Intergas Boiler and Thermostat (Error 03)
Brinkie72
Post by Brinkie72 »
I have the following configuration:
- Opentherm Gateway Nodo (firmware 5.1) / UTP
- Intergas CD Pretige CW6 Central heater and Boiler
- Intergas confort Touch thermostat
In the OT monitor i get the error message Error 03 a lot and there is no communication with the thermostat.
OT monitor gives the message Thermostat disconnected. What can it be?
If i set the gatewat to the option monitor. The thermostat works. But in gateway mode the thermostat does'nt
send a message to the heater. No error on the thermostat.
From the boiler i see the water temperature and domestic hot water mode in the OT monitor.
8:05:12.260909	Error 03
18:05:12.566933	R001B0000	Read-Data 	Outside temperature: 0.00
18:05:12.705711	B601B0000	Data-Inv  	Outside temperature: 0.00
18:05:13.045327	Error 03
18:05:13.639212	R00780000	Read-Data 	Burner operation hours: 0
18:05:14.627221	Error 03
18:05:14.741415	R00780000	Read-Data 	Burner operation hours: 0
18:05:14.908389	BC07805DD	Read-Ack  	Burner operation hours: 1501
18:05:15.415813	Error 03
18:05:15.812663	R900E6400	Write-Data	Maximum relative modulation level: 100.00
18:05:15.903928	B700E0000	Unk-DataId	Maximum relative modulation level: 0.00
18:05:16.209162	Error 03
18:05:16.885299	R007B0000	Read-Data 	DHW burner operation hours: 0
18:05:17.789547	Error 03
18:05:17.958312	R007B0000	Read-Data 	DHW burner operation hours: 0
18:05:18.111796	B407B01FA	Read-Ack  	DHW burner operation hours: 506
18:05:18.576726	Error 03
18:05:19.020044	R00000000	Read-Data 	Status: 00000000 00000000
18:05:19.113996	BC000000C	Read-Ack  	Status: 00000000 00001100
18:05:19.368161	Error 03
18:05:20.089481	R80190000	Read-Data 	Boiler water temperature: 0.00
18:05:20.156914	Error 03
18:05:20.951455	Error 03
18:05:21.160717	R80190000	Read-Data 	Boiler water temperature: 0.00
18:05:21.317528	BC01949FA	Read-Ack  	Boiler water temperature: 73.98
18:05:21.743445	Error 03
18:05:22.229471	R10010000	Write-Data	Control setpoint: 0.00
18:05:22.323735	BD0010000	Write-Ack 	Control setpoint: 0.00
18:05:22.527375	Error 03
18:05:23.319159	Error 03
18:05:23.336964	R80380000	Read-Data 	DHW setpoint: 0.00
18:05:23.432987	B40383C00	Read-Ack  	DHW setpoint: 60.00
18:05:24.110936	Error 03
18:05:24.408713	R00390000	Read-Data 	Max CH water setpoint: 0.00
18:05:24.531707	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
18:05:24.897912	Error 03
18:05:25.476821	R00740000	Read-Data 	Burner starts: 0
18:05:25.628804	B40742E08	Read-Ack  	Burner starts: 11784
18:05:25.689179	Error 03
18:05:26.481292	Error 03
18:05:26.578332	R00120000	Read-Data 	CH water pressure: 0.00
18:05:26.739753	B60120000	Data-Inv  	CH water pressure: 0.00
18:05:27.294949	Error 03
18:05:27.666298	R00000000	Read-Data 	Status: 00000000 00000000
18:05:27.739928	BC000000C	Read-Ack  	Status: 00000000 00001100
18:05:28.058267	Error 03
18:05:28.717703	R80190000	Read-Data 	Boiler water temperature: 0.00
18:05:29.644671	Error 03
18:05:29.790173	R80190000	Read-Data 	Boiler water temperature: 0.00
18:05:29.943355	BC01949F5	Read-Ack  	Boiler water temperature: 73.96
18:05:30.429386	Error 03
18:05:30.854765	R10010000	Write-Data	Control setpoint: 0.00
18:05:30.955259	BD0010000	Write-Ack 	Control setpoint: 0.00
18:05:31.222679	Error 03
18:05:31.924607	R00780000	Read-Data 	Burner operation hours: 0
18:05:32.008954	Error 03
18:05:32.805083	Error 03
18:05:32.996645	R00780000	Read-Data 	Burner operation hours: 0
18:05:33.150711	BC07805DD	Read-Ack  	Burner operation hours: 1501
18:05:33.588976	Error 03
18:05:34.064406	R00110000	Read-Data 	Relative modulation level: 0.00
18:05:34.158786	B40116400	Read-Ack  	Relative modulation level: 100.00
18:05:34.378806	Error 03
18:05:35.186250	Error 03
18:05:35.203586	R001B0000	Read-Data 	Outside temperature: 0.00
18:05:35.279993	B601B0000	Data-Inv  	Outside temperature: 0.00
18:05:35.958658	Error 03
18:05:36.243600	R007B0000	Read-Data 	DHW burner operation hours: 0
18:05:36.360358	B407B01FA	Read-Ack  	DHW burner operation hours: 506
18:05:36.749356	Error 03
18:05:37.307495	R900E6400	Write-Data	Maximum relative modulation level: 100.00
18:05:37.460789	B700E0000	Unk-DataId	Maximum relative modulation level: 0.00
18:05:37.538885	Error 03
18:05:38.328919	Error 03
18:05:38.413368	R00740000	Read-Data 	Burner starts: 0
18:05:38.566167	B40742E08	Read-Ack  	Burner starts: 11784
18:05:39.124628	Error 03
18:05:39.482208	R00000000	Read-Data 	Status: 00000000 00000000
18:05:39.573787	BC000000C	Read-Ack  	Status: 00000000 00001100
18:05:39.913659	Error 03
18:05:40.558311	R80190000	Read-Data 	Boiler water temperature: 0.00
18:05:41.488874	Error 03
18:05:41.640322	R80190000	Read-Data 	Boiler water temperature: 0.00
18:05:41.783014	BC01949D4	Read-Ack  	Boiler water temperature: 73.83
18:05:42.278394	Error 03
18:05:42.721592	R10010000	Write-Data	Control setpoint: 0.00
18:05:42.874865	BD0010000	Write-Ack 	Control setpoint: 0.00
18:05:43.068820	Error 03
18:05:43.793951	R80380000	Read-Data 	DHW setpoint: 0.00
18:05:43.858877	Error 03
18:05:44.648671	Error 03
18:05:44.862698	R80380000	Read-Data 	DHW setpoint: 0.00
18:05:44.980274	B40383C00	Read-Ack  	DHW setpoint: 60.00
18:05:45.445591	Error 03
18:05:45.931758	R00390000	Read-Data 	Max CH water setpoint: 0.00
18:05:46.082356	BC0395000	Read-Ack  	Max CH water setpoint: 80.00
18:05:46.268058	Error 03
18:05:47.018350	Error 03
18:05:47.078335	R00780000	Read-Data 	Burner operation hours: 0
18:05:47.188440	BC07805DD	Read-Ack  	Burner operation hours: 1501
18:05:47.813176	Error 03
18:05:48.121660	R00120000	Read-Data 	CH water pressure: 0.00
18:05:48.204146	B60120000	Data-Inv  	CH water pressure: 0.00
18:05:48.651415	Error 03
18:05:49.172974	R00000000	Read-Data 	Status: 00000000 00000000
18:05:49.297939	BC000000C	Read-Ack  	Status: 00000000 00001100
18:05:49.422443	Error 03
18:05:50.202143	Error 03
18:05:50.325883	R80190000	Read-Data 	Boiler water temperature: 0.00
18:05:50.450209	BC01949CA	Read-Ack  	Boiler water temperature: 73.79
18:05:51.013297	Error 03
18:05:51.392115	R10010000	Write-Data	Control setpoint: 0.00
18:05:51.568747	BD0010000	Write-Ack 	Control setpoint: 0.00
18:05:51.762257	Error 03
18:05:52.497609	R007B0000	Read-Data 	DHW burner operation hours: 0
18:05:53.356683	Error 03
18:05:53.531385	R007B0000	Read-Data 	DHW burner operation hours: 0
18:05:53.663601	B407B01FA	Read-Ack  	DHW burner operation hours: 506
18:05:54.127714	Error 03
18:05:54.629177	R00110000	Read-Data 	Relative modulation level: 0.00
18:05:54.752319	B40116400	Read-Ack  	Relative modulation level: 100.00
18:05:54.919157	Error 03
18:05:55.656834	R001B0000	Read-Data 	Outside temperature: 0.00
18:05:55.721226	Error 03
18:05:56.498335	Error 03
Re: Intergas Boiler and Thermostat (Error 03)
Your log doesn't contain the "Thermostat disconnected" message you report. Please show a log from when the problem starts. If the problem arises before OTmonitor has a chance to connect to the OTGW after powering up everything, try disconnecting and reconnecting just the thermostat while the log is running.
Brinkie72
Post by Brinkie72 »
That did a lot more in the logging...
Thermostat was connected, but after a while disconnected.
I see also low power in the logging.
14:41:38.120816	PR: A=OpenTherm Gateway 5.1
14:41:38.159363	PR: B=17:44 11-02-2021
14:41:38.192539	PR: C=4 MHz
14:41:38.225375	PR: W=A
14:41:38.240881	PR: G=00
14:41:38.258497	PR: I=00
14:41:38.295662	PR: L=FXOPEC
14:41:38.330047	PR: M=M
14:41:38.342483	PR: Q=L
14:41:38.380655	PR: S=17.00
14:41:38.415618	PR: O=t22.50
14:41:38.450144	PR: P=Low power
14:41:38.464200	PR: D=O
14:41:38.500928	PR: R=D
14:41:38.514702	PR: T=11
14:41:38.531924	PR: V=3
14:41:38.757481	PS: 1
14:41:38.769815	00000000/00000000,0.00,00000000/00000000,0.00,0.00,0.00,0/0,0.00,0.00,0.00,0.00,0.00,0.00,0.00,0.00,0.00,0.00,0.00,0,0/0,0/0,0.00,0.00,00000000/00000000,0,0,0,0,0,0,0,0,0,0
14:41:38.787405	PS: 0
14:41:43.303712	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
		   - Smart power: supported (1)
14:41:43.385708	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:43.454794	Medium power
14:41:43.600874	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:43.689056	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:43.738460	High power
14:41:44.549036	Low power
14:41:44.593400	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:44.694908	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:44.746565	Medium power
14:41:44.893944	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:44.988937	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:45.042868	Low power
14:41:45.191466	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:45.290678	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:45.324854	High power
14:41:46.132203	Low power
14:41:46.181491	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:46.293412	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:46.349458	Medium power
14:41:46.479691	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:46.590260	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:46.626107	Low power
14:41:46.777452	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:46.902459	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:46.939287	High power
14:41:47.743323	Low power
14:41:47.792084	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:47.897389	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:47.960158	Medium power
14:41:48.089057	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:48.200873	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:48.240502	Low power
14:41:48.392169	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:48.500144	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:48.539104	High power
14:41:49.348291	Low power
14:41:49.395520	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:49.502299	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:49.566307	Medium power
14:41:49.693521	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:49.809573	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:49.848326	Low power
14:41:49.991675	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:50.103472	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:50.141747	High power
14:41:50.964309	Low power
14:41:51.013196	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:51.102276	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:51.164010	Medium power
14:41:51.309413	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:51.406828	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:51.468573	Low power
14:41:51.607447	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:51.714257	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:51.777858	High power
14:41:52.565123	Low power
14:41:52.619089	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:52.710232	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:52.772181	Medium power
14:41:52.912391	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:53.016047	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:53.079372	Low power
14:41:53.209557	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:53.290987	High power
14:41:54.110837	Low power
14:41:54.164313	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:54.227539	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:54.267384	Medium power
14:41:54.408922	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:54.516842	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:54.555889	Low power
14:41:54.707863	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:54.823187	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:54.864697	Medium power
14:41:54.914193	High power
14:41:55.728068	Low power
14:41:55.781269	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:55.919878	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:55.982647	Medium power
14:41:56.124293	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:56.220289	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:56.284024	Low power
14:41:56.420915	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:56.497248	High power
14:41:57.323826	Low power
14:41:57.372334	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:57.448347	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:57.496225	Medium power
14:41:57.619937	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:57.722985	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:57.792370	Low power
14:41:57.918391	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:58.025368	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:58.087583	Medium power
14:41:58.104341	High power
14:41:58.915003	Low power
14:41:58.963938	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:59.029171	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:59.069233	Medium power
14:41:59.211913	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:59.334164	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:59.407683	Low power
14:41:59.558290	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:41:59.632237	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:41:59.701392	High power
14:42:00.530291	Low power
14:42:00.577089	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:00.649548	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:00.694877	Medium power
14:42:00.824815	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:00.931852	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:00.977396	Low power
14:42:01.122677	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:01.234304	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:01.298229	Medium power
14:42:01.343448	High power
14:42:02.133845	Low power
14:42:02.182345	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:02.250670	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:02.291195	Medium power
14:42:02.436702	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:02.537031	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:02.600908	Low power
14:42:02.727480	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:02.833955	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:02.900697	High power
14:42:03.706756	Low power
14:42:03.754661	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:03.840507	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:03.905541	Medium power
14:42:04.052953	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:04.143803	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:04.207299	Low power
14:42:04.350098	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:04.448864	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:04.511826	High power
14:42:04.528999	Error 03
14:42:05.340628	Low power
14:42:05.389676	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:05.454080	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:05.495255	Medium power
14:42:05.637878	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:05.745309	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:05.785126	Low power
14:42:05.934995	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:06.047070	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:06.087054	Medium power
14:42:06.151110	High power
14:42:06.973503	Low power
14:42:07.021033	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:07.149819	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:07.225458	Medium power
14:42:07.367858	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:07.446211	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:07.515009	Low power
14:42:07.661456	Error 03
14:42:08.535469	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:08.657788	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:08.735921	Medium power
14:42:08.883811	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:08.953654	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:09.031687	Low power
14:42:09.179967	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:09.255894	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:09.296307	High power
14:42:10.120943	Low power
14:42:10.163188	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:10.258022	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:10.318826	Medium power
14:42:10.460121	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:10.558831	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:10.619788	Low power
14:42:10.756677	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:10.824146	High power
14:42:11.638349	Low power
14:42:11.684369	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:11.766843	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:11.835236	Medium power
14:42:11.981564	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:12.063674	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:12.129136	Low power
14:42:12.278651	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:12.363812	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:12.404789	High power
14:42:13.215313	Low power
14:42:13.264381	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:13.367019	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:13.434249	Medium power
14:42:13.561225	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:13.666387	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:13.716537	Low power
14:42:13.857478	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:13.969534	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:14.011482	High power
14:42:14.812359	Low power
14:42:14.867691	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:14.975352	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:15.015824	Medium power
14:42:15.158430	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:15.271567	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:15.312984	Low power
14:42:15.457929	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:15.576905	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:15.615790	High power
14:42:16.425280	Low power
14:42:16.474900	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:16.572236	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:16.635353	Medium power
14:42:16.771295	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:16.877563	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:16.941228	Low power
14:42:17.075025	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:17.182178	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:17.221238	High power
14:42:18.046178	Low power
14:42:18.095116	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:18.178455	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:18.249034	Medium power
14:42:18.392386	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:18.484711	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:18.551866	Low power
14:42:18.688778	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:18.777692	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:18.845096	High power
14:42:19.657333	Low power
14:42:19.700765	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:19.787932	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:19.852897	Medium power
14:42:20.000921	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:20.085610	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:20.161210	Low power
14:42:20.294985	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:20.390314	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:20.466295	High power
14:42:21.265930	Low power
14:42:21.313902	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:21.388925	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:21.464181	Medium power
14:42:21.611295	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:21.694237	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:21.760613	Low power
14:42:21.908404	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:21.989208	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:22.056114	High power
14:42:22.866376	Low power
14:42:22.915484	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:22.997238	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:23.066078	Medium power
14:42:23.212998	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:23.294954	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:23.360748	Low power
14:42:23.510375	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:23.592830	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:23.633535	High power
14:42:24.442963	Low power
14:42:24.491223	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:24.597428	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:24.662273	Medium power
14:42:24.789110	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:24.898226	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:24.939308	Low power
14:42:25.085951	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:25.198091	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:25.239371	High power
14:42:26.040967	Low power
14:42:26.094342	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:26.200771	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:26.244092	Medium power
14:42:26.393163	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:26.507079	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:26.546398	Low power
14:42:26.689293	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:26.750585	High power
14:42:27.548781	Low power
14:42:27.609393	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:27.753121	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:27.821586	Medium power
14:42:27.954724	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:28.040720	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:28.139033	Low power
14:42:28.194798	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:28.335834	High power
14:42:29.097980	Low power
14:42:29.174746	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:29.238853	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:29.314626	Medium power
14:42:29.407798	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:29.519218	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:29.641297	Low power
14:42:29.739919	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:29.845269	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:29.907555	High power
14:42:30.711427	Low power
14:42:30.793859	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:30.910322	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:30.970229	Medium power
14:42:31.096822	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:31.248921	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:31.336387	Low power
14:42:31.459185	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:31.525138	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:31.661337	Medium power
14:42:31.737742	High power
14:42:32.333483	Low power
14:42:32.419839	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:32.537128	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:32.614238	Medium power
14:42:32.729464	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:32.819845	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:32.884441	Low power
14:42:33.027004	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:33.103833	High power
14:42:33.939064	Low power
14:42:33.988325	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:34.056885	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:34.098361	Medium power
14:42:34.229327	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:34.327107	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:34.396142	Low power
14:42:34.532704	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:34.624304	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:34.687681	Medium power
14:42:34.733251	High power
14:42:35.559071	Low power
14:42:35.605480	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:35.727760	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:35.805613	Medium power
14:42:35.952739	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:36.027138	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:36.099666	Low power
14:42:36.253969	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:36.327910	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:36.367619	High power
14:42:37.183264	Low power
14:42:37.234945	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:37.328286	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:37.392193	Medium power
14:42:37.529582	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:37.631723	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:37.693763	Low power
14:42:37.826861	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:37.937357	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:37.999698	Medium power
14:42:38.017338	High power
14:42:38.820377	Low power
14:42:38.869386	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:38.941862	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:39.033808	Medium power
14:42:39.170736	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:39.237804	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:39.325859	Low power
14:42:39.468506	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:39.533447	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:39.614010	High power
14:42:39.947588	Command: GW=1
14:42:39.988888	GW: 1
14:42:40.032145	High power
14:42:40.050892	R00000000	Read-Data 	Status (MsgID=0): 00000000 00000000
		   - CH enable: disabled (0)
		   - DHW enable: disabled (0)
		   - Cooling enable: disabled (0)
		   - OTC active: not active (0)
		   - CH2 enable: disabled (0)
		   - Summer/winter mode: winter (0)
		   - DHW blocking: unblocked (0)
14:42:40.239108	Low power
14:42:40.261648	BC0000000	Read-Ack  	Status (MsgID=0): 00000000 00000000
		   - Fault indication: no fault (0)
		   - CH mode: not active (0)
		   - DHW mode: not active (0)
		   - Flame status: flame off (0)
		   - Cooling status: not active (0)
		   - CH2 mode: not active (0)
		   - Diagnostic indication: no diagnostics (0)
		   - Electricity production: not active (0)
14:42:40.460985	Low power
14:42:40.512593	Error 03
14:42:40.863587	R80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
14:42:40.934756	Thermostat connected
14:42:40.949403	Low power
14:42:40.971861	B401915A8	Read-Ack  	Boiler water temperature (MsgID=25): 21.66
14:42:41.293613	Error 03
14:42:42.085638	Error 03
14:42:42.216362	Low power
14:42:43.052503	Low power
14:42:43.104268	Error 03
14:42:43.157050	Thermostat disconnected
14:42:43.177387	Thermostat connected
14:42:43.745374	Thermostat disconnected
14:42:44.020200	R80190000	Read-Data 	Boiler water temperature (MsgID=25): 0.00
14:42:44.149331	B401915A8	Read-Ack  	Boiler water temperature (MsgID=25): 21.66
14:42:44.617996	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:44.654575	R100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:44.703089	Thermostat connected
14:42:45.238141	High power
14:42:46.050035	Low power
14:42:46.098935	T100201AD	Write-Data	Master configuration (MsgID=2): 00000001 173
14:42:46.255520	BD00201AD	Write-Ack 	Master configuration (MsgID=2): 00000001 173
14:42:46.353979	High power
14:42:47.024631	T00030000	Read-Data 	Slave configuration (MsgID=3): 00000000 0
14:42:47.162802	B400341AD	Read-Ack  	Slave configuration (MsgID=3): 01000001 173
		   - DHW: present (1)
		   - Control type: modulating (0)
		   - Cooling: not supported (0)
		   - DHW: instantaneous (0)
		   - Master pump control: allowed (0)
		   - CH2: not present (0)
		   - Remote water filling: not available (1)
		   - Heat/cool mode control: heat (0)
14:42:47.391588	T807F0000	Read-Data 	Slave product version (MsgID=127): 0 0
14:42:47.560802	B707F0000	Unk-DataId	Slave product version (MsgID=127): 0 0
14:42:47.784630	T107E010F	Write-Data	Master product version (MsgID=126): 1 15
14:42:47.878733	B507E0000	Write-Ack 	Master product version (MsgID=126): 0 0
14:42:48.129913	T00000000	Read-Data 	Status (MsgID=0): 00000000 00000000
Your thermostat is really going nuts with the Smart power feature, changing levels multiple times per second.
You started your log in monitor mode (why?) and there is some churn when you switch to gateway mode while in High power mode. But toward the end of the log things seem to be fine. Starting at 14:42:46.098935, the thermostat requests MsgID 2 and gets a response that the slave supports Smart power. It then switches to High power and from there communication is normal all the way to the end of the log. That sequence is exactly what I would expect for Smart power. So I don't see any evidence of a problem in your log.
Brinkie72
Post by Brinkie72 »
Because of the problems met the thermostat i switched over to monitor.
The thermostat was then functioning normaly.
This morning a switch back to gateway. First a got a lot of error 03's again and the thermostaat was displaying an Ot error.
When a touch (magic fingers i suppose) the thermostaat, i resets and functions normaly.
In the OT monitor no more errors 03 and thermostat set to high power. All functions well.
i don't understand it, bu i'm happy :D