Honeywell wireless CMS927 Chronotherm
rouzi
Post by rouzi »
Actually I have a complex multi-zone heating system with 2 Heat pump , and a Gaz Boiler. The heating system is controlled and managed by a Honeywell W6560C1100 regulation module. To this module is attached a Honeywell wireless CMS927 Chronotherm through a Honeywell R8810 OT gateway.
As I have been building a home automation system, my needs are quiet simple: being able through an HTTP command to:
- Get the room temperature
- write the room temperature setpoint
- Eventually set the specific mode ( absent, economy, etc …)
After a long searches on the Internet I build up the following solution:
- OTGW that I soldered myself connected to
○ W6560C ( as a boiler)
○ The R8810 ( as a thermostat)
○ As Raspberry Pi, through USB
- Raspbery Pi
○ Connected through USB to the OTGW
○ Otmonitor running as daemon
○ Python script pulling the datafile generated by Otmonitor and pushing the desired info to the home automation system
○ Python script writing the TC command to the OTGW
○ Apache server with PHP for the HTTP commands
I successfully made the chain working, but I am facing the following issues:
- The room temperature is not updated by the Chronotherm, and is always at 20°
- The room set point is considered by OTGW but not by the chronotherm, and everything continues as if the override didn't happen.
I tried to interact with the boiler (W6560C ) with the CH and the CS command, and it is working fine, but it looks like nothing is being exchanged between the OTGW and the chronotherm.
BTW, changing the setpoint on the Chronotherm is reflected both on the OTGW and the boiler.
So I am assuming that the CMS927 Chronotherm is not compatible with OTGW as:
- it is not providing the room temperature to the OTGW, nor the boiler
- It is not accepting the override of the room setpoint
So I am now investigating in different approach of Investing in a CMT 937 or CMT907 Chronotherm, leaving behind the wireless part as this looks to work fine with both OTGW and the W6560C.
Before doing that, I would like to ensure that problems I am facing is not due to any issues with my build of the OTGW, I followed successfully the diagnostic process of the PCB.
below this message a logfile, would it be possible for some you to check it to see, if there is something to understand from it?
Kindly regards,
Rouzi
13:08:30.241203  T80000200  Read-Data   Status: 00000010 00000000
13:08:30.420495  B40000200  Read-Ack    Status: 00000010 00000000
13:08:30.779435  T80000200  Read-Data   Status: 00000010 00000000
13:08:30.897390  B40000200  Read-Ack    Status: 00000010 00000000
13:08:31.318973  T80000200  Read-Data   Status: 00000010 00000000
13:08:31.442436  B40000200  Read-Ack    Status: 00000010 00000000
13:08:31.854222  T00050000  Read-Data   Application-specific flags: 00000000 0
13:08:31.973783  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:08:32.393846  T80190000  Read-Data   Boiler water temperature: 0.00
13:08:32.514093  B401917CA  Read-Ack    Boiler water temperature: 23.79
13:08:32.934829  T10010A00  Write-Data  Control setpoint: 10.00
13:08:33.066296  BD0010A00  Write-Ack   Control setpoint: 10.00
13:08:33.470991  T80000200  Read-Data   Status: 00000010 00000000
13:08:33.590813  B40000200  Read-Ack    Status: 00000010 00000000
13:08:34.010757  T80000200  Read-Data   Status: 00000010 00000000
13:08:34.134365  B40000200  Read-Ack    Status: 00000010 00000000
13:08:34.552868  T80000200  Read-Data   Status: 00000010 00000000
13:08:34.669311  B40000200  Read-Ack    Status: 00000010 00000000
13:08:35.090278  T80000200  Read-Data   Status: 00000010 00000000
13:08:35.211806  B40000200  Read-Ack    Status: 00000010 00000000
13:08:35.630605  T80000200  Read-Data   Status: 00000010 00000000
13:08:35.750958  B40000200  Read-Ack    Status: 00000010 00000000
13:08:36.167613  T00050000  Read-Data   Application-specific flags: 00000000 0
13:08:36.289294  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:08:36.707435  T80190000  Read-Data   Boiler water temperature: 0.00
13:08:36.828842  BC01917C7  Read-Ack    Boiler water temperature: 23.78
13:08:37.255236  T10010A00  Write-Data  Control setpoint: 10.00
13:08:37.372873  BD0010A00  Write-Ack   Control setpoint: 10.00
13:08:37.794288  T80000200  Read-Data   Status: 00000010 00000000
13:08:37.912763  B40000200  Read-Ack    Status: 00000010 00000000
13:08:38.335204  T80000200  Read-Data   Status: 00000010 00000000
13:08:38.453524  B40000200  Read-Ack    Status: 00000010 00000000
13:08:38.873597  T80000200  Read-Data   Status: 00000010 00000000
13:08:38.993180  B40000200  Read-Ack    Status: 00000010 00000000
13:08:39.415390  T80000200  Read-Data   Status: 00000010 00000000
13:08:39.535735  B40000200  Read-Ack    Status: 00000010 00000000
13:08:39.955716  T80000200  Read-Data   Status: 00000010 00000000
13:08:40.074472  B40000200  Read-Ack    Status: 00000010 00000000
13:08:40.494337  T80000200  Read-Data   Status: 00000010 00000000
13:08:40.614048  B40000200  Read-Ack    Status: 00000010 00000000
13:08:41.035625  T80000200  Read-Data   Status: 00000010 00000000
13:08:41.153741  B40000200  Read-Ack    Status: 00000010 00000000
13:08:41.574753  T90800002  Write-Data  Message ID 128: 2
13:08:41.694865  B50800002  Write-Ack   Message ID 128: 2
13:08:42.119332  T80383C00  Read-Data   DHW setpoint: 60.00
13:08:42.238503  B40383C00  Read-Ack    DHW setpoint: 60.00
13:08:42.655942  T00395A00  Read-Data   Max CH water setpoint: 90.00
13:08:42.778884  BC0395A00  Read-Ack    Max CH water setpoint: 90.00
13:08:43.199695  T00050000  Read-Data   Application-specific flags: 00000000 0
13:08:43.317086  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:08:43.739344  T80190000  Read-Data   Boiler water temperature: 0.00
13:08:43.860206  B401917C5  Read-Ack    Boiler water temperature: 23.77
13:08:44.279939  T10010A00  Write-Data  Control setpoint: 10.00
13:08:44.400033  BD0010A00  Write-Ack   Control setpoint: 10.00
13:08:44.825491  T900E6400  Write-Data  Maximum relative modulation level: 100.00
13:08:44.943235  BF00E6400  Unk-DataId  Maximum relative modulation level: 100.00
13:08:45.362266  T90181400  Write-Data  Room temperature: 20.00
13:08:45.480493  BF0181400  Unk-DataId  Room temperature: 20.00
13:08:45.902218  T10101080  Write-Data  Room setpoint: 16.50
13:08:46.023277  B70101080  Unk-DataId  Room setpoint: 16.50
13:08:46.076826  AD0101080  Write-Ack   Room setpoint: 16.50
13:08:46.447673  T00050000  Read-Data   Application-specific flags: 00000000 0
13:08:46.564163  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:08:46.988935  T80190000  Read-Data   Boiler water temperature: 0.00
13:08:47.110226  BC01917C7  Read-Ack    Boiler water temperature: 23.78
13:08:47.528625  T10010A00  Write-Data  Control setpoint: 10.00
13:08:47.649131  BD0010A00  Write-Ack   Control setpoint: 10.00
13:08:48.065225  T801C0000  Read-Data   Return water temperature: 0.00
13:08:48.187408  B701C0000  Unk-DataId  Return water temperature: 0.00
13:08:48.610274  T00110000  Read-Data   Relative modulation level: 0.00
13:08:48.730582  BF0110000  Unk-DataId  Relative modulation level: 0.00
13:08:49.150660  T00090000  Read-Data   Remote override room setpoint: 0.00
13:08:49.269786  BF0090000  Unk-DataId  Remote override room setpoint: 0.00
13:08:49.325828  A40091900  Read-Ack    Remote override room setpoint: 25.00
13:08:49.689754  T801A0000  Read-Data   DHW temperature: 0.00
13:08:49.810299  B601ABAE2  Data-Inv    DHW temperature: -69.12
13:08:49.865427  AD004AA7D  Write-Ack   Remote command: 170 125
13:08:50.233059  T801A0000  Read-Data   DHW temperature: 0.00
13:08:50.357839  B601ABAE2  Data-Inv    DHW temperature: -69.12
13:08:50.778667  T001B0000  Read-Data   Outside temperature: 0.00
13:08:50.898898  B401B0FB0  Read-Ack    Outside temperature: 15.69
13:08:51.314294  T80000200  Read-Data   Status: 00000010 00000000
13:08:51.434668  B40000200  Read-Ack    Status: 00000010 00000000
13:08:51.855990  T00050000  Read-Data   Application-specific flags: 00000000 0
13:08:51.978660  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:08:52.400069  T80190000  Read-Data   Boiler water temperature: 0.00
13:08:52.519409  BC01917C2  Read-Ack    Boiler water temperature: 23.76
13:08:52.939113  T10010A00  Write-Data  Control setpoint: 10.00
13:08:53.061295  BD0010A00  Write-Ack   Control setpoint: 10.00
13:08:53.475847  T80130000  Read-Data   DHW flow rate: 0.00
13:08:53.596889  B70130000  Unk-DataId  DHW flow rate: 0.00
13:08:54.015555  T00120000  Read-Data   CH water pressure: 0.00
13:08:54.135869  BF0120000  Unk-DataId  CH water pressure: 0.00
13:08:54.562801  T10830000  Write-Data  Message ID 131: 0
13:08:54.679267  BD0830000  Write-Ack   Message ID 131: 0
13:08:55.092406  T80000200  Read-Data   Status: 00000010 00000000
13:08:55.212414  B40000200  Read-Ack    Status: 00000010 00000000
13:08:55.632716  T80000200  Read-Data   Status: 00000010 00000000
13:08:55.751398  B40000200  Read-Ack    Status: 00000010 00000000
13:08:56.204440  T80000200  Read-Data   Status: 00000010 00000000
13:08:56.296149  B40000200  Read-Ack    Status: 00000010 00000000
13:08:56.715343  T00050000  Read-Data   Application-specific flags: 00000000 0
13:08:56.834003  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:08:57.259692  T80190000  Read-Data   Boiler water temperature: 0.00
13:08:57.382007  BC01917C2  Read-Ack    Boiler water temperature: 23.76
13:08:57.802953  T10010A00  Write-Data  Control setpoint: 10.00
13:08:57.925594  BD0010A00  Write-Ack   Control setpoint: 10.00
13:08:58.345312  T80000200  Read-Data   Status: 00000010 00000000
13:08:58.460392  B40000200  Read-Ack    Status: 00000010 00000000
13:08:58.881893  T80000200  Read-Data   Status: 00000010 00000000
13:08:59.002406  B40000200  Read-Ack    Status: 00000010 00000000
13:08:59.422447  T80000200  Read-Data   Status: 00000010 00000000
13:08:59.542928  B40000200  Read-Ack    Status: 00000010 00000000
13:08:59.962592  T80000200  Read-Data   Status: 00000010 00000000
13:09:00.080514  B40000200  Read-Ack    Status: 00000010 00000000
13:09:00.503345  T80000200  Read-Data   Status: 00000010 00000000
13:09:00.626258  B40000200  Read-Ack    Status: 00000010 00000000
13:09:01.048845  T80000200  Read-Data   Status: 00000010 00000000
13:09:01.168064  B40000200  Read-Ack    Status: 00000010 00000000
13:09:01.588050  T80000200  Read-Data   Status: 00000010 00000000
13:09:01.707576  B40000200  Read-Ack    Status: 00000010 00000000
13:09:02.126197  T00050000  Read-Data   Application-specific flags: 00000000 0
13:09:02.246422  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:09:02.664251  T80190000  Read-Data   Boiler water temperature: 0.00
13:09:02.785726  BC01917C2  Read-Ack    Boiler water temperature: 23.76
13:09:03.204325  T10010A00  Write-Data  Control setpoint: 10.00
13:09:03.326073  BD0010A00  Write-Ack   Control setpoint: 10.00
13:09:03.751913  T80000200  Read-Data   Status: 00000010 00000000
13:09:03.862870  B40000200  Read-Ack    Status: 00000010 00000000
13:09:04.244428  Command: TT=30
13:09:04.270681  TT: 30.00
13:09:04.323506  T80000200  Read-Data   Status: 00000010 00000000
13:09:04.400826  B40000200  Read-Ack    Status: 00000010 00000000
13:09:04.452102  AD004AA96  Write-Ack   Remote command: 170 150
13:09:04.826627  T80000200  Read-Data   Status: 00000010 00000000
13:09:04.944290  B40000200  Read-Ack    Status: 00000010 00000000
13:09:05.366391  T80000200  Read-Data   Status: 00000010 00000000
13:09:05.486197  B40000200  Read-Ack    Status: 00000010 00000000
13:09:05.907175  T80000200  Read-Data   Status: 00000010 00000000
13:09:06.028093  B40000200  Read-Ack    Status: 00000010 00000000
13:09:06.448156  T00050000  Read-Data   Application-specific flags: 00000000 0
13:09:06.567101  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:09:06.985844  T80190000  Read-Data   Boiler water temperature: 0.00
13:09:07.108265  B401917C0  Read-Ack    Boiler water temperature: 23.75
13:09:07.527291  T10010A00  Write-Data  Control setpoint: 10.00
13:09:07.645588  BD0010A00  Write-Ack   Control setpoint: 10.00
13:09:08.064184  T80000200  Read-Data   Status: 00000010 00000000
13:09:08.185676  B40000200  Read-Ack    Status: 00000010 00000000
13:09:08.605035  T80000200  Read-Data   Status: 00000010 00000000
13:09:08.725840  B40000200  Read-Ack    Status: 00000010 00000000
13:09:09.144998  T80000200  Read-Data   Status: 00000010 00000000
13:09:09.263384  B40000200  Read-Ack    Status: 00000010 00000000
13:09:09.688064  T80000200  Read-Data   Status: 00000010 00000000
13:09:09.808396  B40000200  Read-Ack    Status: 00000010 00000000
13:09:10.228774  T80000200  Read-Data   Status: 00000010 00000000
13:09:10.348263  B40000200  Read-Ack    Status: 00000010 00000000
13:09:10.766667  T80000200  Read-Data   Status: 00000010 00000000
13:09:10.887424  B40000200  Read-Ack    Status: 00000010 00000000
13:09:11.308094  T80000200  Read-Data   Status: 00000010 00000000
13:09:11.427542  B40000200  Read-Ack    Status: 00000010 00000000
13:09:11.846803  T00050000  Read-Data   Application-specific flags: 00000000 0
13:09:11.965761  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:09:12.385536  T80190000  Read-Data   Boiler water temperature: 0.00
13:09:12.506617  B401917C0  Read-Ack    Boiler water temperature: 23.75
13:09:12.924640  T10010A00  Write-Data  Control setpoint: 10.00
13:09:13.050244  BD0010A00  Write-Ack   Control setpoint: 10.00
13:09:13.467806  T80000200  Read-Data   Status: 00000010 00000000
13:09:13.587753  B40000200  Read-Ack    Status: 00000010 00000000
13:09:14.006525  T80000200  Read-Data   Status: 00000010 00000000
13:09:14.125890  B40000200  Read-Ack    Status: 00000010 00000000
13:09:14.548459  T80000200  Read-Data   Status: 00000010 00000000
13:09:14.667260  B40000200  Read-Ack    Status: 00000010 00000000
13:09:15.091403  T80000200  Read-Data   Status: 00000010 00000000
13:09:15.211390  B40000200  Read-Ack    Status: 00000010 00000000
13:09:15.630571  T80000200  Read-Data   Status: 00000010 00000000
13:09:15.753036  B40000200  Read-Ack    Status: 00000010 00000000
13:09:16.172303  T80000200  Read-Data   Status: 00000010 00000000
13:09:16.290119  B40000200  Read-Ack    Status: 00000010 00000000
13:09:16.714885  T00050000  Read-Data   Application-specific flags: 00000000 0
13:09:16.833629  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:09:17.255308  T80190000  Read-Data   Boiler water temperature: 0.00
13:09:17.375049  B401917BD  Read-Ack    Boiler water temperature: 23.74
13:09:17.793360  T10010A00  Write-Data  Control setpoint: 10.00
13:09:17.914208  BD0010A00  Write-Ack   Control setpoint: 10.00
13:09:18.338753  T80000200  Read-Data   Status: 00000010 00000000
13:09:18.457397  B40000200  Read-Ack    Status: 00000010 00000000
13:09:18.878624  T80000200  Read-Data   Status: 00000010 00000000
13:09:18.998810  B40000200  Read-Ack    Status: 00000010 00000000
13:09:19.417173  T80000200  Read-Data   Status: 00000010 00000000
13:09:19.537979  B40000200  Read-Ack    Status: 00000010 00000000
13:09:19.957141  T80000200  Read-Data   Status: 00000010 00000000
13:09:20.078570  B40000200  Read-Ack    Status: 00000010 00000000
13:09:20.500094  T80000200  Read-Data   Status: 00000010 00000000
13:09:20.621889  B40000200  Read-Ack    Status: 00000010 00000000
13:09:21.037517  T80000200  Read-Data   Status: 00000010 00000000
13:09:21.160803  B40000200  Read-Ack    Status: 00000010 00000000
13:09:21.578393  T80000200  Read-Data   Status: 00000010 00000000
13:09:21.695955  B40000200  Read-Ack    Status: 00000010 00000000
13:09:22.113686  T00050000  Read-Data   Application-specific flags: 00000000 0
13:09:22.234546  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:09:22.654461  T80190000  Read-Data   Boiler water temperature: 0.00
13:09:22.775670  B401917BD  Read-Ack    Boiler water temperature: 23.74
13:09:23.197334  T10010A00  Write-Data  Control setpoint: 10.00
13:09:23.316904  BD0010A00  Write-Ack   Control setpoint: 10.00
13:09:23.743894  T80000200  Read-Data   Status: 00000010 00000000
13:09:23.859666  B40000200  Read-Ack    Status: 00000010 00000000
13:09:24.281182  T80000200  Read-Data   Status: 00000010 00000000
13:09:24.398939  B40000200  Read-Ack    Status: 00000010 00000000
13:09:24.816875  T80000200  Read-Data   Status: 00000010 00000000
13:09:24.936387  B40000200  Read-Ack    Status: 00000010 00000000
13:09:25.363099  T80000200  Read-Data   Status: 00000010 00000000
13:09:25.481783  B40000200  Read-Ack    Status: 00000010 00000000
13:09:25.905258  T80000200  Read-Data   Status: 00000010 00000000
13:09:26.027206  B40000200  Read-Ack    Status: 00000010 00000000
13:09:26.445986  T00050000  Read-Data   Application-specific flags: 00000000 0
13:09:26.562612  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:09:26.987566  T80190000  Read-Data   Boiler water temperature: 0.00
13:09:27.107368  B401917B8  Read-Ack    Boiler water temperature: 23.72
13:09:27.529319  T10010A00  Write-Data  Control setpoint: 10.00
13:09:27.646593  BD0010A00  Write-Ack   Control setpoint: 10.00
13:09:28.067688  T80000200  Read-Data   Status: 00000010 00000000
13:09:28.187534  B40000200  Read-Ack    Status: 00000010 00000000
13:09:28.606907  T80000200  Read-Data   Status: 00000010 00000000
13:09:28.725712  B40000200  Read-Ack    Status: 00000010 00000000
13:09:29.148326  T80000200  Read-Data   Status: 00000010 00000000
13:09:29.275365  B40000200  Read-Ack    Status: 00000010 00000000
13:09:29.684100  T80000200  Read-Data   Status: 00000010 00000000
13:09:29.805917  B40000200  Read-Ack    Status: 00000010 00000000
13:09:30.225962  T80000200  Read-Data   Status: 00000010 00000000
13:09:30.343829  B40000200  Read-Ack    Status: 00000010 00000000
13:09:30.763619  T80000200  Read-Data   Status: 00000010 00000000
13:09:30.883201  B40000200  Read-Ack    Status: 00000010 00000000
13:09:31.309816  T80000200  Read-Data   Status: 00000010 00000000
13:09:31.395108  Command: CH=1
13:09:31.422173  CH: 1
13:09:31.476854  B40000200  Read-Ack    Status: 00000010 00000000
13:09:31.850854  T00050000  Read-Data   Application-specific flags: 00000000 0
13:09:31.969210  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:09:32.391371  T80190000  Read-Data   Boiler water temperature: 0.00
13:09:32.511339  B401917B8  Read-Ack    Boiler water temperature: 23.72
13:09:32.930545  T10010A00  Write-Data  Control setpoint: 10.00
13:09:33.054102  BD0010A00  Write-Ack   Control setpoint: 10.00
13:09:33.468935  T80000200  Read-Data   Status: 00000010 00000000
13:09:33.589802  B40000200  Read-Ack    Status: 00000010 00000000
13:09:34.007038  T80000200  Read-Data   Status: 00000010 00000000
13:09:34.129758  B40000200  Read-Ack    Status: 00000010 00000000
13:09:34.548890  T80000200  Read-Data   Status: 00000010 00000000
13:09:34.668579  B40000200  Read-Ack    Status: 00000010 00000000
13:09:35.088563  T80000200  Read-Data   Status: 00000010 00000000
13:09:35.205974  B40000200  Read-Ack    Status: 00000010 00000000
13:09:35.629368  T80000200  Read-Data   Status: 00000010 00000000
13:09:35.749308  B40000200  Read-Ack    Status: 00000010 00000000
13:09:36.170454  T80000200  Read-Data   Status: 00000010 00000000
13:09:36.291825  B40000200  Read-Ack    Status: 00000010 00000000
13:09:36.707650  T00050000  Read-Data   Application-specific flags: 00000000 0
13:09:36.829029  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:09:37.248661  T80190000  Read-Data   Boiler water temperature: 0.00
13:09:37.367931  B401917B8  Read-Ack    Boiler water temperature: 23.72
13:09:37.784374  T10010A00  Write-Data  Control setpoint: 10.00
13:09:37.903568  BD0010A00  Write-Ack   Control setpoint: 10.00
13:09:38.328907  T80000200  Read-Data   Status: 00000010 00000000
13:09:38.449570  B40000200  Read-Ack    Status: 00000010 00000000
13:09:39.375721  T80000200  Read-Data   Status: 00000010 00000000
13:09:39.493731  B40000200  Read-Ack    Status: 00000010 00000000
13:09:39.915009  T80000200  Read-Data   Status: 00000010 00000000
13:09:40.034742  B40000200  Read-Ack    Status: 00000010 00000000
13:09:40.456825  T80000200  Read-Data   Status: 00000010 00000000
13:09:40.575420  B40000200  Read-Ack    Status: 00000010 00000000
13:09:40.993351  T80000200  Read-Data   Status: 00000010 00000000
13:09:41.115726  B40000200  Read-Ack    Status: 00000010 00000000
13:09:41.535819  T90800002  Write-Data  Message ID 128: 2
13:09:41.654507  B50800002  Write-Ack   Message ID 128: 2
13:09:42.075891  T80383C00  Read-Data   DHW setpoint: 60.00
13:09:42.194772  B40383C00  Read-Ack    DHW setpoint: 60.00
13:09:42.612987  T00395A00  Read-Data   Max CH water setpoint: 90.00
13:09:42.731157  BC0395A00  Read-Ack    Max CH water setpoint: 90.00
13:09:43.153680  T80000200  Read-Data   Status: 00000010 00000000
13:09:43.271887  B40000200  Read-Ack    Status: 00000010 00000000
13:09:43.696074  T00050000  Read-Data   Application-specific flags: 00000000 0
13:09:43.815925  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:09:44.234861  T80190000  Read-Data   Boiler water temperature: 0.00
13:09:44.356338  BC01917B5  Read-Ack    Boiler water temperature: 23.71
13:09:44.775666  T10010A00  Write-Data  Control setpoint: 10.00
13:09:44.894981  BD0010A00  Write-Ack   Control setpoint: 10.00
13:09:45.318173  T900E6400  Write-Data  Maximum relative modulation level: 100.00
13:09:45.387342  Command: CS=45
13:09:45.414940  CS: 45.00
13:09:45.469492  BF00E6400  Unk-DataId  Maximum relative modulation level: 100.00
13:09:45.861410  T90181400  Write-Data  Room temperature: 20.00
13:09:45.980978  BF0181400  Unk-DataId  Room temperature: 20.00
13:09:46.399918  T10101080  Write-Data  Room setpoint: 16.50
13:09:46.519555  B70101080  Unk-DataId  Room setpoint: 16.50
13:09:46.574015  AD0101080  Write-Ack   Room setpoint: 16.50
13:09:46.943146  T00050000  Read-Data   Application-specific flags: 00000000 0
13:09:47.057945  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:09:47.484114  T80190000  Read-Data   Boiler water temperature: 0.00
13:09:47.604152  BC01917B5  Read-Ack    Boiler water temperature: 23.71
13:09:48.022992  T10010A00  Write-Data  Control setpoint: 10.00
13:09:48.076127  R10012D00  Write-Data  Control setpoint: 45.00
13:09:48.142216  BD0012D00  Write-Ack   Control setpoint: 45.00
13:09:48.202162  AD0010A00  Write-Ack   Control setpoint: 10.00
13:09:48.565882  T801C0000  Read-Data   Return water temperature: 0.00
13:09:48.685644  B701C0000  Unk-DataId  Return water temperature: 0.00
13:09:49.104548  T00110000  Read-Data   Relative modulation level: 0.00
13:09:49.223476  BF0110000  Unk-DataId  Relative modulation level: 0.00
13:09:49.643348  T00090000  Read-Data   Remote override room setpoint: 0.00
13:09:49.761745  BF0090000  Unk-DataId  Remote override room setpoint: 0.00
13:09:49.814160  AC0091E00  Read-Ack    Remote override room setpoint: 30.00
13:09:50.184254  T00090000  Read-Data   Remote override room setpoint: 0.00
13:09:50.302589  BF0090000  Unk-DataId  Remote override room setpoint: 0.00
13:09:50.352137  AD004AA96  Write-Ack   Remote command: 170 150
13:09:50.726826  T00090000  Read-Data   Remote override room setpoint: 0.00
13:09:50.850287  BF0090000  Unk-DataId  Remote override room setpoint: 0.00
13:09:50.903892  AC0091E00  Read-Ack    Remote override room setpoint: 30.00
13:09:51.267192  T00090000  Read-Data   Remote override room setpoint: 0.00
13:09:51.384424  BF0090000  Unk-DataId  Remote override room setpoint: 0.00
13:09:51.436601  AD004AA96  Write-Ack   Remote command: 170 150
13:09:51.844009  T80000200  Read-Data   Status: 00000010 00000000
13:09:51.861596  R00000300  Read-Data   Status: 00000011 00000000
13:09:51.931751  BC0000300  Read-Ack    Status: 00000011 00000000
13:09:51.986385  A40000200  Read-Ack    Status: 00000010 00000000
13:09:52.344041  T00050000  Read-Data   Application-specific flags: 00000000 0
13:09:52.464209  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:09:52.885350  T80190000  Read-Data   Boiler water temperature: 0.00
13:09:53.006234  BC01917AE  Read-Ack    Boiler water temperature: 23.68
13:09:53.423699  T10010A00  Write-Data  Control setpoint: 10.00
13:09:53.474817  R10012D00  Write-Data  Control setpoint: 45.00
13:09:53.598202  BD0012D00  Write-Ack   Control setpoint: 45.00
13:09:53.644564  AD0010A00  Write-Ack   Control setpoint: 10.00
13:09:53.967454  T00090000  Read-Data   Remote override room setpoint: 0.00
13:09:54.087991  BF0090000  Unk-DataId  Remote override room setpoint: 0.00
13:09:54.141271  AC0091E00  Read-Ack    Remote override room setpoint: 30.00
13:09:54.505774  T801A0000  Read-Data   DHW temperature: 0.00
13:09:54.626091  B601ABAE2  Data-Inv    DHW temperature: -69.12
13:09:54.678777  AD004AA96  Write-Ack   Remote command: 170 150
13:09:55.048553  T801A0000  Read-Data   DHW temperature: 0.00
13:09:55.172439  B601ABAE2  Data-Inv    DHW temperature: -69.12
13:09:55.587063  T001B0000  Read-Data   Outside temperature: 0.00
13:09:55.708736  BC01B0FB8  Read-Ack    Outside temperature: 15.72
13:09:56.126852  T80130000  Read-Data   DHW flow rate: 0.00
13:09:56.245524  B70130000  Unk-DataId  DHW flow rate: 0.00
13:09:56.664098  T00050000  Read-Data   Application-specific flags: 00000000 0
13:09:56.783930  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:09:57.203696  T80190000  Read-Data   Boiler water temperature: 0.00
13:09:57.325169  BC01917AE  Read-Ack    Boiler water temperature: 23.68
13:09:57.741554  T10010A00  Write-Data  Control setpoint: 10.00
13:09:57.794620  R10012D00  Write-Data  Control setpoint: 45.00
13:09:57.861177  BD0012D00  Write-Ack   Control setpoint: 45.00
13:09:57.918750  AD0010A00  Write-Ack   Control setpoint: 10.00
13:09:58.281959  T00120000  Read-Data   CH water pressure: 0.00
13:09:58.403396  BF0120000  Unk-DataId  CH water pressure: 0.00
13:09:58.825116  T10830000  Write-Data  Message ID 131: 0
13:09:58.946034  BD0830000  Write-Ack   Message ID 131: 0
13:09:59.368259  T80000200  Read-Data   Status: 00000010 00000000
13:09:59.427893  R00000300  Read-Data   Status: 00000011 00000000
13:09:59.487890  BC000030A  Read-Ack    Status: 00000011 00001010
13:09:59.534010  A4000020A  Read-Ack    Status: 00000010 00001010
13:09:59.909190  T80000200  Read-Data   Status: 00000010 00000000
13:09:59.964487  R00000300  Read-Data   Status: 00000011 00000000
13:10:00.030962  BC000030A  Read-Ack    Status: 00000011 00001010
13:10:00.086023  A4000020A  Read-Ack    Status: 00000010 00001010
13:10:00.449055  T80000200  Read-Data   Status: 00000010 00000000
13:10:00.505304  R00000300  Read-Data   Status: 00000011 00000000
13:10:00.566945  BC000030A  Read-Ack    Status: 00000011 00001010
13:10:00.619772  A4000020A  Read-Ack    Status: 00000010 00001010
13:10:00.989368  T80000200  Read-Data   Status: 00000010 00000000
13:10:01.040748  R00000300  Read-Data   Status: 00000011 00000000
13:10:01.109705  BC000030A  Read-Ack    Status: 00000011 00001010
13:10:01.164837  A4000020A  Read-Ack    Status: 00000010 00001010
13:10:01.539604  T80000200  Read-Data   Status: 00000010 00000000
13:10:01.590804  R00000300  Read-Data   Status: 00000011 00000000
13:10:01.649351  BC000030A  Read-Ack    Status: 00000011 00001010
13:10:01.707798  A4000020A  Read-Ack    Status: 00000010 00001010
13:10:02.070741  T00050000  Read-Data   Application-specific flags: 00000000 0
13:10:02.190963  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:10:02.617645  T80190000  Read-Data   Boiler water temperature: 0.00
13:10:02.732560  BC01917AE  Read-Ack    Boiler water temperature: 23.68
13:10:03.152789  T10010A00  Write-Data  Control setpoint: 10.00
13:10:03.208110  R10012D00  Write-Data  Control setpoint: 45.00
13:10:03.274924  BD0012D00  Write-Ack   Control setpoint: 45.00
13:10:03.327925  AD0010A00  Write-Ack   Control setpoint: 10.00
13:10:03.691458  T80000200  Read-Data   Status: 00000010 00000000
13:10:03.750343  R00000300  Read-Data   Status: 00000011 00000000
13:10:03.811422  BC000030A  Read-Ack    Status: 00000011 00001010
13:10:03.864218  A4000020A  Read-Ack    Status: 00000010 00001010
13:10:04.232796  T80000200  Read-Data   Status: 00000010 00000000
13:10:04.286298  R00000300  Read-Data   Status: 00000011 00000000
13:10:04.353004  BC000030A  Read-Ack    Status: 00000011 00001010
13:10:04.409466  A4000020A  Read-Ack    Status: 00000010 00001010
13:10:04.773109  T80000200  Read-Data   Status: 00000010 00000000
13:10:04.826526  R00000300  Read-Data   Status: 00000011 00000000
13:10:04.893650  BC000030A  Read-Ack    Status: 00000011 00001010
13:10:04.949520  A4000020A  Read-Ack    Status: 00000010 00001010
13:10:05.316532  T80000200  Read-Data   Status: 00000010 00000000
13:10:05.362463  R00000300  Read-Data   Status: 00000011 00000000
13:10:05.435468  BC000030A  Read-Ack    Status: 00000011 00001010
13:10:05.487828  A4000020A  Read-Ack    Status: 00000010 00001010
13:10:05.860535  T80000200  Read-Data   Status: 00000010 00000000
13:10:05.912066  R00000300  Read-Data   Status: 00000011 00000000
13:10:05.981513  BC000030A  Read-Ack    Status: 00000011 00001010
13:10:06.033903  A4000020A  Read-Ack    Status: 00000010 00001010
13:10:06.400312  T80000200  Read-Data   Status: 00000010 00000000
13:10:06.452217  R00000300  Read-Data   Status: 00000011 00000000
13:10:06.518048  BC000030A  Read-Ack    Status: 00000011 00001010
13:10:06.569896  A4000020A  Read-Ack    Status: 00000010 00001010
13:10:06.943123  T00050000  Read-Data   Application-specific flags: 00000000 0
13:10:07.059204  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:10:07.478090  T80190000  Read-Data   Boiler water temperature: 0.00
13:10:07.601339  BC01917AE  Read-Ack    Boiler water temperature: 23.68
13:10:07.666976  Command: CS=0
13:10:07.701601  CS: 0.00
13:10:08.021936  T10010A00  Write-Data  Control setpoint: 10.00
13:10:08.141519  BD0010A00  Write-Ack   Control setpoint: 10.00
13:10:08.560524  T80000200  Read-Data   Status: 00000010 00000000
13:10:08.682757  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:09.099984  T80000200  Read-Data   Status: 00000010 00000000
13:10:09.275912  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:09.639733  T80000200  Read-Data   Status: 00000010 00000000
13:10:09.760700  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:10.179578  T80000200  Read-Data   Status: 00000010 00000000
13:10:10.297800  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:10.718887  T80000200  Read-Data   Status: 00000010 00000000
13:10:10.839227  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:11.256783  T80000200  Read-Data   Status: 00000010 00000000
13:10:11.379580  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:11.795966  T80000200  Read-Data   Status: 00000010 00000000
13:10:11.916243  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:12.335464  T00050000  Read-Data   Application-specific flags: 00000000 0
13:10:12.455053  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:10:12.875620  T80190000  Read-Data   Boiler water temperature: 0.00
13:10:12.995556  BC01917AE  Read-Ack    Boiler water temperature: 23.68
13:10:13.417096  T10010A00  Write-Data  Control setpoint: 10.00
13:10:13.537172  BD0010A00  Write-Ack   Control setpoint: 10.00
13:10:13.960577  T80000200  Read-Data   Status: 00000010 00000000
13:10:14.081952  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:14.504602  T80000200  Read-Data   Status: 00000010 00000000
13:10:14.626261  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:15.048823  T80000200  Read-Data   Status: 00000010 00000000
13:10:15.165938  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:15.585325  T80000200  Read-Data   Status: 00000010 00000000
13:10:15.703189  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:16.127046  T80000200  Read-Data   Status: 00000010 00000000
13:10:16.248434  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:16.667169  T80000200  Read-Data   Status: 00000010 00000000
13:10:16.788737  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:17.224919  T00050000  Read-Data   Application-specific flags: 00000000 0
13:10:17.328204  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:10:17.745461  T80190000  Read-Data   Boiler water temperature: 0.00
13:10:17.865592  BC01917AB  Read-Ack    Boiler water temperature: 23.67
13:10:18.290359  T10010A00  Write-Data  Control setpoint: 10.00
13:10:18.409178  BD0010A00  Write-Ack   Control setpoint: 10.00
13:10:18.828062  T80000200  Read-Data   Status: 00000010 00000000
13:10:18.949657  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:19.366832  T80000200  Read-Data   Status: 00000010 00000000
13:10:19.486668  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:19.907992  T80000200  Read-Data   Status: 00000010 00000000
13:10:20.028681  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:20.450363  T80000200  Read-Data   Status: 00000010 00000000
13:10:20.567689  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:20.989809  T80000200  Read-Data   Status: 00000010 00000000
13:10:21.105979  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:21.525983  T80000200  Read-Data   Status: 00000010 00000000
13:10:21.647446  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:22.069582  T80000200  Read-Data   Status: 00000010 00000000
13:10:22.192579  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:22.609900  T00050000  Read-Data   Application-specific flags: 00000000 0
13:10:22.733087  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:10:23.149262  T80190000  Read-Data   Boiler water temperature: 0.00
13:10:23.267788  BC01917AB  Read-Ack    Boiler water temperature: 23.67
13:10:23.691896  T10010A00  Write-Data  Control setpoint: 10.00
13:10:23.809500  BD0010A00  Write-Ack   Control setpoint: 10.00
13:10:24.231392  T80000200  Read-Data   Status: 00000010 00000000
13:10:24.349279  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:24.769802  T80000200  Read-Data   Status: 00000010 00000000
13:10:24.889798  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:25.313301  T80000200  Read-Data   Status: 00000010 00000000
13:10:25.433276  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:25.853135  T80000200  Read-Data   Status: 00000010 00000000
13:10:25.972909  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:26.396856  T80000200  Read-Data   Status: 00000010 00000000
13:10:26.516880  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:26.935650  T00050000  Read-Data   Application-specific flags: 00000000 0
13:10:27.054576  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:10:27.476831  T80190000  Read-Data   Boiler water temperature: 0.00
13:10:27.594036  BC01917A8  Read-Ack    Boiler water temperature: 23.66
13:10:28.017951  T10010A00  Write-Data  Control setpoint: 10.00
13:10:28.138977  BD0010A00  Write-Ack   Control setpoint: 10.00
13:10:28.564774  T80000200  Read-Data   Status: 00000010 00000000
13:10:28.684934  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:29.102002  T80000200  Read-Data   Status: 00000010 00000000
13:10:29.221516  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:29.643840  T80000200  Read-Data   Status: 00000010 00000000
13:10:29.761780  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:30.186353  T80000200  Read-Data   Status: 00000010 00000000
13:10:30.303271  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:30.727112  T80000200  Read-Data   Status: 00000010 00000000
13:10:30.845775  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:31.269374  T80000200  Read-Data   Status: 00000010 00000000
13:10:31.391220  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:31.809260  T80000200  Read-Data   Status: 00000010 00000000
13:10:31.931547  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:32.354167  T00050000  Read-Data   Application-specific flags: 00000000 0
13:10:32.474112  BC0050000  Read-Ack    Application-specific flags: 00000000 0
13:10:32.900247  T80190000  Read-Data   Boiler water temperature: 0.00
13:10:33.018077  B401917A6  Read-Ack    Boiler water temperature: 23.65
13:10:33.439349  T10010A00  Write-Data  Control setpoint: 10.00
13:10:33.558865  BD0010A00  Write-Ack   Control setpoint: 10.00
13:10:33.983312  T80000200  Read-Data   Status: 00000010 00000000
13:10:34.102871  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:34.523841  T80000200  Read-Data   Status: 00000010 00000000
13:10:34.644247  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:35.060725  T80000200  Read-Data   Status: 00000010 00000000
13:10:35.181412  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:35.602763  T80000200  Read-Data   Status: 00000010 00000000
13:10:35.721549  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:36.141435  T80000200  Read-Data   Status: 00000010 00000000
13:10:36.261382  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:36.683534  T80000200  Read-Data   Status: 00000010 00000000
13:10:36.799031  B4000020A  Read-Ack    Status: 00000010 00001010
13:10:37.218706  T00050000  Read-Data   Application-specific flags: 00000000 0
13:10:37.336376  BC0050000  Read-Ack    Application-specific flags: 00000000 0
Re: Honeywell wireless CMS927 Chronotherm
The gateway appears to be under the impression that the attached thermostat is a Remeha Celcia 20. As a result it doesn't handle the room override setpoint procedure entirely correctly. Did you ever issue an FT=C command? If so, send an FT=D command to make it operate correctly for your thermostat again. I'm not promising that the setpoint override will work then, but at least what it's doing now is not right.
rouzi
Post by rouzi »
Well thanks a lot for taking the time to read though my post.
I have tried almost all the command, so it is quiet possible that I issued the command an FT=C command.
As suggested, I issued the FT=D command.
From what I see, nothing really changed
Before doing anything I had on the OTmonitor
- Outside temperature: 21.07 ( this is right)
- Room temperature: 20 ( this value has been always unchanged, despite the thermostat is displaying 24°)
- Room setpoint: 20 (this is right, the same value than the thermostat
- Remote override room : 0
1) set room setpoint with the Thermostat at 16°
The Otmonitor showed:
- Outside temperature: 21.14 ( this is right)
- Room temperature: 20 ( unchanged)
- Room setpoint: 16
- Remote override room setpoint: 0
2) issued the TC=26
logs:
17:24:46.877370 Command: TC=26
17:24:46.903663 TC: 26.00
2 min later the Otmonitor showed:
- Outside temperature: 21.17 ( this is right)
- Room setpoint: 16
- Remote override room setpoint: 26
logs:
17:25:41.549471 T00090000 Read-Data Remote override room setpoint: 0.00
17:25:41.669173 BF0090000 Unk-DataId Remote override room setpoint: 0.00
17:25:41.720380 A40091A00 Read-Ack Remote override room setpoint: 26.00
17:25:42.089073 T00090000 Read-Data Remote override room setpoint: 0.00
17:25:42.208371 BF0090000 Unk-DataId Remote override room setpoint: 0.00
17:25:42.264466 A40091A00 Read-Ack Remote override room setpoint: 26.00
17:25:42.627241 T00090000 Read-Data Remote override room setpoint: 0.00
17:25:42.745978 BF0090000 Unk-DataId Remote override room setpoint: 0.00
17:25:42.804023 A40091A00 Read-Ack Remote override room setpoint: 26.00
5 minutes later
- Room setpoint: 16
the logs showed:
17:29:42.528581 BF0110000 Unk-DataId Relative modulation level: 0.00
17:29:42.948991 T00090000 Read-Data Remote override room setpoint: 0.00
17:29:43.067276 BF0090000 Unk-DataId Remote override room setpoint: 0.00
17:29:43.119330 AC0090000 Read-Ack Remote override room setpoint: 0.00
17:29:43.491572 T00090000 Read-Data Remote override room setpoint: 0.00
17:29:43.608753 BF0090000 Unk-DataId Remote override room setpoint: 0.00
17:29:43.662054 AC0090000 Read-Ack Remote override room setpoint: 0.00
17:29:44.029981 T00090000 Read-Data Remote override room setpoint: 0.00
17:29:44.147944 BF0090000 Unk-DataId Remote override room setpoint: 0.00
17:29:44.208480 AC0090000 Read-Ack Remote override room setpoint: 0.00
Does this shows a normal gateway operations? Should I conclude that the Gateway is just running as it is supposed, and that the CMS927, does simply don't accept the remote override?
Many thanks,
Rouzi
That looks better, in the sense that the gateway now sends the correct messages. If the thermostat then doesn't react to the setpoint override, the gateway gives up after a while. I'm afraid the conclusion now has to be that setpoint override doesn't work with your thermostat.
rouzi
Post by rouzi »
Thanks a lot for your reply.
I think that now I will buy a new chronotherm, (and sell my CMT927RF!)
While looking on the supported thermostats: http://otgw.tclcode.com/matrix.cgi#thermostats
I saw that the Honeywell Chronotherm Touch Modulation TH8200M1003 is well supported
http://shop.kamerthermostaat.com/epages ... H8200M1003
before ordering, I wanted to check if somebody has been using this Chronotherm, and if he can confirm that the override room setpoint is working.
I would be also keen if some could recommand any other modulation thermostat.
Rouzi
i have that one and is working good, i can also set the outside temp on the display.
rouzi
Post by rouzi »
Thank you.:)
I will order it and tell you if it is working.
Would that be a positive contribution if I post some of my logs, or upload them somewhere, as on the boiler side ( the honeywell W6560C ) is rather working fine?
Rouzi
Logs for any combination of thermostat and boiler that has not been posted before are very welcome at http://otgw.tclcode.com/equipment.html.
Perhaps I should also start a new topic where people can report their experiences with thermostats for the benefit of people who are trying to decide which thermostat to get.
rouzi
Post by rouzi »
OK I will post my logs to http://otgw.tclcode.com/equipment.html
I received today my Honeywell Chronotherm touch modulation
Spend a couple of hours to install it. And everything is working great! the room temperature, and the override. Great!
thanks for your help and advise.
Still one big issu!
it looks that this thermostat has been buidl only for the Netherland! the Manual, the menus on the touch screen etc ... is only in dutch!
It tooks me some google translate to make it work. Mywife and I should start learning Dutch ;)
bwired,
any idea where to get an english manuel? an to change the menu lauguage?
Rouzi