USB Gateway no response on diagnostics
joho500
Post by joho500 »
I have a pre-assembled gateway, USB-type. First I flashed the gateway firmware and connected the thermostat. No respons and the display of the thermostat shows 'Wiring error'. For testing I attached the boiler and I did receive good data from that side.
To diagnose the problem with the thermostat side I flashed the diagnostic firmware. I get no respons entering options 2 and 3. Option 5 shows 0.00V both for the thermostat and the boiler and a reference voltage of 1.21V.
Does this mean that the gateway is physically broken? Or is something else wrong?
Thanks in advance for your help.
Joost
Re: USB Gateway no response on diagnostics
Unless you ran test 5 with the thermostat connector shorted, it should not show 0V for the thermostat. Given that the thermostat can be powered from the gateway, the problem can't be much else than a bad connection of R5.
However, I assume you ordered a pre-assembled gateway because you're not very comfortable with a soldering iron. If there's also not an acquaintance nearby who can help you sort out the problem around R5, you'll have to contact the webshop for a return request.
joho500
Post by joho500 »
Thanks. I'll try to solder it myself and see if it helps.
Joost