
20:15:35.272641  B40000200  Read-Ack    Status: 00000010 00000000
20:15:38.157307  T80000200  Read-Data   Status: 00000010 00000000
20:15:38.224256  B40000200  Read-Ack    Status: 00000010 00000000
20:15:39.158748  T80000200  Read-Data   Status: 00000010 00000000
20:15:39.280802  B40000200  Read-Ack    Status: 00000010 00000000
20:15:40.161574  T80000200  Read-Data   Status: 00000010 00000000
20:15:40.268007  B40000200  Read-Ack    Status: 00000010 00000000
20:15:41.156374  T80000200  Read-Data   Status: 00000010 00000000
20:15:41.246497  B40000200  Read-Ack    Status: 00000010 00000000
20:15:42.159194  T80000200  Read-Data   Status: 00000010 00000000
20:15:42.233139  B40000200  Read-Ack    Status: 00000010 00000000
20:15:43.158445  T80000200  Read-Data   Status: 00000010 00000000
20:15:43.217962  B40000200  Read-Ack    Status: 00000010 00000000
20:15:44.157335  T80000200  Read-Data   Status: 00000010 00000000
20:15:44.271810  B40000200  Read-Ack    Status: 00000010 00000000
20:15:45.157667  T80000200  Read-Data   Status: 00000010 00000000
20:15:45.256683  B40000200  Read-Ack    Status: 00000010 00000000
20:15:52.150611  T80000200  Read-Data   Status: 00000010 00000000
20:15:52.727524  T10010000  Write-Data  Control setpoint: 0.00
20:15:52.849867  BD0010000  Write-Ack   Control setpoint: 0.00
20:15:54.136173  T801A0000  Read-Data   DHW temperature: 0.00
20:15:54.256608  B401A0000  Read-Ack    DHW temperature: 0.00
20:15:54.400153  T001B6000  Read-Data   Outside temperature: 96.00
20:15:56.151450  T80000200  Read-Data   Status: 00000010 00000000
20:15:57.149572  T80000200  Read-Data   Status: 00000010 00000000
20:15:58.152663  T80000200  Read-Data   Status: 00000010 00000000
20:15:58.264650  B40000200  Read-Ack    Status: 00000010 00000000
20:16:00.150945  T80000200  Read-Data   Status: 00000010 00000000
20:16:00.234908  B40000200  Read-Ack    Status: 00000010 00000000
20:16:01.149429  T80000200  Read-Data   Status: 00000010 00000000
20:16:01.218719  B40000200  Read-Ack    Status: 00000010 00000000
20:16:02.147410  T80000200  Read-Data   Status: 00000010 00000000
20:16:02.271936  B40000200  Read-Ack    Status: 00000010 00000000
20:16:03.147566  T80000200  Read-Data   Status: 00000010 00000000
20:16:07.147144  T80000200  Read-Data   Status: 00000010 00000000
20:16:07.263674  B40000200  Read-Ack    Status: 00000010 00000000
20:16:09.143263  T80000200  Read-Data   Status: 00000010 00000000
20:16:09.233558  B40000200  Read-Ack    Status: 00000010 00000000
20:16:10.147512  T80000200  Read-Data   Status: 00000010 00000000
20:16:10.219284  B40000200  Read-Ack    Status: 00000010 00000000
20:16:12.142769  T80000200  Read-Data   Status: 00000010 00000000
20:16:13.143930  T80000200  Read-Data   Status: 00000010 00000000
20:16:13.239296  B40000200  Read-Ack    Status: 00000010 00000000
20:16:15.140323  T80000200  Read-Data   Status: 00000010 00000000
20:16:16.143183  T80000200  Read-Data   Status: 00000010 00000000
20:16:16.263317  B40000200  Read-Ack    Status: 00000010 00000000
20:16:19.144365  T80000200  Read-Data   Status: 00000010 00000000
20:16:19.216803  B40000200  Read-Ack    Status: 00000010 00000000
20:16:21.140980  T80000200  Read-Data   Status: 00000010 00000000
20:16:21.257850  B40000200  Read-Ack    Status: 00000010 00000000
20:16:25.137809  T80000200  Read-Data   Status: 00000010 00000000
20:16:25.264118  B40000200  Read-Ack    Status: 00000010 00000000
20:16:27.136529  T80000200  Read-Data   Status: 00000010 00000000
20:16:27.235357  B40000200  Read-Ack    Status: 00000010 00000000
20:16:28.140930  T80000200  Read-Data   Status: 00000010 00000000
20:16:28.218846  B40000200  Read-Ack    Status: 00000010 00000000
20:16:30.137033  T80000200  Read-Data   Status: 00000010 00000000
20:16:30.256409  B40000200  Read-Ack    Status: 00000010 00000000
20:16:31.135969  T80000200  Read-Data   Status: 00000010 00000000
20:16:31.239809  B40000200  Read-Ack    Status: 00000010 00000000
20:16:35.133455  T80000200  Read-Data   Status: 00000010 00000000
20:16:36.133633  T80000200  Read-Data   Status: 00000010 00000000
20:16:36.234008  B40000200  Read-Ack    Status: 00000010 00000000
20:16:37.134709  T80000200  Read-Data   Status: 00000010 00000000
20:16:37.216516  B40000200  Read-Ack    Status: 00000010 00000000
20:16:38.134148  T80000200  Read-Data   Status: 00000010 00000000
20:16:38.200390  B40000200  Read-Ack    Status: 00000010 00000000
20:16:39.131796  T80000200  Read-Data   Status: 00000010 00000000
20:16:39.256897  B40000200  Read-Ack    Status: 00000010 00000000
20:16:40.132292  T80000200  Read-Data   Status: 00000010 00000000
20:16:41.130598  T80000200  Read-Data   Status: 00000010 00000000
20:16:43.131199  T80000200  Read-Data   Status: 00000010 00000000
20:16:43.192768  B40000200  Read-Ack    Status: 00000010 00000000
20:16:44.130373  T80000200  Read-Data   Status: 00000010 00000000
20:16:44.247791  B40000200  Read-Ack    Status: 00000010 00000000
20:16:45.132240  T80000200  Read-Data   Status: 00000010 00000000
20:16:45.233818  B40000200  Read-Ack    Status: 00000010 00000000
20:16:46.129212  T80000200  Read-Data   Status: 00000010 00000000
20:16:46.216750  B40000200  Read-Ack    Status: 00000010 00000000
20:16:47.130663  T80000200  Read-Data   Status: 00000010 00000000
20:16:47.200085  B40000200  Read-Ack    Status: 00000010 00000000
20:16:52.127544  T80000200  Read-Data   Status: 00000010 00000000
20:16:55.000507  T001B0000  Read-Data   Outside temperature: 0.00
20:16:59.123755  T80000200  Read-Data   Status: 00000010 00000000
20:16:59.223364  B40000200  Read-Ack    Status: 00000010 00000000
20:17:03.217978  T80000200  Read-Data   Status: 00000010 00000000
20:17:03.233427  B40000200  Read-Ack    Status: 00000010 00000000
20:17:04.123650  T80000200  Read-Data   Status: 00000010 00000000
20:17:04.216758  B40000200  Read-Ack    Status: 00000010 00000000
20:17:05.119404  T80000200  Read-Data   Status: 00000010 00000000
20:17:06.120304  T80000200  Read-Data   Status: 00000010 00000000
20:17:06.180770  B40000200  Read-Ack    Status: 00000010 00000000
20:17:08.123038  T80000200  Read-Data   Status: 00000010 00000000
20:17:08.226845  B40000200  Read-Ack    Status: 00000010 00000000
20:17:09.121968  T80000200  Read-Data   Status: 00000010 00000000
20:17:10.121558  T80000200  Read-Data   Status: 00000010 00000000
20:17:12.121960  T80000200  Read-Data   Status: 00000010 00000000
20:17:12.233221  B40000200  Read-Ack    Status: 00000010 00000000
20:17:13.117125  T80000200  Read-Data   Status: 00000010 00000000
20:17:14.122532  T80000200  Read-Data   Status: 00000010 00000000
20:17:14.203284  B40000200  Read-Ack    Status: 00000010 00000000
20:17:15.115682  T80000200  Read-Data   Status: 00000010 00000000
20:17:15.190468  B40000200  Read-Ack    Status: 00000010 00000000
20:17:19.116624  T80000200  Read-Data   Status: 00000010 00000000
20:17:19.192088  B40000200  Read-Ack    Status: 00000010 00000000
20:17:24.112073  T80000200  Read-Data   Status: 00000010 00000000
20:17:25.112364  T80000200  Read-Data   Status: 00000010 00000000
20:17:25.169573  B40000200  Read-Ack    Status: 00000010 00000000
20:17:27.113227  T80000200  Read-Data   Status: 00000010 00000000
20:17:27.209009  B40000200  Read-Ack    Status: 00000010 00000000
20:17:28.112760  T80000200  Read-Data   Status: 00000010 00000000
20:17:28.195704  B40000200  Read-Ack    Status: 00000010 00000000
20:17:29.108607  T80000200  Read-Data   Status: 00000010 00000000
20:17:29.175717  B40000200  Read-Ack    Status: 00000010 00000000
20:17:30.109932  T80000200  Read-Data   Status: 00000010 00000000
20:17:30.233013  B40000200  Read-Ack    Status: 00000010 00000000
20:17:33.110389  T80000200  Read-Data   Status: 00000010 00000000
20:17:33.178630  B40000200  Read-Ack    Status: 00000010 00000000
20:17:36.106140  T80000200  Read-Data   Status: 00000010 00000000
20:17:37.107174  T80000200  Read-Data   Status: 00000010 00000000
20:17:38.105926  T80000200  Read-Data   Status: 00000010 00000000
20:17:39.106346  T80000200  Read-Data   Status: 00000010 00000000
20:17:39.231122  B40000200  Read-Ack    Status: 00000010 00000000
20:17:41.103914  T80000200  Read-Data   Status: 00000010 00000000
20:17:41.201352  B40000200  Read-Ack    Status: 00000010 00000000
20:17:42.105379  T80000200  Read-Data   Status: 00000010 00000000
20:17:42.185610  B40000200  Read-Ack    Status: 00000010 00000000
20:17:45.101297  T80000200  Read-Data   Status: 00000010 00000000
20:17:45.207923  B40000200  Read-Ack    Status: 00000010 00000000
20:17:48.102861  T80000200  Read-Data   Status: 00000010 00000000
20:17:48.163341  B40000200  Read-Ack    Status: 00000010 00000000
20:17:50.099759  T80000200  Read-Data   Status: 00000010 00000000
20:17:51.100115  T80000200  Read-Data   Status: 00000010 00000000
20:17:51.184849  B40000200  Read-Ack    Status: 00000010 00000000
20:17:52.675260  T10010000  Write-Data  Control setpoint: 0.00
20:17:53.824370  T80190000  Read-Data   Boiler water temperature: 0.00
20:17:54.398592  T801A0000  Read-Data   DHW temperature: 0.00
20:17:54.975371  T001B0000  Read-Data   Outside temperature: 0.00
20:17:55.049350  BF01B0000  Unk-DataId  Outside temperature: 0.00
20:17:57.098565  T80000200  Read-Data   Status: 00000010 00000000
20:17:57.161214  B40000200  Read-Ack    Status: 00000010 00000000
20:17:58.099631  T80000200  Read-Data   Status: 00000010 00000000
20:17:58.215812  B40000200  Read-Ack    Status: 00000010 00000000
20:18:00.098552  T80000200  Read-Data   Status: 00000010 00000000
20:18:01.096797  T80000200  Read-Data   Status: 00000010 00000000
20:18:01.170606  B40000200  Read-Ack    Status: 00000010 00000000
20:18:03.096762  T80000200  Read-Data   Status: 00000010 00000000
20:18:03.208029  B40000200  Read-Ack    Status: 00000010 00000000
20:18:04.096586  T80000200  Read-Data   Status: 00000010 00000000
20:18:04.191653  B40000200  Read-Ack    Status: 00000010 00000000
20:18:05.094076  T80000200  Read-Data   Status: 00000010 00000000
20:18:05.174131  B40000200  Read-Ack    Status: 00000010 00000000
20:18:06.095834  T80000200  Read-Data   Status: 00000010 00000000
20:18:06.160012  B40000200  Read-Ack    Status: 00000010 00000000
20:18:07.094225  T80000200  Read-Data   Status: 00000010 00000000
20:18:07.218046  B40000200  Read-Ack    Status: 00000010 00000000
20:18:08.091368  T80000200  Read-Data   Status: 00000010 00000000
20:18:08.200311  B40000200  Read-Ack    Status: 00000010 00000000
20:18:09.092897  T80000200  Read-Data   Status: 00000010 00000000
20:18:09.184221  B40000200  Read-Ack    Status: 00000010 00000000
20:18:12.091105  T80000200  Read-Data   Status: 00000010 00000000
20:18:12.208168  B40000200  Read-Ack    Status: 00000010 00000000
20:18:14.091062  T80000200  Read-Data   Status: 00000010 00000000
20:18:16.091434  T80000200  Read-Data   Status: 00000010 00000000
20:18:17.093181  T80000200  Read-Data   Status: 00000010 00000000
20:18:17.202025  B40000200  Read-Ack    Status: 00000010 00000000
20:18:18.089753  T80000200  Read-Data   Status: 00000010 00000000
20:18:18.183227  B40000200  Read-Ack    Status: 00000010 00000000
20:18:23.088580  T80000200  Read-Data   Status: 00000010 00000000
20:18:25.086798  T80000200  Read-Data   Status: 00000010 00000000
20:18:25.146513  B40000200  Read-Ack    Status: 00000010 00000000
20:18:26.084917  T80060200  Read-Data   Remote parameter flags: 00000010 00000000
20:18:26.200886  B40000200  Read-Ack    Status: 00000010 00000000
20:18:27.087617  T80000200  Read-Data   Status: 00000010 00000000
20:18:27.184799  B40000200  Read-Ack    Status: 00000010 00000000
20:18:36.081986  T80000200  Read-Data   Status: 00000010 00000000
20:18:36.182825  B40000200  Read-Ack    Status: 00000010 00000000
20:18:39.081303  T80000200  Read-Data   Status: 00000010 00000000
20:18:41.080118  T80000200  Read-Data   Status: 00000010 00000000
20:18:41.175142  B40000200  Read-Ack    Status: 00000010 00000000
20:18:43.080154  T80000200  Read-Data   Status: 00000010 00000000
20:18:43.144685  B40000200  Read-Ack    Status: 00000010 00000000
20:18:46.076535  T80000200  Read-Data   Status: 00000010 00000000
20:18:46.166894  B40000200  Read-Ack    Status: 00000010 00000000
20:18:48.076883  T80000200  Read-Data   Status: 00000010 00000000
20:18:48.136584  B40000200  Read-Ack    Status: 00000010 00000000
20:18:51.075005  T80000200  Read-Data   Status: 00000010 00000000
20:18:51.159467  B40000200  Read-Ack    Status: 00000010 00000000
20:18:55.158071  T80000200  Read-Data   Status: 00000010 00000000
20:18:56.071552  T80000200  Read-Data   Status: 00000010 00000000
20:18:58.071424  T80000200  Read-Data   Status: 00000010 00000000
20:18:59.070329  T80000200  Read-Data   Status: 00000010 00000000
20:19:01.074984  T80000200  Read-Data   Status: 00000010 00000000
20:19:01.146512  B40000200  Read-Ack    Status: 00000010 00000000
20:19:02.108267  T80000200  Read-Data   Status: 00000010 00000000
20:19:02.129150  B40000200  Read-Ack    Status: 00000010 00000000
20:19:03.069660  T80000200  Read-Data   Status: 00000010 00000000
20:19:03.184571  B40000200  Read-Ack    Status: 00000010 00000000
20:19:07.071993  T80000200  Read-Data   Status: 00000010 00000000
20:19:08.065645  T80000200  Read-Data   Status: 00000010 00000000
20:19:08.253713  B40000200  Read-Ack    Status: 00000010 00000000
20:19:10.072269  T80000200  Read-Data   Status: 00000010 00000000
20:19:10.143988  B40000200  Read-Ack    Status: 00000010 00000000
20:19:12.067305  T80000200  Read-Data   Status: 00000010 00000000
20:19:18.064429  T80000200  Read-Data   Status: 00000010 00000000
20:19:18.160449  B40000200  Read-Ack    Status: 00000010 00000000
20:19:19.062653  T80000200  Read-Data   Status: 00000010 00000000
20:19:19.144333  B40000200  Read-Ack    Status: 00000010 00000000
20:19:20.063772  T80000200  Read-Data   Status: 00000010 00000000
20:19:20.125799  B40000200  Read-Ack    Status: 00000010 00000000
20:19:21.061208  T80000200  Read-Data   Status: 00000010 00000000
20:19:21.181766  B40000200  Read-Ack    Status: 00000010 00000000
20:19:27.059421  T80000200  Read-Data   Status: 00000010 00000000
20:19:27.158385  B40000200  Read-Ack    Status: 00000010 00000000
20:19:28.059020  T80000200  Read-Data   Status: 00000010 00000000
20:19:28.144367  B40000200  Read-Ack    Status: 00000010 00000000
20:19:29.056841  T80000200  Read-Data   Status: 00000010 00000000
20:19:29.129039  B40000200  Read-Ack    Status: 00000010 00000000
20:19:30.059718  T87FF8200  Read-Data   Message ID 255: 33280
20:19:36.169537  T80000200  Read-Data   Status: 00000010 00000000
20:19:37.054799  T80000200  Read-Data   Status: 00000010 00000000
20:19:37.141379  B40000200  Read-Ack    Status: 00000010 00000000
20:19:38.056353  T80000200  Read-Data   Status: 00000010 00000000
20:19:38.126990  B40000200  Read-Ack    Status: 00000010 00000000
20:19:45.051829  T80000200  Read-Data   Status: 00000010 00000000
20:19:46.051016  T80000200  Read-Data   Status: 00000010 00000000
20:19:46.140115  B40000200  Read-Ack    Status: 00000010 00000000
20:19:47.052481  T80000200  Read-Data   Status: 00000010 00000000
20:19:47.125252  B40000200  Read-Ack    Status: 00000010 00000000
20:19:49.049966  T80000200  Read-Data   Status: 00000010 00000000
20:19:50.048491  T80000200  Read-Data   Status: 00000010 00000000
20:19:50.150478  B40000200  Read-Ack    Status: 00000010 00000000
20:19:54.593178  T001B0000  Read-Data   Outside temperature: 0.00
20:19:54.651779  BF01B0000  Unk-DataId  Outside temperature: 0.00
20:19:56.047053  T80000200  Read-Data   Status: 00000010 00000000
20:19:57.043791  T80000200  Read-Data   Status: 00000010 00000000
20:19:57.116909  B40000200  Read-Ack    Status: 00000010 00000000
20:20:01.045266  T80000200  Read-Data   Status: 00000010 00000000
20:20:02.043595  T80000200  Read-Data   Status: 00000010 00000000
20:20:02.105510  B40000200  Read-Ack    Status: 00000010 00000000
20:20:03.043783  T80000200  Read-Data   Status: 00000010 00000000
20:20:04.043716  T80000200  Read-Data   Status: 00000010 00000000
20:20:04.142976  B40000200  Read-Ack    Status: 00000010 00000000
20:20:06.042307  T80000200  Read-Data   Status: 00000010 00000000
20:20:07.041227  T80000200  Read-Data   Status: 00000010 00000000
20:20:07.165216  B40000200  Read-Ack    Status: 00000010 00000000
20:20:08.044394  T80000200  Read-Data   Status: 00000010 00000000
20:20:10.039754  T80000200  Read-Data   Status: 00000010 00000000
20:20:10.118556  B40000200  Read-Ack    Status: 00000010 00000000
20:20:11.039447  T80000200  Read-Data   Status: 00000010 00000000
20:20:12.042078  T80000200  Read-Data   Status: 00000010 00000000
20:20:12.159350  B40000200  Read-Ack    Status: 00000010 00000000
20:20:13.041562  T80000200  Read-Data   Status: 00000010 00000000
20:20:13.138131  B40000200  Read-Ack    Status: 00000010 00000000
20:20:14.037112  T80000200  Read-Data   Status: 00000010 00000000
20:20:15.038261  T80000200  Read-Data   Status: 00000010 00000000
20:20:15.112536  B40000200  Read-Ack    Status: 00000010 00000000
20:20:18.036608  T80000200  Read-Data   Status: 00000010 00000000
20:20:19.038544  T80000200  Read-Data   Status: 00000010 00000000
20:20:20.036876  T80000200  Read-Data   Status: 00000010 00000000
20:20:21.034920  T80000200  Read-Data   Status: 00000010 00000000
20:20:21.158639  B40000200  Read-Ack    Status: 00000010 00000000
20:20:23.032692  T80000200  Read-Data   Status: 00000010 00000000
20:20:23.126823  B40000200  Read-Ack    Status: 00000010 00000000
20:20:24.034231  T80000200  Read-Data   Status: 00000010 00000000
20:20:24.111184  B40000200  Read-Ack    Status: 00000010 00000000
20:20:26.034112  T80000200  Read-Data   Status: 00000010 00000000
20:20:28.034716  T80000200  Read-Data   Status: 00000010 00000000
20:20:29.033855  T9FF80200  Write-Data  Message ID 248: 512
20:20:29.106863  B40000200  Read-Ack    Status: 00000010 00000000
20:20:30.031111  T80000200  Read-Data   Status: 00000010 00000000
20:20:30.160498  B40000200  Read-Ack    Status: 00000010 00000000
20:20:32.031277  T80000200  Read-Data   Status: 00000010 00000000
20:20:32.128199  B40000200  Read-Ack    Status: 00000010 00000000
20:20:37.029452  T80000200  Read-Data   Status: 00000010 00000000
20:20:37.118695  B40000200  Read-Ack    Status: 00000010 00000000
20:20:39.028290  T80000200  Read-Data   Status: 00000010 00000000
20:20:39.089225  B40000200  Read-Ack    Status: 00000010 00000000
20:20:40.029412  T80000200  Read-Data   Status: 00000010 00000000
20:20:40.140493  B40000200  Read-Ack    Status: 00000010 00000000
20:20:41.027322  T80000200  Read-Data   Status: 00000010 00000000
20:20:41.124557  B40000200  Read-Ack    Status: 00000010 00000000
20:20:42.025164  T80000200  Read-Data   Status: 00000010 00000000
20:20:46.042194  T80000200  Read-Data   Status: 00000010 00000000
20:20:46.120667  B40000200  Read-Ack    Status: 00000010 00000000
20:20:47.024417  T80000200  Read-Data   Status: 00000010 00000000
20:20:47.100924  B40000200  Read-Ack    Status: 00000010 00000000
20:20:48.026965  T80000200  Read-Data   Status: 00000010 00000000
20:20:48.090212  B40000200  Read-Ack    Status: 00000010 00000000
20:20:49.021077  T80000200  Read-Data   Status: 00000010 00000000
20:20:50.025846  T80000200  Read-Data   Status: 00000010 00000000
20:20:50.122992  B40000200  Read-Ack    Status: 00000010 00000000
20:20:52.595780  T10010000  Write-Data  Control setpoint: 0.00
20:20:53.745446  T80190000  Read-Data   Boiler water temperature: 0.00
20:20:53.853447  B40192E00  Read-Ack    Boiler water temperature: 46.00
20:20:54.775418  T80000200  Read-Data   Status: 00000010 00000000
20:20:54.839563  B40000200  Read-Ack    Status: 00000010 00000000
20:20:55.021812  T80000200  Read-Data   Status: 00000010 00000000
20:20:57.020248  T80000200  Read-Data   Status: 00000010 00000000
20:20:57.086247  B40000200  Read-Ack    Status: 00000010 00000000
20:20:58.020647  T80000200  Read-Data   Status: 00000010 00000000
20:20:58.141572  B40000200  Read-Ack    Status: 00000010 00000000
20:20:59.017585  T80000200  Read-Data   Status: 00000010 00000000
20:20:59.124310  B40000200  Read-Ack    Status: 00000010 00000000
20:21:04.014576  T80000200  Read-Data   Status: 00000010 00000000
20:21:06.017648  T80000200  Read-Data   Status: 00000010 00000000
20:21:06.088034  B40000200  Read-Ack    Status: 00000010 00000000
20:21:07.014691  T80000200  Read-Data   Status: 00000010 00000000
20:21:07.142665  B40000200  Read-Ack    Status: 00000010 00000000
20:21:08.018830  T80000200  Read-Data   Status: 00000010 00000000
20:21:08.125182  B40000200  Read-Ack    Status: 00000010 00000000
20:21:09.015202  T80000200  Read-Data   Status: 00000010 00000000
20:21:09.112332  B40000200  Read-Ack    Status: 00000010 00000000
20:21:11.030972  T80000200  Read-Data   Status: 00000010 00000000
20:21:12.124518  Error FF
20:21:14.013046  T80000200  Read-Data   Status: 00000010 00000000
20:21:14.102803  B40000200  Read-Ack    Status: 00000010 00000000
20:21:16.012441  T80000200  Read-Data   Status: 00000010 00000000
20:21:16.071200  B40000200  Read-Ack    Status: 00000010 00000000
20:21:17.011849  T80000200  Read-Data   Status: 00000010 00000000
20:21:17.119186  B40000200  Read-Ack    Status: 00000010 00000000
20:21:18.010712  T80000200  Read-Data   Status: 00000010 00000000
20:21:21.007488  T80000200  Read-Data   Status: 00000010 00000000
20:21:23.008614  T80000200  Read-Data   Status: 00000010 00000000
20:21:23.101327  B40000200  Read-Ack    Status: 00000010 00000000
20:21:24.010470  T80000200  Read-Data   Status: 00000010 00000000
20:21:24.085375  B40000200  Read-Ack    Status: 00000010 00000000
20:21:30.006768  T80000200  Read-Data   Status: 00000010 00000000
20:21:30.066657  B40000200  Read-Ack    Status: 00000010 00000000
20:21:34.005072  T80000200  Read-Data   Status: 00000010 00000000
20:21:34.073985  B40000200  Read-Ack    Status: 00000010 00000000
20:21:36.004812  T80000200  Read-Data   Status: 00000010 00000000
20:21:36.111322  B40000200  Read-Ack    Status: 00000010 00000000
20:21:39.001227  T80000200  Read-Data   Status: 00000010 00000000
20:21:39.062431  B40000200  Read-Ack    Status: 00000010 00000000
20:21:40.003288  T80000200  Read-Data   Status: 00000010 00000000
20:21:43.003668  T80000200  Read-Data   Status: 00000010 00000000
20:21:43.074395  B40000200  Read-Ack    Status: 00000010 00000000
20:21:44.999037  T80000200  Read-Data   Status: 00000010 00000000
20:21:45.110653  B40000200  Read-Ack    Status: 00000010 00000000
20:21:47.998019  T80000200  Read-Data   Status: 00000010 00000000
20:21:48.063599  B40000200  Read-Ack    Status: 00000010 00000000
20:21:48.996345  T80000200  Read-Data   Status: 00000010 00000000
20:21:50.997481  T80000200  Read-Data   Status: 00000010 00000000
20:21:51.086075  B40000200  Read-Ack    Status: 00000010 00000000
20:21:51.995334  T80000200  Read-Data   Status: 00000010 00000000
20:21:52.073323  B40000200  Read-Ack    Status: 00000010 00000000
20:21:55.317401  T80000200  Read-Data   Status: 00000010 00000000
20:21:55.994321  T80000200  Read-Data   Status: 00000010 00000000
20:21:58.991917  T80000200  Read-Data   Status: 00000010 00000000
20:21:59.101114  B40000200  Read-Ack    Status: 00000010 00000000
20:22:00.995576  T80000200  Read-Data   Status: 00000010 00000000
20:22:01.070530  B40000200  Read-Ack    Status: 00000010 00000000
20:22:01.990493  T80000200  Read-Data   Status: 00000010 00000000
20:22:02.066426  Error 03
20:22:02.993188  T80000200  Read-Data   Status: 00000010 00000000
20:22:03.110449  B40000200  Read-Ack    Status: 00000010 00000000
20:22:03.990523  T80000200  Read-Data   Status: 00000010 00000000
20:22:04.093579  B40000200  Read-Ack    Status: 00000010 00000000
20:22:06.989047  T80000200  Read-Data   Status: 00000010 00000000
20:22:07.988711  T80000200  Read-Data   Status: 00000010 00000000
20:22:08.104991  B40000200  Read-Ack    Status: 00000010 00000000
20:22:08.989916  T80000200  Read-Data   Status: 00000010 00000000
20:22:09.988823  T80000200  Read-Data   Status: 00000010 00000000
20:22:10.069986  B40000200  Read-Ack    Status: 00000010 00000000
20:22:10.986862  T80000200  Read-Data   Status: 00000010 00000000
20:22:11.055277  B40000200  Read-Ack    Status: 00000010 00000000
20:22:12.986104  T80000200  Read-Data   Status: 00000010 00000000
20:22:13.093705  B40000200  Read-Ack    Status: 00000010 00000000
20:22:14.984755  T80000200  Read-Data   Status: 00000010 00000000
20:22:15.061861  B40000200  Read-Ack    Status: 00000010 00000000
20:22:15.985182  T80000200  Read-Data   Status: 00000010 00000000
20:22:16.046911  B40000200  Read-Ack    Status: 00000010 00000000
20:22:16.983408  T80000200  Read-Data   Status: 00000010 00000000
20:22:17.099901  B40000200  Read-Ack    Status: 00000010 00000000
20:22:18.984346  T80000200  Read-Data   Status: 00000010 00000000
20:22:19.069789  B40000200  Read-Ack    Status: 00000010 00000000
20:22:19.982755  T80000200  Read-Data   Status: 00000010 00000000
20:22:20.053812  B40000200  Read-Ack    Status: 00000010 00000000
20:22:20.983888  T80000200  Read-Data   Status: 00000010 00000000
20:22:21.041190  B40000200  Read-Ack    Status: 00000010 00000000
20:22:21.989182  T80000200  Read-Data   Status: 00000010 00000000
20:22:22.094307  B40000200  Read-Ack    Status: 00000010 00000000
20:22:22.983510  T80000200  Read-Data   Status: 00000010 00000000
20:22:23.983269  T80000200  Read-Data   Status: 00000010 00000000
20:22:26.979910  T83000200  Read-Data   Status: 00000010 00000000
20:22:27.981544  T80000200  Read-Data   Status: 00000010 00000000
20:22:28.073505  B40000200  Read-Ack    Status: 00000010 00000000
20:22:28.979420  T80000200  Read-Data   Status: 00000010 00000000
20:22:29.055429  B40000200  Read-Ack    Status: 00000010 00000000
20:22:29.977873  T80000200  Read-Data   Status: 00000010 00000000
20:22:31.976202  T80000200  Read-Data   Status: 00000010 00000000
20:22:32.080287  B40000200  Read-Ack    Status: 00000010 00000000
20:22:36.019919  T80000200  Read-Data   Status: 00000010 00000000
20:22:36.085264  B40000200  Read-Ack    Status: 00000010 00000000
20:22:36.975598  T80000200  Read-Data   Status: 00000010 00000000
20:22:37.071600  B40000200  Read-Ack    Status: 00000010 00000000
20:22:37.975107  T80000200  Read-Data   Status: 00000010 00000000
20:22:38.052411  B40000200  Read-Ack    Status: 00000010 00000000
20:22:38.975357  T80000200  Read-Data   Status: 00000010 00000000
20:22:39.040827  B40000200  Read-Ack    Status: 00000010 00000000
20:22:39.974777  T80000200  Read-Data   Status: 00000010 00000000
20:22:40.093579  B40000200  Read-Ack    Status: 00000010 00000000
20:22:40.973693  T80000200  Read-Data   Status: 00000010 00000000
20:22:44.977099  T80000200  Read-Data   Status: 00000010 00000000
20:22:45.089538  B40000200  Read-Ack    Status: 00000010 00000000
20:22:46.972335  T80000200  Read-Data   Status: 00000010 00000000
20:22:47.054389  B40000200  Read-Ack    Status: 00000010 00000000
20:22:47.971451  T80000200  Read-Data   Status: 00000010 00000000
20:22:48.038930  B40000200  Read-Ack    Status: 00000010 00000000
20:22:53.324034  T80190000  Read-Data   Boiler water temperature: 0.00
20:22:53.384806  B40192E00  Read-Ack    Boiler water temperature: 46.00
20:22:55.246973  T80000200  Read-Data   Status: 00000010 00000000
20:22:55.350886  B40000200  Read-Ack    Status: 00000010 00000000
20:22:55.970066  T80000200  Read-Data   Status: 00000010 00000000
20:22:56.054604  B40000200  Read-Ack    Status: 00000010 00000000
20:22:56.967383  T98000200  Write-Data  Status: 00000010 00000000
20:22:59.968763  T80000200  Read-Data   Status: 00000010 00000000
20:23:01.966302  T80000200  Read-Data   Status: 00000010 00000000
20:23:02.029917  B40000200  Read-Ack    Status: 00000010 00000000
20:23:03.966941  T80000200  Read-Data   Status: 00000010 00000000
20:23:04.073024  B40000200  Read-Ack    Status: 00000010 00000000
20:23:04.963304  T80000200  Read-Data   Status: 00000010 00000000
20:23:05.057078  B40000200  Read-Ack    Status: 00000010 00000000
20:23:05.961568  T80000200  Read-Data   Status: 00000010 00000000
20:23:06.048259  Error 03
20:23:06.962407  T80000200  Read-Data   Status: 00000010 00000000
20:23:07.023221  B40000200  Read-Ack    Status: 00000010 00000000
20:23:08.962998  T80000200  Read-Data   Status: 00000010 00000000
20:23:10.961745  T80000200  Read-Data   Status: 00000010 00000000
20:23:11.028721  B40000200  Read-Ack    Status: 00000010 00000000
20:23:11.961451  T80000200  Read-Data   Status: 00000010 00000000
20:23:12.084947  B40000200  Read-Ack    Status: 00000010 00000000
20:23:13.960904  T80000200  Read-Data   Status: 00000010 00000000
20:23:14.056937  B40000200  Read-Ack    Status: 00000010 00000000
20:23:14.958950  T80000200  Read-Data   Status: 00000010 00000000
20:23:15.037794  B40000200  Read-Ack    Status: 00000010 00000000
20:23:19.956846  T80000200  Read-Data   Status: 00000010 00000000
20:23:20.030136  B40000200  Read-Ack    Status: 00000010 00000000
20:23:21.959514  T80000200  Read-Data   Status: 00000010 00000000
20:23:22.068406  B40000200  Read-Ack    Status: 00000010 00000000
20:23:22.955456  T80000200  Read-Data   Status: 00000010 00000000
20:23:23.053199  B40000200  Read-Ack    Status: 00000010 00000000
20:23:28.957620  T80000200  Read-Data   Status: 00000010 00000000
20:23:29.028367  B40000200  Read-Ack    Status: 00000010 00000000
20:23:32.035520  T80000200  Read-Data   Status: 00000010 00000000
20:23:32.053828  B40000200  Read-Ack    Status: 00000010 00000000
20:23:32.949726  T80000200  Read-Data   Status: 00000010 00000000
20:23:33.039166  B40000200  Read-Ack    Status: 00000010 00000000
20:23:33.952595  T80000200  Read-Data   Status: 00000010 00000000
20:23:34.022200  B40000200  Read-Ack    Status: 00000010 00000000
20:23:35.951187  T80000200  Read-Data   Status: 00000010 00000000
20:23:36.061531  B40000200  Read-Ack    Status: 00000010 00000000
20:23:37.948596  T80000200  Read-Data   Status: 00000010 00000000
20:23:38.949971  T80000200  Read-Data   Status: 00000010 00000000
20:23:39.015259  B40000200  Read-Ack    Status: 00000010 00000000
20:23:39.950029  T80000200  Read-Data   Status: 00000010 00000000
20:23:40.069412  B40000200  Read-Ack    Status: 00000010 00000000
20:23:40.947744  T80000200  Read-Data   Status: 00000010 00000000
20:23:41.054179  B40000200  Read-Ack    Status: 00000010 00000000
20:23:44.948111  T80000200  Read-Data   Status: 00000010 00000000
20:23:45.060747  B40000200  Read-Ack    Status: 00000010 00000000
20:23:47.949007  T80000200  Read-Data   Status: 00000010 00000000
20:23:48.946238  T80000200  Read-Data   Status: 00000010 00000000
20:23:49.066424  B40000200  Read-Ack    Status: 00000010 00000000
20:23:49.944935  T80000200  Read-Data   Status: 00000010 00000000
20:23:50.056539  B40000200  Read-Ack    Status: 00000010 00000000
20:23:50.944032  T80000200  Read-Data   Status: 00000010 00000000
20:23:52.516373  T10010000  Write-Data  Control setpoint: 0.00
20:23:53.093332  T100E0000  Write-Data  Maximum relative modulation level: 0.00
20:23:53.216820  BD00E0000  Write-Ack   Maximum relative modulation level: 0.00
20:23:53.356865  T80190000  Read-Data   Boiler water temperature: 0.00
20:23:53.430436  B40192E00  Read-Ack    Boiler water temperature: 46.00
20:23:54.941690  T80000200  Read-Data   Status: 00000010 00000000
20:23:56.942582  T80000200  Read-Data   Status: 00000010 00000000
20:23:57.940212  T80000200  Read-Data   Status: 00000010 00000000
20:23:57.998843  B40000200  Read-Ack    Status: 00000010 00000000
20:23:58.941270  T80000200  Read-Data   Status: 00000010 00000000
20:23:59.053038  B40000200  Read-Ack    Status: 00000010 00000000
20:24:00.937163  T80000200  Read-Data   Status: 00000010 00000000
20:24:01.021521  B40000200  Read-Ack    Status: 00000010 00000000
20:24:07.934485  T80000200  Read-Data   Status: 00000010 00000000
20:24:08.935715  T80000200  Read-Data   Status: 00000010 00000000
20:24:09.037494  B40000200  Read-Ack    Status: 00000010 00000000
20:24:16.991616  T80000200  Read-Data   Status: 00000010 00000000
20:24:17.051429  B40000200  Read-Ack    Status: 00000010 00000000
20:24:24.929276  T80000200  Read-Data   Status: 00000010 00000000
20:24:24.998383  B40000200  Read-Ack    Status: 00000010 00000000
20:24:25.926527  T80000200  Read-Data   Status: 00000010 00000000
20:24:26.930266  T80000800  Read-Data   Status: 00001000 00000000
20:24:31.925104  T8000C200  Read-Data   Status: 11000010 00000000
20:24:34.923855  T80000200  Read-Data   Status: 00000010 00000000
20:24:34.982841  B40000200  Read-Ack    Status: 00000010 00000000
20:24:38.925605  T80000200  Read-Data   Status: 00000010 00000000
20:24:38.987294  B40000200  Read-Ack    Status: 00000010 00000000
20:24:41.923609  T80000200  Read-Data   Status: 00000010 00000000
20:24:42.018651  B40000200  Read-Ack    Status: 00000010 00000000
20:24:42.920868  T80000200  Read-Data   Status: 00000010 00000000
20:24:43.918192  T80000200  Read-Data   Status: 00000010 00000000
20:24:43.981895  B40000200  Read-Ack    Status: 00000010 00000000
20:24:44.920789  T80000200  Read-Data   Status: 00000010 00000000
20:24:45.922329  T83FFC200  Read-Data   Message ID 255: 49664
20:24:48.918344  T80000200  Read-Data   Status: 00000010 00000000
20:24:49.046247  B40000200  Read-Ack    Status: 00000010 00000000
20:24:49.918190  T80000200  Read-Data   Status: 00000010 00000000
20:24:53.644841  T80190000  Read-Data   Boiler water temperature: 0.00
20:24:53.750992  B40192D00  Read-Ack    Boiler water temperature: 45.00
20:24:53.891314  T801A0000  Read-Data   DHW temperature: 0.00
20:24:53.965654  B401A0000  Read-Ack    DHW temperature: 0.00
20:24:54.682399  T80000200  Read-Data   Status: 00000010 00000000
20:24:55.255367  T80000200  Read-Data   Status: 00000010 00000000
20:24:55.373602  B40000200  Read-Ack    Status: 00000010 00000000
20:24:56.918375  T80000200  Read-Data   Status: 00000010 00000000
20:24:57.917388  T80000200  Read-Data   Status: 00000010 00000000
20:24:57.975176  B40000200  Read-Ack    Status: 00000010 00000000
20:24:58.915321  T80000200  Read-Data   Status: 00000010 00000000
20:24:59.027376  B40000200  Read-Ack    Status: 00000010 00000000
20:25:00.911861  T80000200  Read-Data   Status: 00000010 00000000
20:25:00.996648  B40000200  Read-Ack    Status: 00000010 00000000
20:25:01.912588  T80000200  Read-Data   Status: 00000010 00000000
20:25:01.988671  B40000200  Read-Ack    Status: 00000010 00000000
20:25:03.912513  T80006200  Read-Data   Status: 01100010 00000000
20:25:07.910265  T80000200  Read-Data   Status: 00000010 00000000
20:25:09.910588  T80000200  Read-Data   Status: 00000010 00000000
20:25:10.000217  B40000200  Read-Ack    Status: 00000010 00000000
20:25:10.907861  T80000200  Read-Data   Status: 00000010 00000000
20:25:10.978809  B40000200  Read-Ack    Status: 00000010 00000000
20:25:16.905532  T81FF6000  Read-Data   Message ID 255: 24576
20:25:17.100905  B40000200  Read-Ack    Status: 00000010 00000000
20:25:18.905048  T80000200  Read-Data   Status: 00000010 00000000
20:25:18.997077  B40000200  Read-Ack    Status: 00000010 00000000
20:25:19.907340  T80000200  Read-Data   Status: 00000010 00000000
20:25:19.981311  B40000200  Read-Ack    Status: 00000010 00000000
20:25:21.906993  T80000200  Read-Data   Status: 00000010 00000000
20:25:22.020306  B40000200  Read-Ack    Status: 00000010 00000000
20:25:23.905311  T80000200  Read-Data   Status: 00000010 00000000
20:25:26.905110  T80000200  Read-Data   Status: 00000010 00000000
20:25:27.012158  B40000200  Read-Ack    Status: 00000010 00000000
20:25:28.899743  T80000200  Read-Data   Status: 00000010 00000000
20:25:28.980172  B40000200  Read-Ack    Status: 00000010 00000000
20:25:30.901137  T81FFE200  Read-Data   Message ID 255: 57856
20:25:31.936707  T80000200  Read-Data   Status: 00000010 00000000
20:25:32.004554  B40000200  Read-Ack    Status: 00000010 00000000
20:25:32.898014  T8FC00200  Read-Data   Message ID 192: 512
20:25:36.897555  T80000200  Read-Data   Status: 00000010 00000000
20:25:36.996329  B40000200  Read-Ack    Status: 00000010 00000000
20:25:37.895942  T80000200  Read-Data   Status: 00000010 00000000
20:25:37.973608  B40000200  Read-Ack    Status: 00000010 00000000
20:25:38.901971  T80000200  Read-Data   Status: 00000010 00000000
20:25:39.899663  T80000200  Read-Data   Status: 00000010 00000000
20:25:40.019733  B40000200  Read-Ack    Status: 00000010 00000000
20:25:41.894419  T80000200  Read-Data   Status: 00000010 00000000
20:25:43.894262  T80000200  Read-Data   Status: 00000010 00000000
20:25:45.895469  T80000200  Read-Data   Status: 00000010 00000000
20:25:45.997502  B40000200  Read-Ack    Status: 00000010 00000000
20:25:47.892037  T80000200  Read-Data   Status: 00000010 00000000
20:25:48.892903  T80000200  Read-Data   Status: 00000010 00000000
20:25:50.893396  T80000200  Read-Data   Status: 00000010 00000000
20:25:53.614804  T80190000  Read-Data   Boiler water temperature: 0.00
20:25:54.189880  T801A0000  Read-Data   DHW temperature: 0.00
20:25:54.293673  B401A0000  Read-Ack    DHW temperature: 0.00
20:25:55.004530  T80000200  Read-Data   Status: 00000010 00000000
20:25:55.066385  B40000200  Read-Ack    Status: 00000010 00000000
20:25:56.888389  T80000200  Read-Data   Status: 00000010 00000000
20:25:56.964239  B40000200  Read-Ack    Status: 00000010 00000000
20:26:03.888349  T80000200  Read-Data   Status: 00000010 00000000
20:26:03.995455  B40000200  Read-Ack    Status: 00000010 00000000
20:26:04.882979  T80180200  Read-Data   Room temperature: 2.00
20:26:05.887942  T80000200  Read-Data   Status: 00000010 00000000
20:26:05.965414  B40000200  Read-Ack    Status: 00000010 00000000
20:26:06.883120  TBFFD8200  Reserved    Message ID 253: 33280
20:26:08.882364  T80000200  Read-Data   Status: 00000010 00000000
20:26:08.987863  B40000200  Read-Ack    Status: 00000010 00000000
20:26:10.880520  T80000200  Read-Data   Status: 00000010 00000000
20:26:10.957120  B40000200  Read-Ack    Status: 00000010 00000000
20:26:11.880742  T80000200  Read-Data   Status: 00000010 00000000
20:26:11.940622  B40000200  Read-Ack    Status: 00000010 00000000
20:26:13.881971  T80000200  Read-Data   Status: 00000010 00000000
20:26:13.978754  B40000200  Read-Ack    Status: 00000010 00000000
20:26:18.880501  T80000200  Read-Data   Status: 00000010 00000000
20:26:18.973190  B40000200  Read-Ack    Status: 00000010 00000000
20:26:21.876816  T80000200  Read-Data   Status: 00000010 00000000
20:26:21.995260  B40000200  Read-Ack    Status: 00000010 00000000
20:26:22.876016  T80000200  Read-Data   Status: 00000010 00000000
20:26:23.877533  T80000200  Read-Data   Status: 00000010 00000000
20:26:23.965577  B40000200  Read-Ack    Status: 00000010 00000000
20:26:24.877363  T80000200  Read-Data   Status: 00000010 00000000
20:26:24.948218  B40000200  Read-Ack    Status: 00000010 00000000
20:26:26.874915  T80000200  Read-Data   Status: 00000010 00000000
20:26:26.988274  B40000200  Read-Ack    Status: 00000010 00000000
20:26:27.876475  T80000200  Read-Data   Status: 00000010 00000000
20:26:27.971354  B40000200  Read-Ack    Status: 00000010 00000000
20:26:28.875915  T80000200  Read-Data   Status: 00000010 00000000
20:26:30.873724  T80000200  Read-Data   Status: 00000010 00000000
20:26:32.875223  T80000200  Read-Data   Status: 00000010 00000000
20:26:32.962608  B40000200  Read-Ack    Status: 00000010 00000000
20:26:34.870820  T80000200  Read-Data   Status: 00000010 00000000
20:26:34.931392  B40000200  Read-Ack    Status: 00000010 00000000
20:26:37.868812  T80000200  Read-Data   Status: 00000010 00000000
20:26:37.957582  B40000200  Read-Ack    Status: 00000010 00000000
20:26:39.868920  T80000200  Read-Data   Status: 00000010 00000000
20:26:39.994497  B40000200  Read-Ack    Status: 00000010 00000000
20:26:40.868627  T83000200  Read-Data   Status: 00000010 00000000
20:26:41.868241  T80000200  Read-Data   Status: 00000010 00000000
20:26:41.957854  B40000200  Read-Ack    Status: 00000010 00000000
20:26:42.868501  T80000200  Read-Data   Status: 00000010 00000000
20:26:42.947981  B40000200  Read-Ack    Status: 00000010 00000000
20:26:46.865285  T80001A00  Read-Data   Status: 00011010 00000000
20:26:47.866363  T80000200  Read-Data   Status: 00000010 00000000
20:26:47.939010  B40000200  Read-Ack    Status: 00000010 00000000
20:26:48.865938  T80000200  Read-Data   Status: 00000010 00000000
20:26:48.923878  B40000200  Read-Ack    Status: 00000010 00000000
20:26:49.862451  T80000200  Read-Data   Status: 00000010 00000000
20:26:50.863332  T80000200  Read-Data   Status: 00000010 00000000
20:26:50.963571  B40000200  Read-Ack    Status: 00000010 00000000
20:26:52.441113  T10010000  Write-Data  Control setpoint: 0.00
20:26:52.537672  BD0010000  Write-Ack   Control setpoint: 0.00
20:26:52.648848  T100E0000  Write-Data  Maximum relative modulation level: 0.00
20:26:54.948624  T80000200  Read-Data   Status: 00000010 00000000
20:26:56.861143  T80060200  Read-Data   Remote parameter flags: 00000010 00000000
Error 03: 	22684
Re: OTGW not working: where to start debugging
You appear to have many bit errors, but no error 04. That is quite surprising. Also surprising is that both sides (thermostat and boiler) show communication issues. Sometimes the boiler doesn't respond. But the thermostat also repeats messages a lot, which is usually a sign that it didn't receive the response. The first thing I would suggest to check is the power supply. There have been some problems with devices that were powered using a USB cable that gave a significant power drop. Make sure the 5V on the board really is reasonably close to 5V.
Other than that, just follow the relevant steps of the trouble shooting instructions.
Bobsled0935
thanks. I'll start with checking power next time I'm over there.