I have built a Open Gateway kit and all the (not connected boiler and thermostat) tests were succesfull.
When I connected only the thermostat (Honeywell Chronotherm Vision modulation) the display comes up with connection error (aansluitfout).
The thermostat supply is in accordance with spec (6.7 V).

Running diagnostic (V1.1) with only thermostat connected give for

test 2 a lot of numbers
00030000 Read-Data Slave configuration: 00000000 0
510,1004,508,500,508,500,509,499,509,499,508,500,508,500,509,499,511,499,509,499,509,500,508,500,509,500,508,500,1012,500,509,1006,508,499,509,499,508,499,509,499,509,500,509,499,509,500,511,499,509,499,509,499,509,500,509,499,509,499,509,500,508,500,1007.

Enter test number: 5
Thermostat: 0.79, 2.12
Boiler: 0.00
Reference: 1.22

Anyone an idea were to look or what to do

regards
Piet
pga_nitwit
Starting Member
Starting Member
Posts: 2
Joined: Thu Oct 06, 2016 9:34 pm

Re: Thermostat connection error

Post by pga_nitwit »

by connecting the boiler too the connection error disappeared and there was a normal view on the display.

So error solved continue with testing the next steps.

rgds

Piet
hvxl
Senior Member
Senior Member
Posts: 2035
Joined: Sat Jun 05, 2010 11:59 am
Contact:

Re: Thermostat connection error

Post by hvxl »

There was no error. Everything you reported was exactly as expected.