Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by hvxl »

You can easily check for yourself what happens by simply disconnecting your thermostat. But here are the gory details: The gateway will repeatedly send the following sequence of messages:
  • MsgID 0: Master and Slave Status flags
  • MsgID 25: Boiler flow water temperature
  • MsgID 1: Control Setpoint
  • UserDefined
  • MsgID 17: Relative Modulation Level
  • MsgID 27: Outside temperature
  • MsgID 28: Return water temperature
  • MsgID 14: Maximum relative modulation level setting
  • UserDefined
  • MsgID 0: Master and Slave Status flags
  • MsgID 25: Boiler flow water temperature
  • MsgID 1: Control Setpoint
  • MsgID 56: DHW Setpoint
  • MsgID 57: Max CH water Setpoint
  • UserDefined
  • MsgID 18: Water pressure in CH circuit
The "UserDefined" slots are filled from the list of alternatives. If the gateway learns (or was told via the UI command) that some of the other messages are not supported by the boiler, it will fill those slots with messages from the list of alternatives as well. If the list of alternatives is empty, it sends MsgID 0.

Note: This list is not set in stone and may change in the future.
Last edited by hvxl on Sun Dec 15, 2013 3:59 pm, edited 1 time in total.
Schelte
sappien
Starting Member
Starting Member
Posts: 38
Joined: Fri Oct 16, 2009 11:11 am
Location: Netherlands

Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by sappien »

Since I've flashed version 4 I don't get the Return water temperature.. (Remeha Calenta iSense)

00000000/00000000,20.00,00000011/00000011,100.00,0/0,19.00,0.00,1.10,20.70,29.80,0.00,17.80,0.00,65/40,66/20,50.00,30.00,4328,5264,2064,3520,618,684,5404,113

Bug? Or did I forget something?
hvxl
Senior Member
Senior Member
Posts: 2031
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by hvxl »

The iSense doesn't request the return water temperature. To obtain that information from the boiler you have to add MsgID 28 to the list of alternatives (AA=28). You probably did that in the past, but that setting is lost when you flash the firmware.
Schelte
sappien
Starting Member
Starting Member
Posts: 38
Joined: Fri Oct 16, 2009 11:11 am
Location: Netherlands

Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by sappien »

that rings a bell :D
Dickuk
Starting Member
Starting Member
Posts: 15
Joined: Fri Nov 02, 2012 10:31 pm

Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by Dickuk »

hvxl wrote:You can easily check for yourself what happens by simply disconnecting your thermostat. But here are the gory details: The gateway will repeatedly send the following sequence of messages:
  • MsgID 18: Water pressure in CH circuit
  • MsgID 0: Master and Slave Status flags
  • MsgID 25: Boiler flow water temperature
  • MsgID 1: Control Setpoint
  • UserDefined
  • MsgID 17: Relative Modulation Level
  • MsgID 27: Outside temperature
  • MsgID 28: Return water temperature
  • MsgID 14: Maximum relative modulation level setting
  • UserDefined
  • MsgID 0: Master and Slave Status flags
  • MsgID 25: Boiler flow water temperature
  • MsgID 1: Control Setpoint
  • MsgID 56: DHW Setpoint
  • MsgID 57: Max CH water Setpoint
  • UserDefined
The "UserDefined" slots are filled from the list of alternatives. If the gateway learns (or was told via the UI command) that some of the other messages are not supported by the boiler, it will fill those slots with messages from the list of alternatives as well. If the list of alternatives is empty, it sends MsgID 0.

Note: This list is not set in stone and may change in the future.
That's great, thanks.
nlrb
Member
Member
Posts: 78
Joined: Sun Nov 06, 2011 9:41 pm

Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by nlrb »

Hi Schelte,

Just tried firmware version 4.0a9, but after the following sequence of events it doesn't respond to commands anymore. Last command it responds to is LA=X. After that no response on the command LB=R. (Note that my code was written for FW 3.4, so it doesn't recognize the responses and prints an error - you can ignore that).

Code: Select all

OTG: Sent command PR=A
OTG: Incoming data = PR: A=OpenTherm Gateway 4.0a9
OTG: otgHandleVersion cmd = PR: A=OpenTherm Gateway 4.0a9, version = 4.0a9
OTG: Sent command PR=M
OTG: Sent command PR=L
OTG: Sent command PR=T
OTG: Sent command PR=V
OTG: Sent command PR=W
OTG: Incoming data = PR: M=G
OTG: Error for cmd: GW; expected [0|1] but got PR: M=G
OTG: Incoming data = PR: L=FXOMPC
OTG: Sent command LA=X
OTG: Sent command LB=R
OTG: Sent command LC=O
OTG: Sent command LD=E
OTG: Incoming data = PR: T=1
OTG: Sent command IT=0
OTG: Incoming data = PR: V=3
OTG: Incoming data = PR: W=A
OTG: Incoming data = LA: X
OTG: Error: expected OK but got LA: X
OTG: Incoming data = T80000200
hvxl
Senior Member
Senior Member
Posts: 2031
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by hvxl »

I don't know exactly what your program does. It looks like it bombards the gateway with commands without waiting for a response. Don't do that. The gateway is not designed to cope with that. If it worked with 3.4, that was just luck. Of course the gateway should not hang if you do and I will look into it, but you may still find that some commands could be ignored because the gateway was not ready yet.
Schelte
nlrb
Member
Member
Posts: 78
Joined: Sun Nov 06, 2011 9:41 pm

Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by nlrb »

Clear. It indeed worked with 3.4. But I'll implement a queue at the sending side.
hvxl
Senior Member
Senior Member
Posts: 2031
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by hvxl »

I managed to reproduce the problem you described. The problem was that the LED setting had to be written to EEPROM. That takes around 4 milliseconds. During that time the code didn't service the serial port. However, you continued to send more data which caused a buffer overrun. Subsequently the code failed to detect and handle that situation. So from that point onward the gateway would not receive any serial data anymore.

I checked the code of firmware 3.4 and confirmed that it would have the same problem. You say your script worked with 3.4. My guess is you only used it when the LEDs were already configured as you wanted. In that case the code detects no change is necessary and cleverly skips the EEPROM write operation.

Your method intrigued me, and now that responses can more easily be linked to their commands it makes sense to support it. So I started calculating: An EEPROM write takes 4 milliseconds. The shortest serial command is 4 characters + CR. Each character has a start and stop bit, adding up to a minimum of 50 bits for a command. At 9600 baud that takes 5.2 milliseconds. That means that the serial transmission of a possible next command takes long enough for the EEPROM write to complete.

So rather than just cleaning up when an overrun occurs, I decided it might be better to keep an eye on the serial interface while waiting for the EEPROM write to complete. As a result your bombardment of serial commands can now be handled by the gateway. The only time you need to allow the gateway some time is when you change the setback temperature. For that setting it may need to write 2 bytes to EEPROM, which takes 8 milliseconds.

But even if you immediately follow the SB command with another command, it will not hang up the serial interface. The command is just ignored, or leads to an error message. Sending a few LF characters after an SB command should provide the delay necessary for the gateway do its thing. Linefeeds are ignored by the gateway.

I can't think of any scenario that might still cause an overrun on the serial interface. But if it does happen, the code will now clean it up correctly.

These fixes are available in firmware 4.0a10.
Schelte
nlrb
Member
Member
Posts: 78
Joined: Sun Nov 06, 2011 9:41 pm

Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by nlrb »

hvxl wrote:I checked the code of firmware 3.4 and confirmed that it would have the same problem. You say your script worked with 3.4. My guess is you only used it when the LEDs were already configured as you wanted. In that case the code detects no change is necessary and cleverly skips the EEPROM write operation.
It worked with 3.4, but also my code checks the LED setting first before programming, as I didn't want to waste write cycles. Good to know that the FW already checks. But since I check, the LED write commands were only issued once and it worked in that case. But timing on the sender side could have been different (thread might have had some interruptions).
hvxl wrote:I can't think of any scenario that might still cause an overrun on the serial interface. But if it does happen, the code will now clean it up correctly.[/url]
Thanks for fixing. I've implemented a write queue anyway as I want the code to work with FW 3.4 as well.
hvxl wrote:These fixes are available in firmware 4.0a10.
Just tried this version and noticed that still some messages are prefixed with a counter.

Code: Select all

20:50:24.343355	R80750000	Read-Data 	CH pump starts: 0
20:50:24.492523	B70750000	Unk-DataId	CH pump starts: 0
20:50:24.494418	117AC0090000
20:50:24.862522	T80190000	Read-Data 	Boiler water temperature: 0.00
20:50:25.010853	BC0193C80	Read-Ack  	Boiler water temperature: 60.50
20:50:25.410116	T80640000	Read-Data 	Remote override function: 00000000
20:50:25.411552	R80760000	Read-Data 	DHW pump/valve starts: 0
20:50:25.565124	B70760000	Unk-DataId	DHW pump/valve starts: 0
20:50:25.566631	118A40640000
20:50:25.929178	T80000200	Read-Data 	Status: 00000010 00000000
20:50:26.076831	B40000200	Read-Ack  	Status: 00000010 00000000
20:50:26.462146	T80000200	Read-Data 	Status: 00000010 00000000
20:50:26.610259	B40000200	Read-Ack  	Status: 00000010 00000000
20:50:26.995309	T80000200	Read-Data 	Status: 00000010 00000000
20:50:27.150159	B40000200	Read-Ack  	Status: 00000010 00000000
20:50:27.528430	T80000200	Read-Data 	Status: 00000010 00000000
20:50:27.676016	B40000200	Read-Ack  	Status: 00000010 00000000
20:50:28.061934	T80000200	Read-Data 	Status: 00000010 00000000
20:50:28.209815	B40000200	Read-Ack  	Status: 00000010 00000000
20:50:28.594740	T10010A00	Write-Data	Control setpoint: 10.00
20:50:28.749823	BD0010A00	Write-Ack 	Control setpoint: 10.00
20:50:29.139441	T90101500	Write-Data	Room setpoint: 21.00
20:50:29.141287	R00770000	Read-Data 	DHW burner starts: 0
20:50:29.289846	BF0770000	Unk-DataId	DHW burner starts: 0
20:50:29.291556	119A50101500
20:50:29.661147	T80190000	Read-Data 	Boiler water temperature: 0.00
20:50:29.808778	BC0193C80	Read-Ack  	Boiler water temperature: 60.50
hvxl
Senior Member
Senior Member
Posts: 2031
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by hvxl »

nlrb wrote:It worked with 3.4, but also my code checks the LED setting first before programming, as I didn't want to waste write cycles.
You may want to check your code then. Your log shows the LEDs are reported as FXOMPC. So LED C is set to O, yet your code still issues a LC=O command.
nlrb wrote:Just tried this version and noticed that still some messages are prefixed with a counter.
You mention that as if it is something I should know about. I don't. Obviously it's hard for me to fix problems I don't know about. So please report these issues when you see them. It looks like these are the default alternatives that your boiler doesn't support. They are printed as the gateway deletes them from the list. So it should stop pretty quickly.
Schelte
nlrb
Member
Member
Posts: 78
Joined: Sun Nov 06, 2011 9:41 pm

Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by nlrb »

hvxl wrote:You may want to check your code then. Your log shows the LEDs are reported as FXOMPC. So LED C is set to O, yet your code still issues a LC=O command.
That was because in FW 3.4 the LED status was 4 characters and in FW 4.0 it is 6. So the strings didn't match and it executed a write.
nlrb wrote:You mention that as if it is something I should know about. I don't. Obviously it's hard for me to fix problems I don't know about. So please report these issues when you see them. It looks like these are the default alternatives that your boiler doesn't support. They are printed as the gateway deletes them from the list. So it should stop pretty quickly.
I thought that someone had already reported that (read that somewhere), but apparently I was mistaken. It indeed looks like the non supported alternatives.
hvxl
Senior Member
Senior Member
Posts: 2031
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by hvxl »

nlrb wrote:I thought that someone had already reported that (read that somewhere), but apparently I was mistaken. It indeed looks like the non supported alternatives.
Someone reported seeing outside temperatures. Although somewhat related, this is something else and requires its own fix.
Schelte
nlrb
Member
Member
Posts: 78
Joined: Sun Nov 06, 2011 9:41 pm

Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by nlrb »

I have the problem with 4.0a10 that the Max. relative modulation level gets set without using the MM command. The DD command seems to act as the MM command.

Code: Select all

17:51:29.250752	T9018164A	Write-Data	Room temperature: 22.29
17:51:29.399672	B5018164A	Write-Ack 	Room temperature: 22.29
17:51:29.602571	AA: 13
17:51:29.782649	T00000300	Read-Data 	Status: 00000011 00000000
17:51:29.938138	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:30.317180	T00000300	Read-Data 	Status: 00000011 00000000
17:51:30.463815	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:30.847333	T00000300	Read-Data 	Status: 00000011 00000000
17:51:30.997566	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:31.382513	T00000300	Read-Data 	Status: 00000011 00000000
17:51:31.539016	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:31.916714	T00000300	Read-Data 	Status: 00000011 00000000
17:51:32.062621	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:32.447964	T00000300	Read-Data 	Status: 00000011 00000000
17:51:32.596391	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:32.980015	T90012C00	Write-Data	Control setpoint: 44.00
17:51:33.136036	B50012C00	Write-Ack 	Control setpoint: 44.00
17:51:33.514835	T900E6400	Write-Data	Maximum relative modulation level: 100.00
17:51:33.661871	BF00E6400	Unk-DataId	Maximum relative modulation level: 100.00
17:51:34.044239	T80190000	Read-Data 	Boiler water temperature: 0.00
17:51:34.195537	BC0193080	Read-Ack  	Boiler water temperature: 48.50
17:51:34.580357	T00000300	Read-Data 	Status: 00000011 00000000
17:51:34.735415	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:35.114772	T00000300	Read-Data 	Status: 00000011 00000000
17:51:35.260827	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:35.646015	T00000300	Read-Data 	Status: 00000011 00000000
17:51:35.794460	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:36.180173	T00000300	Read-Data 	Status: 00000011 00000000
17:51:36.324754	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:36.715077	T00000300	Read-Data 	Status: 00000011 00000000
17:51:36.858656	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:37.249403	T00000300	Read-Data 	Status: 00000011 00000000
17:51:37.393390	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:37.784767	T00050000	Read-Data 	Application-specific flags: 00000000 0
17:51:37.932941	BC0050000	Read-Ack  	Application-specific flags: 00000000 0
17:51:38.316569	T90012C00	Write-Data	Control setpoint: 44.00
17:51:38.472439	B50012C00	Write-Ack 	Control setpoint: 44.00
17:51:38.851122	T80190000	Read-Data 	Boiler water temperature: 0.00
17:51:38.998430	BC0193080	Read-Ack  	Boiler water temperature: 48.50
17:51:39.383800	T00000300	Read-Data 	Status: 00000011 00000000
17:51:39.531687	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:39.916436	T00000300	Read-Data 	Status: 00000011 00000000
17:51:40.071347	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:40.451080	T00000300	Read-Data 	Status: 00000011 00000000
17:51:40.596954	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:40.982134	T00000300	Read-Data 	Status: 00000011 00000000
17:51:41.130246	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:41.514713	T00000300	Read-Data 	Status: 00000011 00000000
17:51:41.670180	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:42.049269	T80381400	Read-Data 	DHW setpoint: 20.00
17:51:42.195272	BC038001A	Read-Ack  	DHW setpoint: 0.10
17:51:42.579635	T00395000	Read-Data 	Max CH water setpoint: 80.00
17:51:42.732936	BC03950FF	Read-Ack  	Max CH water setpoint: 81.00
17:51:43.116114	T00395000	Read-Data 	Max CH water setpoint: 80.00
17:51:43.269485	BC03950FF	Read-Ack  	Max CH water setpoint: 81.00
17:51:43.664909	T00395000	Read-Data 	Max CH water setpoint: 80.00
17:51:43.808224	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
17:51:44.199266	T90012C00	Write-Data	Control setpoint: 44.00
17:51:44.352181	B50012C00	Write-Ack 	Control setpoint: 44.00
17:51:44.734126	T80190000	Read-Data 	Boiler water temperature: 0.00
17:51:44.890132	BC0193080	Read-Ack  	Boiler water temperature: 48.50
17:51:45.267593	T00000300	Read-Data 	Status: 00000011 00000000
17:51:45.413806	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:45.799718	T00000300	Read-Data 	Status: 00000011 00000000
17:51:45.947101	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:46.336764	T00110000	Read-Data 	Relative modulation level: 0.00
17:51:46.487079	BC0112E00	Read-Ack  	Relative modulation level: 46.00
17:51:46.864683	T00000300	Read-Data 	Status: 00000011 00000000
17:51:47.011710	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:47.397467	T00000300	Read-Data 	Status: 00000011 00000000
17:51:47.536274	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:47.933773	T90012C00	Write-Data	Control setpoint: 44.00
17:51:48.085138	B50012C00	Write-Ack 	Control setpoint: 44.00
17:51:48.464640	T00000300	Read-Data 	Status: 00000011 00000000
17:51:48.610963	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:48.995297	T80190000	Read-Data 	Boiler water temperature: 0.00
17:51:49.144604	BC01931FF	Read-Ack  	Boiler water temperature: 50.00
17:51:49.530178	T00000300	Read-Data 	Status: 00000011 00000000
17:51:49.683878	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:50.073657	T00120000	Read-Data 	CH water pressure: 0.00
17:51:50.076393	R800D0000	Read-Data 	Fault buffer entry: 0 0
17:51:50.221803	B400D0000	Read-Ack  	Fault buffer entry: 0 0
17:51:50.225097	AF0120000	Unk-DataId	CH water pressure: 0.00
17:51:50.595541	T00000300	Read-Data 	Status: 00000011 00000000
17:51:50.743404	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:51.129721	T00000300	Read-Data 	Status: 00000011 00000000
17:51:51.274016	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:51.664644	T00000300	Read-Data 	Status: 00000011 00000000
17:51:51.808475	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:52.199233	T00000300	Read-Data 	Status: 00000011 00000000
17:51:52.342437	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:52.733667	T90012C00	Write-Data	Control setpoint: 44.00
17:51:52.882160	B50012C00	Write-Ack 	Control setpoint: 44.00
17:51:53.266695	T00000300	Read-Data 	Status: 00000011 00000000
17:51:53.421878	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:53.800906	T80190000	Read-Data 	Boiler water temperature: 0.00
17:51:53.947652	BC0193100	Read-Ack  	Boiler water temperature: 49.00
17:51:54.332105	T00000300	Read-Data 	Status: 00000011 00000000
17:51:54.481091	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:54.866717	T00000300	Read-Data 	Status: 00000011 00000000
17:51:55.020818	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:55.399120	T00000300	Read-Data 	Status: 00000011 00000000
17:51:55.546727	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:55.931651	T00000300	Read-Data 	Status: 00000011 00000000
17:51:56.080012	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:56.464500	T00000300	Read-Data 	Status: 00000011 00000000
17:51:56.619772	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:56.999599	T00000300	Read-Data 	Status: 00000011 00000000
17:51:57.145834	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:57.530248	T00000300	Read-Data 	Status: 00000011 00000000
17:51:57.679559	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:58.064658	T90012C00	Write-Data	Control setpoint: 44.00
17:51:58.219251	B50012C00	Write-Ack 	Control setpoint: 44.00
17:51:58.597680	T00000300	Read-Data 	Status: 00000011 00000000
17:51:58.739041	BC000030A	Read-Ack  	Status: 00000011 00001010
17:51:59.147402	T80190000	Read-Data 	Boiler water temperature: 0.00
17:51:59.299299	B40193180	Read-Ack  	Boiler water temperature: 49.50
17:51:59.679091	T00000300	Read-Data 	Status: 00000011 00000000
17:51:59.824962	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:00.209316	T00000300	Read-Data 	Status: 00000011 00000000
17:52:00.358588	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:00.743486	T00000300	Read-Data 	Status: 00000011 00000000
17:52:00.889711	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:01.274870	T00000300	Read-Data 	Status: 00000011 00000000
17:52:01.418086	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:01.809495	T00000300	Read-Data 	Status: 00000011 00000000
17:52:01.958277	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:02.344795	T00000300	Read-Data 	Status: 00000011 00000000
17:52:02.488540	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:02.878274	T90012C00	Write-Data	Control setpoint: 44.00
17:52:03.023703	B50012C00	Write-Ack 	Control setpoint: 44.00
17:52:03.415285	T801C0000	Read-Data 	Return water temperature: 0.00
17:52:03.557783	BC01C0200	Read-Ack  	Return water temperature: 2.00
17:52:03.947724	T80190000	Read-Data 	Boiler water temperature: 0.00
17:52:04.097625	B40193180	Read-Ack  	Boiler water temperature: 49.50
17:52:04.482872	T00000300	Read-Data 	Status: 00000011 00000000
17:52:04.637284	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:05.016367	T00000300	Read-Data 	Status: 00000011 00000000
17:52:05.157372	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:05.548331	T00000300	Read-Data 	Status: 00000011 00000000
17:52:05.687753	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:06.079036	T00000300	Read-Data 	Status: 00000011 00000000
17:52:06.222815	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:06.616343	T00000300	Read-Data 	Status: 00000011 00000000
17:52:06.762942	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:07.148391	T00000300	Read-Data 	Status: 00000011 00000000
17:52:07.288017	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:07.679688	T10012B00	Write-Data	Control setpoint: 43.00
17:52:07.822494	BD0012B00	Write-Ack 	Control setpoint: 43.00
17:52:08.213526	T001B0000	Read-Data 	Outside temperature: 0.00
17:52:08.368048	B601B0000	Data-Inv  	Outside temperature: 0.00
17:52:08.370907	A401B0980	Read-Ack  	Outside temperature: 9.50
17:52:08.748031	T80190000	Read-Data 	Boiler water temperature: 0.00
17:52:08.896335	B40193180	Read-Ack  	Boiler water temperature: 49.50
17:52:09.281190	T00000300	Read-Data 	Status: 00000011 00000000
17:52:09.426978	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:09.812012	T00000300	Read-Data 	Status: 00000011 00000000
17:52:09.955944	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:10.346596	T00000300	Read-Data 	Status: 00000011 00000000
17:52:10.486831	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:10.877003	T00000300	Read-Data 	Status: 00000011 00000000
17:52:11.021950	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:11.412124	T00000300	Read-Data 	Status: 00000011 00000000
17:52:11.556239	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:11.946931	T00000300	Read-Data 	Status: 00000011 00000000
17:52:12.086284	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:12.477510	T00000300	Read-Data 	Status: 00000011 00000000
17:52:12.621506	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:13.011843	T10012B00	Write-Data	Control setpoint: 43.00
17:52:13.155353	BD0012B00	Write-Ack 	Control setpoint: 43.00
17:52:13.558044	T801A0000	Read-Data 	DHW temperature: 0.00
17:52:13.561537	R00110000	Read-Data 	Relative modulation level: 0.00
17:52:13.697557	BC0113300	Read-Ack  	Relative modulation level: 51.00
17:52:13.700433	A701A0000	Unk-DataId	DHW temperature: 0.00
17:52:14.108111	T80190000	Read-Data 	Boiler water temperature: 0.00
17:52:14.255023	BC01932FF	Read-Ack  	Boiler water temperature: 51.00
17:52:14.639885	T00000300	Read-Data 	Status: 00000011 00000000
17:52:14.785788	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:15.170443	T00000300	Read-Data 	Status: 00000011 00000000
17:52:15.314847	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:15.704481	T00000300	Read-Data 	Status: 00000011 00000000
17:52:15.854851	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:16.239489	T00000300	Read-Data 	Status: 00000011 00000000
17:52:16.395473	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:16.774364	T00000300	Read-Data 	Status: 00000011 00000000
17:52:16.920402	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:17.305130	T00000300	Read-Data 	Status: 00000011 00000000
17:52:17.454502	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:17.839505	T10012B00	Write-Data	Control setpoint: 43.00
17:52:17.994265	BD0012B00	Write-Ack 	Control setpoint: 43.00
17:52:18.383276	T00090000	Read-Data 	Remote override room setpoint: 0.00
17:52:18.386335	R00030000	Read-Data 	Slave configuration: 00000000 0
17:52:18.525450	B40031300	Read-Ack  	Slave configuration: 00010011 0
17:52:18.528339	AC0090000	Read-Ack  	Remote override room setpoint: 0.00
17:52:18.905196	T80190000	Read-Data 	Boiler water temperature: 0.00
17:52:19.053708	BC0193203	Read-Ack  	Boiler water temperature: 50.01
17:52:19.449174	T80640000	Read-Data 	Remote override function: 00000000
17:52:19.452073	R00110000	Read-Data 	Relative modulation level: 0.00
17:52:19.604887	BC0113500	Read-Ack  	Relative modulation level: 53.00
17:52:19.607748	AC0640001	Read-Ack  	Remote override function: 00000001
17:52:19.972372	T00000300	Read-Data 	Status: 00000011 00000000
17:52:20.119627	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:20.505147	T00000300	Read-Data 	Status: 00000011 00000000
17:52:20.653310	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:20.868048	DD: 13
17:52:21.036629	T00000300	Read-Data 	Status: 00000011 00000000
17:52:21.182928	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:21.567482	T00000300	Read-Data 	Status: 00000011 00000000
17:52:21.710976	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:22.102670	T00000300	Read-Data 	Status: 00000011 00000000
17:52:22.251861	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:22.636658	T10012B00	Write-Data	Control setpoint: 43.00
17:52:22.791459	BD0012B00	Write-Ack 	Control setpoint: 43.00
17:52:23.180741	T90101600	Write-Data	Room setpoint: 22.00
17:52:23.183732	R800D0000	Read-Data 	Fault buffer entry: 0 0
17:52:23.322572	B400D0000	Read-Ack  	Fault buffer entry: 0 0
17:52:23.325352	A50101600	Write-Ack 	Room setpoint: 22.00
17:52:23.701942	T80190000	Read-Data 	Boiler water temperature: 0.00
17:52:23.850786	B40193280	Read-Ack  	Boiler water temperature: 50.50
17:52:24.234747	T00000300	Read-Data 	Status: 00000011 00000000
17:52:24.390954	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:24.769434	T00000300	Read-Data 	Status: 00000011 00000000
17:52:24.916563	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:25.301989	T00000300	Read-Data 	Status: 00000011 00000000
17:52:25.450085	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:25.834170	T00000300	Read-Data 	Status: 00000011 00000000
17:52:25.989806	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:26.369277	T00000300	Read-Data 	Status: 00000011 00000000
17:52:26.515920	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:26.900105	T00000300	Read-Data 	Status: 00000011 00000000
17:52:27.049193	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:27.436261	T00000300	Read-Data 	Status: 00000011 00000000
17:52:27.589407	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:27.967339	T10012B00	Write-Data	Control setpoint: 43.00
17:52:28.108859	BD0012B00	Write-Ack 	Control setpoint: 43.00
17:52:28.500298	T9018165D	Write-Data	Room temperature: 22.36
17:52:28.639491	B5018165D	Write-Ack 	Room temperature: 22.36
17:52:29.048345	T80190000	Read-Data 	Boiler water temperature: 0.00
17:52:29.194680	B40193280	Read-Ack  	Boiler water temperature: 50.50
17:52:29.579651	T00000300	Read-Data 	Status: 00000011 00000000
17:52:29.728556	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:30.114939	T00000300	Read-Data 	Status: 00000011 00000000
17:52:30.268406	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:30.647201	T00000300	Read-Data 	Status: 00000011 00000000
17:52:30.792031	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:31.179739	T00000300	Read-Data 	Status: 00000011 00000000
17:52:31.329280	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:31.714228	T00000300	Read-Data 	Status: 00000011 00000000
17:52:31.867929	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:32.246995	T00000300	Read-Data 	Status: 00000011 00000000
17:52:32.394932	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:32.779887	T10012B00	Write-Data	Control setpoint: 43.00
17:52:32.927452	BD0012B00	Write-Ack 	Control setpoint: 43.00
17:52:33.325439	T900E6400	Write-Data	Maximum relative modulation level: 100.00
17:52:33.328147	R900E0D00	Write-Data	Maximum relative modulation level: 13.00
17:52:33.478752	BF00E0D00	Unk-DataId	Maximum relative modulation level: 13.00
17:52:33.481323	A500E6400	Write-Ack 	Maximum relative modulation level: 100.00
17:52:33.846444	T80190000	Read-Data 	Boiler water temperature: 0.00
17:52:33.992613	B40193280	Read-Ack  	Boiler water temperature: 50.50
17:52:34.377145	T00000300	Read-Data 	Status: 00000011 00000000
17:52:34.526362	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:34.912457	T00000300	Read-Data 	Status: 00000011 00000000
17:52:35.066195	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:35.444820	T00000300	Read-Data 	Status: 00000011 00000000
17:52:35.592047	BC000030A	Read-Ack  	Status: 00000011 00001010
17:52:35.977739	T00000300	Read-Data 	Status: 00000011 00000000
hvxl
Senior Member
Senior Member
Posts: 2031
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Opentherm Gateway 4.0 alpha/beta testers wanted

Post by hvxl »

nlrb wrote:I have the problem with 4.0a10 that the Max. relative modulation level gets set without using the MM command. The DD command seems to act as the MM command.
Confirmed. Any command consisting of two equal letters other than AA or TT will act as if the MM command was issued. Thanks for reporting. I will fix it for the next version.

You're doing an excellent job testing this thing. That bug could have stayed in there for years without me noticing. (You know there's no DD command, right?).
Schelte