[Bug] Flapping CH enable bit in standalone mode
fox
Post by fox »
I received a brand new board from NodoShop and struggled a lot before succeeding to control my Central Heating.
I believe this is a bug. I want to share it in the hope it will be fixed.
I also found a way to get around it, it could be useful for other users! :)
Steps to reproduce
- Be in standalone mode (remove Thermostat from header)
- Have an empty list of Alternative Data IDs
- Try to make the boiler heat your house by using CS/CH serial commands
(Note that CS command is honored only for 1min before going back to CS=0. This is written in the doc but it took me time to understand this. So, you need to regularly send CS=x messages and send one CH=1 message.)
Expected behavior
The boiler should heat the house
Actual behavior
Boiler is never heating.
Analysis
The gateway is sending contradictory Status (ID 0) messages (master status). Sometimes it says it enables the CH bit, sometimes it says it disables the CH bit.
The boiler never even activates Central Heating because before it can do that, the gateway has already sent again a CH=0 to the boiler.
09:01:56.666493 R80000100 Read-Data Status (MsgID=0): 00000001 00000000
09:01:56.861462 B40000100 Read-Ack Status (MsgID=0): 00000001 00000000
09:01:57.660599 R80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:01:57.761334 B401932E6 Read-Ack Boiler water temperature (MsgID=25): 50.90
09:01:58.656872 R10015000 Write-Data Control setpoint (MsgID=1): 80.00
09:01:58.764957 BD0015000 Write-Ack Control setpoint (MsgID=1): 80.00
09:01:59.652308 R00000000 Read-Data Status (MsgID=0): 00000000 00000000
09:01:59.772792 BC0000000 Read-Ack Status (MsgID=0): 00000000 00000000
09:02:00.649589 R00110000 Read-Data Relative modulation level (MsgID=17): 0.00
09:02:00.774836 BC0110000 Read-Ack Relative modulation level (MsgID=17): 0.00
09:02:01.645980 R001B0000 Read-Data Outside temperature (MsgID=27): 0.00
09:02:01.779431 B601B0000 Data-Inv Outside temperature (MsgID=27): 0.00
09:02:02.644223 R801C0000 Read-Data Return water temperature (MsgID=28): 0.00
09:02:02.785102 B701C0000 Unk-DataId Return water temperature (MsgID=28): 0.00
09:02:03.812008 R900E6400 Write-Data Maximum relative modulation level (MsgID=14): 100.00
09:02:03.817862 B500E6400 Write-Ack Maximum relative modulation level (MsgID=14): 100.00
09:02:04.640376 R00000000 Read-Data Status (MsgID=0): 00000000 00000000
09:02:04.798870 BC0000000 Read-Ack Status (MsgID=0): 00000000 00000000
09:02:05.638310 R80000100 Read-Data Status (MsgID=0): 00000001 00000000
09:02:05.803047 B40000100 Read-Ack Status (MsgID=0): 00000001 00000000
09:02:06.636330 R80190000 Read-Data Boiler water temperature (MsgID=25): 0.00
09:02:06.809914 B401932CD Read-Ack Boiler water temperature (MsgID=25): 50.80
09:02:07.635943 R10015000 Write-Data Control setpoint (MsgID=1): 80.00
09:02:07.818106 BD0015000 Write-Ack Control setpoint (MsgID=1): 80.00
09:02:08.634461 R80380000 Read-Data DHW setpoint (MsgID=56): 0.00
09:02:08.823002 BC0383200 Read-Ack DHW setpoint (MsgID=56): 50.00
09:02:09.634351 R00390000 Read-Data Max CH water setpoint (MsgID=57): 0.00
09:02:09.733010 BC0395000 Read-Ack Max CH water setpoint (MsgID=57): 80.00
09:02:10.633089 R00000000 Read-Data Status (MsgID=0): 00000000 00000000
09:02:10.738061 BC0000000 Read-Ack Status (MsgID=0): 00000000 00000000
09:02:11.785176 R00120000 Read-Data CH water pressure (MsgID=18): 0.00
09:02:11.874188 B40120166 Read-Ack CH water pressure (MsgID=18): 1.40
It took time for me to understand what to do to make it work.
I noticed the messages sent in standalone mode are documented here:
https://otgw.tclcode.com/standalone.html#intro
They always occur in this order:
MsgID 0: Master and Slave Status flags
MsgID 25: Boiler flow water temperature
MsgID 1: Control Setpoint
UserDefined
MsgID 17: Relative Modulation Level
MsgID 27: Outside temperature
MsgID 28: Return water temperature
MsgID 14: Maximum relative modulation level setting
UserDefined
MsgID 56: DHW Setpoint
MsgID 57: Max CH water Setpoint
UserDefined
MsgID 18: Water pressure in CH circuit
When comparing my messages log with this list, we quickly see that correct Status messages (CH=1) are the Status messages in the list, and wrong ones with the bug (CH=0) are those replacing the UserDefined slots.
UserDefined slots are filled by the alternative ID list. But if the list is empty, it send a Status (ID0) message.
The bug is: when filling up a UserDefined slot, if the alternative ID list is empty, the Status sent is an all-zero status, not reflecting the real status the gateway wants to send.
Work Around
The way to get around that is to add a minimum of 1 alternative ID, to make sure that UserDefined slots will never attempt to send the buggy Status message.
Re: [Bug] Flapping CH enable bit in standalone mode
Thank you for your very detailed analysis. I will work on fixing this bug.
One small remark: Only one alternative ID should be needed. The OTGW goes through the list whenever it is scheduled to send a user defined message, and starts again from the top when the list is exhausted. It doesn't map each alternative ID to a specific slot in the sequence.
fox
Post by fox »
Thanks for your answer!
Yes, actually I had noticed the behavior like you say: only 1 alternative ID is enough. With 1 alternative ID, all UserDefined slots are filled with that.
I edited my post accordingly.
EP94
Post by EP94 »
Adding an alternative ID solved to "Flapping CH enable bit" problem; the "Central heating mode" stays enabled. However, the flame starts for a random short amount of time and then stops while the CH bit is still enabled and the water temperature is not yet at the desired setpoint. I'm sending the CS=xx command every 4 seconds. Is this also part of the bug or am i doing something wrong?
EP94
Post by EP94 »
Logging:
10:07:07.350526	GW: 1
10:07:07.357965
10:07:07.410501	MM: 70
10:07:07.423700
10:07:07.432640	CS: 66.00
10:07:07.441762
10:07:07.450374	CH: 1
10:07:07.457419
10:07:08.016940	R00780000	Read-Data 	Burner operation hours: 0
10:07:08.021182
10:07:08.126151	B40780288	Read-Ack  	Burner operation hours: 648
10:07:08.137545
10:07:09.091022	R00110000	Read-Data 	Relative modulation level: 0.00
10:07:09.099271
10:07:09.192846	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:07:09.200512
10:07:10.115927	R80310000	Read-Data 	Max CH setpoint boundaries: 0 0
10:07:10.131882
10:07:10.239153	B40315500	Read-Ack  	Max CH setpoint boundaries: 85 0
10:07:10.247091
10:07:11.139000	R801C0000	Read-Data 	Return water temperature: 0.00
10:07:11.139836
10:07:11.242272	BC01C1900	Read-Ack  	Return water temperature: 25.00
10:07:11.244778
10:07:12.166476	R900E4600	Write-Data	Maximum relative modulation level: 70.00
10:07:12.167534
10:07:12.274366	B500E4600	Write-Ack 	Maximum relative modulation level: 70.00
10:07:12.275892
10:07:13.205049	R80310000	Read-Data 	Max CH setpoint boundaries: 0 0
10:07:13.206022
10:07:13.330267	B40315500	Read-Ack  	Max CH setpoint boundaries: 85 0
10:07:13.330842
10:07:14.239096	R80000100	Read-Data 	Status: 00000001 00000000
10:07:14.239805
10:07:14.416515	B40000100	Read-Ack  	Status: 00000001 00000000
10:07:14.419703
10:07:15.276981	R80190000	Read-Data 	Boiler water temperature: 0.00
10:07:15.277988
10:07:15.375371	BC0191900	Read-Ack  	Boiler water temperature: 25.00
10:07:15.376923
10:07:16.311403	R10014200	Write-Data	Control setpoint: 66.00
10:07:16.313080
10:07:16.434611	BD0014200	Write-Ack 	Control setpoint: 66.00
10:07:16.435209
10:07:17.351612	R80380000	Read-Data 	DHW setpoint: 0.00
10:07:17.352324
10:07:17.487602	B40383C00	Read-Ack  	DHW setpoint: 60.00
10:07:17.489860
10:07:18.408563	R00390000	Read-Data 	Max CH water setpoint: 0.00
10:07:18.409273
10:07:18.543462	BC0394B00	Read-Ack  	Max CH water setpoint: 75.00
10:07:18.545290
10:07:19.433259	R007B0000	Read-Data 	DHW burner operation hours: 0
10:07:19.434731
10:07:19.535743	BC07B0055	Read-Ack  	DHW burner operation hours: 85
10:07:19.536670
10:07:20.464239	R00120000	Read-Data 	CH water pressure: 0.00
10:07:20.464646
10:07:20.574633	B401201CC	Read-Ack  	CH water pressure: 1.80
10:07:20.575204
10:07:21.498258	R80000100	Read-Data 	Status: 00000001 00000000
10:07:21.500506
10:07:21.632297	BC0000102	Read-Ack  	Status: 00000001 00000010
10:07:21.634119
10:07:22.537504	R80190000	Read-Data 	Boiler water temperature: 0.00
10:07:22.538870
10:07:22.709972	BC0191A00	Read-Ack  	Boiler water temperature: 26.00
10:07:22.710642
10:07:23.573848	R10014200	Write-Data	Control setpoint: 66.00
10:07:23.574563
10:07:23.668694	BD0014200	Write-Ack 	Control setpoint: 66.00
10:07:23.670058
10:07:24.608766	R00740000	Read-Data 	Burner starts: 0
10:07:24.609423
10:07:24.723891	B407411E5	Read-Ack  	Burner starts: 4581
10:07:24.725257
10:07:25.371866	CS: 66.00
10:07:25.372670
10:07:25.679690	R00110000	Read-Data 	Relative modulation level: 0.00
10:07:25.681159
10:07:25.779397	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:07:25.781010
10:07:26.702502	R007B0000	Read-Data 	DHW burner operation hours: 0
10:07:26.703122
10:07:26.835258	BC07B0055	Read-Ack  	DHW burner operation hours: 85
10:07:26.837030
10:07:27.727981	R801C0000	Read-Data 	Return water temperature: 0.00
10:07:27.730117
10:07:27.888655	BC01C1900	Read-Ack  	Return water temperature: 25.00
10:07:27.889143
10:07:28.374193	CS: 65.00
10:07:28.375406
10:07:28.761208	R900E4600	Write-Data	Maximum relative modulation level: 70.00
10:07:28.763017
10:07:28.887534	B500E4600	Write-Ack 	Maximum relative modulation level: 70.00
10:07:28.889805
10:07:29.799372	R00770000	Read-Data 	DHW burner starts: 0
10:07:29.799966
10:07:29.922979	BC0770AB2	Read-Ack  	DHW burner starts: 2738
10:07:29.924486
10:07:30.831894	R80000100	Read-Data 	Status: 00000001 00000000
10:07:30.832539
10:07:30.991106	BC0000102	Read-Ack  	Status: 00000001 00000010
10:07:30.993655
10:07:31.369512	CS: 66.00
10:07:31.370124
10:07:31.925103	R80190000	Read-Data 	Boiler water temperature: 0.00
10:07:31.925707
10:07:31.972184	BC0191900	Read-Ack  	Boiler water temperature: 25.00
10:07:31.973009
10:07:32.905766	R10014200	Write-Data	Control setpoint: 66.00
10:07:32.908011
10:07:33.051636	BD0014200	Write-Ack 	Control setpoint: 66.00
10:07:33.052368
10:07:33.973633	R80380000	Read-Data 	DHW setpoint: 0.00
10:07:33.974095
10:07:34.062903	B40383C00	Read-Ack  	DHW setpoint: 60.00
10:07:34.064691
10:07:34.384201	CS: 65.00
10:07:34.388117
10:07:34.980835	R00390000	Read-Data 	Max CH water setpoint: 0.00
10:07:34.981460
10:07:35.100036	BC0394B00	Read-Ack  	Max CH water setpoint: 75.00
10:07:35.101203
10:07:36.010402	R00780000	Read-Data 	Burner operation hours: 0
10:07:36.010957
10:07:36.159225	B40780288	Read-Ack  	Burner operation hours: 648
10:07:36.160803
10:07:37.044773	R00120000	Read-Data 	CH water pressure: 0.00
10:07:37.045458
10:07:37.147610	B401201CC	Read-Ack  	CH water pressure: 1.80
10:07:37.148722
10:07:37.386065	CS: 66.00
10:07:37.388815
10:07:38.067589	R80000100	Read-Data 	Status: 00000001 00000000
10:07:38.068134
10:07:38.201813	B4000010A	Read-Ack  	Status: 00000001 00001010
10:07:38.203498
10:07:39.106236	R80190000	Read-Data 	Boiler water temperature: 0.00
10:07:39.110103
10:07:39.253841	B40191D00	Read-Ack  	Boiler water temperature: 29.00
10:07:39.255098
10:07:40.143396	R10014200	Write-Data	Control setpoint: 66.00
10:07:40.144468
10:07:40.241489	BD0014200	Write-Ack 	Control setpoint: 66.00
10:07:40.243683
10:07:40.424797	CS: 65.00
10:07:40.425315
10:07:41.179612	R80310000	Read-Data 	Max CH setpoint boundaries: 0 0
10:07:41.182205
10:07:41.294397	B40315500	Read-Ack  	Max CH setpoint boundaries: 85 0
10:07:41.294972
10:07:42.221676	R00110000	Read-Data 	Relative modulation level: 0.00
10:07:42.222163
10:07:42.355656	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:07:42.356355
10:07:43.265096	R80310000	Read-Data 	Max CH setpoint boundaries: 0 0
10:07:43.265627
10:07:43.375228	CS: 66.00
10:07:43.376666
10:07:43.421773	B40315500	Read-Ack  	Max CH setpoint boundaries: 85 0
10:07:43.423004
10:07:44.315551	R801C0000	Read-Data 	Return water temperature: 0.00
10:07:44.316437
10:07:44.388128	BC01C1900	Read-Ack  	Return water temperature: 25.00
10:07:44.389102
10:07:45.339307	R900E4600	Write-Data	Maximum relative modulation level: 70.00
10:07:45.340731
10:07:45.442579	B500E4600	Write-Ack 	Maximum relative modulation level: 70.00
10:07:45.444734
10:07:46.371307	R007B0000	Read-Data 	DHW burner operation hours: 0
10:07:46.372690
10:07:46.413886	CS: 65.00
10:07:46.416187
10:07:46.498358	BC07B0055	Read-Ack  	DHW burner operation hours: 85
10:07:46.499083
10:07:47.413634	R80000100	Read-Data 	Status: 00000001 00000000
10:07:47.415010
10:07:47.572240	B4000010A	Read-Ack  	Status: 00000001 00001010
10:07:47.574090
10:07:48.444410	R80190000	Read-Data 	Boiler water temperature: 0.00
10:07:48.444854
10:07:48.617110	B40192200	Read-Ack  	Boiler water temperature: 34.00
10:07:48.618824
10:07:49.371885	CS: 66.00
10:07:49.373614
10:07:49.481230	R10014200	Write-Data	Control setpoint: 66.00
10:07:49.481905
10:07:49.640905	BD0014200	Write-Ack 	Control setpoint: 66.00
10:07:49.643677
10:07:50.517529	R80380000	Read-Data 	DHW setpoint: 0.00
10:07:50.518134
10:07:50.664963	B40383C00	Read-Ack  	DHW setpoint: 60.00
10:07:50.666901
10:07:51.576007	R00390000	Read-Data 	Max CH water setpoint: 0.00
10:07:51.577226
10:07:51.701965	BC0394B00	Read-Ack  	Max CH water setpoint: 75.00
10:07:51.702719
10:07:52.406638	CS: 65.00
10:07:52.412291
10:07:52.609655	R00740000	Read-Data 	Burner starts: 0
10:07:52.610238
10:07:52.753164	B407411E6	Read-Ack  	Burner starts: 4582
10:07:52.753765
10:07:53.633882	R00120000	Read-Data 	CH water pressure: 0.00
10:07:53.635850
10:07:53.742289	B401201CC	Read-Ack  	CH water pressure: 1.80
10:07:53.744804
10:07:54.661896	R80000100	Read-Data 	Status: 00000001 00000000
10:07:54.662417
10:07:54.794061	B4000010A	Read-Ack  	Status: 00000001 00001010
10:07:54.794940
10:07:55.374590	CS: 66.00
10:07:55.375831
10:07:55.704050	R80190000	Read-Data 	Boiler water temperature: 0.00
10:07:55.704640
10:07:55.850823	B40192100	Read-Ack  	Boiler water temperature: 33.00
10:07:55.852274
10:07:56.743260	R10014200	Write-Data	Control setpoint: 66.00
10:07:56.744726
10:07:56.834884	BD0014200	Write-Ack 	Control setpoint: 66.00
10:07:56.835618
10:07:57.777717	R007B0000	Read-Data 	DHW burner operation hours: 0
10:07:57.778547
10:07:57.886913	BC07B0055	Read-Ack  	DHW burner operation hours: 85
10:07:57.887482
10:07:58.377455	CS: 65.00
10:07:58.378089
10:07:58.813408	R00110000	Read-Data 	Relative modulation level: 0.00
10:07:58.814236
10:07:58.938341	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:07:58.939430
10:07:59.853315	R00770000	Read-Data 	DHW burner starts: 0
10:07:59.855210
10:07:59.994200	BC0770AB2	Read-Ack  	DHW burner starts: 2738
10:07:59.995507
10:08:00.904102	R801C0000	Read-Data 	Return water temperature: 0.00
10:08:00.904901
10:08:01.052004	BC01C1900	Read-Ack  	Return water temperature: 25.00
10:08:01.052885
10:08:01.385624	CS: 66.00
10:08:01.388326
10:08:01.931343	R900E4600	Write-Data	Maximum relative modulation level: 70.00
10:08:01.932465
10:08:02.034567	B500E4600	Write-Ack 	Maximum relative modulation level: 70.00
10:08:02.035409
10:08:02.958403	R00780000	Read-Data 	Burner operation hours: 0
10:08:02.958993
10:08:03.093151	B40780288	Read-Ack  	Burner operation hours: 648
10:08:03.093988
10:08:03.998318	R80000100	Read-Data 	Status: 00000001 00000000
10:08:04.003688
10:08:04.181434	B4000010A	Read-Ack  	Status: 00000001 00001010
10:08:04.182100
10:08:04.386500	CS: 65.00
10:08:04.388230
10:08:05.037694	R80190000	Read-Data 	Boiler water temperature: 0.00
10:08:05.038110
10:08:05.128166	BC0192000	Read-Ack  	Boiler water temperature: 32.00
10:08:05.128753
10:08:06.072902	R10014100	Write-Data	Control setpoint: 65.00
10:08:06.073429
10:08:06.184914	BD0014100	Write-Ack 	Control setpoint: 65.00
10:08:06.185381
10:08:07.109538	R80380000	Read-Data 	DHW setpoint: 0.00
10:08:07.110009
10:08:07.253453	B40383C00	Read-Ack  	DHW setpoint: 60.00
10:08:07.254530
10:08:07.388349	CS: 66.00
10:08:07.388820
10:08:08.160294	R00390000	Read-Data 	Max CH water setpoint: 0.00
10:08:08.161044
10:08:08.291056	BC0394B00	Read-Ack  	Max CH water setpoint: 75.00
10:08:08.292972
10:08:09.198714	R80310000	Read-Data 	Max CH setpoint boundaries: 0 0
10:08:09.199335
10:08:09.301668	B40315500	Read-Ack  	Max CH setpoint boundaries: 85 0
10:08:09.302308
10:08:10.226618	R00120000	Read-Data 	CH water pressure: 0.00
10:08:10.228827
10:08:10.328953	B401201CC	Read-Ack  	CH water pressure: 1.80
10:08:10.329522
10:08:10.373069	CS: 65.00
10:08:10.373664
10:08:11.255486	R00000000	Read-Data 	Status: 00000000 00000000
10:08:11.256073
10:08:11.387931	BC000000A	Read-Ack  	Status: 00000000 00001010
10:08:11.390128
10:08:12.291553	R80190000	Read-Data 	Boiler water temperature: 0.00
10:08:12.292520
10:08:12.475934	BC0192000	Read-Ack  	Boiler water temperature: 32.00
10:08:12.478051
10:08:13.331018	R10010000	Write-Data	Control setpoint: 0.00
10:08:13.332056
10:08:13.400278	GW: 1
10:08:13.401045
10:08:13.451968	MM: 70
10:08:13.452571
10:08:13.465614	CS: 66.00
10:08:13.469320
10:08:13.473153	BD0010000	Write-Ack 	Control setpoint: 0.00
10:08:13.477477
10:08:13.482028	CH: 1
10:08:13.485801
10:08:14.421020	R80310000	Read-Data 	Max CH setpoint boundaries: 0 0
10:08:14.422107
10:08:14.483058	B40315500	Read-Ack  	Max CH setpoint boundaries: 85 0
10:08:14.483691
10:08:15.402285	R00110000	Read-Data 	Relative modulation level: 0.00
10:08:15.402723
10:08:15.534312	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:08:15.535146
10:08:16.475589	R007B0000	Read-Data 	DHW burner operation hours: 0
10:08:16.477745
10:08:16.521791	GW: 1
10:08:16.522631
10:08:16.534338	MM: 70
10:08:16.539468
10:08:16.543894	CS: 66.00
10:08:16.548547
10:08:16.552627	CH: 1
10:08:16.556626
10:08:16.601468	BC07B0055	Read-Ack  	DHW burner operation hours: 85
10:08:16.603588
10:08:17.493065	R801C0000	Read-Data 	Return water temperature: 0.00
10:08:17.494841
10:08:17.589530	BC01C1900	Read-Ack  	Return water temperature: 25.00
10:08:17.593056
10:08:18.518800	R900E4600	Write-Data	Maximum relative modulation level: 70.00
10:08:18.531563
10:08:18.631087	B500E4600	Write-Ack 	Maximum relative modulation level: 70.00
10:08:18.631853
10:08:19.491490	GW: 1
10:08:19.493503
10:08:19.533291	MM: 70
10:08:19.535005
10:08:19.544709	CS: 66.00
10:08:19.548850
10:08:19.552840	CH: 1
10:08:19.556764
10:08:19.581487	R00740000	Read-Data 	Burner starts: 0
10:08:19.583488
10:08:19.683812	B407411E6	Read-Ack  	Burner starts: 4582
10:08:19.685703
10:08:20.593048	R80000100	Read-Data 	Status: 00000001 00000000
10:08:20.593908
10:08:20.747706	B40000100	Read-Ack  	Status: 00000001 00000000
10:08:20.750958
10:08:21.632107	R80190000	Read-Data 	Boiler water temperature: 0.00
10:08:21.633302
10:08:21.724846	B40191B00	Read-Ack  	Boiler water temperature: 27.00
10:08:21.726258
10:08:22.513626	CS: 66.00
10:08:22.514690
10:08:22.661863	R10014200	Write-Data	Control setpoint: 66.00
10:08:22.665887
10:08:22.778097	BD0014200	Write-Ack 	Control setpoint: 66.00
10:08:22.780076
10:08:23.698097	R80380000	Read-Data 	DHW setpoint: 0.00
10:08:23.700997
10:08:23.832146	B40383C00	Read-Ack  	DHW setpoint: 60.00
10:08:23.834955
10:08:24.761515	R00390000	Read-Data 	Max CH water setpoint: 0.00
10:08:24.768219
10:08:24.885611	BC0394B00	Read-Ack  	Max CH water setpoint: 75.00
10:08:24.889880
10:08:25.508933	CS: 65.00
10:08:25.514280
10:08:25.780541	R007B0000	Read-Data 	DHW burner operation hours: 0
10:08:25.782916
10:08:25.936663	BC07B0055	Read-Ack  	DHW burner operation hours: 85
10:08:25.939299
10:08:26.814288	R00120000	Read-Data 	CH water pressure: 0.00
10:08:26.815122
10:08:26.926075	B401201CC	Read-Ack  	CH water pressure: 1.80
10:08:26.927011
10:08:27.846937	R80000100	Read-Data 	Status: 00000001 00000000
10:08:27.848303
10:08:27.976298	BC0000102	Read-Ack  	Status: 00000001 00000010
10:08:27.980017
10:08:28.509221	CS: 66.00
10:08:28.510403
10:08:28.893772	R80190000	Read-Data 	Boiler water temperature: 0.00
10:08:28.900294
10:08:29.040388	BC0191900	Read-Ack  	Boiler water temperature: 25.00
10:08:29.044037
10:08:29.923835	R10014200	Write-Data	Control setpoint: 66.00
10:08:29.925879
10:08:30.020122	BD0014200	Write-Ack 	Control setpoint: 66.00
10:08:30.021701
10:08:30.957679	R00770000	Read-Data 	DHW burner starts: 0
10:08:30.959670
10:08:31.074606	BC0770AB2	Read-Ack  	DHW burner starts: 2738
10:08:31.076335
10:08:31.510820	CS: 65.00
10:08:31.513151
10:08:31.995546	R00110000	Read-Data 	Relative modulation level: 0.00
10:08:31.997724
10:08:32.124309	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:08:32.126792
10:08:33.049321	R00780000	Read-Data 	Burner operation hours: 0
10:08:33.050044
10:08:33.179902	B40780288	Read-Ack  	Burner operation hours: 648
10:08:33.181815
10:08:34.082039	R801C0000	Read-Data 	Return water temperature: 0.00
10:08:34.082873
10:08:34.184000	BC01C1900	Read-Ack  	Return water temperature: 25.00
10:08:34.185721
10:08:34.517926	CS: 66.00
10:08:34.519586
10:08:35.108957	R900E4600	Write-Data	Maximum relative modulation level: 70.00
10:08:35.109384
10:08:35.220008	B500E4600	Write-Ack 	Maximum relative modulation level: 70.00
10:08:35.220506
10:08:36.147276	R80310000	Read-Data 	Max CH setpoint boundaries: 0 0
10:08:36.148000
10:08:36.274382	B40315500	Read-Ack  	Max CH setpoint boundaries: 85 0
10:08:36.275217
10:08:37.186675	R80000100	Read-Data 	Status: 00000001 00000000
10:08:37.187229
10:08:37.348020	BC0000102	Read-Ack  	Status: 00000001 00000010
10:08:37.349950
10:08:37.508627	CS: 65.00
10:08:37.510457
10:08:38.220203	R80190000	Read-Data 	Boiler water temperature: 0.00
10:08:38.220971
10:08:38.319566	BC0191900	Read-Ack  	Boiler water temperature: 25.00
10:08:38.322217
10:08:39.254955	R10014100	Write-Data	Control setpoint: 65.00
10:08:39.256205
10:08:39.408036	BD0014100	Write-Ack 	Control setpoint: 65.00
10:08:39.409383
10:08:40.330903	R80380000	Read-Data 	DHW setpoint: 0.00
10:08:40.334491
10:08:40.430764	B40383C00	Read-Ack  	DHW setpoint: 60.00
10:08:40.431988
10:08:40.533527	CS: 66.00
10:08:40.534074
10:08:41.331741	R00390000	Read-Data 	Max CH water setpoint: 0.00
10:08:41.332747
10:08:41.479465	BC0394B00	Read-Ack  	Max CH water setpoint: 75.00
10:08:41.480168
10:08:42.378254	R80310000	Read-Data 	Max CH setpoint boundaries: 0 0
10:08:42.379039
10:08:42.534435	B40315500	Read-Ack  	Max CH setpoint boundaries: 85 0
10:08:42.535412
10:08:43.412203	R00120000	Read-Data 	CH water pressure: 0.00
10:08:43.414482
10:08:43.517062	CS: 65.00
10:08:43.517467
10:08:43.558839	B401201CC	Read-Ack  	CH water pressure: 1.80
10:08:43.559733
10:08:44.446504	R80000100	Read-Data 	Status: 00000001 00000000
10:08:44.450970
10:08:44.630279	BC0000102	Read-Ack  	Status: 00000001 00000010
10:08:44.631787
10:08:45.480307	R80190000	Read-Data 	Boiler water temperature: 0.00
10:08:45.481065
10:08:45.631123	BC0191900	Read-Ack  	Boiler water temperature: 25.00
10:08:45.631759
10:08:46.513149	CS: 66.00
10:08:46.513574
10:08:46.564140	R10014200	Write-Data	Control setpoint: 66.00
10:08:46.565076
10:08:46.611987	BD0014200	Write-Ack 	Control setpoint: 66.00
10:08:46.612777
10:08:47.555868	R007B0000	Read-Data 	DHW burner operation hours: 0
10:08:47.556385
10:08:47.700967	BC07B0055	Read-Ack  	DHW burner operation hours: 85
10:08:47.701567
10:08:48.592623	R00110000	Read-Data 	Relative modulation level: 0.00
10:08:48.593187
10:08:48.725725	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:08:48.726512
10:08:49.543781	CS: 65.00
10:08:49.544509
10:08:49.635748	R00740000	Read-Data 	Burner starts: 0
10:08:49.637287
10:08:49.776035	B407411E6	Read-Ack  	Burner starts: 4582
10:08:49.778202
10:08:50.665473	R801C0000	Read-Data 	Return water temperature: 0.00
10:08:50.666131
10:08:50.774486	BC01C1900	Read-Ack  	Return water temperature: 25.00
10:08:50.777455
10:08:51.700788	R900E4600	Write-Data	Maximum relative modulation level: 70.00
10:08:51.707610
10:08:51.815008	B500E4600	Write-Ack 	Maximum relative modulation level: 70.00
10:08:51.824034
10:08:52.513215	CS: 66.00
10:08:52.518455
10:08:52.758750	R007B0000	Read-Data 	DHW burner operation hours: 0
10:08:52.762617
10:08:52.884010	BC07B0055	Read-Ack  	DHW burner operation hours: 85
10:08:52.888740
10:08:53.788833	R80000100	Read-Data 	Status: 00000001 00000000
10:08:53.793684
10:08:53.934623	BC0000102	Read-Ack  	Status: 00000001 00000010
10:08:53.941885
Note: the toggling between CS 65 and CS 66 is me trying to find a workaround for the problem
Something is not working as intended. At 10:08:11.255486, the OTGW seems to have cleared the control setpoint.
Which firmware are you using? Then I can try to reproduce the situation.
EP94
Post by EP94 »
Thank you for the reply. I'm on firmware 5.5.
I can reproduce the issue with firmware 5.5. A fix I already made for firmware 5.6 (to be released soon) also resolves this problem.
EP94
Post by EP94 »
Thank you for the effort!
EP94
Post by EP94 »
Can confirm that the issue is fixed in version 5.6!