Incident Report — OTGW WiFi and ATAG A244EC non responsive
Aboreon
Post by Aboreon »
Hardware and Firmware Details
  • OTGW Model: WiFi version purchased from Nodo-shop
  • OTGW Developer: Robert van den Breemen
  • OTGW Firmware Version: 0.10.2+50c3ed2
  • Firmware Compilation Date: Mar 14, 2023 23:02:12
  • PIC Firmware: Available, Version 2.1 (Device: pic16f1847, Type: diagnose)
  • Arduino Core: 2_7_4 (Espressif SDK: 2.2.2-dev)
  • CPU Speed: 160 MHz
  • Flash Chip: 4 MB (LittleFS: 1 MB)
  • MAC Address: F4:CF:A2:FA:1A:5A
  • IP Address: 192.168.50.22
  • Heap Mem (Free/Max): 14584 / 13232 bytes
  • Sketch Size (Used/Free): 597664 / 1499136 bytes
  • WiFi Network: TSEO (Signal: -65 dBm, Quality: 80% - Amazing)
  • MQTT Connected: Yes
  • HA Integration: True
  • Thermostat Connected: False (this goes to true when the gateway firmware is active
  • Boiler Connected: False
  • Uptime: 00:22 (h:m)
  • Reboots: 26
  • Last Reset Reason: External System
Setup Goals
  • Final Goal: Inventum EVA thermostat → OTGW → Inventum Spaarpomp → ATAG A244EC
  • Current Test Setup: Tado thermostat → OTGW → ATAG A244EC
Just Tado smart thermostat + ATAG A244EC
This works well, I can start and stop the heating by increasing and lowering the temp on the thermostat
Problem Description with opentherm gateway
When using the normal gateway firmware it seems to register the thermostat and gives responses like which to my understanding are correct. Thermostat put messages in the log and on MQTT
20:23:59.497289	T00390000	Read-Data 	Max CH water setpoint: 0.00
20:24:00.001877	T00390000	Read-Data 	Max CH water setpoint: 0.00
20:43:40.497470	T00240000	Read-Data 	Electrical current through burner flame: 0.00
20:43:40.998797	T00240000	Read-Data 	Electrical current through burner flame: 0.00
20:43:36.999114	T007B0000	Read-Data 	DHW burner operation hours: 0
20:44:43.976385	T80394600	Read-Data 	Max CH water setpoint: 70.00
20:44:44.458994	T80394600	Read-Data 	Max CH water setpoint: 70.00
No boiler messages, if I just swap out the OTGW and connect the thermostat directly this works fine but when adding the OTGW it goes to error C61
From the manual ATAG manual: "C 61 geen communicatie via Z-bus (reset alleen mogelijk door spanningsonderbreking)"
Which means no communication via Z-Bus reset only possible via power interrupt
When I try to do this it go to "normal" operating status but still no response or data from the boiler in the OTtools
OTGW Diagnostics (via https://otgw.tclcode.com/diagnose.html)
Test 1 (LED test):
looks good
Test 2 (Pulse timing):
90181700  Write-Data  Room temperature: 23.00
505,512,496,1004,495,504,996,1003,496,496,503,504,496,503,496,504,495,504,496,503,996,502,497,1003,496,504,495,504,495,504,496,504,495,504,995,1004,995,503,496,503,496,1004,495,504,495,504,496,504,495,504,495,504,496,504,495,504,995.
Test 3: Bit timing boiler
No output
Test #4: Delay symmetry
Error: Interfaces don't appear to be looped
Test #5: Voltage levels
Power supply: 3.339 V
Reference: 1.222 V
Thermostat: 0.896 / 1.998 V
Boiler: 0.000 V
Reference voltage setting (0..9): [default]
Test #6: Idle times
T: 467.114
T: 466.945
T: 466.925
Now what I do not understand or know how to troubleshoot further is why the boiler does not seem to be able to do anything.
Hopefully anyone here has any ideas or tips for me. thanks!
Re: Incident Report — OTGW WiFi and ATAG A244EC non responsive
Aboreon wrote: Wed Jul 16, 2025 9:20 pm Test #4: Delay symmetry
This indicates a hardware fault of the OTGW or a bad connection, assuming you followed the test instructions and looped the OTGW thermostat terminals to the boiler terminals as shown in the picture below.
Make sure you properly soldered the connector onto the PCB.
Aboreon
Post by Aboreon »
Hallo Schelte,
Thanks for the response I did not do the looping. However now I did and it still gives the same problem.
I let Nodo solder and flash the otgw.
WhatsApp Image 2025-07-17 at 18.50.30.jpeg (100.3 KiB) Viewed 496 times
result still
Enter test number: 4
### Error: Interfaces don't appear to be looped
which I gues means I need to contact nodo or any other tips i can try?
That is strange. The Nodo shop fully tests a board before shipping when you buy the solder service. Have you connected something other than an Opentherm connection to the board at some point that may have damaged some components?
Do you have a multimeter? If so, please measure the voltage on the boiler pins of the connector on the bottom of the board with the OTGW powered and the loops in place. There should be some noticeable voltage there. Somewhere in the range of 5V to 20V. If not, there is a bad connection between the wires and the connector. If you do see the voltage, you can try to swap the wires on one side to reverse the polarity. That will direct the current through two different diodes. I'm not sure if the Nodo shop tests both polarities.
If the problem persists and you are up for it, we can investigate further step by step to determine what is broken. But given that you bought the solder service, I guess you would probably prefer to send the board back for investigation.
Aboreon
Post by Aboreon »
Hello Schelte,
Managed to borrow a multimeter. Hope im doing this right, see screen
otgw multimeter
otgw multimeter
it seems like it registers 1.5 volts which is far from the 5v to 20v you mentioned.
To your question:
Have you connected something other than an Opentherm connection to the board at some point that may have damaged some components? maybe
- I have had on-off from my atag boiler connected before the opentherm. (was at that moment not aware that I needed to switch the connector in the CV)
- I have a hybrid system with an inventum heatpump this has a poweradaptor in between the heatpump and the thermostat which has an external powersource When I measure this output it gives 22.7v towards the thermostat and about 6.6 towards the heatpump. (I have had it connected on both sides I think when trying. Aftwards I switched to my tado thermostat to get it working first with just a thermostat and CV and leave the heatpump out of it.
let me know what you think, thanks for the support!
You measure correctly, as far as I can tell. But the result is not correct. I checked with one of my own OTGW's and I get 16.9V.
I do not expect connecting the on/off input of a boiler to the OTGW to cause any damage. Such an input doesn't normally provide a lot of current as it is designed to be short-circuited. However, a power injector intended to supply power to a thermostat is likely to be able to supply a fair bit of current. At 22.7V that may very well have blown out a zener diode. Most likely D10.
A blown zener will usually present itself as a short-circuit. This results in the boiler interface being reduced to 2 diodes and an EB junction of a PNP transistor, essentially another diode. Each diode causes a voltage drop of around 0.6V. So three of them would result in about 1.8V. That's not too far off the 1.55V you measured, supporting the hypothesis that the zener is blown.
Considering that you had to borrow a multimeter, I think it's safe to assume you don't have the tools nor the desire to replace an SMD component yourself. I suggest you send the device back to the nodo-shop for investigation and repair.