Sporadic shanges of remote override room setpoint.
cyril
Post by cyril »
Hi all!
Sometimes I see sporadic changes of remote override room setpoint. New value is fractional. I presume it's influence of electromagnetic fields or power violations. But log not contain any garbage. Value simply changes. Thermostat is Honeywell Round Modulation. Boiler is Baxi Main Four 240F.
Any help appreciated.
cyril
Re: Sporadic shanges of remote override room setpoint.
Post by cyril »
At 14:31:49 Remote override room setpoint changes to 19.38 without any external action.
14:31:25.961923  BD0010A00  Write-Ack   Control setpoint: 10.00
14:31:26.800391  T80000200  Read-Data   Status: 00000010 00000000
14:31:27.046132  B40000200  Read-Ack    Status: 00000010 00000000
14:31:27.863133  T00090000  Read-Data   Remote override room setpoint: 0.00
14:31:27.894585  R00030000  Read-Data   Slave configuration: 00000000 0
14:31:28.121564  BC0030101  Read-Ack    Slave configuration: 00000001 1
14:31:28.125791  AC0090000  Read-Ack    Remote override room setpoint: 0.00
14:31:28.939421  T80190000  Read-Data   Boiler water temperature: 0.00
14:31:29.187126  B40193600  Read-Ack    Boiler water temperature: 54.00
14:31:30.011780  T10010A00  Write-Data  Control setpoint: 10.00
14:31:30.277186  BD0010A00  Write-Ack   Control setpoint: 10.00
14:31:31.103629  T80000200  Read-Data   Status: 00000010 00000000
14:31:31.327919  B40000200  Read-Ack    Status: 00000010 00000000
14:31:32.155013  T90101000  Write-Data  Room setpoint: 16.00
14:31:32.163812  R801A0000  Read-Data   DHW temperature: 0.00
14:31:32.436689  BC01A3400  Read-Ack    DHW temperature: 52.00
14:31:32.437730  A50101000  Write-Ack   Room setpoint: 16.00
14:31:33.235174  T80190000  Read-Data   Boiler water temperature: 0.00
14:31:33.476728  B40193600  Read-Ack    Boiler water temperature: 54.00
14:31:34.336326  T10010A00  Write-Data  Control setpoint: 10.00
14:31:34.543167  BD0010A00  Write-Ack   Control setpoint: 10.00
14:31:35.381881  T80000200  Read-Data   Status: 00000010 00000000
14:31:35.630023  B40000284  Read-Ack    Status: 00000010 10000100
14:31:36.446584  T9018170F  Write-Data  Room temperature: 23.06
14:31:36.487093  R80380000  Read-Data   DHW setpoint: 0.00
14:31:36.710946  BC0383700  Read-Ack    DHW setpoint: 55.00
14:31:36.711934  AF018170F  Unk-DataId  Room temperature: 23.06
14:31:37.509103  T80190000  Read-Data   Boiler water temperature: 0.00
14:31:37.759086  B40193600  Read-Ack    Boiler water temperature: 54.00
14:31:38.599966  T10010A00  Write-Data  Control setpoint: 10.00
14:31:38.817956  BD0010A00  Write-Ack   Control setpoint: 10.00
14:31:39.658298  T80000200  Read-Data   Status: 00000010 00000000
14:31:39.892894  BC000028C  Read-Ack    Status: 00000010 10001100
14:31:40.755778  T00110000  Read-Data   Relative modulation level: 0.00
14:31:40.978862  B40116400  Read-Ack    Relative modulation level: 100.00
14:31:41.790733  T80190000  Read-Data   Boiler water temperature: 0.00
14:31:42.035302  B40193600  Read-Ack    Boiler water temperature: 54.00
14:31:42.876500  T10010A00  Write-Data  Control setpoint: 10.00
14:31:43.131715  BD0010A00  Write-Ack   Control setpoint: 10.00
14:31:43.945155  T80000200  Read-Data   Status: 00000010 00000000
14:31:44.254733  BC0000208  Read-Ack    Status: 00000010 00001000
14:31:45.035442  T00390000  Read-Data   Max CH water setpoint: 0.00
14:31:45.249247  B4039004C  Read-Ack    Max CH water setpoint: 0.30
14:31:46.097038  T80190000  Read-Data   Boiler water temperature: 0.00
14:31:46.383720  BC0193B00  Read-Ack    Boiler water temperature: 59.00
14:31:47.161385  T10010A00  Write-Data  Control setpoint: 10.00
14:31:47.387702  BD0010A00  Write-Ack   Control setpoint: 10.00
14:31:48.239351  T80000200  Read-Data   Status: 00000010 00000000
14:31:48.475277  B40000200  Read-Ack    Status: 00000010 00000000
14:31:49.308222  T00090000  Read-Data   Remote override room setpoint: 0.00
14:31:49.313922  R00030000  Read-Data   Slave configuration: 00000000 0
14:31:49.537984  BC0030101  Read-Ack    Slave configuration: 00000001 1
14:31:49.546444  AC0091260  Read-Ack    Remote override room setpoint: 18.38
14:31:50.366899  T80190000  Read-Data   Boiler water temperature: 0.00
14:31:50.631306  BC0193700  Read-Ack    Boiler water temperature: 55.00
14:31:51.670457  T10010A00  Write-Data  Control setpoint: 10.00
14:31:51.676503  BD0010A00  Write-Ack   Control setpoint: 10.00
14:31:52.533647  T80000200  Read-Data   Status: 00000010 00000000
14:31:52.759731  B40000200  Read-Ack    Status: 00000010 00000000
14:31:53.600361  T90101000  Write-Data  Room setpoint: 16.00
14:31:53.601273  R801A0000  Read-Data   DHW temperature: 0.00
14:31:53.836766  BC01A2900  Read-Ack    DHW temperature: 41.00
14:31:53.837666  A50101000  Write-Ack   Room setpoint: 16.00
14:31:54.727949  T80190000  Read-Data   Boiler water temperature: 0.00
14:31:54.951811  B40193600  Read-Ack    Boiler water temperature: 54.00
14:31:55.791112  T10010A00  Write-Data  Control setpoint: 10.00
14:31:56.116935  BD0010A00  Write-Ack   Control setpoint: 10.00
14:31:56.901140  T80000200  Read-Data   Status: 00000010 00000000
14:31:57.121154  B40000200  Read-Ack    Status: 00000010 00000000
14:31:57.941468  T9018170F  Write-Data  Room temperature: 23.06
14:31:57.954356  R80380000  Read-Data   DHW setpoint: 0.00
14:31:58.181168  BC0383700  Read-Ack    DHW setpoint: 55.00
14:31:58.210129  AF018170F  Unk-DataId  Room temperature: 23.06
14:31:59.005117  T80190000  Read-Data   Boiler water temperature: 0.00
14:31:59.242461  B40193600  Read-Ack    Boiler water temperature: 54.00
14:32:00.081696  T10010A00  Write-Data  Control setpoint: 10.00
14:32:00.302311  BD0010A00  Write-Ack   Control setpoint: 10.00
14:32:01.157212  T80000200  Read-Data   Status: 00000010 00000000
14:32:01.394219  B40000200  Read-Ack    Status: 00000010 00000000
14:32:02.234213  T00110000  Read-Data   Relative modulation level: 0.00
14:32:02.468298  BC0110000  Read-Ack    Relative modulation level: 0.00
14:32:03.312247  T80190000  Read-Data   Boiler water temperature: 0.00
14:32:03.548657  B40193600  Read-Ack    Boiler water temperature: 54.00
14:32:04.375546  T10010A00  Write-Data  Control setpoint: 10.00
14:32:04.626240  BD0010A00  Write-Ack   Control setpoint: 10.00
14:32:05.434006  T80000200  Read-Data   Status: 00000010 00000000
14:32:05.677678  B40000200  Read-Ack    Status: 00000010 00000000
14:32:06.505524  T00390000  Read-Data   Max CH water setpoint: 0.00
14:32:06.755627  B4039004C  Read-Ack    Max CH water setpoint: 0.30
14:32:07.584954  T80190000  Read-Data   Boiler water temperature: 0.00
14:32:07.804145  B40193600  Read-Ack    Boiler water temperature: 54.00
14:32:08.662636  T10010A00  Write-Data  Control setpoint: 10.00
14:32:08.911165  BD0010A00  Write-Ack   Control setpoint: 10.00
14:32:09.725794  T80000200  Read-Data   Status: 00000010 00000000
14:32:09.964164  B40000200  Read-Ack    Status: 00000010 00000000
14:32:10.799557  T00090000  Read-Data   Remote override room setpoint: 0.00
14:32:10.800504  R00030000  Read-Data   Slave configuration: 00000000 0
14:32:11.035807  BC0030101  Read-Ack    Slave configuration: 00000001 1
14:32:11.036879  AC0091260  Read-Ack    Remote override room setpoint: 18.38
14:32:11.875924  T80190000  Read-Data   Boiler water temperature: 0.00
14:32:12.101598  B40193500  Read-Ack    Boiler water temperature: 53.00
14:32:12.929198  T10010A00  Write-Data  Control setpoint: 10.00
14:32:13.170701  BD0010A00  Write-Ack   Control setpoint: 10.00
14:32:14.008581  T80000200  Read-Data   Status: 00000010 00000000
14:32:14.338340  B40000200  Read-Ack    Status: 00000010 00000000
14:32:15.109059  T90101000  Write-Data  Room setpoint: 16.00
14:32:15.110093  R801A0000  Read-Data   DHW temperature: 0.00
14:32:15.319639  BC01A2A00  Read-Ack    DHW temperature: 42.00
14:32:15.336540  A50101000  Write-Ack   Room setpoint: 16.00
14:32:16.199069  T80190000  Read-Data   Boiler water temperature: 0.00
14:32:16.401210  B40193500  Read-Ack    Boiler water temperature: 53.00
14:32:17.267991  T10010A00  Write-Data  Control setpoint: 10.00
14:32:17.461502  BD0010A00  Write-Ack   Control setpoint: 10.00
14:32:18.400104  T80000200  Read-Data   Status: 00000010 00000000
14:32:18.581310  B40000200  Read-Ack    Status: 00000010 00000000
14:32:19.431446  T9018170F  Write-Data  Room temperature: 23.06
14:32:19.438409  R80380000  Read-Data   DHW setpoint: 0.00
14:32:19.677239  BC0383700  Read-Ack    DHW setpoint: 55.00
14:32:19.679468  AF018170F  Unk-DataId  Room temperature: 23.06
14:32:20.507040  T80190000  Read-Data   Boiler water temperature: 0.00
14:32:20.782833  B40193500  Read-Ack    Boiler water temperature: 53.00
14:32:21.597537  T10010A00  Write-Data  Control setpoint: 10.00
14:32:21.802960  BD0010A00  Write-Ack   Control setpoint: 10.00
14:32:22.656066  T80000200  Read-Data   Status: 00000010 00000000
14:32:22.894722  B40000200  Read-Ack    Status: 00000010 00000000
14:32:23.722142  T00110000  Read-Data   Relative modulation level: 0.00
14:32:23.949628  BC0110000  Read-Ack    Relative modulation level: 0.00
14:32:24.784340  T80190000  Read-Data   Boiler water temperature: 0.00
14:32:25.029154  B40193500  Read-Ack    Boiler water temperature: 53.00
14:32:25.870638  T10010A00  Write-Data  Control setpoint: 10.00
14:32:26.102281  BD0010A00  Write-Ack   Control setpoint: 10.00
14:32:26.938568  T80000200  Read-Data   Status: 00000010 00000000
14:32:27.161179  B40000200  Read-Ack    Status: 00000010 00000000
14:32:28.022092  T00390000  Read-Data   Max CH water setpoint: 0.00
14:32:28.285267  B4039004C  Read-Ack    Max CH water setpoint: 0.30
14:32:29.067279  T80190000  Read-Data   Boiler water temperature: 0.00
14:32:29.305880  B40193600  Read-Ack    Boiler water temperature: 54.00
14:32:30.177142  T10010A00  Write-Data  Control setpoint: 10.00
14:32:30.383977  BD0010A00  Write-Ack   Control setpoint: 10.00
14:32:31.222721  T80000200  Read-Data   Status: 00000010 00000000
14:32:31.445054  B40000200  Read-Ack    Status: 00000010 00000000
14:32:32.288282  T00090000  Read-Data   Remote override room setpoint: 0.00
14:32:32.383337  R00030000  Read-Data   Slave configuration: 00000000 0
14:32:32.536139  BC0030101  Read-Ack    Slave configuration: 00000001 1
14:32:32.541022  AC0091260  Read-Ack    Remote override room setpoint: 18.38
14:32:33.375682  T80190000  Read-Data   Boiler water temperature: 0.00
14:32:33.583997  BC0193700  Read-Ack    Boiler water temperature: 55.00
14:32:34.432396  T10010A00  Write-Data  Control setpoint: 10.00
14:32:34.685580  BD0010A00  Write-Ack   Control setpoint: 10.00
14:32:35.496990  T80000200  Read-Data   Status: 00000010 00000000
14:32:35.752540  B40000200  Read-Ack    Status: 00000010 00000000
14:32:36.572480  T90101000  Write-Data  Room setpoint: 16.00
14:32:36.579600  R801A0000  Read-Data   DHW temperature: 0.00
14:32:36.813262  B401A3000  Read-Ack    DHW temperature: 48.00
14:32:36.819247  A50101000  Write-Ack   Room setpoint: 16.00
14:32:37.655584  T80190000  Read-Data   Boiler water temperature: 0.00
14:32:37.887637  BC0193700  Read-Ack    Boiler water temperature: 55.00
14:32:38.717719  T10010A00  Write-Data  Control setpoint: 10.00
14:32:38.943127  BD0010A00  Write-Ack   Control setpoint: 10.00
14:32:39.800883  T80000200  Read-Data   Status: 00000010 00000000
14:32:40.030928  B40000200  Read-Ack    Status: 00000010 00000000
14:32:40.878134  T90181711  Write-Data  Room temperature: 23.07
14:32:40.879368  R80380000  Read-Data   DHW setpoint: 0.00
14:32:41.103468  BC0383700  Read-Ack    DHW setpoint: 55.00
14:32:41.117100  AF0181711  Unk-DataId  Room temperature: 23.07
14:32:41.936519  T80190000  Read-Data   Boiler water temperature: 0.00
14:32:42.214404  BC0193800  Read-Ack    Boiler water temperature: 56.00
14:32:43.004076  T10010A00  Write-Data  Control setpoint: 10.00
14:32:43.275968  BD0010A00  Write-Ack   Control setpoint: 10.00
14:32:44.068444  T80000200  Read-Data   Status: 00000010 00000000
14:32:44.340069  B40000200  Read-Ack    Status: 00000010 00000000
14:32:45.154773  T00110000  Read-Data   Relative modulation level: 0.00
14:32:45.401498  BC0110000  Read-Ack    Relative modulation level: 0.00
14:32:46.237826  T80190000  Read-Data   Boiler water temperature: 0.00
14:32:46.456930  BC0193800  Read-Ack    Boiler water temperature: 56.00
14:32:47.282200  T10010A00  Write-Data  Control setpoint: 10.00
14:32:47.523158  BD0010A00  Write-Ack   Control setpoint: 10.00
14:32:48.390947  T80000200  Read-Data   Status: 00000010 00000000
14:32:48.597281  B40000200  Read-Ack    Status: 00000010 00000000
14:32:49.431909  T00390000  Read-Data   Max CH water setpoint: 0.00
14:32:49.664077  B4039004C  Read-Ack    Max CH water setpoint: 0.30
14:32:50.500950  T80190000  Read-Data   Boiler water temperature: 0.00
14:32:50.803235  BC0193800  Read-Ack    Boiler water temperature: 56.00
14:32:51.572141  T10010A00  Write-Data  Control setpoint: 10.00
14:32:51.816885  BD0010A00  Write-Ack   Control setpoint: 10.00
14:32:52.643668  T80000200  Read-Data   Status: 00000010 00000000
14:32:52.890010  B40000200  Read-Ack    Status: 00000010 00000000
14:32:53.725282  T00090000  Read-Data   Remote override room setpoint: 0.00
14:32:53.726317  R00030000  Read-Data   Slave configuration: 00000000 0
14:32:53.985875  BC0030101  Read-Ack    Slave configuration: 00000001 1
14:32:53.986953  AC0091260  Read-Ack    Remote override room setpoint: 18.38
14:32:54.786809  T80190000  Read-Data   Boiler water temperature: 0.00
14:32:55.026541  BC0193800  Read-Ack    Boiler water temperature: 56.00
14:32:55.854768  T10015A00  Write-Data  Control setpoint: 90.00
14:32:56.087313  BD0015A00  Write-Ack   Control setpoint: 90.00
14:32:56.926922  T80000200  Read-Data   Status: 00000010 00000000
14:32:57.184249  B40000284  Read-Ack    Status: 00000010 10000100
14:32:58.022215  T9010125E  Write-Data  Room setpoint: 18.37
14:32:58.026762  R801A0000  Read-Data   DHW temperature: 0.00
14:32:58.356521  B401A3300  Read-Ack    DHW temperature: 51.00
14:32:58.357393  A5010125E  Write-Ack   Room setpoint: 18.37
14:32:59.073817  T80190000  Read-Data   Boiler water temperature: 0.00
14:32:59.305543  BC0193800  Read-Ack    Boiler water temperature: 56.00
14:33:00.146638  T10010A00  Write-Data  Control setpoint: 10.00
14:33:00.420072  BD0010A00  Write-Ack   Control setpoint: 10.00
14:33:01.228248  T80000200  Read-Data   Status: 00000010 00000000
14:33:01.458718  B40000200  Read-Ack    Status: 00000010 00000000
14:33:02.284601  T90181711  Write-Data  Room temperature: 23.07
14:33:02.363697  R80380000  Read-Data   DHW setpoint: 0.00
14:33:02.546095  BC0383700  Read-Ack    DHW setpoint: 55.00
14:33:02.547155  AF0181711  Unk-DataId  Room temperature: 23.07
14:33:03.364248  T80190000  Read-Data   Boiler water temperature: 0.00
14:33:03.588332  BC0193400  Read-Ack    Boiler water temperature: 52.00
14:33:04.473864  T10010A00  Write-Data  Control setpoint: 10.00
14:33:04.706409  BD0010A00  Write-Ack   Control setpoint: 10.00
14:33:05.510090  T80000200  Read-Data   Status: 00000010 00000000
14:33:05.733060  B40000200  Read-Ack    Status: 00000010 00000000
14:33:06.584159  T00110000  Read-Data   Relative modulation level: 0.00
14:33:06.831921  BC0110000  Read-Ack    Relative modulation level: 0.00
14:33:07.646426  T80190000  Read-Data   Boiler water temperature: 0.00
14:33:07.877019  B40192E00  Read-Ack    Boiler water temperature: 46.00
14:33:08.725187  T10010A00  Write-Data  Control setpoint: 10.00
14:33:08.969193  BD0010A00  Write-Ack   Control setpoint: 10.00
14:33:09.799536  T80000200  Read-Data   Status: 00000010 00000000
14:33:10.032907  B40000200  Read-Ack    Status: 00000010 00000000
14:33:10.862660  T00390000  Read-Data   Max CH water setpoint: 0.00
14:33:11.089187  B4039004C  Read-Ack    Max CH water setpoint: 0.30
14:33:12.075547  T80190000  Read-Data   Boiler water temperature: 0.00
14:33:12.216697  BC0192C00  Read-Ack    Boiler water temperature: 44.00
14:33:13.003552  T10010A00  Write-Data  Control setpoint: 10.00
14:33:13.240507  BD0010A00  Write-Ack   Control setpoint: 10.00
14:33:14.068631  T80000200  Read-Data   Status: 00000010 00000000
14:33:14.389741  B40000200  Read-Ack    Status: 00000010 00000000
14:33:15.207225  T00090000  Read-Data   Remote override room setpoint: 0.00
14:33:15.218084  R00030000  Read-Data   Slave configuration: 00000000 0
14:33:15.450151  BC0030101  Read-Ack    Slave configuration: 00000001 1
14:33:15.482635  AC0091260  Read-Ack    Remote override room setpoint: 18.38
14:33:16.281137  T80190000  Read-Data   Boiler water temperature: 0.00
14:33:16.527330  BC0192C00  Read-Ack    Boiler water temperature: 44.00
14:33:17.348513  T10010A00  Write-Data  Control setpoint: 10.00
14:33:17.603074  BD0010A00  Write-Ack   Control setpoint: 10.00
14:33:18.453522  T80000200  Read-Data   Status: 00000010 00000000
14:33:18.698763  B40000200  Read-Ack    Status: 00000010 00000000
14:33:19.489686  T9010125E  Write-Data  Room setpoint: 18.37
14:33:19.505878  R801A0000  Read-Data   DHW temperature: 0.00
14:33:19.743374  BC01A2900  Read-Ack    DHW temperature: 41.00
14:33:19.744420  A5010125E  Write-Ack   Room setpoint: 18.37
14:33:20.571060  T80190000  Read-Data   Boiler water temperature: 0.00
14:33:20.805599  BC0192C00  Read-Ack    Boiler water temperature: 44.00
14:33:21.647182  T10010A00  Write-Data  Control setpoint: 10.00
14:33:21.885622  BD0010A00  Write-Ack   Control setpoint: 10.00
14:33:22.730191  T80000200  Read-Data   Status: 00000010 00000000
14:33:23.026908  B40000200  Read-Ack    Status: 00000010 00000000
14:33:23.794593  T90181714  Write-Data  Room temperature: 23.08
14:33:23.795702  R80380000  Read-Data   DHW setpoint: 0.00
14:33:24.020137  BC0383700  Read-Ack    DHW setpoint: 55.00
14:33:24.047059  AF0181714  Unk-DataId  Room temperature: 23.08
14:33:24.926070  T80190000  Read-Data   Boiler water temperature: 0.00
14:33:25.156377  BC0192C00  Read-Ack    Boiler water temperature: 44.00
14:33:26.046921  T10010A00  Write-Data  Control setpoint: 10.00
14:33:26.283385  BD0010A00  Write-Ack   Control setpoint: 10.00
14:33:27.068276  T80000200  Read-Data   Status: 00000010 00000000
14:33:27.301482  B40000200  Read-Ack    Status: 00000010 00000000
14:33:28.178533  T00110000  Read-Data   Relative modulation level: 0.00
14:33:28.385297  BC0110000  Read-Ack    Relative modulation level: 0.00
14:33:29.205883  T80190000  Read-Data   Boiler water temperature: 0.00
14:33:29.440156  BC0192C00  Read-Ack    Boiler water temperature: 44.00
14:33:30.326153  T10010A00  Write-Data  Control setpoint: 10.00
14:33:30.515817  BD0010A00  Write-Ack   Control setpoint: 10.00
14:33:31.339792  T80000200  Read-Data   Status: 00000010 00000000
14:33:31.579972  B40000200  Read-Ack    Status: 00000010 00000000
14:33:32.425772  T00390000  Read-Data   Max CH water setpoint: 0.00
14:33:32.656596  B4039004C  Read-Ack    Max CH water setpoint: 0.30
14:33:33.495243  T80190000  Read-Data   Boiler water temperature: 0.00
14:33:33.725761  BC0192C00  Read-Ack    Boiler water temperature: 44.00
14:33:34.584068  T10010A00  Write-Data  Control setpoint: 10.00
14:33:34.825195  BD0010A00  Write-Ack   Control setpoint: 10.00
14:33:35.702056  T80000200  Read-Data   Status: 00000010 00000000
14:33:35.955318  B40000200  Read-Ack    Status: 00000010 00000000
14:33:36.773809  T00090000  Read-Data   Remote override room setpoint: 0.00
14:33:36.809979  R00030000  Read-Data   Slave configuration: 00000000 0
14:33:37.000543  BC0030101  Read-Ack    Slave configuration: 00000001 1
14:33:37.012662  AC0091260  Read-Ack    Remote override room setpoint: 18.38
14:33:37.842657  T80190000  Read-Data   Boiler water temperature: 0.00
14:33:38.094411  B40192B00  Read-Ack    Boiler water temperature: 43.00
14:33:38.911807  T10010A00  Write-Data  Control setpoint: 10.00
14:33:39.144638  BD0010A00  Write-Ack   Control setpoint: 10.00
14:33:39.984059  T80000200  Read-Data   Status: 00000010 00000000
14:33:40.276241  B40000200  Read-Ack    Status: 00000010 00000000
14:33:41.051529  T9010125E  Write-Data  Room setpoint: 18.37
14:33:41.086568  R801A0000  Read-Data   DHW temperature: 0.00
14:33:41.282459  BC01A2600  Read-Ack    DHW temperature: 38.00
14:33:41.300943  A5010125E  Write-Ack   Room setpoint: 18.37
14:33:42.141427  T80190000  Read-Data   Boiler water temperature: 0.00
14:33:42.384069  B40192B00  Read-Ack    Boiler water temperature: 43.00
14:33:43.193896  T10010A00  Write-Data  Control setpoint: 10.00
14:33:43.446947  BD0010A00  Write-Ack   Control setpoint: 10.00
14:33:44.328309  T80000200  Read-Data   Status: 00000010 00000000
14:33:44.503913  B40000200  Read-Ack    Status: 00000010 00000000
14:33:45.338472  T90181714  Write-Data  Room temperature: 23.08
14:33:45.369278  R80380000  Read-Data   DHW setpoint: 0.00
14:33:45.596023  BC0383700  Read-Ack    DHW setpoint: 55.00
14:33:45.600064  AF0181714  Unk-DataId  Room temperature: 23.08
14:33:46.476344  T80190000  Read-Data   Boiler water temperature: 0.00
14:33:46.698459  B40192B00  Read-Ack    Boiler water temperature: 43.00
14:33:47.545870  T10010A00  Write-Data  Control setpoint: 10.00
14:33:47.786726  BD0010A00  Write-Ack   Control setpoint: 10.00
14:33:48.619004  T80000200  Read-Data   Status: 00000010 00000000
14:33:48.867717  B40000200  Read-Ack    Status: 00000010 00000000
14:33:49.695279  T00110000  Read-Data   Relative modulation level: 0.00
14:33:49.924423  BC0110000  Read-Ack    Relative modulation level: 0.00
14:33:50.788776  T80190000  Read-Data   Boiler water temperature: 0.00
14:33:51.005039  B40192B00  Read-Ack    Boiler water temperature: 43.00
14:33:51.854954  T10010A00  Write-Data  Control setpoint: 10.00
14:33:52.066231  BD0010A00  Write-Ack   Control setpoint: 10.00
14:33:52.906958  T80000200  Read-Data   Status: 00000010 00000000
14:33:53.157632  B40000200  Read-Ack    Status: 00000010 00000000
14:33:54.159831  T00390000  Read-Data   Max CH water setpoint: 0.00
14:33:54.208621  B4039004C  Read-Ack    Max CH water setpoint: 0.30
14:33:55.041424  T80190000  Read-Data   Boiler water temperature: 0.00
14:33:55.284335  BC0192A00  Read-Ack    Boiler water temperature: 42.00
14:33:56.157447  T10010A00  Write-Data  Control setpoint: 10.00
14:33:56.370426  BD0010A00  Write-Ack   Control setpoint: 10.00
14:33:57.187753  T80000200  Read-Data   Status: 00000010 00000000
14:33:57.424987  B40000200  Read-Ack    Status: 00000010 00000000
14:33:58.273421  T00090000  Read-Data   Remote override room setpoint: 0.00
14:33:58.366204  R00030000  Read-Data   Slave configuration: 00000000 0
14:33:58.518721  BC0030101  Read-Ack    Slave configuration: 00000001 1
14:33:58.519708  AC0091260  Read-Ack    Remote override room setpoint: 18.38
14:33:59.340432  T80190000  Read-Data   Boiler water temperature: 0.00
14:33:59.568663  BC0192A00  Read-Ack    Boiler water temperature: 42.00
14:34:00.406895  T10010A00  Write-Data  Control setpoint: 10.00
14:34:00.640590  BD0010A00  Write-Ack   Control setpoint: 10.00
14:34:01.479685  T80000200  Read-Data   Status: 00000010 00000000
14:34:01.703619  B40000200  Read-Ack    Status: 00000010 00000000
14:34:02.540429  T9010125E  Write-Data  Room setpoint: 18.37
14:34:02.566096  R801A0000  Read-Data   DHW temperature: 0.00
14:34:02.791661  BC01A1F00  Read-Ack    DHW temperature: 31.00
14:34:02.802099  A5010125E  Write-Ack   Room setpoint: 18.37
14:34:03.625644  T80190000  Read-Data   Boiler water temperature: 0.00
14:34:03.876698  BC0192A00  Read-Ack    Boiler water temperature: 42.00
14:34:04.726504  T10010A00  Write-Data  Control setpoint: 10.00
14:34:04.924613  BD0010A00  Write-Ack   Control setpoint: 10.00
14:34:05.769283  T80000200  Read-Data   Status: 00000010 00000000
14:34:06.049332  B40000200  Read-Ack    Status: 00000010 00000000
14:34:06.847251  T90181717  Write-Data  Room temperature: 23.09
14:34:06.848355  R80380000  Read-Data   DHW setpoint: 0.00
14:34:07.059298  BC0383700  Read-Ack    DHW setpoint: 55.00
14:34:07.085847  AF0181717  Unk-DataId  Room temperature: 23.09
14:34:07.904459  T80190000  Read-Data   Boiler water temperature: 0.00
14:34:08.186334  BC0192A00  Read-Ack    Boiler water temperature: 42.00
14:34:08.976701  T10010A00  Write-Data  Control setpoint: 10.00
14:34:09.206463  BD0010A00  Write-Ack   Control setpoint: 10.00
14:34:10.041563  T80000200  Read-Data   Status: 00000010 00000000
14:34:10.343088  B40000200  Read-Ack    Status: 00000010 00000000
14:34:11.124007  T00110000  Read-Data   Relative modulation level: 0.00
14:34:11.361650  BC0110000  Read-Ack    Relative modulation level: 0.00
14:34:12.226252  T80190000  Read-Data   Boiler water temperature: 0.00
14:34:12.467898  BC0192A00  Read-Ack    Boiler water temperature: 42.00
14:34:13.292890  T10010A00  Write-Data  Control setpoint: 10.00
14:34:13.545093  BD0010A00  Write-Ack   Control setpoint: 10.00
14:34:14.341689  T80000200  Read-Data   Status: 00000010 00000000
14:34:14.568294  B40000200  Read-Ack    Status: 00000010 00000000
14:34:15.403151  T00390000  Read-Data   Max CH water setpoint: 0.00
14:34:15.649637  B4039004C  Read-Ack    Max CH water setpoint: 0.30
14:34:16.476205  T80190000  Read-Data   Boiler water temperature: 0.00
14:34:16.711927  BC0192A00  Read-Ack    Boiler water temperature: 42.00
14:34:17.570404  T10010A00  Write-Data  Control setpoint: 10.00
14:34:17.794898  BD0010A00  Write-Ack   Control setpoint: 10.00
14:34:18.635247  T80000200  Read-Data   Status: 00000010 00000000
14:34:18.847759  B40000200  Read-Ack    Status: 00000010 00000000
14:34:19.691335  T00090000  Read-Data   Remote override room setpoint: 0.00
14:34:19.703967  R00030000  Read-Data   Slave configuration: 00000000 0
14:34:19.938454  BC0030101  Read-Ack    Slave configuration: 00000001 1
14:34:19.939485  AC0091260  Read-Ack    Remote override room setpoint: 18.38
14:34:20.760807  T80190000  Read-Data   Boiler water temperature: 0.00
14:34:21.004638  BC0192A00  Read-Ack    Boiler water temperature: 42.00
14:34:21.836453  T10010A00  Write-Data  Control setpoint: 10.00
14:34:22.066605  BD0010A00  Write-Ack   Control setpoint: 10.00
14:34:22.898589  T80000200  Read-Data   Status: 00000010 00000000
14:34:23.159522  B40000200  Read-Ack    Status: 00000010 00000000
14:34:23.974688  T9010125E  Write-Data  Room setpoint: 18.37
14:34:23.981895  R801A0000  Read-Data   DHW temperature: 0.00
14:34:24.239751  B401A2100  Read-Ack    DHW temperature: 33.00
14:34:24.240645  A5010125E  Write-Ack   Room setpoint: 18.37
14:34:25.056737  T80190000  Read-Data   Boiler water temperature: 0.00
14:34:25.284028  BC0192900  Read-Ack    Boiler water temperature: 41.00
14:34:26.152696  T10010A00  Write-Data  Control setpoint: 10.00
14:34:26.370228  BD0010A00  Write-Ack   Control setpoint: 10.00
14:34:27.189128  T80000200  Read-Data   Status: 00000010 00000000
14:34:27.436005  B40000200  Read-Ack    Status: 00000010 00000000
14:34:28.333831  T90181717  Write-Data  Room temperature: 23.09
14:34:28.334821  R80380000  Read-Data   DHW setpoint: 0.00
14:34:28.505773  BC0383700  Read-Ack    DHW setpoint: 55.00
14:34:28.626465  AF0181717  Unk-DataId  Room temperature: 23.09
14:34:29.353313  T80190000  Read-Data   Boiler water temperature: 0.00
14:34:29.583232  BC0192900  Read-Ack    Boiler water temperature: 41.00
14:34:30.398246  T10010A00  Write-Data  Control setpoint: 10.00
14:34:30.674865  BD0010A00  Write-Ack   Control setpoint: 10.00
14:34:31.476709  T80000200  Read-Data   Status: 00000010 00000000
14:34:31.712801  B40000200  Read-Ack    Status: 00000010 00000000
14:34:32.552355  T00110000  Read-Data   Relative modulation level: 0.00
14:34:32.785701  BC0110000  Read-Ack    Relative modulation level: 0.00
14:34:33.613489  T80190000  Read-Data   Boiler water temperature: 0.00
14:34:33.851117  BC0192900  Read-Ack    Boiler water temperature: 41.00
14:34:34.696145  T10010A00  Write-Data  Control setpoint: 10.00
14:34:34.934854  BD0010A00  Write-Ack   Control setpoint: 10.00
14:34:35.768406  T80000200  Read-Data   Status: 00000010 00000000
14:34:35.983969  B40000200  Read-Ack    Status: 00000010 00000000
14:34:36.861478  T00390000  Read-Data   Max CH water setpoint: 0.00
14:34:37.067185  B4039004C  Read-Ack    Max CH water setpoint: 0.30
14:34:37.905170  T80190000  Read-Data   Boiler water temperature: 0.00
14:34:38.208491  BC0192900  Read-Ack    Boiler water temperature: 41.00
14:34:38.985882  T10010A00  Write-Data  Control setpoint: 10.00
14:34:39.284385  BD0010A00  Write-Ack   Control setpoint: 10.00
14:34:40.053161  T80000200  Read-Data   Status: 00000010 00000000
14:34:40.331764  B40000200  Read-Ack    Status: 00000010 00000000
14:34:41.121600  T00090000  Read-Data   Remote override room setpoint: 0.00
14:34:41.128694  R00030000  Read-Data   Slave configuration: 00000000 0
14:34:41.360230  BC0030101  Read-Ack    Slave configuration: 00000001 1
14:34:41.361489  AC0091260  Read-Ack    Remote override room setpoint: 18.38
14:34:42.263830  T80190000  Read-Data   Boiler water temperature: 0.00
14:34:42.630487  B40192800  Read-Ack    Boiler water temperature: 40.00
14:34:43.275083  T10010A00  Write-Data  Control setpoint: 10.00
14:34:43.507850  BD0010A00  Write-Ack   Control setpoint: 10.00
14:34:44.333418  T80000200  Read-Data   Status: 00000010 00000000
14:34:44.569096  B40000200  Read-Ack    Status: 00000010 00000000
14:34:45.404914  T9010125E  Write-Data  Room setpoint: 18.37
14:34:45.412122  R801A0000  Read-Data   DHW temperature: 0.00
14:34:45.650613  B401A2100  Read-Ack    DHW temperature: 33.00
14:34:45.660581  A5010125E  Write-Ack   Room setpoint: 18.37
14:34:46.486224  T80190000  Read-Data   Boiler water temperature: 0.00
14:34:46.714345  B40192800  Read-Ack    Boiler water temperature: 40.00
14:34:47.575745  T10010A00  Write-Data  Control setpoint: 10.00
14:34:47.793472  BD0010A00  Write-Ack   Control setpoint: 10.00
14:34:48.626072  T80000200  Read-Data   Status: 00000010 00000000
14:34:48.849679  B40000200  Read-Ack    Status: 00000010 00000000
14:34:49.703975  T10181719  Write-Data  Room temperature: 23.10
14:34:49.705082  R80380000  Read-Data   DHW setpoint: 0.00
14:34:49.925182  BC0383700  Read-Ack    DHW setpoint: 55.00
14:34:49.939465  A70181719  Unk-DataId  Room temperature: 23.10
14:34:50.774350  T80190000  Read-Data   Boiler water temperature: 0.00
14:34:51.010138  B40192800  Read-Ack    Boiler water temperature: 40.00
14:34:51.835329  T10010A00  Write-Data  Control setpoint: 10.00
14:34:52.070401  BD0010A00  Write-Ack   Control setpoint: 10.00
14:34:52.938508  T80000200  Read-Data   Status: 00000010 00000000
14:34:53.151775  B40000200  Read-Ack    Status: 00000010 00000000
14:34:54.054964  T00110000  Read-Data   Relative modulation level: 0.00
14:34:54.318403  BC0110000  Read-Ack    Relative modulation level: 0.00
14:34:55.140669  T80190000  Read-Data   Boiler water temperature: 0.00
14:34:55.354170  B40192700  Read-Ack    Boiler water temperature: 39.00
14:34:56.206201  T10010A00  Write-Data  Control setpoint: 10.00
14:34:56.448475  BD0010A00  Write-Ack   Control setpoint: 10.00
14:34:57.255168  T80000200  Read-Data   Status: 00000010 00000000
14:34:57.498322  B40000200  Read-Ack    Status: 00000010 00000000
14:34:58.324141  T00390000  Read-Data   Max CH water setpoint: 0.00
14:34:58.582507  B4039004C  Read-Ack    Max CH water setpoint: 0.30
14:34:59.410499  T80190000  Read-Data   Boiler water temperature: 0.00
14:34:59.632216  B40192700  Read-Ack    Boiler water temperature: 39.00
14:35:00.476405  T10010A00  Write-Data  Control setpoint: 10.00
14:35:00.714689  BD0010A00  Write-Ack   Control setpoint: 10.00
14:35:01.707601  T80000200  Read-Data   Status: 00000010 00000000
14:35:01.825013  B40000200  Read-Ack    Status: 00000010 00000000
14:35:01.826683  Command (via relay server, from 10.10.100.3:42322): PS=1
14:35:01.872404  PS: 1
14:35:01.999597  00000010/00000000,10.00,00000000/00000000,0.00,0/0,18.37,0.00,0.00,23.10,39.00,33.00,19.38,0.00,0/0,0/0,55.00,0.30,0,0,0,0,0,0,0,0
14:35:02.896938  Command (via relay server, from 10.10.100.3:42323): PS=0
14:35:02.996623  PS: 0
14:35:03.697008  T80190000  Read-Data   Boiler water temperature: 0.00
14:35:03.926248  B40192700  Read-Ack    Boiler water temperature: 39.00
14:35:04.756256  T10010A00  Write-Data  Control setpoint: 10.00
14:35:04.984357  BD0010A00  Write-Ack   Control setpoint: 10.00
14:35:05.834197  T80000200  Read-Data   Status: 00000010 00000000
14:35:06.076331  B40000200  Read-Ack    Status: 00000010 00000000
14:35:06.940534  T9010125E  Write-Data  Room setpoint: 18.37
14:35:06.941540  R801A0000  Read-Data   DHW temperature: 0.00
14:35:07.185683  BC01A2000  Read-Ack    DHW temperature: 32.00
14:35:07.186571  A5010125E  Write-Ack   Room setpoint: 18.37
14:35:07.985776  T80190000  Read-Data   Boiler water temperature: 0.00
14:35:08.310022  BC0192600  Read-Ack    Boiler water temperature: 38.00
14:35:09.038523  T10010A00  Write-Data  Control setpoint: 10.00
14:35:09.286064  BD0010A00  Write-Ack   Control setpoint: 10.00
14:35:10.121783  T80000200  Read-Data   Status: 00000010 00000000
14:35:10.345299  B40000200  Read-Ack    Status: 00000010 00000000
14:35:11.185712  T10181719  Write-Data  Room temperature: 23.10
14:35:11.195729  R80380000  Read-Data   DHW setpoint: 0.00
14:35:11.427743  BC0383700  Read-Ack    DHW setpoint: 55.00
14:35:11.448529  A70181719  Unk-DataId  Room temperature: 23.10
14:35:12.284363  T80190000  Read-Data   Boiler water temperature: 0.00
14:35:12.488415  BC0192600  Read-Ack    Boiler water temperature: 38.00
14:35:13.338507  T10010A00  Write-Data  Control setpoint: 10.00
14:35:13.599333  BD0010A00  Write-Ack   Control setpoint: 10.00
14:35:14.428282  T80000200  Read-Data   Status: 00000010 00000000
14:35:14.656644  B40000200  Read-Ack    Status: 00000010 00000000
14:35:15.470942  T00110000  Read-Data   Relative modulation level: 0.00
14:35:15.708507  BC0110000  Read-Ack    Relative modulation level: 0.00
14:35:16.543880  T80190000  Read-Data   Boiler water temperature: 0.00
14:35:16.781736  BC0192600  Read-Ack    Boiler water temperature: 38.00
14:35:17.615597  T10010A00  Write-Data  Control setpoint: 10.00
14:35:17.843385  BD0010A00  Write-Ack   Control setpoint: 10.00
14:35:18.686695  T80000200  Read-Data   Status: 00000010 00000000
14:35:18.918938  B40000200  Read-Ack    Status: 00000010 00000000
14:35:19.749776  T00390000  Read-Data   Max CH water setpoint: 0.00
14:35:19.984658  B4039004C  Read-Ack    Max CH water setpoint: 0.30
14:35:20.828011  T80190000  Read-Data   Boiler water temperature: 0.00
14:35:21.061705  BC0192600  Read-Ack    Boiler water temperature: 38.00
14:35:21.907381  T10010A00  Write-Data  Control setpoint: 10.00
14:35:22.161795  BD0010A00  Write-Ack   Control setpoint: 10.00
14:35:22.965907  T80000200  Read-Data   Status: 00000010 00000000
14:35:23.242601  B40000200  Read-Ack    Status: 00000010 00000000
14:35:24.054975  T00090000  Read-Data   Remote override room setpoint: 0.00
14:35:24.055869  R00030000  Read-Data   Slave configuration: 00000000 0
14:35:24.280606  BC0030101  Read-Ack    Slave configuration: 00000001 1
14:35:24.290815  AC0091260  Read-Ack    Remote override room setpoint: 18.38
14:35:25.120978  T80190000  Read-Data   Boiler water temperature: 0.00
14:35:25.340777  BC0192600  Read-Ack    Boiler water temperature: 38.00
14:35:26.219673  T10010A00  Write-Data  Control setpoint: 10.00
14:35:26.425151  BD0010A00  Write-Ack   Control setpoint: 10.00
14:35:27.256919  T80000200  Read-Data   Status: 00000010 00000000
14:35:27.503271  B40000200  Read-Ack    Status: 00000010 00000000
14:35:28.352099  T9010125E  Write-Data  Room setpoint: 18.37
14:35:28.353117  R801A0000  Read-Data   DHW temperature: 0.00
14:35:28.578224  BC01A1F00  Read-Ack    DHW temperature: 31.00
14:35:28.581290  A5010125E  Write-Ack   Room setpoint: 18.37
14:35:29.396786  T80190000  Read-Data   Boiler water temperature: 0.00
14:35:29.642590  BC0192500  Read-Ack    Boiler water temperature: 37.00
14:35:30.471243  T10010A00  Write-Data  Control setpoint: 10.00
14:35:30.699455  BD0010A00  Write-Ack   Control setpoint: 10.00
14:35:31.535636  T80000200  Read-Data   Status: 00000010 00000000
14:35:31.799294  B40000200  Read-Ack    Status: 00000010 00000000
14:35:32.614183  T10181719  Write-Data  Room temperature: 23.10
14:35:32.621585  R80380000  Read-Data   DHW setpoint: 0.00
14:35:32.882264  BC0383700  Read-Ack    DHW setpoint: 55.00
14:35:32.883389  A70181719  Unk-DataId  Room temperature: 23.10
14:35:33.704794  T80190000  Read-Data   Boiler water temperature: 0.00
14:35:33.926912  BC0192500  Read-Ack    Boiler water temperature: 37.00
14:35:34.755586  T10010A00  Write-Data  Control setpoint: 10.00
14:35:35.006462  BD0010A00  Write-Ack   Control setpoint: 10.00
14:35:35.826816  T80000200  Read-Data   Status: 00000010 00000000
14:35:36.057730  B40000200  Read-Ack    Status: 00000010 00000000
14:35:36.897457  T00110000  Read-Data   Relative modulation level: 0.00
14:35:37.135417  BC0110000  Read-Ack    Relative modulation level: 0.00
14:35:37.988545  T80190000  Read-Data   Boiler water temperature: 0.00
14:35:38.255001  BC0192500  Read-Ack    Boiler water temperature: 37.00
14:35:39.038932  T10010A00  Write-Data  Control setpoint: 10.00
14:35:39.283954  BD0010A00  Write-Ack   Control setpoint: 10.00
14:35:40.171230  T80000200  Read-Data   Status: 00000010 00000000
14:35:40.363352  B40000200  Read-Ack    Status: 00000010 00000000
14:35:41.182048  T00390000  Read-Data   Max CH water setpoint: 0.00
14:35:41.412581  B4039004C  Read-Ack    Max CH water setpoint: 0.30
14:35:42.266054  T80190000  Read-Data   Boiler water temperature: 0.00
14:35:42.504372  BC0192500  Read-Ack    Boiler water temperature: 37.00
14:35:43.335697  T10010A00  Write-Data  Control setpoint: 10.00
14:35:43.562207  BD0010A00  Write-Ack   Control setpoint: 10.00
14:35:44.405142  T80000200  Read-Data   Status: 00000010 00000000
14:35:44.641824  B40000200  Read-Ack    Status: 00000010 00000000
14:35:45.476495  T00090000  Read-Data   Remote override room setpoint: 0.00
14:35:45.477448  R00030000  Read-Data   Slave configuration: 00000000 0
14:35:45.724389  BC0030101  Read-Ack    Slave configuration: 00000001 1
14:35:45.725464  AC0091260  Read-Ack    Remote override room setpoint: 18.38
14:35:46.541053  T80190000  Read-Data   Boiler water temperature: 0.00
14:35:46.784607  BC0192500  Read-Ack    Boiler water temperature: 37.00
14:35:47.611145  T10010A00  Write-Data  Control setpoint: 10.00
14:35:47.855883  BD0010A00  Write-Ack   Control setpoint: 10.00
14:35:48.695088  T80000200  Read-Data   Status: 00000010 00000000
14:35:48.922305  B40000200  Read-Ack    Status: 00000010 00000000
14:35:49.761174  T9010125E  Write-Data  Room setpoint: 18.37
14:35:49.762160  R801A0000  Read-Data   DHW temperature: 0.00
14:35:50.008100  BC01A1F00  Read-Ack    DHW temperature: 31.00
14:35:50.009223  A5010125E  Write-Ack   Room setpoint: 18.37
14:35:50.834156  T80190000  Read-Data   Boiler water temperature: 0.00
14:35:51.057633  B40192400  Read-Ack    Boiler water temperature: 36.00
14:35:51.898438  T10010A00  Write-Data  Control setpoint: 10.00
14:35:52.140462  BD0010A00  Write-Ack   Control setpoint: 10.00
14:35:52.975787  T80000200  Read-Data   Status: 00000010 00000000
14:35:53.226270  B40000200  Read-Ack    Status: 00000010 00000000
14:35:54.062487  T1018171C  Write-Data  Room temperature: 23.11
14:35:54.063904  R80380000  Read-Data   DHW setpoint: 0.00
14:35:54.309909  BC0383700  Read-Ack    DHW setpoint: 55.00
14:35:54.310874  A7018171C  Unk-DataId  Room temperature: 23.11
14:35:55.115451  T80190000  Read-Data   Boiler water temperature: 0.00
14:35:55.359647  B40192400  Read-Ack    Boiler water temperature: 36.00
14:35:56.208291  T10010A00  Write-Data  Control setpoint: 10.00
14:35:56.420444  BD0010A00  Write-Ack   Control setpoint: 10.00
14:35:57.262204  T80000200  Read-Data   Status: 00000010 00000000
14:35:57.501895  B40000200  Read-Ack    Status: 00000010 00000000
14:35:58.347570  T00110000  Read-Data   Relative modulation level: 0.00
14:35:58.554935  BC0110000  Read-Ack    Relative modulation level: 0.00
14:35:59.399596  T80190000  Read-Data   Boiler water temperature: 0.00
14:35:59.638974  B40192400  Read-Ack    Boiler water temperature: 36.00
14:36:00.467964  T10010A00  Write-Data  Control setpoint: 10.00
14:36:00.711794  BD0010A00  Write-Ack   Control setpoint: 10.00
14:36:01.538338  T80000200  Read-Data   Status: 00000010 00000000
14:36:01.789313  B40000200  Read-Ack    Status: 00000010 00000000
14:36:02.616165  T00390000  Read-Data   Max CH water setpoint: 0.00
14:36:02.854834  B4039004C  Read-Ack    Max CH water setpoint: 0.30
14:36:03.686279  T80190000  Read-Data   Boiler water temperature: 0.00
14:36:03.915688  B40192400  Read-Ack    Boiler water temperature: 36.00
14:36:04.766434  T10010A00  Write-Data  Control setpoint: 10.00
14:36:05.011511  BD0010A00  Write-Ack   Control setpoint: 10.00
14:36:05.834400  T80000200  Read-Data   Status: 00000010 00000000
14:36:06.133386  B40000200  Read-Ack    Status: 00000010 00000000
14:36:07.067311  T00090000  Read-Data   Remote override room setpoint: 0.00
14:36:07.068391  R00030000  Read-Data   Slave configuration: 00000000 0
14:36:07.135917  BC0030101  Read-Ack    Slave configuration: 00000001 1
14:36:07.144972  AC0091260  Read-Ack    Remote override room setpoint: 18.38
14:36:07.982762  T80190000  Read-Data   Boiler water temperature: 0.00
14:36:08.232874  B40192400  Read-Ack    Boiler water temperature: 36.00
14:36:09.056288  T10010A00  Write-Data  Control setpoint: 10.00
14:36:09.276823  BD0010A00  Write-Ack   Control setpoint: 10.00
14:36:10.148418  T80000200  Read-Data   Status: 00000010 00000000
14:36:10.355977  B40000200  Read-Ack    Status: 00000010 00000000
14:36:11.191619  T9010125E  Write-Data  Room setpoint: 18.37
14:36:11.192606  R801A0000  Read-Data   DHW temperature: 0.00
14:36:11.435674  BC01A1F00  Read-Ack    DHW temperature: 31.00
14:36:11.444616  A5010125E  Write-Ack   Room setpoint: 18.37
14:36:12.275615  T80190000  Read-Data   Boiler water temperature: 0.00
14:36:12.495156  B40192400  Read-Ack    Boiler water temperature: 36.00
14:36:13.354584  T10010A00  Write-Data  Control setpoint: 10.00
14:36:13.587461  BD0010A00  Write-Ack   Control setpoint: 10.00
14:36:14.397398  T80000200  Read-Data   Status: 00000010 00000000
14:36:14.643942  B40000200  Read-Ack    Status: 00000010 00000000
14:36:15.466592  T1018171C  Write-Data  Room temperature: 23.11
14:36:15.483896  R80380000  Read-Data   DHW setpoint: 0.00
14:36:15.726680  BC0383700  Read-Ack    DHW setpoint: 55.00
14:36:15.727802  A7018171C  Unk-DataId  Room temperature: 23.11
14:36:16.535781  T80190000  Read-Data   Boiler water temperature: 0.00
14:36:16.782167  BC0192300  Read-Ack    Boiler water temperature: 35.00
14:36:17.611808  T10010A00  Write-Data  Control setpoint: 10.00
14:36:17.857741  BD0010A00  Write-Ack   Control setpoint: 10.00
14:36:18.688669  T80000200  Read-Data   Status: 00000010 00000000
14:36:18.934452  B40000200  Read-Ack    Status: 00000010 00000000
14:36:19.752060  T00110000  Read-Data   Relative modulation level: 0.00
14:36:19.988749  BC0110000  Read-Ack    Relative modulation level: 0.00
14:36:20.829348  T80190000  Read-Data   Boiler water temperature: 0.00
14:36:21.072429  BC0192300  Read-Ack    Boiler water temperature: 35.00
14:36:21.897438  T10010A00  Write-Data  Control setpoint: 10.00
14:36:22.159578  BD0010A00  Write-Ack   Control setpoint: 10.00
14:36:22.988829  T80000200  Read-Data   Status: 00000010 00000000
14:36:23.265574  B40000200  Read-Ack    Status: 00000010 00000000
14:36:24.052000  T00390000  Read-Data   Max CH water setpoint: 0.00
14:36:24.321399  B4039004C  Read-Ack    Max CH water setpoint: 0.30
14:36:25.123651  T80190000  Read-Data   Boiler water temperature: 0.00
14:36:25.346919  BC0192300  Read-Ack    Boiler water temperature: 35.00
14:36:26.206021  T10010A00  Write-Data  Control setpoint: 10.00
14:36:26.581716  BD0010A00  Write-Ack   Control setpoint: 10.00
14:36:27.259817  T80000200  Read-Data   Status: 00000010 00000000
14:36:27.497250  B40000200  Read-Ack    Status: 00000010 00000000
14:36:28.380992  T00090000  Read-Data   Remote override room setpoint: 0.00
14:36:28.382027  R00030000  Read-Data   Slave configuration: 00000000 0
14:36:28.575188  BC0030101  Read-Ack    Slave configuration: 00000001 1
14:36:28.576214  AC0091260  Read-Ack    Remote override room setpoint: 18.38
14:36:29.406986  T80190000  Read-Data   Boiler water temperature: 0.00
14:36:29.645670  BC0192300  Read-Ack    Boiler water temperature: 35.00
14:36:30.477107  T10010A00  Write-Data  Control setpoint: 10.00
14:36:30.703578  BD0010A00  Write-Ack   Control setpoint: 10.00
14:36:31.538809  T80000200  Read-Data   Status: 00000010 00000000
14:36:31.791575  B40000200  Read-Ack    Status: 00000010 00000000
14:36:32.613025  T9010125E  Write-Data  Room setpoint: 18.37
14:36:32.622521  R801A0000  Read-Data   DHW temperature: 0.00
14:36:32.840799  BC01A1F00  Read-Ack    DHW temperature: 31.00
14:36:32.859305  A5010125E  Write-Ack   Room setpoint: 18.37
14:36:33.705215  T80190000  Read-Data   Boiler water temperature: 0.00
14:36:33.924871  BC0192300  Read-Ack    Boiler water temperature: 35.00
14:36:34.785456  T10010A00  Write-Data  Control setpoint: 10.00
14:36:35.006065  BD0010A00  Write-Ack   Control setpoint: 10.00
14:36:35.840205  T80000200  Read-Data   Status: 00000010 00000000
14:36:36.057585  B40000200  Read-Ack    Status: 00000010 00000000
14:36:36.918172  T9018171E  Write-Data  Room temperature: 23.12
14:36:36.919517  R80380000  Read-Data   DHW setpoint: 0.00
14:36:37.145006  BC0383700  Read-Ack    DHW setpoint: 55.00
14:36:37.152518  AF018171E  Unk-DataId  Room temperature: 23.12
14:36:37.986110  T80190000  Read-Data   Boiler water temperature: 0.00
14:36:38.256800  BC0192300  Read-Ack    Boiler water temperature: 35.00
14:36:39.042715  T10010A00  Write-Data  Control setpoint: 10.00
14:36:39.292504  BD0010A00  Write-Ack   Control setpoint: 10.00
14:36:40.150926  T80000200  Read-Data   Status: 00000010 00000000
14:36:40.375781  B40000200  Read-Ack    Status: 00000010 00000000
14:36:41.186967  T00110000  Read-Data   Relative modulation level: 0.00
14:36:41.436326  BC0110000  Read-Ack    Relative modulation level: 0.00
14:36:42.260994  T80190000  Read-Data   Boiler water temperature: 0.00
14:36:42.528046  BC0192300  Read-Ack    Boiler water temperature: 35.00
14:36:43.331588  T10010A00  Write-Data  Control setpoint: 10.00
14:36:43.589304  BD0010A00  Write-Ack   Control setpoint: 10.00
14:36:44.416626  T80000200  Read-Data   Status: 00000010 00000000
14:36:44.634369  B40000200  Read-Ack    Status: 00000010 00000000
14:36:45.465565  T00390000  Read-Data   Max CH water setpoint: 0.00
Please report the results of the following commands:
PR=G
PR=I
PR=S
cyril
Post by cyril »
G=27
I=11
S=16.00
I'am using outside temperature sensor.
cyril
Post by cyril »
Yesterday value changes to integer 16.00 So fractional value sets not always. Also I have observed if value changes to not integer, after this changing over iphone.html can't set integer value. Only by using command?/TT=. One time per 5 minutes I'am sending PS=1 and PS=0 commands over relay port by using bash script. May it affect to remote override room temperature value changing? Also, it seems to working good around two month after installing. From july it starts to this behave.
This shouldn't happen and I can't think of any reason why it would. If things worked fine for a while and then suddenly started behaving differently without any change on the way the device is used, I'm starting to suspect a bit in the EEPROM may have flipped. An easy thing to try is to reflash the firmware. See if that makes any difference.
cyril
Post by cyril »
I am glad to report, since I have disabled sending PS=1, PS=0 commands over relay port all working good around three weeks. Obviously, using outside temperature sensor by this way was bad idea.