Viessmann Vitovent 300 Opentherm Gateway

This Forum is about the Opentherm gateway (OTGW) from Schelte

Moderator: hvxl

Post Reply
michal.konopinski
Starting Member
Starting Member
Posts: 3
Joined: Mon Jan 13, 2014 10:36 am

Viessmann Vitovent 300 Opentherm Gateway

Post by michal.konopinski »

Hello

Yesterday i successfully build and run OpenthermGateway with ventilation only device: Viessmann Vitovent 300. The transmission log file is already uploaded to device matrix.
I found only one problem with timings in transmission from controller(thermostat?), something is wrong with last "bit" (see attached file with diagnostic). This results in Error 01(or Error 03 if ignore non-significant transitions) in transmission:(.It is possible to workaround this problem?
My second question, is there a possibility to override "Control setpoint V/H", like for heating?
In otmonitor for few msgId("Relative ventilation","Control setpoint V/H",... ) program shows only one byte of data but important information is in the second byte :).

Regards
Michał Konopiński

Edit:
Changing firmware to gateway-4.0b1.hex removes all transmission errors :)

Edit2:
I'm found some documents about this device:
http://www.viessmann.ua/content/dam/int ... VASR02.pdf
Attachments
otlog-20140112-part.zip
otmonitor log file
(119.83 KiB) Downloaded 366 times
otdiagnostic.zip
OTG diagnostic log
(2.11 KiB) Downloaded 369 times
hvxl
Senior Member
Senior Member
Posts: 2030
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Viessmann Vitovent 300 Opentherm Gateway

Post by hvxl »

I have added a VS command in firmware version 4.0b3, that will allow you to override the Ventilation Setpoint. Since I don't have a ventilation/heat-recovery system myself, I could only do limited testing. Please let me know whether the command works correctly.

I will fix the incorrect display of the V/H message ID's you mentioned in the next version of otmonitor.
Schelte
michal.konopinski
Starting Member
Starting Member
Posts: 3
Joined: Mon Jan 13, 2014 10:36 am

Re: Viessmann Vitovent 300 Opentherm Gateway

Post by michal.konopinski »

Thnk You,

it looks like it works fine, but how to cancel this command?

The descripion for VS command may be inappropriate in my case, the controller sends only 3 special values:
0 - Off
1 - Reduced ventilation
2 - Standard ventilation
3 - Maximum ventilation

the values for this modes can be read/write by "TSP setting V/H" command.

Regards
Michał Konopiński
Attachments
otlog-20140208.zip
new firmware log
(951 Bytes) Downloaded 372 times
hvxl
Senior Member
Senior Member
Posts: 2030
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Viessmann Vitovent 300 Opentherm Gateway

Post by hvxl »

You can cancel the override by specifying a non-numeric value, e.g.: VS=-, or VS=N.
Schelte
michal.konopinski
Starting Member
Starting Member
Posts: 3
Joined: Mon Jan 13, 2014 10:36 am

Re: Viessmann Vitovent 300 Opentherm Gateway

Post by michal.konopinski »

Yes, it works :)

I checked more closely :
0 - Off
1 - Reduced ventilation
2 - Standard ventilation
3,4,5 - Maximum ventilation
6-16 makes ventilation at 16%(probably technical limitation, ventilators can't go slower?)
17-100 makes ventilation at 17% to 100%
>100 makes 100%

For me, everything works even better than I expected, thank you very much :)

Regards
Michał
Post Reply

Return to “Opentherm Gateway Forum”