time changing on chronotherm 4
arnoldg
Post by arnoldg »
I have a chronotherm 4 connected to my openthermgateway and know the time on the chronotherm is changing several times a day.
Why is this and what can i do to prevent it.
Re: time changing on chronotherm 4
Is someone or something sending bad SC commands to the gateway?
Can you provide a otmonitor log for a period covering such an event?
arnoldg
Post by arnoldg »
Well at this time there is nothing connected to the otg so there aren't send any signals from the otg to the thermostate or boiler.
I will hook up a computer to log the data packets.
adegoeij
Post by adegoeij »
I am experiencing the same issue.
By chronotherm 4 (CMT8851M100) time is going back to 00:00 regularly.
My setup is this:
Boiler: AWB 3HR23T
Thermostat: Honeywell Chronotherm IV (CMT8851M100)
Opentherm-GW USB interface connected to Raspberry Pi with rasbian and otmonitor(ARM)
otmonitor is setup in relay mode and Domiticz setup at another Pi reads the status via the relay.
I have the logfile enable and sofar i did not see any SC command to set the time (logging enable since a few hours)
But i will continue monitoring/logging and get back
Same question goes for you then: Can you provide a otmonitor log for a period covering such an event?
Tomas
Post by Tomas »
I have a very similar issue with same model Chronotherm 4 (T8851M1000), the clock does not work well when connected to the Opentherm Gateway. In my case it does not reset fully back to 00:00 but it runs far slower than it should be. After some research I think this log describes the issue:
09:24:50.089909	T10142918	Write-Data	Day of week and time of day: Mon 09:24
09:24:50.148684	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
09:24:50.195107	AD0142918	Write-Ack 	Day of week and time of day: Mon 09:24
09:25:31.057034	T10142918	Write-Data	Day of week and time of day: Mon 09:24
09:25:31.150066	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
09:25:31.154009	AD0142918	Write-Ack 	Day of week and time of day: Mon 09:24
09:26:31.093830	T90142919	Write-Data	Day of week and time of day: Mon 09:25
09:26:31.144204	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
09:26:31.211638	A50142919	Write-Ack 	Day of week and time of day: Mon 09:25
09:27:52.075767	T9014291A	Write-Data	Day of week and time of day: Mon 09:26
09:27:52.167749	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
09:27:52.168644	A5014291A	Write-Ack 	Day of week and time of day: Mon 09:26
09:28:53.059286	T1014291B	Write-Data	Day of week and time of day: Mon 09:27
09:28:53.150881	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
09:28:53.151476	AD014291B	Write-Ack 	Day of week and time of day: Mon 09:27
09:29:43.078857	T1014291B	Write-Data	Day of week and time of day: Mon 09:27
09:29:43.171775	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
09:29:43.172409	AD014291B	Write-Ack 	Day of week and time of day: Mon 09:27
Looking at the display, the thermostat resets the time to the value received in the Write-Ack message, which is a time with hours/minutes only. So when the clock of the thermostat is at 09:24:50 when sending the message, it receives an ACK with "09:24" in it and will reset the clock to "09:24:00". Then some time later it will send another message, if that other message is less than 1 minute after the previous (as is the case in the log at 09:25:31) then the internal clock will now be 09:24:31 and it will receive another ACK with "09:24" again resetting the thermostat clock to "09:24:00". Which causes the clock in the thermostat to quickly fall behind the correct time.
To confirm this theory I check with the gateway in monitoring mode. In that case the boiler responds with "Unk-DataId" only, and then the thermostat clock keeps counting time correctly.
I think the solution is to adjust the gateway firmware to only send a Write-Ack with time value in case an "SC" command has been received in the last 61 seconds.
I never experienced this behavior when I was using the Chronotherm Modulation (I assume that's what you are referring to, because the Chronotherm 4 is an on/off thermostat). But I mostly used to send the current time to the OTGW. With that method, the clock of the thermostat was accurate to the second after a while.
Looking back at my old logs, I see that my Chronotherm Modulation would send MsgID 20 at intervals of 1 minute, or just slightly longer. I guess that would prevent the issue from ever happening. But as I mentioned, the clock used to be accurate to the second when I sent the time. If the seconds would be reset to 0 upon receiving the response, I would expect that it would have been up to one minute behind.
So, I'm wondering why your Chronotherm Modulation is requesting MsgID 20 at more irregular intervals than mine did. Does something happen that causes it to start its message sequence over? Understandably you filtered the log you provided, but I would really like to take a look at a full log covering this slowing of the clock.
Tomas
Post by Tomas »
I've created a longer log of about 10 minutes, the time was correct within ~5 seconds at 10:30 when I switched from monitor to gateway mode and it ended up behind by 4 minutes at 10:40. The log below is shortened to stay within the maximum post size of the forum, but here is the full log: https://pastebin.com/GBFBLbMe
10:30:23.507578	GW: 1
10:30:23.883507	T80190000	Read-Data 	Boiler water temperature: 0.00
10:30:24.864470	T80190000	Read-Data 	Boiler water temperature: 0.00
10:30:25.893651	T80190000	Read-Data 	Boiler water temperature: 0.00
10:30:26.018420	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:30:26.875499	T10010A00	Write-Data	Control setpoint: 10.00
10:30:26.983976	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:30:27.859351	T80640000	Read-Data 	Remote override function: 00000000
10:30:27.978621	Error 03
10:30:28.896307	T80000200	Read-Data 	Status: 00000010 00000000
10:30:28.954382	B40000200	Read-Ack  	Status: 00000010 00000000
10:30:29.875249	T80190000	Read-Data 	Boiler water temperature: 0.00
10:30:29.973310	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:30:30.871976	T10010A00	Write-Data	Control setpoint: 10.00
10:30:30.967557	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:30:31.897783	T80640000	Read-Data 	Remote override function: 00000000
10:30:32.877200	T80640000	Read-Data 	Remote override function: 00000000
10:30:32.964229	B70640000	Unk-DataId	Remote override function: 00000000
10:30:32.973635	A40640000	Read-Ack  	Remote override function: 00000000
10:30:33.897693	T80190000	Read-Data 	Boiler water temperature: 0.00
10:30:34.003355	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:30:34.896713	T10010A00	Write-Data	Control setpoint: 10.00
10:30:34.964646	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:30:35.882747	T00110000	Read-Data 	Relative modulation level: 0.00
10:30:35.941192	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:30:36.911160	T10181505	Write-Data	Room temperature: 21.02
10:30:36.968612	BF0180000	Unk-DataId	Room temperature: 0.00
10:30:37.888071	T90101480	Write-Data	Room setpoint: 20.50
10:30:37.980996	B70100000	Unk-DataId	Room setpoint: 0.00
10:30:37.983469	AD0100000	Write-Ack 	Room setpoint: 0.00
10:30:38.888976	T80000200	Read-Data 	Status: 00000010 00000000
10:30:38.938892	B40000200	Read-Ack  	Status: 00000010 00000000
10:30:39.903424	T80190000	Read-Data 	Boiler water temperature: 0.00
10:30:39.963714	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:30:40.887305	T10010A00	Write-Data	Control setpoint: 10.00
10:30:41.006459	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:30:41.869738	T00110000	Read-Data 	Relative modulation level: 0.00
10:30:41.977721	Error 03
10:30:42.899705	T00110000	Read-Data 	Relative modulation level: 0.00
10:30:43.009126	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:30:43.889550	T80190000	Read-Data 	Boiler water temperature: 0.00
10:30:43.978917	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:30:44.868735	T10010A00	Write-Data	Control setpoint: 10.00
10:30:44.929621	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:30:45.895141	T10148A1E	Write-Data	Day of week and time of day: Thu 10:30
10:30:46.870696	T10148A1E	Write-Data	Day of week and time of day: Thu 10:30
10:30:46.979632	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
10:30:46.983052	AD0148A1E	Write-Ack 	Day of week and time of day: Thu 10:30
10:30:47.869865	T801C0000	Read-Data 	Return water temperature: 0.00
10:30:47.980102	BC01C2F00	Read-Ack  	Return water temperature: 47.00
10:30:48.864268	T80000200	Read-Data 	Status: 00000010 00000000
10:30:48.933062	B40000200	Read-Ack  	Status: 00000010 00000000
10:30:49.896162	T80190000	Read-Data 	Boiler water temperature: 0.00
10:30:49.991107	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:30:50.881102	T10010A00	Write-Data	Control setpoint: 10.00
10:30:50.987635	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:30:51.908465	T00110000	Read-Data 	Relative modulation level: 0.00
10:30:51.955623	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:30:52.910007	T801A0000	Read-Data 	DHW temperature: 0.00
10:30:53.889774	T80190000	Read-Data 	Boiler water temperature: 0.00
10:30:53.962333	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:30:54.909810	T10010A00	Write-Data	Control setpoint: 10.00
10:30:54.966858	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:30:55.937625	T801A0000	Read-Data 	DHW temperature: 0.00
10:30:55.996715	Error 04
10:30:56.005324	EC05A3200
10:30:56.871760	T801A0000	Read-Data 	DHW temperature: 0.00
10:30:57.925948	T801A0000	Read-Data 	DHW temperature: 0.00
10:30:57.978487	BC01A3200	Read-Ack  	DHW temperature: 50.00
10:30:58.881585	T80000200	Read-Data 	Status: 00000010 00000000
10:30:58.990066	B40000200	Read-Ack  	Status: 00000010 00000000
10:30:59.896550	T80000200	Read-Data 	Status: 00000010 00000000
10:30:59.976806	B40000200	Read-Ack  	Status: 00000010 00000000
10:31:00.905900	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:01.012748	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:31:01.882778	T10010A00	Write-Data	Control setpoint: 10.00
10:31:01.979769	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:31:02.864291	T10383FFF	Write-Data	DHW setpoint: 64.00
10:31:02.976360	BD0383FFF	Write-Ack 	DHW setpoint: 64.00
10:31:03.895600	T90395AFC	Write-Data	Max CH water setpoint: 90.98
10:31:04.004883	B50395AFC	Write-Ack 	Max CH water setpoint: 90.98
10:31:04.891468	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:04.948865	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:31:05.870759	T10010A00	Write-Data	Control setpoint: 10.00
10:31:05.931938	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:31:06.899258	T00090000	Read-Data 	Remote override room setpoint: 0.00
10:31:06.958452	BF0090000	Unk-DataId	Remote override room setpoint: 0.00
10:31:07.012224	AC0090000	Read-Ack  	Remote override room setpoint: 0.00
10:31:07.887204	T00090000	Read-Data 	Remote override room setpoint: 0.00
10:31:07.986143	BF0090000	Unk-DataId	Remote override room setpoint: 0.00
10:31:07.989056	AC0090000	Read-Ack  	Remote override room setpoint: 0.00
10:31:08.862484	T00090000	Read-Data 	Remote override room setpoint: 0.00
10:31:08.971951	BF0090000	Unk-DataId	Remote override room setpoint: 0.00
10:31:08.974510	AC0090000	Read-Ack  	Remote override room setpoint: 0.00
10:31:09.908109	T80000200	Read-Data 	Status: 00000010 00000000
10:31:10.025755	Error 03
10:31:10.892604	T80000200	Read-Data 	Status: 00000010 00000000
10:31:11.872370	T80000200	Read-Data 	Status: 00000010 00000000
10:31:11.930659	B40000200	Read-Ack  	Status: 00000010 00000000
10:31:12.897388	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:12.988876	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:31:13.883681	T10010A00	Write-Data	Control setpoint: 10.00
10:31:13.943161	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:31:14.862528	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:14.975913	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:31:15.898568	T10010A00	Write-Data	Control setpoint: 10.00
10:31:16.002650	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:31:16.876858	T80640000	Read-Data 	Remote override function: 00000000
10:31:16.987732	B70640000	Unk-DataId	Remote override function: 00000000
10:31:16.997877	A40640000	Read-Ack  	Remote override function: 00000000
10:31:17.877084	T00110000	Read-Data 	Relative modulation level: 0.00
10:31:18.894683	T00110000	Read-Data 	Relative modulation level: 0.00
10:31:18.952338	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:31:19.884062	T80000200	Read-Data 	Status: 00000010 00000000
10:31:19.976747	B40000200	Read-Ack  	Status: 00000010 00000000
10:31:20.896180	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:20.944470	Error 03
10:31:21.889399	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:21.949273	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:31:22.882085	T10010A00	Write-Data	Control setpoint: 10.00
10:31:22.975108	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:31:23.899897	T00110000	Read-Data 	Relative modulation level: 0.00
10:31:24.024504	Error 03
10:31:24.881547	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:25.867157	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:25.961069	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:31:26.905400	T10010A00	Write-Data	Control setpoint: 10.00
10:31:26.967068	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:31:27.887627	T00110000	Read-Data 	Relative modulation level: 0.00
10:31:28.002277	Error 03
10:31:28.913954	T00110000	Read-Data 	Relative modulation level: 0.00
10:31:29.007904	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:31:29.897051	T80000200	Read-Data 	Status: 00000010 00000000
10:31:29.991666	B40000200	Read-Ack  	Status: 00000010 00000000
10:31:30.893664	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:30.988012	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:31:31.883531	T10010A00	Write-Data	Control setpoint: 10.00
10:31:31.937755	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:31:32.909918	T00110000	Read-Data 	Relative modulation level: 0.00
10:31:33.000787	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:31:33.892026	T90181508	Write-Data	Room temperature: 21.03
10:31:33.950586	BF0180000	Unk-DataId	Room temperature: 0.00
10:31:34.871888	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:34.981264	Error 03
10:31:35.905446	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:35.996713	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:31:36.893507	T10010A00	Write-Data	Control setpoint: 10.00
10:31:36.951315	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:31:37.869489	T90101480	Write-Data	Room setpoint: 20.50
10:31:37.965708	B70100000	Unk-DataId	Room setpoint: 0.00
10:31:37.971380	AD0100000	Write-Ack 	Room setpoint: 0.00
10:31:38.899090	T10148A1E	Write-Data	Day of week and time of day: Thu 10:30
10:31:39.884030	T80000200	Read-Data 	Status: 00000010 00000000
10:31:39.940391	B40000200	Read-Ack  	Status: 00000010 00000000
10:31:40.859667	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:40.966899	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:31:41.907617	T10010A00	Write-Data	Control setpoint: 10.00
10:31:41.968092	Error 03
10:31:42.886403	T10010A00	Write-Data	Control setpoint: 10.00
10:31:43.903954	T10010A00	Write-Data	Control setpoint: 10.00
10:31:43.965435	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:31:44.911273	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:44.968280	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:31:45.872602	T10010A00	Write-Data	Control setpoint: 10.00
10:31:45.980509	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:31:46.905008	T00110000	Read-Data 	Relative modulation level: 0.00
10:31:47.000020	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:31:47.898731	T90148A1F	Write-Data	Day of week and time of day: Thu 10:31
10:31:47.955151	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
10:31:48.001172	A50148A1F	Write-Ack 	Day of week and time of day: Thu 10:31
10:31:48.878243	T801C0000	Read-Data 	Return water temperature: 0.00
10:31:48.989524	B401C2E00	Read-Ack  	Return water temperature: 46.00
10:31:49.866320	T80000200	Read-Data 	Status: 00000010 00000000
10:31:50.892573	T80000200	Read-Data 	Status: 00000010 00000000
10:31:51.002014	B40000200	Read-Ack  	Status: 00000010 00000000
10:31:51.880367	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:51.994877	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:31:52.871041	T10010A00	Write-Data	Control setpoint: 10.00
10:31:52.967544	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:31:53.909463	T00110000	Read-Data 	Relative modulation level: 0.00
10:31:53.967510	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:31:54.884450	T80190000	Read-Data 	Boiler water temperature: 0.00
10:31:54.993855	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:31:55.885503	T10010A00	Write-Data	Control setpoint: 10.00
10:31:55.937484	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:31:56.910458	T801A0000	Read-Data 	DHW temperature: 0.00
10:31:57.020629	BC01A3200	Read-Ack  	DHW temperature: 50.00
10:31:57.890494	T001B0000	Read-Data 	Outside temperature: 0.00
10:31:57.998523	B401BE0FF	Read-Ack  	Outside temperature: -31.00
10:31:58.874131	T00120000	Read-Data 	CH water pressure: 0.00
10:31:58.945192	B40120166	Read-Ack  	CH water pressure: 1.40
10:31:59.869997	T80000200	Read-Data 	Status: 00000010 00000000
10:31:59.981773	Error 03
10:32:00.903036	T80000200	Read-Data 	Status: 00000010 00000000
10:32:00.960564	B40000260	Read-Ack  	Status: 00000010 01100000
10:32:01.878633	T80190000	Read-Data 	Boiler water temperature: 0.00
10:32:01.942143	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:32:02.910736	T10010A00	Write-Data	Control setpoint: 10.00
10:32:02.970996	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:32:03.905085	T10383FFF	Write-Data	DHW setpoint: 64.00
10:32:04.890603	T80190000	Read-Data 	Boiler water temperature: 0.00
10:32:04.958953	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:32:05.912039	T10010A00	Write-Data	Control setpoint: 10.00
10:32:06.045003	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:32:06.950875	T10383FFF	Write-Data	DHW setpoint: 64.00
10:32:06.952179	BD0383FFF	Write-Ack 	DHW setpoint: 64.00
10:32:07.878940	T90395AFC	Write-Data	Max CH water setpoint: 90.98
10:32:07.935687	B50395AFC	Write-Ack 	Max CH water setpoint: 90.98
10:32:08.898300	T00090000	Read-Data 	Remote override room setpoint: 0.00
10:32:08.898615	R00060000	Read-Data 	Remote parameter flags: 00000000 00000000
10:32:09.012760	B40060301	Read-Ack  	Remote parameter flags: 00000011 00000001
10:32:09.013468	AC0090000	Read-Ack  	Remote override room setpoint: 0.00
10:32:09.897922	T80000200	Read-Data 	Status: 00000010 00000000
10:32:09.998947	Error 03
10:32:10.879683	T80000200	Read-Data 	Status: 00000010 00000000
10:32:11.903292	T80000200	Read-Data 	Status: 00000010 00000000
10:32:11.999012	B40000200	Read-Ack  	Status: 00000010 00000000
10:32:12.886811	T80190000	Read-Data 	Boiler water temperature: 0.00
10:32:12.988177	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:32:13.876171	T10010A00	Write-Data	Control setpoint: 10.00
10:32:13.985373	Error 03
10:32:14.908243	T80190000	Read-Data 	Boiler water temperature: 0.00
10:32:15.003894	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:32:15.893486	T10010A00	Write-Data	Control setpoint: 10.00
10:32:15.986197	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:32:16.890003	T80640000	Read-Data 	Remote override function: 00000000
10:32:16.943124	B70640000	Unk-DataId	Remote override function: 00000000
10:32:16.945975	A40640000	Read-Ack  	Remote override function: 00000000
10:32:17.907110	T00110000	Read-Data 	Relative modulation level: 0.00
10:32:18.881427	T00110000	Read-Data 	Relative modulation level: 0.00
10:32:18.977362	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:32:19.861692	T80000200	Read-Data 	Status: 00000010 00000000
10:32:19.974678	B40000200	Read-Ack  	Status: 00000010 00000000
10:32:20.904342	T80190000	Read-Data 	Boiler water temperature: 0.00
10:32:20.994788	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:32:21.878568	T10010A00	Write-Data	Control setpoint: 10.00
10:32:21.986509	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:32:22.874162	T00110000	Read-Data 	Relative modulation level: 0.00
10:32:22.972775	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:32:23.898448	T90181508	Write-Data	Room temperature: 21.03
10:32:24.022724	Error 04
10:32:24.028326	EF0180002
10:32:24.875717	T80190000	Read-Data 	Boiler water temperature: 0.00
10:32:25.916990	T80190000	Read-Data 	Boiler water temperature: 0.00
10:32:25.966370	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:32:26.898100	T10010A00	Write-Data	Control setpoint: 10.00
10:32:26.952575	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:32:27.869897	T90181508	Write-Data	Room temperature: 21.03
10:32:27.970249	BF01BFFFF	Unk-DataId	Outside temperature: -0.00
10:32:28.870208	T90181508	Write-Data	Room temperature: 21.03
10:32:29.902403	T80000200	Read-Data 	Status: 00000010 00000000
10:32:29.961277	B40000200	Read-Ack  	Status: 00000010 00000000
10:32:30.880567	T80190000	Read-Data 	Boiler water temperature: 0.00
10:32:30.946991	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:32:31.866461	T10010A00	Write-Data	Control setpoint: 10.00
10:32:31.968460	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:32:32.907120	T00110000	Read-Data 	Relative modulation level: 0.00
10:32:32.958934	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:32:33.888445	T10181512	Write-Data	Room temperature: 21.07
10:32:33.943301	BF0180000	Unk-DataId	Room temperature: 0.00
10:32:34.879421	T80190000	Read-Data 	Boiler water temperature: 0.00
10:32:34.989851	Error 03
10:32:35.898572	T80190000	Read-Data 	Boiler water temperature: 0.00
10:32:35.967036	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:32:36.883443	T10010A00	Write-Data	Control setpoint: 10.00
10:32:36.941640	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:32:37.870770	T90101480	Write-Data	Room setpoint: 20.50
10:32:37.928290	B70100000	Unk-DataId	Room setpoint: 0.00
10:32:37.978949	AD0100000	Write-Ack 	Room setpoint: 0.00
10:32:38.908160	T90148A1F	Write-Data	Day of week and time of day: Thu 10:31
10:32:39.880077	T80000200	Read-Data 	Status: 00000010 00000000
10:32:39.994783	B40000200	Read-Ack  	Status: 00000010 00000000
10:32:40.872509	T80190000	Read-Data 	Boiler water temperature: 0.00
10:32:40.933050	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:32:41.893422	T10010A00	Write-Data	Control setpoint: 10.00
10:32:41.995996	Error 04
10:32:42.000804	ED0810A00
10:32:42.865208	T10010A00	Write-Data	Control setpoint: 10.00
10:32:43.901024	T10010A00	Write-Data	Control setpoint: 10.00
10:32:44.000573	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:32:44.892082	T80190000	Read-Data 	Boiler water temperature: 0.00
10:32:44.992157	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:32:45.868689	T10010A00	Write-Data	Control setpoint: 10.00
10:32:45.969409	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:32:46.904679	T00110000	Read-Data 	Relative modulation level: 0.00
10:32:47.006719	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:32:47.887081	T90148A20	Write-Data	Day of week and time of day: Thu 10:32
10:32:47.988322	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
10:32:47.999310	A50148A20	Write-Ack 	Day of week and time of day: Thu 10:32
10:32:48.878890	T801C0000	Read-Data 	Return water temperature: 0.00
10:32:48.990987	Error 03
10:32:49.907058	T80000200	Read-Data 	Status: 00000010 00000000
10:32:49.971028	B40000200	Read-Ack  	Status: 00000010 00000000
10:32:50.888641	T80190000	Read-Data 	Boiler water temperature: 0.00
10:32:51.007571	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:32:51.877824	T10010A00	Write-Data	Control setpoint: 10.00
10:32:51.976509	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:32:52.858962	T00110000	Read-Data 	Relative modulation level: 0.00
10:32:52.979390	Error 03
10:32:53.900936	T00110000	Read-Data 	Relative modulation level: 0.00
10:32:53.949230	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:32:54.876445	T80190000	Read-Data 	Boiler water temperature: 0.00
10:32:54.978265	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:32:55.912078	T10010A00	Write-Data	Control setpoint: 10.00
10:32:56.032423	Error 03
10:32:56.882993	T10010A00	Write-Data	Control setpoint: 10.00
10:32:57.871200	T10010A00	Write-Data	Control setpoint: 10.00
10:32:57.964508	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:32:58.910151	T801C0000	Read-Data 	Return water temperature: 0.00
10:32:58.957102	B401C2E00	Read-Ack  	Return water temperature: 46.00
10:32:59.905428	T80000200	Read-Data 	Status: 00000010 00000000
10:32:59.963802	B40000200	Read-Ack  	Status: 00000010 00000000
10:33:00.865240	T80000200	Read-Data 	Status: 00000010 00000000
10:33:00.932599	B40000200	Read-Ack  	Status: 00000010 00000000
10:33:01.903917	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:02.016982	Error 03
10:33:02.879932	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:02.939243	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:33:03.873249	T10010A00	Write-Data	Control setpoint: 10.00
10:33:03.941754	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:33:04.889284	T10383FFF	Write-Data	DHW setpoint: 64.00
10:33:05.011690	Error 03
10:33:05.862784	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:05.965280	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:33:06.904033	T10010A00	Write-Data	Control setpoint: 10.00
10:33:07.009847	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:33:07.884509	T10383FFF	Write-Data	DHW setpoint: 64.00
10:33:07.953829	Error 04
10:33:08.010977	E90383FFF
10:33:08.888514	T10383FFF	Write-Data	DHW setpoint: 64.00
10:33:08.956986	BD0383FFF	Write-Ack 	DHW setpoint: 64.00
10:33:09.891318	T90395AFC	Write-Data	Max CH water setpoint: 90.98
10:33:10.007984	Error 03
10:33:10.920516	T80000200	Read-Data 	Status: 00000010 00000000
10:33:11.932493	T80000200	Read-Data 	Status: 00000010 00000000
10:33:11.979867	BC00002E0	Read-Ack  	Status: 00000010 11100000
10:33:12.896398	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:12.954105	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:33:13.887140	T10010A00	Write-Data	Control setpoint: 10.00
10:33:13.970975	BD1FF0A00	Write-Ack 	Message ID 255: 2560
10:33:14.914906	T10010A00	Write-Data	Control setpoint: 10.00
10:33:15.898446	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:15.963473	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:33:16.920829	T10010A00	Write-Data	Control setpoint: 10.00
10:33:17.901948	T10010A00	Write-Data	Control setpoint: 10.00
10:33:18.895344	T10010A00	Write-Data	Control setpoint: 10.00
10:33:19.899297	T10010A00	Write-Data	Control setpoint: 10.00
10:33:19.959569	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:33:20.880056	T80000200	Read-Data 	Status: 00000010 00000000
10:33:21.909605	T80000200	Read-Data 	Status: 00000010 00000000
10:33:22.880265	T80000200	Read-Data 	Status: 00000010 00000000
10:33:22.985640	B40000200	Read-Ack  	Status: 00000010 00000000
10:33:23.876635	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:24.899770	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:25.880300	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:26.895247	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:26.954736	BC0194000	Read-Ack  	Boiler water temperature: 64.00
10:33:27.933613	T10010A00	Write-Data	Control setpoint: 10.00
10:33:27.995562	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:33:28.865970	T90395AFC	Write-Data	Max CH water setpoint: 90.98
10:33:29.897292	T90395AFC	Write-Data	Max CH water setpoint: 90.98
10:33:29.948038	B50395AFC	Write-Ack 	Max CH water setpoint: 90.98
10:33:30.885149	T80000200	Read-Data 	Status: 00000010 00000000
10:33:30.946693	BC00002E0	Read-Ack  	Status: 00000010 11100000
10:33:31.868443	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:31.968195	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:33:32.897916	T10010A00	Write-Data	Control setpoint: 10.00
10:33:32.997931	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:33:33.889117	T00090000	Read-Data 	Remote override room setpoint: 0.00
10:33:33.892395	R00300000	Read-Data 	DHW setpoint boundaries: 0 0
10:33:33.939375	B40303F26	Read-Ack  	DHW setpoint boundaries: 63 38
10:33:33.994889	AC0090000	Read-Ack  	Remote override room setpoint: 0.00
10:33:34.872666	T80640000	Read-Data 	Remote override function: 00000000
10:33:34.875908	R00050000	Read-Data 	Application-specific flags: 00000000 0
10:33:34.928518	BC0050000	Read-Ack  	Application-specific flags: 00000000 0
10:33:34.986083	A40640000	Read-Ack  	Remote override function: 00000000
10:33:35.904541	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:35.958358	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:33:36.875126	T10010A00	Write-Data	Control setpoint: 10.00
10:33:36.987890	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:33:37.861837	T00110000	Read-Data 	Relative modulation level: 0.00
10:33:37.963338	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:33:38.903047	T9018151C	Write-Data	Room temperature: 21.11
10:33:39.889376	T9018151C	Write-Data	Room temperature: 21.11
10:33:39.945860	BF0180000	Unk-DataId	Room temperature: 0.00
10:33:40.911156	T80000200	Read-Data 	Status: 00000010 00000000
10:33:40.972200	B40000200	Read-Ack  	Status: 00000010 00000000
10:33:41.890484	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:42.006802	Error 03
10:33:42.872748	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:43.899087	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:43.952153	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:33:44.877688	T10010A00	Write-Data	Control setpoint: 10.00
10:33:44.982754	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:33:45.912124	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:46.886990	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:46.994076	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:33:47.875615	T10010A00	Write-Data	Control setpoint: 10.00
10:33:47.933251	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:33:48.898074	T00110000	Read-Data 	Relative modulation level: 0.00
10:33:49.004228	Error 03
10:33:49.880373	T00110000	Read-Data 	Relative modulation level: 0.00
10:33:50.868799	T80000200	Read-Data 	Status: 00000010 00000000
10:33:50.968325	B40000200	Read-Ack  	Status: 00000010 00000000
10:33:51.898707	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:51.961873	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:33:52.886816	T10010A00	Write-Data	Control setpoint: 10.00
10:33:52.956593	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:33:53.917177	T00110000	Read-Data 	Relative modulation level: 0.00
10:33:53.982707	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:33:54.887614	T90101480	Write-Data	Room setpoint: 20.50
10:33:54.991421	B70100000	Unk-DataId	Room setpoint: 0.00
10:33:55.001688	AD0100000	Write-Ack 	Room setpoint: 0.00
10:33:55.873682	T80190000	Read-Data 	Boiler water temperature: 0.00
10:33:55.984610	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:33:56.904220	T10010A00	Write-Data	Control setpoint: 10.00
10:33:57.007241	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:33:57.900741	T10148A21	Write-Data	Day of week and time of day: Thu 10:33
10:33:57.963057	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
10:33:57.966681	AD0148A21	Write-Ack 	Day of week and time of day: Thu 10:33
10:33:58.890198	T801C0000	Read-Data 	Return water temperature: 0.00
10:33:59.005647	B401C2D00	Read-Ack  	Return water temperature: 45.00
10:33:59.877868	T801A0000	Read-Data 	DHW temperature: 0.00
10:33:59.996883	Error 03
10:34:00.908167	T80000200	Read-Data 	Status: 00000010 00000000
10:34:00.972916	B40000200	Read-Ack  	Status: 00000010 00000000
10:34:01.891718	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:01.953024	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:34:02.878079	T10010A00	Write-Data	Control setpoint: 10.00
10:34:02.934589	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:34:03.911220	T10383FFF	Write-Data	DHW setpoint: 64.00
10:34:03.967324	BD0383FFF	Write-Ack 	DHW setpoint: 64.00
10:34:04.888159	T90395AFC	Write-Data	Max CH water setpoint: 90.98
10:34:04.996249	B50395AFC	Write-Ack 	Max CH water setpoint: 90.98
10:34:05.888224	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:05.938657	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:34:06.909683	T10010A00	Write-Data	Control setpoint: 10.00
10:34:06.966775	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:34:07.899801	T00090000	Read-Data 	Remote override room setpoint: 0.00
10:34:07.956997	BF0090000	Unk-DataId	Remote override room setpoint: 0.00
10:34:08.012823	AC0090000	Read-Ack  	Remote override room setpoint: 0.00
10:34:08.889998	T80640000	Read-Data 	Remote override function: 00000000
10:34:08.939779	B70640000	Unk-DataId	Remote override function: 00000000
10:34:08.984673	A40640000	Read-Ack  	Remote override function: 00000000
10:34:09.904750	T00110000	Read-Data 	Relative modulation level: 0.00
10:34:10.057928	Error 04
10:34:10.061193	EC01101FF
10:34:10.889286	T80000200	Read-Data 	Status: 00000010 00000000
10:34:11.875634	T80000200	Read-Data 	Status: 00000010 00000000
10:34:11.985714	B40000200	Read-Ack  	Status: 00000010 00000000
10:34:12.904240	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:12.961767	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:34:13.897746	T10010A00	Write-Data	Control setpoint: 10.00
10:34:14.011108	Error 03
10:34:14.878237	T10010A00	Write-Data	Control setpoint: 10.00
10:34:15.897121	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:15.950932	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:34:16.901786	T10010A00	Write-Data	Control setpoint: 10.00
10:34:16.952838	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:34:17.923797	T00110000	Read-Data 	Relative modulation level: 0.00
10:34:18.892593	T00110000	Read-Data 	Relative modulation level: 0.00
10:34:18.945007	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:34:19.871256	T10181522	Write-Data	Room temperature: 21.13
10:34:19.978207	BF0180000	Unk-DataId	Room temperature: 0.00
10:34:20.910498	T80000200	Read-Data 	Status: 00000010 00000000
10:34:21.002686	B40000200	Read-Ack  	Status: 00000010 00000000
10:34:21.896038	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:21.952247	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:34:22.872506	T10010A00	Write-Data	Control setpoint: 10.00
10:34:22.973220	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:34:23.927935	T00110000	Read-Data 	Relative modulation level: 0.00
10:34:23.977807	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:34:24.892987	T90101480	Write-Data	Room setpoint: 20.50
10:34:25.865173	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:25.964634	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:34:26.902574	T10010A00	Write-Data	Control setpoint: 10.00
10:34:26.967681	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:34:27.898344	T90101480	Write-Data	Room setpoint: 20.50
10:34:27.971278	Error 03
10:34:28.907153	T90101480	Write-Data	Room setpoint: 20.50
10:34:29.012480	B70100000	Unk-DataId	Room setpoint: 0.00
10:34:29.028504	AD0100000	Write-Ack 	Room setpoint: 0.00
10:34:29.899917	T10148A21	Write-Data	Day of week and time of day: Thu 10:33
10:34:29.958834	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
10:34:30.004745	AD0148A21	Write-Ack 	Day of week and time of day: Thu 10:33
10:34:30.896111	T80000200	Read-Data 	Status: 00000010 00000000
10:34:31.012386	B40000200	Read-Ack  	Status: 00000010 00000000
10:34:31.886210	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:31.952810	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:34:32.870637	T10010A00	Write-Data	Control setpoint: 10.00
10:34:32.932680	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:34:33.910086	T00110000	Read-Data 	Relative modulation level: 0.00
10:34:33.967420	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:34:34.885095	T801C0000	Read-Data 	Return water temperature: 0.00
10:34:34.995702	Error 03
10:34:35.863840	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:36.899051	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:36.953394	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:34:37.884954	T10010A00	Write-Data	Control setpoint: 10.00
10:34:37.938076	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:34:38.920933	T801C0000	Read-Data 	Return water temperature: 0.00
10:34:39.885132	T801C0000	Read-Data 	Return water temperature: 0.00
10:34:39.987249	B401C2D00	Read-Ack  	Return water temperature: 45.00
10:34:40.874715	T80000200	Read-Data 	Status: 00000010 00000000
10:34:40.968008	B40000200	Read-Ack  	Status: 00000010 00000000
10:34:41.904175	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:42.020482	Error 04
10:34:42.023563	E40393F00
10:34:42.890533	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:43.916277	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:43.967906	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:34:44.890247	T10010A00	Write-Data	Control setpoint: 10.00
10:34:44.990312	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:34:45.877293	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:45.979960	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:34:46.901680	T10010A00	Write-Data	Control setpoint: 10.00
10:34:46.995827	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:34:47.889217	T00110000	Read-Data 	Relative modulation level: 0.00
10:34:47.950238	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:34:48.866644	T801A0000	Read-Data 	DHW temperature: 0.00
10:34:48.977096	BC01A3200	Read-Ack  	DHW temperature: 50.00
10:34:49.917123	T001B0000	Read-Data 	Outside temperature: 0.00
10:34:49.983308	B401BE0FF	Read-Ack  	Outside temperature: -31.00
10:34:50.899202	T80000200	Read-Data 	Status: 00000010 00000000
10:34:50.997140	BC00002E0	Read-Ack  	Status: 00000010 11100000
10:34:51.894811	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:51.991090	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:34:52.870991	T10010A00	Write-Data	Control setpoint: 10.00
10:34:52.993293	Error 03
10:34:53.900917	T10010A00	Write-Data	Control setpoint: 10.00
10:34:53.991862	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:34:54.876771	T00110000	Read-Data 	Relative modulation level: 0.00
10:34:54.943752	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:34:55.863059	T80190000	Read-Data 	Boiler water temperature: 0.00
10:34:55.964293	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:34:56.905691	T10010A00	Write-Data	Control setpoint: 10.00
10:34:57.870430	T10010A00	Write-Data	Control setpoint: 10.00
10:34:57.985133	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:34:58.906184	T00120000	Read-Data 	CH water pressure: 0.00
10:34:58.969180	B40120166	Read-Ack  	CH water pressure: 1.40
10:34:59.904540	T80000200	Read-Data 	Status: 00000010 00000000
10:35:00.016674	B40000260	Read-Ack  	Status: 00000010 01100000
10:35:00.877689	T80000200	Read-Data 	Status: 00000010 00000000
10:35:00.947438	B40000260	Read-Ack  	Status: 00000010 01100000
10:35:01.897013	T80000200	Read-Data 	Status: 00000010 00000000
10:35:01.983338	B40000260	Read-Ack  	Status: 00000010 01100000
10:35:02.935712	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:02.995932	Error 03
10:35:03.885278	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:04.921032	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:04.981577	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:35:05.913179	T10010A00	Write-Data	Control setpoint: 10.00
10:35:06.015808	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:35:06.896618	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:06.949509	Error 03
10:35:07.894462	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:07.994715	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:35:08.874550	T10010A00	Write-Data	Control setpoint: 10.00
10:35:08.983295	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:35:09.920889	T10383FFF	Write-Data	DHW setpoint: 64.00
10:35:10.040334	Error 04
10:35:10.048315	ED0383FBF
10:35:10.893748	T10383FFF	Write-Data	DHW setpoint: 64.00
10:35:11.883588	T80000200	Read-Data 	Status: 00000010 00000000
10:35:11.937927	BC00002E0	Read-Ack  	Status: 00000010 11100000
10:35:12.920058	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:12.969914	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:35:13.886401	T10010A00	Write-Data	Control setpoint: 10.00
10:35:14.002187	Error 04
10:35:14.008711	E90010A00
10:35:14.874257	T10010A00	Write-Data	Control setpoint: 10.00
10:35:15.958673	T10010A00	Write-Data	Control setpoint: 10.00
10:35:15.969606	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:35:16.879476	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:16.992183	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:35:17.855905	T10010A00	Write-Data	Control setpoint: 10.00
10:35:17.958496	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:35:18.905609	T10383FFF	Write-Data	DHW setpoint: 64.00
10:35:18.967502	BD0383FFF	Write-Ack 	DHW setpoint: 64.00
10:35:19.889189	T90395AFC	Write-Data	Max CH water setpoint: 90.98
10:35:19.948031	B50395AFC	Write-Ack 	Max CH water setpoint: 90.98
10:35:20.872478	T00090000	Read-Data 	Remote override room setpoint: 0.00
10:35:20.875546	R00050000	Read-Data 	Application-specific flags: 00000000 0
10:35:20.980867	Error 03
10:35:21.887583	T80000200	Read-Data 	Status: 00000010 00000000
10:35:22.000475	B40000200	Read-Ack  	Status: 00000010 00000000
10:35:22.876156	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:22.942330	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:35:23.898815	T10010A00	Write-Data	Control setpoint: 10.00
10:35:24.004915	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:35:24.894964	T00090000	Read-Data 	Remote override room setpoint: 0.00
10:35:24.901603	R00050000	Read-Data 	Application-specific flags: 00000000 0
10:35:25.873873	T00090000	Read-Data 	Remote override room setpoint: 0.00
10:35:25.878466	R00050000	Read-Data 	Application-specific flags: 00000000 0
10:35:25.973864	BC0050000	Read-Ack  	Application-specific flags: 00000000 0
10:35:25.977825	AC0090000	Read-Ack  	Remote override room setpoint: 0.00
10:35:26.916969	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:26.964619	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:35:27.883691	T10010A00	Write-Data	Control setpoint: 10.00
10:35:27.993814	Error 03
10:35:28.867390	T10010A00	Write-Data	Control setpoint: 10.00
10:35:29.882936	T10010A00	Write-Data	Control setpoint: 10.00
10:35:29.986177	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:35:30.886194	T80640000	Read-Data 	Remote override function: 00000000
10:35:30.983896	B70640000	Unk-DataId	Remote override function: 00000000
10:35:30.988616	A40640000	Read-Ack  	Remote override function: 00000000
10:35:31.872817	T80000200	Read-Data 	Status: 00000010 00000000
10:35:31.972884	B40000200	Read-Ack  	Status: 00000010 00000000
10:35:32.889560	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:33.004006	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:35:33.877609	T10010A00	Write-Data	Control setpoint: 10.00
10:35:33.978485	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:35:34.878517	T00110000	Read-Data 	Relative modulation level: 0.00
10:35:34.928182	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:35:35.910395	T90181520	Write-Data	Room temperature: 21.13
10:35:35.970888	BF0180000	Unk-DataId	Room temperature: 0.00
10:35:36.888765	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:36.996747	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:35:37.876103	T10010A00	Write-Data	Control setpoint: 10.00
10:35:37.973208	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:35:38.893496	T90101480	Write-Data	Room setpoint: 20.50
10:35:39.024901	B70100000	Unk-DataId	Room setpoint: 0.00
10:35:39.028868	AD0100000	Write-Ack 	Room setpoint: 0.00
10:35:39.883114	T10148A22	Write-Data	Day of week and time of day: Thu 10:34
10:35:39.948057	BF0140000	Unk-DataId	Day of week and time of day: Unk 00:00
10:35:39.996452	AD0148A22	Write-Ack 	Day of week and time of day: Thu 10:34
10:35:40.883364	T801C0000	Read-Data 	Return water temperature: 0.00
10:35:40.978346	B401C2D00	Read-Ack  	Return water temperature: 45.00
10:35:41.862340	T80000200	Read-Data 	Status: 00000010 00000000
10:35:41.967285	B40000200	Read-Ack  	Status: 00000010 00000000
10:35:42.902631	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:43.001246	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:35:43.886875	T10010A00	Write-Data	Control setpoint: 10.00
10:35:43.989521	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:35:44.874748	T00110000	Read-Data 	Relative modulation level: 0.00
10:35:44.978114	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:35:45.900035	T801A0000	Read-Data 	DHW temperature: 0.00
10:35:45.984101	BC01A3200	Read-Ack  	DHW temperature: 50.00
10:35:46.887213	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:46.997235	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:35:47.869324	T10010A00	Write-Data	Control setpoint: 10.00
10:35:47.970165	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:35:48.903547	T001B0000	Read-Data 	Outside temperature: 0.00
10:35:49.006522	Error 04
10:35:49.009773	E401BE8FF
10:35:49.891591	T001B0000	Read-Data 	Outside temperature: 0.00
10:35:50.875880	T001B0000	Read-Data 	Outside temperature: 0.00
10:35:50.968446	B401BE0FF	Read-Ack  	Outside temperature: -31.00
10:35:51.904397	T80000200	Read-Data 	Status: 00000010 00000000
10:35:51.962458	BC00002E0	Read-Ack  	Status: 00000010 11100000
10:35:52.890704	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:52.946116	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:35:53.876693	T10010A00	Write-Data	Control setpoint: 10.00
10:35:53.931160	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:35:54.894377	T00110000	Read-Data 	Relative modulation level: 0.00
10:35:54.996688	BC0110000	Read-Ack  	Relative modulation level: 0.00
10:35:55.913123	T00120000	Read-Data 	CH water pressure: 0.00
10:35:55.963674	B40120166	Read-Ack  	CH water pressure: 1.40
10:35:56.876566	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:57.899510	T80190000	Read-Data 	Boiler water temperature: 0.00
10:35:57.996070	B40193F00	Read-Ack  	Boiler water temperature: 63.00
10:35:58.881405	T10010A00	Write-Data	Control setpoint: 10.00
10:35:58.980256	BD0010A00	Write-Ack 	Control setpoint: 10.00
10:35:59.860825	T80000200	Read-Data 	Status: 00000010 00000000
10:35:59.981504	Error 03
One hypothesis would be that it changes the message sequence in response to failed messages, because I also have this: https://www.domoticaforum.eu/viewtopic. ... 804#p97804
I attempted to simulate your situation using the interface firmware. I made a script that generates appropriate response, but skips a couple every now and then, which is what it would also look like to your thermostat. (When the OTGW detects an error in gateway mode, it doesn't send anything to the thermostat.) But after running like that for 3 hours, the clock is still correct. So, either I'm not reproducing the situation accurately enough, or your Chronotherm Modulation behaves different than mine. Maybe it has different firmware. On startup, mine says:
  • T107E0100 Write-Data Master product version: 1 0
Of course there is no guarantee that information is actually updated with new firmware.
Tomas
Post by Tomas »
What is the best way to get that attribute? Pull the plug from the thermostat to the gateway, reconnect it while OpenTherm Monitor is logging, or is there some smarter way to make it send the software version?
It also seems there are different Chronotherm Modulation versions, mine has a sticker on the back with "T8851M1000" maybe yours is a slightly different or updated model?
The sticker on my Chronotherm Modulation says: T8851M1000 4T40 AD5C 0837 5.
Pulling the thermostat plug from the gateway for a few seconds would work for getting the thermostat to report its software version again. You can also pull the thermostat off the wall and put it back. I don't know any smarter way to do it.
Tomas
Post by Tomas »
Update on this: I haven't managed to make the thermostat report a software version. But I did manage to find another Chronotherm with the same model (T8851M1000), now connected to the same boiler and gateway. This one does not have the same behavior. When it receives a time input from the gateway it only changes the minutes and just keeps counting the seconds as it was. So it doesn't drift.
So it's very likely that there was either a problem with the thermostat or a bug in the firmware version that was fixed in the one I have now.